    • CommentAuthorShepherd
    • CommentTimeFeb 6th 2009
     
    Just wondering how possible it is to retro-fit this to

    a) Existing house
    b) Under existing slab of concrete (on which we are going to build the conservatory)

    House is a bungalow on a concrete slab - I was just looking at it and wondering - would it be possible to drill holes diagonally in under the house slab (large lumps of granite permitting), do the pipe bit, then put the concrete skirt I've seen in the diagrams around the house?

    Conservatory - basically the same question, but here I'd be happier drilling holes in through the concrete and sealing them up afterwards.

    At this stage just curious really - though nice to know as I'd want to do the drilling through the conservatory-foundations-to-be before building the conservatory on it with all the damp proofing entailed.
    • CommentAuthortony
    • CommentTimeFeb 6th 2009
     
    yes possible but not easy -- a vertical bore hole will often stand up whereas a diagonal are not so stable-- boreholes can be drilled diagonally.

    I would forget it under the glass room.
    • CommentAuthorpmcc
    • CommentTimeFeb 6th 2009
     
    Shepherd, I'm also looking at retrofitting some kind of ground heat store to my house. I have a similar situation: house has concrete foundation with large ventilated underfloor cavity, plus very large adjoining garage/workshop with concrete floor.

    So far I've looked at various models of how heat would be held underground and how to transport it in & out. My preference at the moment is to use air, similar to the original AGS description.

    Pros: simple, few parts to go wrong, easy to collect heat through home-made solar panels, easy to transport heat in & out of store, low energy footprint to operate

    Cons: Large length of underground pipe needed, because air does not conduct very well through the walls of plastic tubes, drain needed to handle condensation in underground pipe

    Initially I thought of drilling holes under the house & garage. Various stuff needs to be done for a ground heat store to work in this situation which I won't describe now.

    Even with water as the medium pipes placed in these holes will only insert heat slowly during the summer and retrieve slowly in winter, due to limited surface area of pipe for conduction. Also, a fairly powerful pump will be needed to squeeze the water up and down the holes. I've not yet done precise modelling on the ratio of energy in (to operate the pump) to energy out (change in water temperature), but suspect it won't look too good unless there is quite a long carry of underground pipe to provide effective heat transfer.

    To me, the point of an inter-seasonal store is to move away from dependency on electric power to operate complicate mechanical heating systems. An air-based design with mostly horizontal orientation appeals because it only needs a single 5w fan to operate. Perhaps with good design it may run only through natural thermosyphoning, at least for part of the year.

    So, I suspect your question should be "what are the costs involved with retrofitting and operating AGS". No doubt it can be done given sufficient money and effort, but can it be done effectively for the average semi-rural house for under £5k? By effective I mean a suitable ratio of energy invested for energy returned, say 50x over 10 years.
    • CommentAuthorralphd
    • CommentTimeFeb 6th 2009
     
    ppmc: If you have a dirt floor in your basement (it's not clear to me from your description) then dig a trench down the middle of your basement, about 3-4' wide, lay 3 or 4 runds of PE pipe (3/4" or 1"; the stuff sells for ~20c/ft here in Canada), cover it with concrete grout, and then lay 1" of polystyrene foam over it.
    • CommentAuthorpmcc
    • CommentTimeFeb 6th 2009
     
    ralph, that's sort of what I'm thinking of doing.

    Unfortunately the house is 1974 timber-frame construction with concrete foundation and no basement. The under-floor space is on average 3 feet high but is purely for ventilation of floor joists. It looks quite challenging to dig a reasonable series of trenches in that, made worse by structural walls every couple of metres. AGS in its pure form as described by Don Stephens is pretty hard to retrofit on my type of house.

    However, no reason why I couldn't dig up the garage floor to a reasonable depth, say 2 metres, lay the pipe, backfill, cover with thick insulation and overlay with hard surface. Garage is roughly 6m x 6m, surrounded on all sides by hard standing, making the rain apron easy. Practical challenges are getting suitable size digger into the garage without wrecking it and possible awkward stuff like rocks under the surface.

    Of course, it's only worth doing all this if sufficient heat can be stored, retained and then extracted to make a significant difference during winter. I'm playing with some numbers and will post them once I'm a bit more confident that the model is reasonable.
    • CommentAuthorralphd
    • CommentTimeFeb 8th 2009
     
    Posted By: pmccralph, that's sort of what I'm thinking of doing.

    Unfortunately the house is 1974 timber-frame construction with concrete foundation and no basement. The under-floor space is on average 3 feet high but is purely for ventilation of floor joists. It looks quite challenging to dig a reasonable series of trenches in that, made worse by structural walls every couple of metres. AGS in its pure form as described by Don Stephens is pretty hard to retrofit on my type of house.


