		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170482#Comment_170482</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170482#Comment_170482</guid>
		<pubDate>Sat, 16 Mar 2013 17:39:34 +0000</pubDate>
		<author>Shevek</author>
		<description>
			<![CDATA[We're carrying out a retrofit and targeting EnerPhit, and therefore we need to target at least 0.15 u-value to walls. We're restricted to 150 mm insulation because of our existing eaves detail. So the cost to insulate our 35 m2 existing solid brick walls is as follows:<br /><br />150 mm Grey EPS = 0.18 u-value = Â£400<br />150 mm PIR = 0.15 = Â£600<br /><br />Financially the PIR is a no brainer. So it comes down to:<br />1. CO2 emissions savings of 0.18 vs 0.15<br />2. Environmental impact of EPS vs PIR<br />3. Stability of EPS vs PIR<br />4. Longevity of EPS vs PIR<br />5. Risk of rising damp at ground level where we potentially create a problem due to lack of breathability.<br /><br />So let the games begin... how do they compare?]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170483#Comment_170483</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170483#Comment_170483</guid>
		<pubDate>Sat, 16 Mar 2013 17:39:52 +0000</pubDate>
		<author>Shevek</author>
		<description>
			<![CDATA[Bear in mind our windows will be 0.81 u-value and airtightness target is 1 AH. So it would seem a shame to forgo 0.15 u-value walls when the financial difference is Â£200.<br /><br />Furthermore we're interested in EnerPhit not as just as an arbitrary energy efficiency standard but as a comfort standard. So, for instanceâ€”in order to avoid convection currents and hence draughtsâ€”we want to be able to keep all surfaces in the house at 17 degrees or above without being hugely reliant on heating.]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170486#Comment_170486</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170486#Comment_170486</guid>
		<pubDate>Sat, 16 Mar 2013 18:09:58 +0000</pubDate>
		<author>Milk_No_Sugar</author>
		<description>
			<![CDATA[Not much in it.<br /><br />Happy to have been of assistance.<img src="/newforum/extensions/Vanillacons/smilies/standard/wink.gif" alt=":wink:" title=":wink:" />]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170518#Comment_170518</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170518#Comment_170518</guid>
		<pubDate>Sat, 16 Mar 2013 21:40:04 +0000</pubDate>
		<author>Seret</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Shevek</cite><br />1. CO2 emissions savings of 0.18 vs 0.15<br /></blockquote><br /><br />Depends on several other factors (HDD for your location, type of heating system, its efficiency, it's carbon intensity).<br /><br />That difference in u-value will mean about 50kWh of extra heat would leak out for 2000 HDDs. For a 90% efficient gas boiler you'd be looking at about 10kg CO2e per year difference.<br /><br />So probably about what a hedgehog would fart in that same year.]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170519#Comment_170519</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170519#Comment_170519</guid>
		<pubDate>Sat, 16 Mar 2013 21:50:03 +0000</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[I would say that the breathability of eps would swing it,]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170522#Comment_170522</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170522#Comment_170522</guid>
		<pubDate>Sat, 16 Mar 2013 22:04:27 +0000</pubDate>
		<author>Shevek</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: tony</cite>I would say that the breathability of eps would swing it,</blockquote><br />For what purpose? Lowering risk of interstitial condensation and rising damp?]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170532#Comment_170532</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170532#Comment_170532</guid>
		<pubDate>Sat, 16 Mar 2013 23:02:56 +0000</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[Keeping the house dry and happy with continuous drying of the structure, with impermeable insulation this it not necessarily true.]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170566#Comment_170566</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170566#Comment_170566</guid>
		<pubDate>Sun, 17 Mar 2013 11:14:23 +0000</pubDate>
		<author>seascape</author>
		<description>
			<![CDATA[Think I would go for breathability too.  Just in case during build it's impossible to keep all the water out and also over the years - hair line cracks etc.  Isn't PIR a bit like a plastic bag over your building?]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170570#Comment_170570</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170570#Comment_170570</guid>
		<pubDate>Sun, 17 Mar 2013 12:05:57 +0000</pubDate>
		<author>jamesingram</author>
		<description>
			<![CDATA[<blockquote ><cite >So probably about what a hedgehog would fart in that same year.</blockquote><br />Fantastic abstract realism <img src="/newforum/extensions/Vanillacons/smilies/standard/bigsmile.gif" alt=":bigsmile:" title=":bigsmile:" /></cite>]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170572#Comment_170572</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170572#Comment_170572</guid>
		<pubDate>Sun, 17 Mar 2013 12:09:15 +0000</pubDate>
		<author>DarylP</author>
		<description>
			<![CDATA[seascape, If you never open the doors or windows, or don't have MVHR then your analogy "PIR a bit like a plastic bag over your building?" holds true....<br />but otherwise, I don't think so.....<img src="/newforum/extensions/Vanillacons/smilies/standard/confused.gif" alt=":confused:" title=":confused:" />]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170573#Comment_170573</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170573#Comment_170573</guid>
