      CommentAuthorikimiki
    • CommentTimeSep 20th 2012 edited
     
    We have a 1930s-built semi and we would like to shore up our half of the structure with EWI.

    My question is, what sort of losses can we expect, given that the neighbour's solid wall serves as a giant cooling structure for 'our' solid wall?

    Doesn't heat imparted from within to 'our' solid wall travel along to the neighbour's section of the wall, where it serves to warm the air around the neighbour's house?
    • CommentAuthorTimber
    • CommentTimeSep 20th 2012
     
    Get therm and run some numbers. Remember your neighbour should also be heating their house to a similar temperature, and so not all of the heat that enters the wall goes over to their side and into their house. The main difference will be the outside of their masonry wall will be cold. Yours will be warm (behind the insulation). So at the interface with your wall and their wall there will be a temperature gradent and that is where the heat loss will be. (I think!)
    •  
      CommentAuthorikimiki
    • CommentTimeSep 20th 2012
     
    Are there any routinised therm modelers here who could show me the ropes?

    Presumably there would also be a library of standard buidling types (including UK-style semis) to draw from, rather than having to build the model from scratch? Or is it not a big deal to build from scratch?
    • CommentAuthorMike George
    • CommentTimeSep 21st 2012 edited
     
    Hi ikimiki

    I'm not a Therm user but am wondering why you want to quantify the losses when there's not much you can do about them?

    You could get a reasonable idea by just doing a steady state calculation. For the bridge concerned use the cross sectional area (by far the worst case)

    Q = UA delta T

    Heat Loss = U-value x surface area x temperature difference between inside and out.
    •  
      CommentAuthorSteamyTea
    • CommentTimeSep 21st 2012
     
    Posted By: Mike Georgeam wondering why you want to quantify the losses when there's not much you can do about them?
    Gives you a baseline to work from I would have thought.
    •  
      CommentAuthorfostertom
    • CommentTimeSep 21st 2012
     
    Posted By: Mike GeorgeHeat Loss = U-value x surface area x temperature difference between inside and out.
    U and surface area of what, given that it's a complex junction with oblique/curved heat flow?
    • CommentAuthorTimber
    • CommentTimeSep 21st 2012
     
    Ikimiki

    No standard models I am afraid, you would need to start from scratch, but a 2d model of what you are proposing is very simple to create in Therm.

    If I have a bit of spare time, I will see if I can come up with a simple model, and some advice on modelling.
  1.  
    Posted By: Mike George
    ''Heat Loss = U-value x surface area x temperature difference between inside and out.''

    FT wrote:
    ''U and surface area of what, given that it's a complex junction with oblique/curved heat flow?''

    To some extent I am with Mike, in that if the bridge simply cannot be avoided, don't spend too much time worrying about it, but I also sympathise with those who wish to know exactly what they are losing and why.

    Fostertom's point - what is the surface area you are measuring? - is apt, bcause who is to say where the thermal bridge starts? At what point back down the party wall can a thermal bridge be said to be, or not to be, in existence?

    If you were doing IWI you would return the insulation at internal and party walls, by roughly the length of a piece of string, to ''cloak'' the thermal bridge. Strictly there iss no reason why you should not do this (IWI to cloak the bridge) as an 'improvement' to the (uncloaked) thermal bridge with EWI. To me the only issue (apart from cost and disruption) is whether it can be done without looking stupid.

    As a general point (not specifically related to Ikimiki's Q), in terms of other uncloaked thermal bridges, check carefully the situation where capping details are used (where, for example, there is no oversail at verge or eaves, and the insulation is capped with a plastic or aluminium moulding). Has this left any uninsulated areas within heated rooms? If so, what do you do? IWI above the picture rail? As above, is it feasible? Will it look stupid?!
    • CommentAuthorMike George
    • CommentTimeSep 21st 2012 edited
     
    Posted By: fostertom
    Posted By: Mike GeorgeHeat Loss = U-value x surface area x temperature difference between inside and out.
    U and surface area of what, given that it's a complex junction with oblique/curved heat flow?