    I had to dig a hole under my concrete footing to provide drainage during construction. If I had a source of pressurized water I think it would have been much easier. So I think it is feasible to dig holes big enough to slide a pipe through under your load-bearing walls.

    -Ralph
  1.  
    What about looking at it differently and focusing on the insulated wing/umbrella fitted externally (fitted vertically or horizontally) to create the thermal store?

    This would allow heat to be stored in the ground passively and no need to install pipes etc.. Having the internal space in contact with floor and floor in contact with ground creates the thermal pathway in both directions (as originally designed). Then control the internal space temperature with active/passive solar means (sunspaces, air solar panels etc) because the thermal store will then take up the average annual internal temperature after a few years!

    Existing heating system might be one way of maintaining target internal temperature until thermal store is fully charged?
    • CommentAuthorralphd
    • CommentTimeFeb 8th 2009
     
    Going external would require excavating around the house. I suspect it would cost about £75/hr for the machine and operator.
    • CommentAuthortony
    • CommentTimeFeb 8th 2009
     
    I paid half that for a 13 T machine.
    • CommentAuthorpmcc
    • CommentTimeFeb 9th 2009 edited
     
    Posted By: Jeff Norton (NZ)What about looking at it differently and focusing on the insulated wing/umbrella fitted externally (fitted vertically or horizontally) to create the thermal store? This would allow heat to be stored in the ground passively and no need to install pipes etc.. Having the internal space in contact with floor and floor in contact with ground creates the thermal pathway in both directions (as originally designed).

    Jeff, how many retrofits (at least in the UK) will be able to dig all around the house and have a solid floor in contact with the earth? I suspect not many.

    My house fails on both counts. As mentioned above there is a ventilation space under the ground floors. Perhaps this can be overcome simply by blocking off the ventilation points and assuming that there will not be any condensation because the air under the house is warmer than the joists.

    However, there is also a built-up patio area along the south side of the house which would be very messy and costly to rip up and replace.

    Posted By: ralphdI had to dig a hole under my concrete footing to provide drainage during construction. If I had a source of pressurized water I think it would have been much easier. So I think it is feasible to dig holes big enough to slide a pipe through under your load-bearing walls.

    How could that be done? Dig a big hole at either side, use pressurised water to bore the channel, then slide in the pipe? What happens if there are big rocks in the way? I would worry about 2 things: depth and channel length. Pipe needs to be long and deep enough to get useful heat out during winter.

    After doing some calculations, I reckon that my annual space heating load will be around 10,000kWh. A small wood burner will contribute 30% of that, leaving around 7,000kWh to come from AGS. Required ground volume to store enough heat is 8x8x6m (after looking up relevant values for type of ground, etc). That's not too far away from my 6x6m garage, so with a bit of overlap to the surrounding ground I reckon it can be done. However, there are 2 key practical issues:

    1. Heat input/output has to be deep enough to avoid excessive losses through surface insulation and allow sufficient flux of heat out of the ground during the winter. I've not finished the calculations, but at this stage guess that anything less than 3m will not work well enough.

    2. Conduction of heat through garage walls. This will be an issue for Jeff's under-house suggestion too, where external walls of the house will conduct away heat which will be lost to the environment, unless the walls are externally insulated.

    Going back to the general question posed by the thread, I can see pipe depth & length (to get necessary heat flux from the ground) and conduction through walls as potential limiting factors to successful retrofit of inter-seasonal ground heat storage. Although these are practical problems, they don't look insuperable. The prize for finding workable solutions is so high I'm surprised there is not more interest (perhaps there is and I've not found it yet!).
    • CommentAuthorralphd
    • CommentTimeFeb 9th 2009
     
    Posted By: ralphdGoing external would require excavating around the house. I suspect it would cost about £75/hr for the machine and operator.

    Wow, that's much better than here. I had a slightly bigger excavator do some work in July 2008 and the rate was CAD120/hr. In larger Canadian cities the rates were higher than that.
    •  
      CommentAuthorfostertom
    • CommentTimeFeb 9th 2009 edited
     
    Investigate directional drilling - steerable horizontal drilling http://www.chilternthrustbore.co.uk.

