    • CommentAuthorListysDad
    • CommentTimeMar 10th 2011
     
    I'm planning installing a wood burner in a barn surrounded by trees with no power available - not even solar - and would like to have hot water, so we can shower using a venturi shower, and a bit of heating.

    I'm aware that all the pipework is best run in copper (especially as our local rodents love a nice juicy plastic meal...), that we'll need non plastic header tanks, that the HW cylinder has to have a coil designed for gravity circulation and that we need a rad to dump heat when reqd. But can anyone point me to what needs to be properly considered from a design perspective so I can design the pipework and system to be both safe and effective.

    Remember, we'll have NO power!

    Thanks
  1.  
    Are you just concerned with having hot water and a heat dump rad for safety or do you want to run other rads for heating as well?
    If you are space heating with rads as well as hot water then all the rads can function as a heat dump and if you balance the pipes then everything will get hot. Without electricity the need for heat dump changes since you are not designing for safety in the occasional power cut but rather the norm!
    If you only want to heat the water and have a bit of warmth whilst taking a shower then you can control the heat output by forethought when loading the stove, the need for a heat dump in this case changes to be almost unnecessary.
    The design of the circuit will depend on the levels, stove on ground floor with tank upstairs or in loft gives one design, all on same level gives another design (and other problems)
    By balanced pipes I mean if you come out of the stove with 28mm then tee off with 15mm for a rad 1 then continue with 22mm The next tee would be 15mm for rad 2 and continue with 15mm through the last rad with 15mm out. When picking up the return from rad 2 go to 22mm then pick up the return from rad 1 and go to 28mm back to the stove. This devides the water and therefore the heat equally (assumes equal sized rads). Variations can be made according to the size of the rads but always try to balance the flow and return pipe sizes to share the water (heat) to the size of the rads.
    I don't know where you are but depending on location, depth of pocket and skill level then black iron pipe work might workout much cheaper than copper.
    A bit more info about what you are trying to fit up would be helpful.
    Peter
    • CommentAuthorListysDad
    • CommentTimeMar 11th 2011 edited
     
    Thanks Peter. I'm in Yorkshire.

    Its all to be in a barn so on one level. However, there is a 'higher place' to place the F&E & CWS tanks so we can get a bit of gravity into the equation rather than relying simply on thermodynamics! It's only planned to have one rad for heating but pipework would have to drop down below the floor and come up to it.

    Is it correct that to get best performance it's best to pipe the rad top in bottom out?

    How about control? I'm not at all familiar with manual changeover valves which would presumably be required to swap circulation from HTG to HW and back.

    As there's to be a venturi shower, the higher the stored HW temp the better the shower. I'd simply blend for other outlets.

    Hope that makes more sense!

    David:wink:
    • CommentAuthorevan
    • CommentTimeMar 11th 2011
     
    You don't need any control really. The circuits will work in parallel. Turn the radiator off if you just want hot water.
    • CommentAuthorsune
    • CommentTimeMar 11th 2011
     
    That rad won't work if you want to drop the pipe down to it - gravity doesn't work like that. You could possibly drop a flow pipe down to it and then have a return dropping below the floor......

    The situation you want is for your flow and return pipes to rise from the stove.
    That means that your rad and hot water tank needs to be above the stove.
    You can tap in to the upper tapping on the rads of course and come out of the bottom tappings, but do make sure that they are a decent height up from the flow outlet of your stove. This assumes you are going to put in a 2 pipe system of course....
    Gravity is not powerful enough to push out airlocks and you want to encourage the hot, less dense, water on the stove side to rise up and the cooler, more dense, water on the hot water tank/rads side to fall.

    As Peter says they should be in 28mm copper.
    Peter - I've not tried the trick of downsizing as you move round the circuit. They way that I do it is all large bore metal pipe, tee off to each rad and then balance the rads. I think that the downsizing would work well with the possible caveat that you are assuming that the flow round the loop is equally effective all the way round? Often in gravity systems I find that one section can be more stubborn than the rest and hence here it can help if the whole loop is in 28mm or bigger? What do you think?


