    • CommentAuthorqeipl
    • CommentTimeSep 20th 2012
     
    Posted By: davidfreeborough
    Posted By: qeiplWhy would you invest in expensive machinery just to warm incoming air?
    Because its cheaper to run & saves CO2 emissions.

    David


    What do you mean it's cheaper to run?
    You don't need any machinery to warm air that comes into the house.
    A passive stack extractor will draw fresh air into the building, which will be warmed by the energy in the building.
    • CommentAuthordjh
    • CommentTimeSep 20th 2012 edited
     
    I like the 450 m³/hr demand for air of the Ecocent that is being quoted. Let's look at what it implies.

    IIRC, Building Regs requires that you be able to ventilate the house at least 0.44 ACH. And that rate is higher than other requirements for good internal air quality. So let's say you go slightly higher at 0.45 ACH. Then the 450 m³/hr implies an internal volume for the house of 450 / 0.45 m³ = 1000 m³. If we assume that the ceiling height is 2.5 m³ then we find that the floor area of the house is 400 m².

    That's quite a big house to heat and provide DHW for with one 800 W heat pump. :devil:

    I'm seriously impressed by the implied insulation levels - way better than Passivhaus. Or do we suppose that in reality, houses using these devices are over-ventilated?
    • CommentAuthorqeipl
    • CommentTimeSep 20th 2012
     
    djh,

    I worried about this before I installed my system but the reality is that I don't notice any problem with the air change rate. Maybe because the heat pump runs for half and hour and then sits doing nothing for a while.
    The internal volume of the house is (I think) 270m^3 so half an our of Ecocent is equivalent to 0.8ACH. If the pump is off for the next 2.5 hours that's a 3 hour cycle so the ACH is 0.27, albeit not continuous.

    The Ecocent isn't designed as an MVHR unit but the way I have it set up gives me MVHR at no extra capital or running costs. It might to meet the design requirements of a dedicated MVHR system but it works.

    Malcolm
  1.  
    Posted By: qeiplA passive stack extractor will draw fresh air into the building, which will be warmed by the energy in the building.
    Cooling the building in exactly the same way as an exhaust heat pump.

    David
  2.  
    Stepping back slightly,

    did I understand right that an EAHP should cool the outgoing exhaust air, to a temperature much lower than the ambient air that is being drawn in to replace the exhaust air, thus producing a net energy gain which can be used for DHW/UFH?

    I saw claims on sales sites that the exhaust air could be discharged at -5degC or even -15degC. If replacement ambient air is drawn into the house at +10degC, then there would be a net gain of about (10-(-5))deg x 1kJ/kg = 15 kJ per kg of air, or 2kW from an airflow of 450m3/h (1kg =~ 1m3), plus or minus latent heat.

    Problem would come a) when house needs more net heating than this and b) when ambient temp is lower than this and c) when these claims are not reality

    Can anyone with an EAHP and a thermometer, tell us what temperature it is actually discharging the exhaust air at?
    •  
      CommentAuthorSteamyTea
    • CommentTimeSep 20th 2012
     
    Posted By: WillInAberdeenCan anyone with an EAHP and a thermometer, tell us what temperature it is actually discharging the exhaust air at?


    Posted By: SteamyTeaI would love to see some data from both systems to get to the bottom of this.

    Me too :bigsmile:
    • CommentAuthorqeipl
    • CommentTimeSep 20th 2012
     
    Posted By: davidfreeborough
    Posted By: qeiplA passive stack extractor will draw fresh air into the building, which will be warmed by the energy in the building.
    Cooling the building in exactly the same way as an exhaust heat pump.

    David


    No! There's no heat loss at the intake end of the ventilation process.
    All of the heat loss is at the extraction end.
    • CommentAuthorqeipl
    • CommentTimeSep 20th 2012
     
    Posted By: WillInAberdeen
    Can anyone with an EAHP and a thermometer, tell us what temperature it is actually discharging the exhaust air at?


    I tried to do this on a cold day with a cheap digital thermometer. I think it said the outside air was 2C and it didn't change when I put it in the exhaust duct, even though the exhaust air felt warmer, so I didn't trust the result.
    I never looked into getting a more accurate thermometer.

    However, even if the exhaust air temp of the heat pump is no better than that of MVHR the system is still just as effective as MVHR in terms of recovering heat from extracted air.

