    • CommentAuthorEd Davies
    • CommentTimeAug 14th 2012
     
    In another thread:

    http://www.greenbuildingforum.co.uk/forum114/comments.php?DiscussionID=9430&page=1#Comment_153897

    JSHarrisThe latter point is key, as compensation control assumes a fixed linear relationship between outside temperature and heating requirement. This may or may not be the case, depending on the installation. For example, I tried (and failed) to get such a control system to work on the system I installed in our house in Scotland. The problem was that heat loss was far more dependent on local wind speed around the house than it was on outside air temperature.

    My first thought is that just the effect of wind blowing over the surface of the building can't make that much difference. The thermal resistance from a flat surface to the air next to it is pretty small (of the order of 0.1 m²·K/W, I think). Wind will reduce this but even if it reduces it to zero it'll not make much difference compared with even a moderate amount of insulation.

    What seems much more likely is that wind was blowing in to the insulation, bypassing it. The need to have a reasonably wind-tight layer outboard of the insulation is well understood (at least in theory). Blower door testing is used to check the in-board airtightness layer but has anybody given any thought to verification of the outboard air tightness beyond simple visual inspection?
    •  
      CommentAuthorSteamyTea
    • CommentTimeAug 14th 2012
     
    Posted By: Ed DaviesThe thermal resistance from a flat surface to the air next to it is pretty small

    External is not always flat, lot of houses down here are pebble dashed and they may have double the surface area.

    If you test a house for airtightness, would it not be better to do two test, one pressurising and one depressurising ?
  1.  
    The only test I know of which would capture this effectively is a co-heating test. This involves heating an unoccupied house to a constant temperature with metered electricity (fan heaters) over a number of weeks, so the relationship between heat loss and weather conditions can be established.

    The results are often a lot worse than the advertised U values would imply due to a combination of air leakage & thermal bypass. However, the results can be difficult to interpret if the house is still drying out.

    David
    • CommentAuthorskyewright
    • CommentTimeAug 14th 2012
     
    Posted By: Ed DaviesMy first thought is that just the effect of wind blowing over the surface of the building can't make that much difference.

    Windchill is a significant factor for humans. Why not for buildings too?
    Or is it just a matter of human perception of temperature?

    Another thought: When it's both wet and windy could the wind also be increasing evaporative cooling of the walls?
    •  
      CommentAuthorJSHarris
    • CommentTimeAug 14th 2012
     
    <blockquote><cite>Posted By: Ed Davies</cite>
    What seems much more likely is that wind was blowing in to the insulation, bypassing it. The need to have a reasonably wind-tight layer outboard of the insulation is well understood (at least in theory). </blockquote>

    Not as far as I could see. The house had a brick plinth to floor level and was rendered block above that, painted with the toughest paint I could find (and even that didn't stand up to salt spray that well). It was pretty well sealed externally, had a 50mm cavity between the brick/block skin and the membrane covered, ply faced, timber frame (which would itself have been fairly well sealed, I'd have thought) then a layer of rockwool or similar around 150mm thick, then there was a plasticised foil membrane of some sort, then plasterboard on the inner surface. The roof was a warm roof design, clad with ply inside and out, with a membrane over the outer skin. The window were all Norwegian made DG units, with double seals and multiple catches all around (they were laminated timber frames, tilt and turn type windows). The external doors were pretty massive timber affairs, internally insulated and again with multiple catches around to pull them tight to the seals. The choice of house design took into account the exposed location on the West coast, and used pretty much the best available techniques at the time for keeping draughts out.

    Getting back to wind chill effects, the standard insulation calcs assume a fairly low air velocity across the surfaces. Increase the air velocity and rate of heat transfer increases, quite markedly if the outer skin of the building is at a significant temperature above ambient. Ideally the insulation would be perfect, and the building outer skin would be at ambient, but I'm not at all sure this can be achieved in practice even now, and certainly wasn't the case for my Scottish house built in 1993. Add in that weather variability can change the outer skin temperature up and down fairly quickly, aided and abetted by the wind, and you can have, as I found, some fairly big differences between the heating demand predicted by the outside air temperature and the heating demand that's needed in reality.
    •  
      CommentAuthorSteamyTea
    • CommentTimeAug 14th 2012
     
    Should do a Wind Heating Degree Days and see how it correlates, could also do a Direct Beam Sunlight Heating Degree Days (though not nights) too. And then there is the effect of rain. Suspect what you end up with a a climate score based on all variables.
    • CommentAuthorskyewright
    • CommentTimeAug 14th 2012
     
    Posted By: SteamyTeaShould do a Wind Heating Degree Days and see how it correlates, could also do a Direct Beam Sunlight Heating Degree Days (though not nights) too. And then there is the effect of rain. Suspect what you end up with a a climate score based on all variables.

    I log temp, solar and wind.
    I prepare HDD data. It's definately not enough on its own.
    A bit of solar can make a significant decrease in heating need[1], and a stiff breeze can make a significant increase.

    Could you expand on the concepts of WHDD & DBSHDD? How do I include the wind/solar elemants. A quick google didn't find me any equations.

    [1] A bit of sun helps both actual temps and the perceived need for heating (human response to radiant heat?).
    • CommentAuthorEd Davies
    • CommentTimeAug 14th 2012
     
    Posted By: SteamyTeaExternal is not always flat, lot of houses down here are pebble dashed and they may have double the surface area.

    Indeed, that only strengthens my point that the thermal resistance from the outside surface to the air is negligible.

    If you test a house for airtightness, would it not be better to do two test, one pressurising and one depressurising ?