    If you have a heat leak rad then it should not be able to be turned off - no valves on there and certainly not a trv.
    If you want another rad then you could simply have a trv on it and turn it right down when you want a nice hot tank of water.

    If possible find an old school plumber/heating engineer as they are likely to know all about getting gravity systems working well and should be keyed up on other aspects it is important to get right.
  2.  
    ListysDad - You can drop below the level of the stove return (i.e. below the floor) but only once. That is if you drop below the floor to get to the rad then the stove return height would have to be above the output of the rad. A gravity circuit can go up down up, but it will fail if it goes up down up down. If you imagine the circuit as a circle - even if mis-shaped - then the stove can be anywhere on the circle except the top, however the closer to the bottom the better it will work. The pipe connected to the top of the stove determines the direction of flow. As Sune said you want your flow and return pipes to rise from the stove, this is the ideal but if this is not possible the return pipe can drop below stove and then come up to it.

    In theory you get better performance from a rad if it is top in bottom out but its only marginal unless you are dropping the supply from above. It is also better to have a cross flow rather than in and out on the same side but this will also work.
    All pipes on a gravity circuit must slope but bear in mind the comment above regards direction of up and down slopes. this is to help flow but more importantly to avoid any chance of air locks as this will stop gravity circulation dead.

    The advantage of down sizing the pipe work as the circuit progresses and then up sizing to balance the return is primarily one of cost. the difference between 28mm , 22mm and 15mm copper is significant! Down sizing works well especially if the vertical rise of the circuit is as much or close to the length of the horizontal but can cause problems if the circuit is marginal.

    You can prioritise the DHW by circuit design. The ultimate prioritisation would be to put the DHW and rad in series, the first in line takes all it wants! otherwise if the DHW tank is above the rad then tee off below the tank input to the rad, the lower the more prioritisation will be given to the tank, especially if teed off in a smaller diameter pipe.

    With only one or two rads and a DHW tank I would not have any controls at all, control is by the amount of wood you put on the stove, but definitely put a pressure relief valve on the stove output. If the expansion tank is not connected to the highest point on the system (probably the DHW tank input) then a bleed valve will need to be installed at the high point.

    As it is a small system, if the stove is not too large an output to water and you have at least as much vertical as horizontal then 22m should work, much cheaper than 28mm. Swept elbows and tees will help if you can get them.
    Peter
    • CommentAuthorListysDad
    • CommentTimeMar 13th 2011
     
    Thanks chaps much food for thought.

    I'll try a better description!

    Barn raised off ground by 600mm. Stove on barn floor. HW cylinder approx 2.4m higher. F&E approx 1m higher than cylinder. Heat sink rad at same height at cylinder. Htg rad at same height as stove but 8m away.

    From what I'm gleaning here, the flow from the stove goes through cylinder and sink rad (in series?) then on to input into top of htg rad. Rtn from htg rad can go below floor back to return to boiler. Thats a big circle! 28mm all way(?) Must it all be copper or is plastic acceptable (scuse me for swearing!). Just thinking that with plastic there are virtually no joints!
  3.  
    Do you need heat in the area of the heat dump rad. If not then the heating rad can function as a heat dump. Given the ratio of vertical to horizontal it might be better to mount the heating rad verticaly (i.e. 90 deg from its design) this will raise the start of the heat loss area to above the stove and thus aid circulation. If you do this then a non finned rad would be better . Also given the ratio of V to H I would not put the heat sink rad in series (assuming you need it) but tee off before entering the tank creating a heating loop with both rads as heat sink. The DHW circuit would be stove - tank - return to stove, the heating circuit would be tee off DHW circuit - rads - return to stove. Assuming the DHW circuit is much shorter than the heating circuit this will give priority to the DHW
    Your proposal above suggests both rads in series which would give no to minimal heating until DHW is done.

    Plastic pipe can be used, the problem with plastic pipe is that it sags when hot, this means that air locks can form and with no pump they can not be got rid of. The way around this problem is to support the pipe along its whole length by say fixing a tile batten to the wall and laying the pipe on this. Don't forget all pipes must slope to aid circulation and to be self bleeding.
    Peter
    • CommentAuthorListysDad
    • CommentTimeMar 20th 2011
     
    Thanks Peter. Much appreciated.