    Despite David's protestations the Ecocent is doing the same job as the MVHR.
    Both of them scavenge heat from the outgoing air.
    Both of them use this to heat the air that comes into the building. the fact that the MVHR unit heats the air at the point of entry is irrelevant.
    • CommentAuthorstones
    • CommentTimeSep 20th 2012
     
    As the unfortunate owner of a Nibe Exhaust Air Heat Pump (Fighter F470) I can I think, speak with some degree of authority. To summarise, both David and qeipl have made perfectly valid observations. David I think explains very accurately how the Nibes work. My understanding of what qeipl has achieved, is a workable system using an ASHP inside, getting the benefit of solar gain, thermal mass etc.

    My unit has ventilation integrated into it, an MVHR if you like. I have no trickle vents in the windows, all ventilation being ducted into the house through the Nibe. There is no transfer of heat between extract and supply air as is the case with normal MVHR. The extract air goes through the heat pump side, the resultant energy used to heat water, which is then used to preheat supply air by way of a 'supply battery' (radiator in the duct) and to provide DHW and radiator or UFH.

    In my case the ventilation rate is set at 110m3 per hour. That remains fixed. There is therefore a limited supply of air available from which heat can be extracted.

    With the house kept at a constant 19 C, the CoP of the heat pump remains constant. The problem with the Nibe is the size of the compressor. My unit has a 650w compressor. Running at full capacity it operates for 18 hours per day, the remaining time being required for defrost cycles. The running time can be increased but only by increasing the ventilation rate. At a CoP of 3.06 x 650W x 18 hours gives a maximum real output of 35.8KWH per day. If you assume 15kw of that is for DHW (as in our case) that leaves around 20 kwh to provide space heating and pre warming of supply air. We are bringing in 110 m3 per hour of outdoor air. Once building heat loss is taken into account the Nibe heat pump can only supply enough energy to meet DHW and space heating requirements down to an external temp of around 8C. Any colder and the Nibe needs more energy and starts to use immersion to fill the gap, the colder it gets, the more it obviously uses.

    As stated by David and qeipl, this is the real problem and why there are so many complaints of high running costs. The literature for these heat pumps is very thin on information regarding how much immersion will actually be used. In my case, this equates to an eye watering 2500kwh of immersion per annum.

    I am in the process of engaging with the company that supplied my Nibe as I am very unhappy regarding the high running costs. I will therefore refrain from saying anything else at this stage.

    For those who want some figures, have a look at the thread I started in 2010

    http://www.greenbuildingforum.co.uk/forum114/comments.php?DiscussionID=6696

    has a lot of data relating to how much energy used / temperatures etc.
    • CommentAuthordjh
    • CommentTimeSep 20th 2012 edited
     
    Posted By: qeipl
    Posted By: davidfreeboroughCooling the building in exactly the same way as an exhaust heat pump.


    No! There's no heat loss at the intake end of the ventilation process.
    All of the heat loss is at the extraction end.

    There are two things to consider here. Firstly, temperature is not the same as heat. 'Cooling' is a statement about temperature, not about heat. Secondly, it's largely a matter of accounting conventions. It is possible to have a convention that is based on the 'absolute' thermal energy of the incoming air; equally it is possible, and more usual, to base the convention on the thermal energy relative to some reference temperature, which can be internal ambient temperature. What matters are the flows rather than statements of levels. What matters most is that everybody agree on the accounting convention that is being used!

    For comparison, consider kinetic energy. Most people believe in it and we can do useful calculations, say about the effects of car collisions, based on it. But it can also be argued that it doesn't really exist. It's 'really' just the second order term in a power series expansion of the (relativistic) mass of the object. It's entirely up to the individual which basis you use for calculation; though some calculations go more simply in one representation or the other.
    •  
      CommentAuthorSteamyTea
    • CommentTimeSep 20th 2012
     
    Posted By: djhIt's 'really' just the second order term in a power series expansion of the (relativistic) mass of the object.

    Nah, it's half mass times velocity squared :wink:
  3.  
    Posted By: qeiplDespite David's protestations the Ecocent is doing the same job as the MVHR.
    Both of them scavenge heat from the outgoing air.
    Both of them use this to heat the air that comes into the building. the fact that the MVHR unit heats the air at the point of entry is irrelevant.
    That is not what I said. I said that an exhaust heat pump should not be routninely specified for domestic installations because it consumes a lot more energy & produces a lot more CO2 than an MVHR doing the same job, i.e. heating the cold incoming air up to room temperature.