    See Rehau 'Awadukt Thermo' http://www.greenspec.co.uk/html/product-pages/rehau_awadukt.php which finds that the ground transfer pipes have to go in as close as 1m c/cs and be 200 diam to get the reqd transfer surface - also theirs are manufd from polypropylene not uPVC because the latter (ordinary drain pipes) actually have a foam structure within the body of the plastic, which is quite resistive, thermally. Also their pipes incorporate silver bactericidal, otherwise nasties tend to grow within, as they're frequently liable to condensation. Which explains their probable great cost compared to ordinary drain pipe! Also, consider clay drain pipes, or the duct grade thereof.
  2.  
    Posted By: ralphdWow, that's much better than here. I had a slightly bigger excavator do some work in July 2008 and the rate was CAD120/hr. In larger Canadian cities the rates were higher than that.
    Actually, it's more expensive. Using http://xe.com gives £75 as Can$136 at today's rates.
    • CommentAuthorralphd
    • CommentTimeFeb 9th 2009
     
    I messed up the quoting; half of 75 pounds would be about $70 per hour.
    Posted By: Paul in MontrealI paid half that for a 13 T machine.
  3.  
    Posted By: pmcc
    Posted By: Jeff Norton (NZ)What about looking at it differently and focusing on the insulated wing/umbrella fitted externally (fitted vertically or horizontally) to create the thermal store? This would allow heat to be stored in the ground passively and no need to install pipes etc.. Having the internal space in contact with floor and floor in contact with ground creates the thermal pathway in both directions (as originally designed).
    Jeff, how many retrofits (at least in the UK) will be able to dig all around the house and have a solid floor in contact with the earth? I suspect not many.

    My house fails on both counts. As mentioned above there is a ventilation space under the ground floors. Perhaps this can be overcome simply by blocking off the ventilation points and assuming that there will not be any condensation because the air under the house is warmer than the joists.

    However, there is also a built-up patio area along the south side of the house which would be very messy and costly to rip up and replace.


    I am not saying every project is suitable, and ground coupled buildings are a minimal requirement IMO for individual schemes.
    • CommentAuthorpmcc
    • CommentTimeFeb 9th 2009
     
    Posted By: fostertomhttp://www.greenspec.co.uk/html/product-pages/rehau_awadukt.phpwhich finds that the ground transfer pipes have to go in as close as 1m c/cs and be 200 diam to get the reqd transfer surface


    Thanks Tom, very helpful. Their bumpf reads like the design wishlist I've been putting together :).

    Closeness of the pipes looks very important, depending on the type of ground. I'm modelling 40% damp clay. Over 6 months the heat wave travels 4 metres (ie about two thirds of it still remains within 4 metres of source).

    Heat loss from the house is 3120W. Heat flux from 1 metre of 100mm pipe (assuming various things) is around 28W. So around 110m of pipe are needed. In my 8x8 area that means 2 arrays of pipe 1m apart, with around 3m of vertical separation between them.

    So... hole for the ground store needs to be 8x8 in area. Depth depends on losses through the insulation under the garage surface. In ideal AGS this is irrelevant because it just goes into the house. In the more controlled external variant where it's in an out-building, this will force the hole to be a bit deeper. Let's say the first set of pipes are at 3m and the next set at 5m (need to model this a bit better).

    That's a big hole! Might still be a fair bit cheaper than getting specialist drilling rigs out to make that amount of holes under the house though (local mini-digger + driver for a couple of weekends?).

    Quite likely that the sums behind the numbers above are wrong somewhere :). However, they 'feel' reasonable. If right then meeting most space heating needs for a detached house using an inter-seasonal ground store under an out-building will take a fair bit of pipe and surface insulation (to avoid too deep a hole), but looks quite feasible.

    Next steps are 1. check sums 2. do some preliminary costings.
    •  
      CommentAuthorfostertom
    • CommentTimeFeb 9th 2009
     
    Very good pmcc - how are you doing the modelling?
    Groundworkers I talked to wd bring in (hire the right kind of) big machine and dumper to quickly make a hole like that, rather than ages with a little one. You could backfill it at leisure with a little one.
    • CommentAuthorpmcc
    • CommentTimeFeb 10th 2009
     
    Modelling semi-manually using pencil, paper, spreadsheet and google - with distant echoes of a long-ago education :). Big digger looks like the right approach, but I need to think about how to dig the hole without destroying the garage! Probably start digging the hole outside the double doors to give the digger headroom as it moves inside.

    Just found this thread which discusses and models heat store losses http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=921&page=2. I suspect heat losses to the environment will end up not being the limiting factor, although will need to model it in more detail to be sure. Intuitively, the temperature difference between store and pipe will be much greater than the incremental difference between adjacent ground, so the heat flux should be mostly from ground to pipe during the winter.

    Repeating Mike7's heat loss calculation gives annual loss for my store of 17,000kWh, for projected return of 7000kWh into the house. That looks like fair game to me, despite obvious risk factors such as groundwater and rocks.

    Even in dreich old Scotland it should be easy enough to collect 24,000kWh from the sun during summer. I'll have another look at the collector calcs later.