    Daft question I know, but is there any point in trying to control the DHW temp?

    I was thinking of using a stainless cylinder (but it would only have a std dia coil) and then using a blending valve for sink and basin hot water leaving the piping hot stuff for the shower. What temp would you expect it to reach?
  4.  
    The control for the DHW temp would be the loading or / and control of the stove. If the stove is shut down a bit or has a partial load in it then it will produce less heat, this in turn will produce less flow on the gravity circuit all of which means less heat to DHW and rads. When the DHW is at the same temp as the stove then all the heat will go to the rads.

    Wood stoves should not be run completely shut down as this will cause excess pollution and the tarring up of the chimney. However you can run the stove on partial loads or partially shut down without too many problems as gravity tends to be self regulating and the circulation will shut down as the temp falls so you will not over cool the fire in the same way as with a pumped system.

    What do you mean by a std. dia. coil, dia. of the coil or dia of the pipe from which the coil is made. Most coils are made from 1" pipe but even if it was 3/4" it would still work similarly if the coil was a bit shorter it would also still work, just that in either case the DHW would just take a bit longer to get to the same temp as the stove and whilst it is taking its time more heat would go the rads.

    Use a blending valve for all the DHW. They are normally set for 60 deg. and you really don't need even this temp. for a shower, otherwise you will come out looking worse than a lobster! In fact even with a blending valve it is worth having a thermostatic shower tap.

    The temp you can get the water to will be high, up to boiling depending on how you design the system. The rads should match the output of the stove so this should stop overheating to boiling point or steam. But in any event the running of the system is in your hands. it would be silly to have the whole system humming at about 95 deg and then put a full load on the stove on max throttle. Experience will show how long things take to heat up and what sort of fuel loads go with what building temps.
    Peter
  5.  
    Just an after thought - you can not have plastic pipes within about 1M of the stove
    Peter
    • CommentAuthorListysDad
    • CommentTimeMar 27th 2011
     
    Thanks Peter.
  6.  
    I was interested to read this discussion as am planning something a bit similar - converting a small stone cabin up the mountain. It has will have no electricity. Any help with these questions would be great ....

    The water is coming from the mountain and held in a tank which is higher than 30 feet above the cabin. Water pressure is low to medium - i was hoping to avoid installing a cold water header tank ...would this work ?

    The plan is to run hot water for a shower and washing up (for one person) from the back boiler of a small wood stove( wood stove specs below) using a gravity flow system independent of any electric pump backup. (The pipe work is installed for a radiator for a heat dump- to be hung vertically).

    problem 1 = space. there is no attic, the ceiling is low and there is very little 'spare' space.
    I was hoping that the hot water cylinder might be able to go under the work-surface in the kitchen area(i.e. NOT installed a position higher than the stove). The pipe would be able to go upwards from the back boiler for about 4 ft and then down into the cylinder..would this work ? if so where would the pipe tee off to the heat dump radiator ? and what stops the water getting stuck at the high point of the pipework?

    problem 2 = conflicting advice about whether to get a copper or stainless steel cylinder and how small can this cylinder practically be ? (Given the space limits - the smaller the better- if the system wouldn't get too hot and it would provide enough water for a ' not - power ' shower). I have found one 24 x 15 copper ? would this be OK ? I can't find a small stainless one with a gravity coil .

    We used to heat our water from a stanley range directly into a copper HWC with no coil this type of cylinder doesn't seem to be available any more....



    woodstove boiler specs (Hamco)
    stainless steel boiler for a direct cylinder but also capable of heating a standard sized domestic cylinder and a radiator, these must be provided -
    -expansion tank open to the atmosphere
    -indirect cylinder
    - a gravity circulation to one radiator to dissipate heat