    Posted By: WillInAberdeendid I understand right that an EAHP should cool the outgoing exhaust air, to a temperature much lower than the ambient air that is being drawn in to replace the exhaust air, thus producing a net energy gain which can be used for DHW/UFH?
    Some are capable of doing this. However, you still consume a lot more energy delivering the proportion of the energy recovered by reducing the exhaust air temperature to outside air temperature than an MVHR would doing the same job. So a better approach would be to fit the exhaust heat pump to an MVHR exhaust. However, this would still be limited in power terms by the air flow rate & you'd probably be better placing it outside where the air flow rate is unlimited.

    David
    • CommentAuthorqeipl
    • CommentTimeSep 21st 2012 edited
     
    Posted By: davidfreeboroughI said that an exhaust heat pump should not be routninely specified for domestic installations because it consumes a lot more energy & produces a lot more CO2 than an MVHR doing the same job, i.e. heating the cold incoming air up to room temperature.


    But you're failing to take into account that the exhaust ASHP is only running when it's required for heating water, useful work.
    My exhaust ASHP provides efficient ventilation and it adds energy to the house.
    MVHR on its own provides efficient ventilation but cannot add any energy to the house.
    For a valid comparison with MVHR you have to take account of the energy used by your preferred heating system (gas, external ASHP or whatever).
  4.  
    The exhaust heat pump only adds energy to the house because you're using electricity to run the compressor & recover energy from the extracted air. However, you can add that energy far more cheaply using an MVHR with a gas boiler or external ASHP.

    David
    • CommentAuthorqeipl
    • CommentTimeSep 21st 2012 edited
     
    Posted By: davidfreeboroughThe exhaust heat pump only adds energy to the house because you're using electricity to run the compressor & recover energy from the extracted air.

    No. You still haven't got the main point.
    I'm not running the heat pump to extract energy from the ventilation air.
    I'm running the heat pump to extract energy from the outside air that's being drawn through the house in exactly the same way as an external ASHP. They both use the same air. They both add energy to the house via the water.
    The primary purpose of both is the use the captured energy to heat the water.
    Ventilation heat recovery is additional - an incidental bonus from running the heat pump inside the house.


    However, you can add that energy far more cheaply using an MVHR with a gas boiler or external ASHP.

    Only if the external ASHP (or boiler) + MVHR fans use less energy to do the same amount of work (heating water and ventilating) as the exhaust ASHP.

    The reverse is more likely to be true.
    • CommentAuthormike7
    • CommentTimeSep 21st 2012
     

    I'm running the heat pump to extract energy from the outside air that's being drawn through the house in exactly the same way as an external ASHP.


    ...but by the time you extract energy from that outside air it has become inside air, and the point of extraction is at the exhaust, so it deserves to be called exhaust air at that point. To deny this seems pointless - all the air was outside at some time.

    Elsewhere you claim that mixing the inducted air with warmer air and otherwise heating it by using higher temperature energy from inside results in a higher COP and is thus more efficient than extracting from the ambient outside air. This is false accounting as you are not taking account of the energy cost of the warming process.
  5.  
    Malcolm

    I'm sure you have a workable system which suits your needs, but this does not prove that an exhaust heat pump should be routinely specified for domestic installations in housing association homes & the like.

    You yourself said that "It would be daft to rely solely on an exhaust ASHP. In winter the house would never get warm.The system needs an alternative source of energy when the sun isn't working" & that you use solid fuel for this purpose. Solid fuels are not an option for many & certainly wouldn't be specified for a housing association home. The designer needs to specify something automatic like a gas boiler or external ASHP.

    Posted By: qeiplI'm not running the heat pump to extract energy from the ventilation air. I'm running the heat pump to extract energy from the outside air that's being drawn through the house in exactly the same way as an external ASHP. They both use the same air.
    If the exhaust heat pump exhaust is at outside air temperature then you've not extracted any energy from the outside air. All the energy you've extracted is coming from the house. If the exhaust heat pump exhaust is below outside air temperature then that proportion of the energy is coming from outside, but you're still paying a lot more than you need to recover the rest of it. You stated earlier that you believed the Ecocent exhaust temperature is within a degree or two of outside air temperature, so in your case, I don't believe you're extracting any energy from the outside air.

    However, you can add that energy far more cheaply using an MVHR with a gas boiler or external ASHP.
    Only if the external ASHP (or boiler) + MVHR fans use less energy to do the same amount of work (heating water and ventilating) as the exhaust ASHP. The reverse is more likely to be true.
    Post some numbers which show how an exhaust heat pump is cheaper to run than an MVHR plus ASHP or gas boiler & I'd be happy to review them.