    Isn't that what's normally done?

    The point though is that you can have a perfectly air-tight house as far a normal blower- (or sucker-) door test is concerned and still have the wind wiping through the outer layers totally bypassing the insulation.

    Posted By: JSHarrisIt was pretty well sealed externally, had a 50mm cavity between the brick/block skin and the membrane covered, ply faced, timber frame (which would itself have been fairly well sealed, I'd have thought)...

    Yes, but that's the question: how do you verify that assumption that the outer airtightness layer is good? Particularly when it's hidden in a cavity.

    Posted By: JSHarrisGetting back to wind chill effects, the standard insulation calcs assume a fairly low air velocity across the surfaces. Increase the air velocity and rate of heat transfer increases, quite markedly if the outer skin of the building is at a significant temperature above ambient.

    But the outer skin of the building shouldn't be at significantly higher temperature than ambient so the effect of the drop in thermal resistance with wind shouldn't make much difference.

    Imagine a battery with a 5 ohm and a 0.1 ohm resistor in series across it. If you short the 0.1 ohm resistor you'll only slightly increase the current flowing. 5 ohms corresponds to a wall with a U-value (including the internal but not the external wall/air surface) and 0.1 ohms corresponds to the external wall to air interface.

    Windchill makes a difference if there's evaporation and also if the only insulation you have is the surface/air interface. I wonder how much cooling evaporation from the outside of a building could cause. My initial thought would be only a degree or so at most but intuitions of that sort are notoriously unreliable. Perhaps some measurements are required.

    If evaporation does make much difference then a surface which allows water to run off rather than be trapped would be better.
    •  
      CommentAuthorSteamyTea
    • CommentTimeAug 14th 2012
     
    Posted By: skyewrightCould you expand on the concepts of WHDD & DBSHDD?

    We can all try:
    http://www.greenbuildingforum.co.uk/forum114/comments.php?DiscussionID=9446
    •  
      CommentAuthorJSHarris
    • CommentTimeAug 14th 2012
     
    Ed, I understand where you're coming from, but wind chill is simply the higher rate of heat loss from a body due to air movement, it's not necessarily related to the latent heat of evaporation. Forced air cooling exploits exactly this effect, and is remarkably effective. For example, one of my hobbies is building electric vehicles. I know from a lot of experience that adding a bit of forced air cooling to any component that's getting warm cools it far, far more effectively than just relying on convection.

    Certainly the temperature differentials are much lower with a house, but nevertheless the effect is the same, albeit on a less dramatic scale. One significant effect for our house was the effect of the wind on solar warming. The rear of the house was in both a wind and sun shadow (it faced more or less north east) and tended to stay at a temperature determined by outside air temperature, the front of the house would warm up and cool down very quickly from the effects of wind and sun in combination, significantly changing the heating demand.

    I'm reasonably sure the house was pretty air tight, maybe nothing like as good as some newer houses but much better than most being built at that time. There was never so much as a trace of a draught in the house, or even any appreciable wind noise when it was blowing a hoolie from the west. My heating bill for the year (oil fired CH) averaged around £150, when friends with similar size houses, in more sheltered parts of the village, were paying around three times that figure (IIRC, the oil price then was around 16p/lt).
  2.  
    Our place needs much more heating when its windy (1800s vintage, airtighness slowly improved but still far from perfect). A fall of snow makes the place noticeably warmer, I guess the wind blows snow into all the cracks and gaps and blocks them up.

    JSH, were there ventilated cavities in the wall, floor, roof? The rate of air changes in the cavities/roof/floor increases with the wind speed and direction. In calm weather the air layer in the cavity and the blockwork/slates act as additional insulation layers (OK maybe not much), but when its windy the cavity is flushed out with cold air - the tent flysheet effect. By convention the heat loss calcs assume that the ventilated spaces are always equal to external temperature, but in a ventilated loft in calm midsummer this can be felt not to be true.
    •  
      CommentAuthorJSHarris
    • CommentTimeAug 14th 2012
     
    <blockquote><cite>Posted By: WillInAberdeen</cite>

    JSH, were there ventilated cavities in the wall, floor, roof? The rate of air changes in the cavities/roof/floor increases with the wind speed and direction. In calm weather the air layer in the cavity and the blockwork/slates act as additional insulation layers (OK maybe not much), but when its windy the cavity is flushed out with cold air - the tent flysheet effect. By convention the heat loss calcs assume that the ventilated spaces are always equal to external temperature, but in a ventilated loft in calm midsummer this can be felt not to be true.</blockquote>

    The roof was certainly sealed, as it was boarded out with a warm roof and ready to be converted at some future date into a couple of extra bedrooms. The cavities appeared sealed, there were no air bricks or whatever AFAICR. The floor was similarly sealed, as there was an underfloor crawl space accessible by trap doors, one in the hall floor, one in the kitchen floor, to gain access to all the heating and plumbing (the house was built on a raised slab, with the timber floor being suspended about three feet above the slab). I installed the heating system myself, during late autumn, and I don't recall there being any draughts down in the crawl space, if anything it was a bit warm down there! (although that might well have been from all the cursing.........).

    I always just assumed that the difference was down to forced convection losses when it was windy, TBH, as that seemed most logical to me. The house insulation wasn't great by the standards of today, essentially the timber frame was just filled with about 150 mm of rockwool between the timbers, held in place by the ply torsion skin on the outside face and a shiny plastic/foil membrane on the inner face. There would have been a fair bit of cold bridging through the timbers.