    max operating water temp 95 C

    boiler max operating pressure in bar 1.75 bar

    Boiler Test pressure in bar 2.1 bar

    heat output to water 2.4 Kw
  7.  
    <blockquote><cite>Posted By: Rachel Parry</cite>The water is coming from the mountain and held in a tank which is higher than 30 feet above the cabin. Water pressure is low to medium - i was hoping to avoid installing a cold water header tank ...would this work ?
    </blockquote>
    30ft gives you about 1 bar of pressure. It sounds like you will be using the mountain tank as the header tank for the heating system. I don't think this is a good idea, it would be a risk of blockage if the pipe froze or some other contamination blocked the pipe and you lit the stove - then BANG! Also you would potentially be mixing the heating water with the potable water because of the single feed pipe. If its not for the heating system but just for the potable water then OK - but then some questions about the water source. Washing up water and shower water should be drinking quality. Is the water source a piped spring (best) an open spring (a bit dodgy) or a stream (not a good idea as dead animals can end up in streams)

    <blockquote><cite>Posted By: Rachel Parry</cite>problem 1 = space. there is no attic, the ceiling is low and there is very little 'spare' space.
    I was hoping that the hot water cylinder might be able to go under the work-surface in the kitchen area(i.e. NOT installed a position higher than the stove). The pipe would be able to go upwards from the back boiler for about 4 ft and then down into the cylinder..would this work ? if so where would the pipe tee off to the heat dump radiator ? and what stops the water getting stuck at the high point of the pipework?</blockquote>

    That's a bit marginal. You would have to tee off at the high point to the header tank otherwise you will never get rid of the airlock. The success of the circulation would be in getting enough heat loss in the outflow pipe to get a flow started. The problem with the heat dump rad will be that if it is higher than the tank then the rad will have priority and you might never get hot water in the tank. Classically the rad would tee off just after the stove. In theory you could put the rad after the tank and in series, horizontally mounted, bottom entry and exit as this would give the priority to the DHW but with such a marginal setup I would be nervous about it working properly.

    It would be better to have the tank input above the stove. One option could be to dispense with the heat dump rad and replace it with the cylinder (If you can cope with it sticking out more than a rad) and remove the insulation from the bottom part of the cylinder. This will give you hot water at the top of the cylinder warm at the bottom and the bottom of the cylinder also functioning as a heat dump surface.
  8.  
    You cannot use plastic pipe on solid fuel as stipulated by HETAS. Technically this install is notifiable to building control also. If you boil the system through over loading or poor design you can easily exceed 100oC. In this case water will turn to steam which will increase in volume 1600 and any plastic pipework may split and will not be rated above 100oC.

    If copper is going to costs to much, you could consider low carbon steel?

    Sam
  9.  
    The plastic central heating pipe we have here is rated to 110 deg. (I think) and is either weld or compression fittings, but here I would reckon that copper would be easiest. The problem with iron pipe half way up a mountain with no electricity is that it is more difficult to work with without power tools. Also the availability of both materials and tradesmen who can and are willing to used iron pipework may be an issue.

    BTW where is the stone cabin?
  10.  
    Low carbon steel may be an advantage, unless you are considering installing it all yourself, in which case the tooling required (crimpers and bending machines etc) would outweigh any saving in material costs.

    All the major brands of plastic here in the UK specify that they are not suitable for solid fuel or unregulated heat sources. There may be a brand which has specific type of pipe for solid fuel over here, but I am not aware of it!

    As said before, you should notify building control when a solid fuel appliance is fitted, although a HETAS registered engineer can self certify through the scheme. That said, and I am not condoning it, I am sure many wood burners are installed as DIY, partly due to the fact that many people aren't aware of building control regulations, and partly due to cost saving!

    What ever you do, make sure it is done right as there is a potential to cause serious damage or injury with uncontrollable heat soures such as solid fuel. If you have any questions regarding regulations I may be able to help.

    Sam
  11.  
    thanks Peter ( Sam I think you are responding to someone elses comment - i am not considering using plastic pipes).

    It sounds from what you are saying that I should install a header tank (appropriate height for copper cylinders.)

    I think there is a possibility to put the HWC in the shower room, hung on the wall, this would mean it would be higher than the stove. Am i right in thinking that the 'radiator heat dumper' would have its own closed circuit from the HWC and back ? If so am i right in thinking the pipework needs to go up and around like the stove circuit ? ( Not sure if this would be possible with the new height of the HWC if the out pipe has to come from the top of the HWC.