    David
    • CommentAuthorRobL
    • CommentTimeSep 21st 2012
     
    Hi Qeipl
    I've done a quick comparison of houses, yours and mine, for interest -

    RobL Qeipl
    Cambridge Inverness used for hdd
    HDD 2268 2814 (3 year average heating degree days, http://www.degreedays.net)
    U 0.5 0.18 average over walls, roof, floor.
    floor 130m^2 100m^2
    area 286m^2 220m^2? (total area, walls roof, floor)
    heating 7.8MWh 2.7MWh U*area*HDD*24hours

    We (2adults+2kids, out during day) heat our (upgrading!) 1963 cavity wall house with gas mainly, and last year used a total of 7500KWh gas+1000KWh wood+ 3000KWh electricity. It sounds more than yours, but is actually very similar CO2 to 6MWh elec.
    The summer load last year was 8KWh/day elec +7KWh gas, a bit more than yourselves - I blame kids watching plasma telly+lava lamps Bah Humbug. We have an MVHR(measured 11W average power use, insignificant 70KWh/year), so there's not much losses from air changes. Note that our gas(minus 2.5MWh for DHW)+wood+(elec/2) more or less add up to the heating season load. I've used elec/2, as half of it is used in the heating season. In fact I'm quite impressed with how well those figures stack up without me fudging it! 7.8MWh heating estimated req'd, actual use 7.5MWh+1MWh+3MWh/2-7KWh*365 = 7.4MWh.

    If you were on gas+MVHR, given your heating requirement is so much less than ours, I would expect you would have the same elec bill as us but a gas bill of only 2.7MWh-3MWh/2+2.5MWh(same DHW as us assumed)=3.7MWh gas. If you had MVHR+ASHP, I would expect you to have to provide 3.7MWh heat/year from ashp for heating+DHW, using around 1.5MWh of elec (COP of 2.5), ie a total elec bill of 4.5MWh. In fact your EAHP uses 6MWh-3MWh=3MWh/year, which is about what you'd need with MVHR+ resistance heating eg an immersion or 3 plasma tellies left on all day&night all winter.

    My conclusions are:
    Congrats - your house is awesomeley well insulated! Am jealous.
    Gas+MVHR or ASHP+MVHR is way better than EAHP.
    EAHP is good in summer to heat up water (solar thermal is better still).

    I probably got location a bit out, so HDD and total m^2 area a bit out, so the heating load may be out by a little. Other numbers to add should be upfront install costs, which I've completely left out (I do note that the EAHP was cheap).
  6.  
    Attached is a comparison of:

    1. An exhaust heat pump with a COP of 4;
    2. An MVHR with an efficiency of 90% & an external ASHP with a COP of 3.

    The results are for an outside air temperature of +5°C with exhaust heat pump exhaust temperatures of +5°C & -5°C. In each case I've assumed that the exhaust heat pump has been sized to provide the required ventilation rate & the external ASHP has been sized to produce the same net heat gain as the exhaust heat pump, so that the overall power consumption figures can be directly compared. In a real system the exhaust heat pump & external ASHP would probably be significantly more powerful & run intermittently, but this doesn't affect the comparison.

    At +5°C exhaust temperature, the exhaust air heat pump consumes 571W compared to 281W for the same net heat gain from the MVHR/ASHP combination.

    At -5°C exhaust temperature, the exhaust air heat pump consumes 891W compared to 388W for the same net heat gain from the MVHR/ASHP combination.

    David

    Edit: See later post for easier to read spreadsheet
    • CommentAuthorqeipl
    • CommentTimeSep 22nd 2012
     
    RobL,

    Thanks for the number crunching. It's good to get a real life comparison.
    I think you've over-estimated the energy efficiency of my house, maybe because of the high external area/volume ratio, less than perfect draught-proofing, and the different wind/humidity profiles of Inverness and Skye. Inverness is a lot drier and calmer.

    Here are some recorded numbers to go with some of your assumptions...

    Total annual domestic electricity consumption: 4,150kWh
    Average daily electricity use May-Oct: 10.4kWh
    Non-heating season electricity use: 10.4 x 180 days = c.1,870kWh
    Total heating season electricity use: 4,150 - 1,870 = 2,280kWh
    Assume 1,500kWh of non-water heating electricity use during heating season.
    Electricity used for water heating (DHW + UFH) during heating season: 2,280 - 1,500 = 780kWh
    Electricity used for DHW during May-Oct: 1,870 - 1,500 = 370kWh
    Total annual electricity for DHW + UFH = 780 + 370 = 1,150kWh (compared to your estimate of 3,000kWh).

