    • CommentAuthoran02ew
    • CommentTimeAug 18th 2012
     
    We are struggling to find exactly what we want as far as wood burning stoves are concerned, we have put in the hours trawling the web and leg-work at various eco shows but the option for external air ducted fires seems at least for the present, limited.

    So maybe someone can help. If we kept below 5kw would we even require an air duct? Bearing in mind we are making substantial improvements throughout, airtightness and super insulated being probably the highest two on the list. Hopefully getting an airtightness of less than 1, but probably something between 1-2 air changes per hour. Will the fire work at these levels of air tightness without an external air duct?
    • CommentAuthortony
    • CommentTimeAug 18th 2012
     
    Too dangerous, but if you must have one how about a room sealed one, ie with its combustion air inlet from outside?
    • CommentAuthorSeret
    • CommentTimeAug 19th 2012
     
    Er, Tony, that's exactly the point.

    I would imagine 1 or 2 houses worth of air would be plenty to keep a fire burning. Are you using any kind of mechanical ventilation? Even if you're not required to have a permanent hole in the wall for your fire you could install one that shuts. It'd be a cold bridge but if it's supplying the fire you'd still end up ahead energy wise.
    •  
      CommentAuthornigel
    • CommentTimeAug 19th 2012 edited
     
    Here is a 4kw one with external air supply.

    http://www.woodwarmstoves.co.uk/products/fireview-range/4kwmultifuelstove.ashx

    It seem ideal for an air tight highly insulted house.

    When we were looking the lowest output we could find was 6kw with external air supply.
    • CommentAuthoran02ew
    • CommentTimeAug 19th 2012
     
    Posted By: SeretI would imagine 1 or 2 houses worth of air would be plenty to keep a fire burning.


    Are you suggesting a sub 5kw fire in a sealed house would work? house is around 250m2

    Posted By: SeretAre you using any kind of mechanical ventilation?


    Sorry forgot to mention, a full MVHR system is planned.

    Posted By: SeretEven if you're not required to have a permanent hole in the wall for your fire you could install one that shuts. It'd be a cold bridge but if it's supplying the fire you'd still end up ahead energy wise.


    Not sure i could spend all the time and effort to seal tiny pin holes and cracks only to create a large vent, even if it could be closed off.
  1.  
    Posted By: an02ewNot sure i could spend all the time and effort to seal tiny pin holes and cracks only to create a large vent, even if it could be closed off.


    If the stove is room sealed then the air is just coming in the supply and out the chimney, it's not going to affect your air tightness. Your going to have an even larger vent for your MVHR after all so why not one for the stove?

    It's a question of safety, CO kills, if you have a well sealed house you are introducing a huge safety risk by not having an air supply to the stove, how would you feel if someone died as a result of your decision not to have an air supply to the stove?
    • CommentAuthormike7
    • CommentTimeAug 19th 2012
     
    If it's any help, a 5kW stove would need in the region of 10 to 15m3/hr air when running at rated output, ie quite a small proportion of the airchange rate.
    • CommentAuthoran02ew
    • CommentTimeAug 19th 2012
     
    No CPB youve missed the point, im quite happy to have a room sealed(direct air) fire but the choice is limited and we are struggling to find a suitable style with this option, however maybe i need not have a room sealed fire if i keep it sub 5kw? the house is airtight so will the fire work with no air vent just feeding off the oxegen in the house?
  2.  
    My Contura 5-8kW has an exernal kit fitted. Most of the Contura range are available with external air kits. I am not linked to them.
    Gusty.
    •  
      CommentAuthornigel
    • CommentTimeAug 19th 2012
     
    <blockquote><cite>Posted By: an02ew</cite>No CPB youve missed the point, im quite happy to have a room sealed(direct air) fire but the choice is limited and we are struggling to find a suitable style with this option, however maybe i need not have a room sealed fire if i keep it sub 5kw? the house is airtight so will the fire work with no air vent just feeding off the oxegen in the house?</blockquote>

    I would not do it, its just not worth the risk. The other benefit of room sealed is that the draw of the stove does not create draughts in the room as it will be pulling the air from somewhere. How well the stove works with or without will depend also on the flue height and position and how much draw you get. The lower risk is option is a room sealed one - just depends how important looks are in the equation.
  3.  
    Posted By: an02ewNo CPB youve missed the point,

    Au contraire. Just because the building regs say that you can install a sub 5kW stove without an external air supply doesn't make it safe.

    The UK building regs need to be urgently updated in this regard, they were written at a time before houses were hermetically sealed.

    If you are building an air tight house for safety's sake you need to have an external air supply, end of story.
    • CommentAuthoran02ew
    • CommentTimeAug 19th 2012
     
    Posted By: Chris P BaconIf you are building an air tight house for safety's sake you need to have an external air supply, end of story.