    I still don't fully understand the size requirement for the cylinder. I understand one person uses about 50 a day ? How much more does the cylinder have to hold on top of this ? (ie can I get a 60 capacity cylinder -12 in diameter ) or would it work better to get a 15 x 36 in one ?
    • CommentAuthorcrusoe
    • CommentTimeApr 18th 2012
     
    Listysdad/Rachel: Does no power also mean no mains water? If so, where does water come from?

    CleanEnergies: You are presumably cognizant that you are talking steam flash and not steam production per se (this is an open vent system) - otherwise you would die every time you went to make a cuppa...:wink:
  12.  
    Crusoe - Rachel said
    Posted By: Rachel ParryThe water is coming from the mountain and held in a tank which is higher than 30 feet above the cabin. Water pressure is low to medium - i was hoping to avoid installing a cold water header tank ...would this work ?


    Rachel - The amount of water you store and heat and store will depend upon usage. OK one person might use about 50 a day, but this is for 'normal' living. Is your small stone cabin for extended stays or occasional use. As regards DHW if you count 25l. per shower and you want successive showers then you will need a bigger tank than if you are prepared to light the fire to heat the water between showers or to ensure shower + washing up.

    A couple of questions - is this in the UK, and as the water is coming from the mountain note that washing up water and shower water should be drinking quality. Is the water source a piped spring (best) an open spring (a bit dodgy) or a stream (not a good idea as dead animals can end up in streams) If none for these what sort of water is it.
  13.  
    <blockquote><cite>Posted By: crusoe</cite>Listysdad/Rachel: Does no power also mean no mains water? If so, where does water come from?

    CleanEnergies: You are presumably cognizant that you are talking steam flash and not steam production per se (this is an open vent system) - otherwise you would die every time you went to make a cuppa...<img src="/forum114/extensions/Vanillacons/smilies/standard/wink.gif" alt=":wink:" title=":wink:"></img></blockquote>

    It is the volume of water you have to consider and the size of the vent pipe (22mm for example) compared to a kettle with a couple of litres of water in it, and a hole (spout) of similar size 22mm ish!

    The kettle stops boiling via a thermostat, the solid fuel boiler keeps going. If the vent pipe can't match the expansion rate of the water/steam, something has got to give. This is probably at the extreme end of the scale admittedly.

    You could size the cylinder to match the heat output of the appliance. Correctly sized you would struggle to over heat the system, therefore not requiring a heat leak radiator as such (theoretically) You would probably find though that your appliance is quite small, and/or the cylinder is quite large.

    What is the main purpose of the barn? holiday home? workshop? day room?
    •  
      CommentAuthorSteamyTea
    • CommentTimeApr 19th 2012
     
    Posted By: Peter_in_HungaryThe amount of water you store and heat and store will depend upon usage. OK one person might use about 50 a day, but this is for 'normal' living. Is your small stone cabin for extended stays or occasional use. As regards DHW if you count 25l. per shower

    The temperature is important,
    25lt at 80°C and 50lt at 44°C, assuming incoming water is at 8°C amounts to the same amount of energy. You have to mix both with cold water to get a lower shower temp (this assumes no tank and pipe losses).

    What this amounts to really is how much water can you heat, to what temperature and in what time.

    So say you have a woodburner that is 5kW that has a 2kW back boiler that can deliver water at 90°C.
    And you are willing to allow for 20 minutes initial warm up period and happy to put some logs in if needed.
    In the following hour you can deliver up to kWh of energy at 90°C. Your incoming water is at 8°C.
    How much can you heat up to 50°C and 80°C
    2 kWh is 7200000 J
    Water takes 4180 J for 1 kg to go up in temperature by 1°C

    So to raise 1 kg to 50°C
    1(kg) x 42 (°C) x 4180 (J/(kg.K) = 175560 J

    You have 7200000 J to play with

    720000 / 175560 = 41 kg

    To raise to 80°

    1(kg) x 72 (°C) x 4180 (J/(kg.K) = 300960 J

    7200000 / 300960 J = 24 kg

    So now you need to find a cylinder that fits where you want it to and do the sums.
  14.  
    Excellent reply SteamyTea, I was edging towards the same response but you've explained it in a much better way than I probably would have.