    Sense check...

    Ecocent data sheet shows a COP of 3.3 for air temp 18C and water temp 45C.
    Assume COP = 3
    Energy to hot water (DHW + UFH) during heating season: 780 x 3 = 2,340kWh
    Non-water heating electricity during heating season: 1,500kWh
    Solid fuel energy delivered to heat house: c.1,900kWh
    Total energy to heating during heating season: 2,340 + 1,500 + 1,900 = 5,740kWh, which sounds a bit more plausible alongside your 7,400kWh.

    Comparisons:

    Gas + MVHR ...
    Gas boiler has to deliver 1,150 x 3 = 3,450kWh/year to the water (DHW + UFH) to do the same work as the exhaust ASHP.
    Assume 90% efficiency (gas to hot water cylinder).
    Gas consumption: 3,450/0.9 = 3,833kWh.
    Gas/exhaust ASHP = 3.33
    Don't know the price of gas. Is it less than 1/3 the price of electricity?


    External ASHP + MVHR...
    External ASHP has to deliver 3,450kWh/year to match exhaust ASHP (1,150 x COP3)
    Assume average COP = 2.5 for external heat pump.
    Annual electricity consumption: 3,450/2.5 = 1,380kWh
    External ASHP/exhaust ASHP = 1.2
    Exhaust ASHP is marginally better (could be insignificant if COP differential is less than assumed).

    Both of the above examples exclude the work done by the solid fuel so are direct comparisons with the work done by the exhaust ASHP.

    Please check my sums.

    Cheers,

    Malcolm
    • CommentAuthorqeipl
    • CommentTimeSep 22nd 2012
     
    Posted By: davidfreeboroughAttached is a comparison of:

    1. An exhaust heat pump with a COP of 4;
    2. An MVHR with an efficiency of 90% & an external ASHP with a COP of 3.

    The results ...


    David,

    I'm struggling to understand the calculations. Can you upload a copy of the spreadsheet so that I can see the formulae?

    Malcolm
  7.  
    It seems the website doesn't allow Excel spreadsheets to be uploaded. So I've attached another PDF with a bit more text & a couple of arrows explaining the calculations.

    I've separated the Ventilation Heat Loss calculations for the two systems to allow more representative air flow rates for the exhaust heat pump & MVHR approaches. I've set the exhaust heat pump air flow rate to give net heat gains of 1.0-1.6 kW. I've set the MVHR air flow rate to that required for ventilation, i.e. 0.4 air changes per hour.

    Again there are results for exhaust heat pump exhaust temperatures of +5°C & -5°C. The net heat gain of the exhaust heat pump is copied across to the other system to determine the power required from the external ASHP. Hopefully this is more readable.

    David
  8.  
    David,
    Based on the numbers, you appear to be using a COP of 3 for the exhaust air heat pump, not the 4 specified. Also, not sure why you include fan power there, nor why the ASHP COP doesn't drop with external air temp.

    Also not sure what the Net Heat gain bit on the MHVR + ASHP column is - or at least why it's there.

    Sorry, been an idiot - I see your using the EAHP power as input to eg hot water and calling it net heat gain, which is also why the COP seems wrong.
    • CommentAuthorqeipl
    • CommentTimeSep 22nd 2012
     
    David,

    I'm still struggling.

    Exhaust HP, 5C
    If recovered power is 3067W and the COP is 4 why is the power consumed 1082W?

    Why is the net heat gain the same as the compressor power?
  9.  
    A heat pump with a COP of 4 gets three quarters of its power from the air flow & one quarter from the compressor input power.

    ASHP output power = (compressor input power) + (energy recovered from air flow)

    For an exhaust heat pump:

    Net heat gain = (ASHP output power) - (ventilation heat loss)

    Net heat gain = (compressor input power) + (energy recovered from air flow) - (ventilation heat loss)

    If you set the exhaust air temperature equal to the outside air temperature then all of the energy recovered from the exhaust air flow is required to cover the ventilation heat loss.

    If exhaust air temp. = (outside air temp.) then (ventilation heat loss) = (energy recovered from air flow) &

    (net heat gain) = (compressor input power)

    (power consumed) = (compressor input power) + (fan power)

    If you set the outside temperature to 5°C & the exhaust air temperature to 9°C then all of the exhaust heat pump output power is required to cover the ventilation heat loss.