		<pubDate>Sun, 17 Mar 2013 12:10:41 +0000</pubDate>
		<author>Nick Parsons</author>
		<description>
			<![CDATA[How big a hedgehog? EU standard size?]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170578#Comment_170578</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170578#Comment_170578</guid>
		<pubDate>Sun, 17 Mar 2013 12:19:13 +0000</pubDate>
		<author>joe90</author>
		<description>
			<![CDATA[Brilliant analogy, better than all the graphs.]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170580#Comment_170580</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170580#Comment_170580</guid>
		<pubDate>Sun, 17 Mar 2013 12:27:34 +0000</pubDate>
		<author>jamesingram</author>
		<description>
			<![CDATA[vapour resistance values (r) for : ( from NBT paper )<br />PUR (without foil ) 300 (10,000 with foil, though EWI boards for rendering will be foil less )<br />EPS 150<br />Woodfibre 25<br />Mineral wall 6<br /><br />from bs12524 water vapour resistance factor  <br />PUR 60 (presume PIR polyisocyanurate is same ?)<br />EPS 60<br />wood particle board 5-10<br />mineral wool 1<br />phenolic 50<br /><br />to convert between r and vapour resistance factor see.<br />"excellent illustration here <a href="http://builddesk.co.uk/wp-content/uploads/2013/01/vapourResistances.pdf" target="_self" rel="nofollow">http://builddesk.co.uk/wp-content/uploads/2013/01/vapourResistances.pdf</a>  "]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170583#Comment_170583</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170583#Comment_170583</guid>
		<pubDate>Sun, 17 Mar 2013 12:41:34 +0000</pubDate>
		<author>jamesingram</author>
		<description>
			<![CDATA[Shevek , have you a product in mind for 150mm PIR/PUR no foil faced , might find it's only available in 100mm max so you'd need to glue board together, which might confuse the issue.]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170585#Comment_170585</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170585#Comment_170585</guid>
		<pubDate>Sun, 17 Mar 2013 12:45:46 +0000</pubDate>
		<author>Shevek</author>
		<description>
			<![CDATA[Ah right, thanks James. No I hadn't thought about that or a supplier yet.<br /><br />Am I right in saying there's little difference in breathability from the figures you posted above though? (putting aside glueing sheets)]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170588#Comment_170588</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170588#Comment_170588</guid>
		<pubDate>Sun, 17 Mar 2013 12:53:54 +0000</pubDate>
		<author>RobinB</author>
		<description>
			<![CDATA[Shevek if you're hoping to have a Certified Enerphit building I think you'll need the PIR. By chance was just reading this on Enerphit criteria.<br /><br />http://www.passiv.de/downloads/03_enerphit_criteria_en.pdf]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170589#Comment_170589</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170589#Comment_170589</guid>
		<pubDate>Sun, 17 Mar 2013 12:56:28 +0000</pubDate>
		<author>jamesingram</author>
		<description>
			<![CDATA[Shevek , Seems that way , though SW3000 is PIR rather than PUR  which NBT paper list only with foil at r=43,000.<br />(i'm presuming similar value of 300 without foil ?)<br />though as discussed in Mike George's render breathablilty thread, figures dont tally with BS12524 and sources unclear .<br />The whole area of breathability of products seems quite muddy to me.]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170590#Comment_170590</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170590#Comment_170590</guid>
		<pubDate>Sun, 17 Mar 2013 12:59:44 +0000</pubDate>
		<author>jamesingram</author>
		<description>
			<![CDATA[Shevek on pros/cons Greenspec give outline ( I'm sure yo've seen that already)<br /><a href="http://www.greenspec.co.uk/insulation-oil-derived.php" target="_self" rel="nofollow">http://www.greenspec.co.uk/insulation-oil-derived.php</a><br /><br />One thought not mentioned recently is the long term U value of oil derived foam insulation.<br />some claim those such as PUR/PIR/phenolic degrade over time through offgassing where as EPS is a stable value.<br />from greenspec <br />"Insulation performance can be reduced over the first 3 years due to gas exchange from the cells. This reduction of performance is usually included in the manufacturers declared value of thermal conductivity"<br />some claims around it's worst than this.]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170989#Comment_170989</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170989#Comment_170989</guid>
		<pubDate>Wed, 20 Mar 2013 07:32:00 +0000</pubDate>
		<author>jamesingram</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Shevek</cite>We're carrying out a retrofit and targeting EnerPhit, and therefore we need to target at least 0.15 u-value to walls. We're restricted to 150 mm insulation because of our existing eaves detail. So the cost to insulate our 35 m2 existing solid brick walls is as follows:<br /><br />150 mm Grey EPS = 0.18 u-value = Â£400<br />150 mm PIR = 0.15 = Â£600<br /><br />Financially the PIR is a no brainer. So it comes down to:<br />1. CO2 emissions savings of 0.18 vs 0.15<br />2. Environmental impact of EPS vs PIR<br />3. Stability of EPS vs PIR<br />4. Longevity of EPS vs PIR<br />5. Risk of rising damp at ground level where we potentially create a problem due to lack of breathability.<br /><br />So let the games begin... how do they compare?</blockquote><br /><br />1.some , but little, by Seret figure 600kg CO2e over 60 years (life time of refurb (will EWI last that long)?)<br />2.EPS wins<br />3.EPS wins<br />4.EPS wins <br />5.EPS wins]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170994#Comment_170994</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=170994#Comment_170994</guid>