    Just to add:

    1 kg = 1 litre approx
    •  
      CommentAuthorSteamyTea
    • CommentTimeApr 19th 2012
     
    And Heat and Temperature are not the same thing (in the real world of SI Units)
    • CommentAuthorcrusoe
    • CommentTimeApr 19th 2012 edited
     
    Come on Steamy, nobody in this industry measures water in KG for goodness sake. Like saying I'd like a KG of Coca-Cola please?? Eh what? And 2KW back boilers are unheard of. That's just 6824.24 Btus/hr. Even small Rayburns do a decent 8000 BTu/hr. That reply wouldn't have helped me, let alone LD. :)

    CleanEnergies: No, no we are not on the same wavelength. A ratio is a ratio, volumes are irrelevant. What I am saying is that in THIS kind of system - ie open vented ergo not pressurised, the 1600:1 ratio is not achievable - therefore not a danger, therefore why mention it? Pressurised systems a different story, but the comment is invalid in this context. Not a question of one end of any spectrum, nor vent pipe sizing. Just open vented versus sealed. If you need more info please whisper me as we are a little off-topic.

    Peter: Thanks for the heads-up. with that head - approaching 1 bar, why don't you oversize a thermal store and gravity it - no need for a coil or guessing gravity rad sizing - and use a coil for a pressurised shower. Some start from as little as .2 bar. Any rad required can be gravity fed from the store rather than the WS, thus allowing use of water and rad heated by solar thermal too, assuming a bit of PV for electric somewhere in the master plan?
    •  
      CommentAuthorSteamyTea
    • CommentTimeApr 19th 2012
     
    Posted By: crusoeLike saying I'd like a KG of Coca-Cola

    They buy it in Fluid Ounce in the USA.

    Posted By: crusoeAnd 2KW back boilers are unheard of

    I was shown one the other day, was a 5kW stove with a back boiler, I asked the output of the back boiler and was told it was 2 kW. Personally I would have no idea from looking at it, but the installer told me what it was and then showed me a plate by the consumer unit that had it written on it.
    But assuming that the stove was 5kW, has 6 sides, 4 that radiate/conduct heat, one that mainly convects heat, and one that is at the base and does little other than catch dust, so the one that has the back boiler on can grab up to a quarter of the heat available, or around 1.25 kW ?
    • CommentAuthorcrusoe
    • CommentTimeApr 19th 2012
     
    Touche, except we aren't in the USA so keep it relevant please :devil:

    That's a smally wee stove! But you're assuming a linear distribution of heat in any stove. Never may that happen or your slate hearth will catch fire m'dear. Way more heat output from top of stove than bottom, and sides fair to middling. Boilers rated at 5-6000Btu/ft2 as I remember. That's 1.76 KW/h approx, so a verrry small boiler too. We are talking longboat/caravan heaters here.
    •  
      CommentAuthorSteamyTea
    • CommentTimeApr 19th 2012
     
    It is physically small, about 18" (0.4572 m) all round and in a living room.

    It is interesting this litre, cubic metre, volume thing. When it comes to the physics of Specific Heat Capacity, the kilogram is used (sometimes the gram, but that is not an SI unit).
    The mass of something is is related to the amount of 'stuff' in it, the amount the 'stuff' moves, and the mean speed of that movement accounts for temperature, pressure and volume, a bit of jiggery pokery with algebra to rearranging the units soon leads back to the basic SI units.
  15.  
    Ok,

    Whilst 1600 times may not be relevant in this case, a pressure increase of X amount is possible, which may exceed the rating of any plastic pipe that was used, which was where the original quote was heading towards, albeit maybe using incorrect terminology or figures.

    Bearing in mind I was directing such comments towards a post which appears to be made from a person with limited experience and asking for advise, rather than somebody who know's a thing or two and ready to pounce when you slip up on specifics. :shocked:

    It is all irrelevant now anyhow as it is clear that plastic pipe should not be used and the OP has no intention of doing so.
  16.  
    SHC changes depending on the temperature of the water also, so I always presumed it was because the weight could remain a constant, whereas the volume was a variable?
   