    Thankyou. that is the answer i needed.
    • CommentAuthorfinny
    • CommentTimeAug 19th 2012
     
    Firstly thanks to Keith it now seems possible to answer posters questions in the spirit of the forum! Long may it continue..
    Some good advice above already. That 4 Kw woodwarm looks very good.
    Firstly, is your installation to be signed off? If so, by whom..If BCO then ask them what they want to see, if a HETAS installer then ask them. You will surely get a different answer as they are interpreting Part J in their own way. I would expect a HETAS installer to object to a MHRV unit and a stove vented from the room. As Tony says, how about direct air feed? This will certainly help compliance, but you may find spillage from the stove when you open the door to refuel. A word of caution about direct air feed though, do consider using non-combustible ducting as there is evidence that under extreme air pressure scenarios combustion gases can be drawn back through the ducting:shocked:
    • CommentAuthoran02ew
    • CommentTimeAug 19th 2012
     
    Posted By: nigeljust depends how important looks are in the equation


    Looks and cost! we need a double fronted fire, as it services two rooms
    • CommentAuthoran02ew
    • CommentTimeAug 19th 2012
     
    Finny. i agree, my only option now is to choose one of the few suitable, will also take on board your point about duct pipe, do you think the problem with spillage due to MVHR when i open fire door could be dangerous? could the MVHR be balanced to avoid this?
    • CommentAuthorfinny
    • CommentTimeAug 19th 2012
     
    Have to test it once it's in.. any good installer should look at it for you.. MVHR not my speciality, what you don't want is the system lowering the pressure in the room with the stove in it.. As for spillage, open door a crack, leave it a few seconds to balance the pressure a bit then open slowly..will def help.
    • CommentAuthorJonti
    • CommentTimeAug 19th 2012
     
    Posted By: Chris P BaconThe UK building regs need to be urgently updated in this regard, they were written at a time before houses were hermetically sealed.



    Chris,

    sorry to ruin your illusions but the vast majority of new houses built in the UK are no where near being hermetically sealed and even those that are most will not stay so long term. The building trade should be investing far more in getting their people to realise the whys and hows of modern building:cry:

    Jonti
  4.  
    Forgive me Jonti, I should have included the word "some" in the sentance! :tongue:
    • CommentAuthorHairlocks
    • CommentTimeAug 19th 2012
     
    When I last read the building regs, the exemption allowing to exclude a air vent for a sub 5Kw did not apply to a new build house, only retro fitting.
    • CommentAuthorfinny
    • CommentTimeAug 20th 2012
     
    Actual testing trumps regs..they are only there for guidance, but yes, as a general rule..post 2006 built.
    as per Jonti.. no houses are hermetic, would you want to live in a tupperware box? And now we can actually discuss it freely, I would like to say that in many peoples actual experience, adding a vent for a stove actually improves the air quality in a building. I admit that it is perceived quality improvement, which often does fly in the face of actual figures/statistics.
    There I said it:shocked:
    •  
      CommentAuthorfostertom
    • CommentTimeAug 20th 2012
     
    Wrong to think that 'a houseful' of air is available to a stove when there's no lo-resistance inlet. That air may be there but it won't be flowing into the fire and up the flue. If you get it to burn at all, the combustion gases will find it just as easy (or difficult) to flow back into the room, as up the flue. The suction created by buoyancy of hot gas in a flue is a weak force, so the whole flow path, from outside air into the room into the stove and up, must be of comparable or lower resistance - i.e. wide open. Even worse, the weak draw of the flue can easily be exceeded (creating back-flow) by an extract fan anywhere in the house (or switching a MHVR to 'boost'?) - in which case the combustion air inlet must provide a very-much-easier route (than the flue) to supply the extract airflow in addition to supplying combustion air.

    All of which disappears as a problem, with a balanced flue stove. Good luck! The difficulty is that you want the stove to be double-fronted? A single-fronted stove will still kick out heat from its back - sure you have to actually see flame from both rooms?
    • CommentAuthorfinny
    • CommentTimeAug 20th 2012
     
    <blockquote><cite>Posted By: fostertom</cite>The suction created by buoyancy of hot gas in a flue is a weak force, so the whole flow path, from outside air into the room into the stove and up, must be of comparable or lower resistance</blockquote>
    Sorry Tom, but that is not the basic principle on which flues work. Minimum draw of a flue for a solid fuel appliance is 12 pascals. Unlit. Heat can make it draw more, but heat cannot be relied upon to create draw.
    Was wondering what was keeping you..
    :wink:
    • CommentAuthorCliff Pope
    • CommentTimeAug 20th 2012
     
    I don't know how 5 kw compares with an ordinary open fire, but that can make our uninsulated draughty sitting room feel very stuffy and headachy if we don't open the sliding vents in the floorboards next to the fire.
    • CommentAuthormike7
    • CommentTimeAug 20th 2012 edited
     
    Posted By: finny
    Posted By: fostertomThe suction created by buoyancy of hot gas in a flue is a weak force, so the whole flow path, from outside air into the room into the stove and up, must be of comparable or lower resistance

    Sorry Tom, but that is not the basic principle on which flues work.