    (compressor input power) + (energy recovered from air flow) = (ventilation heat loss) &

    (net heat gain) = 0

    See attached.


    David
  10.  
    Posted By: ChrisEnglandAlso, not sure why you include fan power there, nor why the ASHP COP doesn't drop with external air temp.

    Also not sure what the Net Heat gain bit on the MHVR + ASHP column is - or at least why it's there.

    Sorry, been an idiot - I see your using the EAHP power as input to eg hot water and calling it net heat gain, which is also why the COP seems wrong.
    I've used a COP of 4 for the exhaust heat pump & a COP of 3 for the external ASHP to reflect the lower temperature of the external ASHP's air intake.

    Both exhaust heat pumps & MVHR units require power for fans, so it seems only fair to include them in the comparison. I've assumed the pressure drop across an MVHR heat exchanger is similar to that across the exhaust heat pumps evaporator & so the fan power consumption will be similar.

    The net heat gain figure in the MVHR + ASHP column is an input field to allow direct comparison of the power consumed by two systems which deliver the same net heat gain. It is used 3 lines above to calculate the required ASHP power to deliver the same net heat gain.

    For the MVHR + ASHP system:

    (required ASHP output power) = (MVHR heat loss) + (required net heat gain)

    (compressor input power) = (required ASHP output power) / (ASHP COP)

    (power consumed) = (compressor input power) + (fan power)

    David
  11.  
    David,
    Many thanks - guess it depends on what you count as input for the COP,
    As it stands, your numbers would indicate that the combination MVHR + ASHP is better than EAHP, although continuing to lower exhaust temperatures does lower the difference, but there is an implicit assumption in the MVHR+ASHP case that the house is airtight. If you add an 'uncontrolled' ventilation rate, then matters change somewhat - for example, adding a leakage rate of 0.4 ach, ie equalling your MVHR, then the numbers for MVHR+ASHP and EAHP come out roughly the same. (the assumption on the EAHP side here is that all air goes through the EAHP, which doesn't seem unreasonable for moderate windspeeds as it causes a reduced internal pressure). Now that's a fairly high leakage rate, but is in the area you might expect if refurbishing an older property, I believe. This leads me to suggest that EAHP wouldn't be the best choice for a new build, where hopefully airtighness is controlled, but may well be good for an older property.

    Chris
    • CommentAuthorEd Davies
    • CommentTimeSep 23rd 2012
     
    Fan power will mostly go into the air it blows hence can be largely recovered by the heat pump (except if the design is silly enough to suck the air through the exchanger). ASHP, EAHP or MVHR.
  12.  
    Posted By: ChrisEnglandMany thanks - guess it depends on what you count as input for the COP
    I'm using the standard definition of COP, I'm just starting the calculation in an unusual place because I'm starting from the air flow & the temperature difference between the inside air & the exhaust air. It's important to start from the air flow because with an exhaust heat pump this determines the ventilation heat loss.
    Posted By: ChrisEnglandthere is an implicit assumption in the MVHR+ASHP case that the house is airtight. If you add an 'uncontrolled' ventilation rate, then matters change somewhat - for example, adding a leakage rate of 0.4 ach, ie equalling your MVHR, then the numbers for MVHR+ASHP and EAHP come out roughly the same.
    The heat loss due to air leakage is additional to that due to deliberate ventilation. It needs to be separately accounted for in both the exhaust heat pump & MVHR + ASHP cases.

    An MVHR will be adjusted for balanced flow & so should not pressurise or depressurise the house. This minimises air leakage through the fabric of the building. An exhaust heat pump will tend to depressurise the house leading to increased leakage.

    In addition, an exhaust heat pump with trickle vents as air inlets will have some uncontrolled ventilation due to, for example, air coming in the windward facing trickle vents & leaving through the leeward facing trickle vents. I've ignored this as it depends on the particular installation.

    David
    • CommentAuthorqeipl
    • CommentTimeSep 23rd 2012
     
    Posted By: davidfreeboroughA heat pump with a COP of 4 gets three quarters of its power from the air flow & one quarter ....


    Thanks David. The text explanation helps me to understand the logic of the calcs but I don't yet understand the logic of the assumptions.

    Table "Ventilation Heat Loss - Exhaust Heat Pump": why is ventilation heat loss = 3067kWh?
   