    That's why I said:

    Posted By: Mike GeorgeHi ikimiki

    For the bridge concerned use the cross sectional area (by far the worst case)



    Perhaps I should have said cross sectional area of the wall ie its thickness

    The u-value is straigfhtforward, and can be assumed to be around 2W/m2K for an uninsulated wall

    In reality the losses would be substantially less than the area I suggested. An educated guess would be around a third in my view

    Nick's idea of the cloaking is a good one, but there will still be a thermal bridge through the masonry, allbeit via a longer heat path.

    If I get chance I'll do some numbers for an example, though I suspect in the scheme of things the heat loss is not worth worrying about (unless you want to go down a passive house type route)
    •  
      CommentAuthorikimiki
    • CommentTimeSep 21st 2012
     
    Thanks for weighing in on this gents.

    I am somewhat reassured by the general tenor of the comments here -- namely that it's not worth worrying about in the greater scheme of things, not least of all because there is very little that can be done about it.

    ...Except... ...if it is not a minor efficiency loss, then lack of co-ordination between semi units might turn out to be a factor holding back the rollout of EWI across the solid-walled semi housing stock.

    The effect would be similar in nature to the "slumlord's dilemma". Two neighbouring slum highrises are owned by different slumlords. Upgrading of one will substantially increase the value not only of the upgraded highrise, but also of the neighbouring highrise. The one paying for the upgrade of his own building cannot appropriate the full value of the investment, because it accrues to the owner of the neighbouring highrise. So each slumlord simply waits for the other to implement an upgrade, with the end result that neither undertakes the upgrade.

    In the case of EWI for semis, one unit's installation of EWI won't directly raise the value of the other, but it *will* raise the efficiency of the second-mover's EWI investment.

    But, if people generally aren't aware of this efficiency loss -- or if it is felt to be negligible, as is clearly the case based on what has been posted here -- then it shouldn't affect willingness to invest in EWI after all.
  2.  
    I don't think that the average joe is savvy enough about heat loss to even consider it to be honest
    • CommentAuthordjh
    • CommentTimeSep 21st 2012
     
    Posted By: ikimikiIn the case of EWI for semis, one unit's installation of EWI won't directly raise the value of the other, but it *will* raise the efficiency of the second-mover's EWI investment.

    And similarly, the second-mover's insulation will benefit the first-mover. So if the first-mover's investment makes it more attractive to the second-mover to actually get off their behind and move, so much the better.

    I do think though that the best strategy for flats, terraces, semis, in fact anything other than fully detached, is to encourage street-at-a-time upgrades. It's tricky though, both in terms of costs and what people will accept aesthetically and culturally.
    • CommentAuthorjms452
    • CommentTimeSep 22nd 2012
     
    The base of the wall is often a similar problem and tends to be a greater linear length.
    The good news is that you can potentially' do something about this.

    I would expect that an external soil stack or gas pipe would end up causing worse cold bridging too.
    you can do something about this too.
    • CommentAuthorTimber
    • CommentTimeSep 23rd 2012
     
    Well I made a model, but didn't get round to running numbers.

    It doesn't look terrible (I will post a picture up later)
    •  
      CommentAuthorfostertom
    • CommentTimeSep 23rd 2012
     
    Ah yes, it's Timber who's our Therm man. Could I interest you in the question towards end of http://www.greenbuildingforum.co.uk/forum114/comments.php?DiscussionID=9579&page=1, also, related, in my post 14 Sept in http://www.greenbuildingforum.co.uk/forum114/comments.php?DiscussionID=9565 - is the proportionate area method right, of calc'ing heat flow when e.g there's insulation between studs? Is the flow really linear from hot to cold? Or does it tend to spread out sideways around the conductive interruption?
    •  
      CommentAuthorikimiki
    • CommentTimeSep 24th 2012
     
    *Verrry* curious to learn the results of your model Timber!
    • CommentAuthorMike George
    • CommentTimeSep 24th 2012 edited
     
    Tom,

    I suspect Therm would illustrate a 'bulb' of heat flow from the fixing into the insulation and towards the outside. Is this what you think as well?

    Though this won't tell us whether the heat loss is disproportionate to the cross sectional area of the bridge. This is because any heat transferred from the bridge into the insulation will raise the temperature of the insulation itself 'locally', meaning that the gradient of 'uniform' heat flow otherwise travelling through the insulation [directly alongside the fixing]is 'up and down' rather than linear.