    Hmmm ... I can see that Tom's explanation could be expressed in other ways, but it doesn't seem wrong in principle. Care to expand, finny?


    Minimum draw of a flue for a solid fuel appliance is 12 pascals. Unlit. Heat can make it draw more, but heat cannot be relied upon to create draw.


    How does an unlit stove create any draw without a temperature difference between external air and air in the flue?
    • CommentAuthorfinny
    • CommentTimeAug 20th 2012
     
    <blockquote><cite>Posted By: Cliff Pope</cite>I don't know how 5 kw compares with an ordinary open fire, but that can make our uninsulated draughty sitting room feel very stuffy and headachy if we don't open the sliding vents in the floorboards next to the fire.</blockquote>
    I would condemn this appliance immediately. You should not use it until it has been thoroughly tested by a qualified person. Please tell me you at least have a working Carbon Monoxide alarm in the room..


    <blockquote><cite>Posted By: mike7</cite>Hmmm ... I can see that Tom's explanation could be expressed in other ways, but it doesn't seem wrong in principle. Care to expand, finny?</blockquote>
    It is not the buoyancy of hot air that creates draw.. if it was you would be unable to light it..


    <blockquote><cite>Posted By: mike7</cite>How does an unlit stove create any draw without a temperature difference between external air and air in the flue?</blockquote>
    The density of air is different at the opening of the flue and at the termination of the chimney. This creates draw..commonly called "the stack effect" in ventilation terminology. This is the reason for a recommended minimum flue height of 4.5 metres.
    Hope that helps:bigsmile:
    • CommentAuthormike7
    • CommentTimeAug 20th 2012 edited
     
    Sorry finny - that won't do :sad:

    The air pressure at the bottom of the stack will be higher than at the top by an amount equal to the weight per sq m of the air in the stack. The outside air pressure at the same bottom-of-stack level will be the same as inside, IF the outside air temp and the air in the stack are at the same temperature. Then there will be no pressure difference to generate a stack effect. Only when the flue air is warmer overall and thus less dense than the outside air will a stack effect arise.

    A reverse stack effect occurs when there is a change in the weather causing a sudden rise in outside air temperature so that the air in the flue is for a while cooler, usually resulting in sooty smells.

    Hope that helps, but knowing I have a serious habit of making the straightforward obscure, it may not.

    :bigsmile:
    • CommentAuthorfinny
    • CommentTimeAug 20th 2012
     
    Sounds great Mike but this effect is borne out by experience. Having installed many flues of all shapes and sizes over the years I can categorically say that a flue will draw without any difference in temperature between the air at the inlet and the outlet. The reverse stack effect you talk of can occur, generally in poorly constructed flues. This is the reason why a properly sized and installed flue, ideally insulated elicits such wonder in customers used to the traditional "poke a bit of flue thro the plate only" type installation.
    PS just tested my rayburn flue.. 12 metres, 6 inch liner, insulated over entire length, one 45 degree elbow. indoors 17 degrees, outdoors 22 degrees. 15 pascals..
    •  
      CommentAuthorfostertom
    • CommentTimeAug 20th 2012 edited
     
    mike7 has to be right, whatever longtime rule-of-thumb suggests. Inside air temp at entry to the unlit stove must be warmer than the entire remainder of the circuit.

    Even if outside air is all at same temp, from top of stack down to ground level, it gets warmed by mixing with inside air. Inside air may be warmed by fuel, or by solar gain.

    I'd wager confidently that a flue attached to an unlit stove standing in open air, on a still day with no outside air temp difference from top to bottom of stack, would produce no draw at all. Am I wrong?
    • CommentAuthorfinny
    • CommentTimeAug 20th 2012
     
    <blockquote><cite>Posted By: finny</cite>PS just tested my rayburn flue.. 12 metres, 6 inch liner, insulated over entire length, one 45 degree elbow. indoors 17 degrees, outdoors 22 degrees. 15 pascals..</blockquote>
    What difference doea putting a house on it make? Do the laws of physics change? Am I wrong?
    •  
      CommentAuthorfostertom
    • CommentTimeAug 20th 2012 edited
     
    I edited to add 'unlit' in my last post - might make a difference.

    Posted By: finnyWhat difference doea putting a house on it make? Do the laws of physics change?
    It means there's nothing that's pre-heating the air at the stove's entry. A house or even a shed is likely to be warmer than outside air, if only slightly by solar gain, which means the air at the stove's entry is warmer than the rest of the circuit. No house/shed, then no such pre-warming of that air.

    The draw in a flue must be temp-difference buoyancy - it can't be due to altitude-difference atmospheric pressure, as mike7 explained above.

    if youb really get that draw when colder inside than out, then I may stand corrected - but wd need 2nd and 3rd opinion!
   