    I don't see how any conclusions could accurately be drawn from such a simulation. I also cannot see a method of testing your theory other than the steady state one
    • CommentAuthorTimber
    • CommentTimeSep 24th 2012
     
    Ok, well here are the numbers -

    I assumed a solid 215mm brick wall with a conductivity of 0.77 W/mK giving a U-Value of 2.2 W/m2K.

    I assumed a 150 mm thick layer of EPS for the EWI giving an overall U-Value of 0.2274 W/m2K.

    The model resulted in a PSI value of 0.311 W/mK which is appalingly bad, really.

    Here are the Isotherms and heat flux
    • CommentAuthorTimber
    • CommentTimeSep 24th 2012
     
    Isotherms
      Wall Isotherms.jpg
    • CommentAuthorTimber
    • CommentTimeSep 24th 2012
     
    heat flux
      Wall Heat Flux.png
    • CommentAuthorMike George
    • CommentTimeSep 24th 2012 edited
     
    Hi Timber, trying to get my head around the pics. Can you describe which bit is which please? ie where the fixing is through the insulation.

    Also, in order to come to a conclusionas to the contribution of the fixing, wouldn't you have to make a comparison with something else? I don's see how this can be done? Or am I missing something?

    Edit. I've just realised the simulation is of ikimikis original query rather than the discussion Tom and I are having - donut :shamed:
    • CommentAuthorTimber
    • CommentTimeSep 24th 2012
     
    That is the external/party wall junction in plan. One house having the EWI, the other not.

    As for fixings, renders, plasters etc that has all been omited for simplicity.
  3.  
    Ah, okay. You say the PSI value is appalingly bad. Any chance you can put it into context / give us a comparison.

    Also do you have the Y-value for the area concerned?
    • CommentAuthorTimber
    • CommentTimeSep 24th 2012
     
    Well backstop worst case PSI values for new build are 0.15 W/mK.

    A decent, well designed junction can have PSI values as low as 0.01 W/mk.

    IF both houses had an EWI system, the PSI value would be almost (if not 0 (although the gemoetric effects of internal and external surface area come into play)).
    • CommentAuthorMike George
    • CommentTimeSep 24th 2012 edited
     
    Isn't the PSI value rather meaningless though if it doesn't quantify the actual heat loss in a way u-value allows?
    •  
      CommentAuthorikimiki
    • CommentTimeSep 24th 2012 edited
     
    Very 'pretty' images -- thank you Timber! :-)

    But as for actual informational content, it seems, to my untrained eye, from the isotherm representation that the right-ward shift of the gradient zone is fairly modest.

    Am I right in supposing that one may compute the total energy (& CO2) loss, relative to a fully EWI-clad semi, by introducing the height of the party wall into the calculation?

    Is it a simple formula? Or is it more complex than that?
    • CommentAuthorRobinB
    • CommentTimeSep 24th 2012
     
    Best outcome would be to get neighbour to EWI with you - any chance?

    Failing that, would they allow the EWI to continue a few inches over their property so that the junction with the party wall is completely EWI'd? I'd guess that would greatly improve the PSI values on your side and give them some benefit.
    •  
      CommentAuthorikimiki
    • CommentTimeSep 24th 2012
     
    I'd say, "Almost no chance whatsoever."
    The probability is greater than zero, but not by much! :-/

    The overlap idea sounds good, though without central govt/LAs stepping in to enforce this possibility, I can't see a lot of semi EWI-ers succeeding in getting the neighbours to agree....
    • CommentAuthorcullym
    • CommentTimeSep 25th 2012
     
    I'm looking at doing a similar job on my semi-d and this is one area I was concerned with. I was thinking of adding internal insulation to the party wall to elimate this bridge. It would also help with sound insulation, even though the party wall is solid block I can hear the neighbours plugging things in and out of the sockets on the party wall.
    If I was to IWI the party wall would I need to watch out for interstitial condensation. With the other side of the wall being warm I assume the risk would be minimal.
    • CommentAuthortony
    • CommentTimeSep 25th 2012
     
    minimal except at the outside corner of the room(s)
   