		<pubDate>Wed, 20 Mar 2013 08:03:18 +0000</pubDate>
		<author>Shevek</author>
		<description>
			<![CDATA[So why does everyone think EPS is far more breathable than PIR? Is it because PIR is usually foil-backed?]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171006#Comment_171006</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171006#Comment_171006</guid>
		<pubDate>Wed, 20 Mar 2013 10:38:00 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[<a href="http://www.natural-building.co.uk/images/downloads/Breathability_in_buildings.pdf" target="_self" rel="nofollow">http://www.natural-building.co.uk/images/downloads/Breathability_in_buildings.pdf</a> actually gives ranges of resistivity values - so EPS not just 150, but 100-750, XPS 600-1500, and PU foam not just 300, but 115-1000. So it's wide open.]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171104#Comment_171104</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171104#Comment_171104</guid>
		<pubDate>Thu, 21 Mar 2013 00:14:35 +0000</pubDate>
		<author>Saint</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: jamesingram</cite>Shevek , have you a product in mind for 150mm PIR/PUR no foil faced , might find it's only available in 100mm max so you'd need to glue board together, which might confuse the issue.</blockquote><br /> PUR and PIR without foil faces available in thicknesses up to 600mm, in fact I'm not sure if  you can't actually get 750mm. The bigger the order the better the price of course]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171114#Comment_171114</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171114#Comment_171114</guid>
		<pubDate>Thu, 21 Mar 2013 08:40:53 +0000</pubDate>
		<author>Saint</author>
		<description>
			<![CDATA[Can't really see how EPS can be considered breathable or should I say more correctly vapour permeable when in the BBA certificate 90/2558 for Springvale's EPS Wallshield partial cavity fill boards it says:<br /><br />11 Water vapour penetration<br /><br />11.1 The product has a minimum water vapour<br />resistivity values in the range of 145 MNsgâ€“1mâ€“1<br />for SD grade to 719 MNsgâ€“1mâ€“1 for EHD grade<br />and will therefore provide significant resistance to<br />water vapour transmission. Joints between boards<br />will facilitate the passage of water vapour under<br />normal conditions of temperature and humidity.<br />11.2 If the product is to be used in the external<br />walls of rooms expected to have high humidities,<br />care must be taken to provide adequate permanent<br />ventilation to avoid possible problems from the<br />formation of interstitial condensation in the internal<br />wall leaf.<br /><br />Its not a special grade of EPS, its just made in smaller board sizes to fit in a cavity.<br /><br />Thermal condiuctivites are given as:<br /><br />12 Thermal insulation<br /><br />12.1 For the purpose of U value calculations to<br />determine if the requirements of the Building (or<br />other statutory) Regulations are met, the thermal<br />conductivity ( value) of the insulation board may<br />be taken as shown in Table 3.<br /><br />Table 3 Thermal conductivity values<br />Product Grade Thermal conductivity<br />(W/mK)<br />WallShield SD 0.037<br />WallShield SD lo  0.035<br />WallShield HD 0.035<br />WallShield EHD 0.033<br />MicrofoamX32 â€” 0.032<br />WallShield Platinum Neopor NEO 0.031]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171118#Comment_171118</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171118#Comment_171118</guid>
		<pubDate>Thu, 21 Mar 2013 08:53:36 +0000</pubDate>
		<author>Shevek</author>
		<description>
			<![CDATA[So it seems to me there's no winner on item 5 (vapour permeability). Both PIR and EPS are increasing the risk of interstitial condensation by similar degrees.]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171122#Comment_171122</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171122#Comment_171122</guid>
		<pubDate>Thu, 21 Mar 2013 09:01:46 +0000</pubDate>
		<author>Saint</author>
		<description>
			<![CDATA[Depends where the dewpoint occurs and if the moisture vapour gets through to that point]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171125#Comment_171125</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171125#Comment_171125</guid>
		<pubDate>Thu, 21 Mar 2013 09:11:39 +0000</pubDate>
		<author>Shevek</author>
		<description>
			<![CDATA[True, it comes down to the actual figures, but in principle there's not a big difference.]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171131#Comment_171131</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171131#Comment_171131</guid>
		<pubDate>Thu, 21 Mar 2013 09:54:08 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Yes, when they say things like 11.2 above, which appears to follow from 'significant resistance to water vapour transmission' in 11.1, in fact 11.1 doesn't lead to 11.2, so they're just throwing in vague stuff to cover arse. Short of full VCL resistance as innermost layer, any construction needs to be checked for intersitial condensation.<br /><br />'Significant resistance to water vapour transmission' doesn't mean it's unsuitable for use in 'breathable' construction. It's not all that 'significant' - just 'not near-transparent' as dedicated breather products are. It's still way down the at the low-resistance end of the scale, amongst building materials. As long as the 5x (some say 3x) rule of thumb is applied, so something 5x (or 3x) as resistant is provided inboard, then it should be a safe 'breathable' construction, albeit at a modest rate of 'breathing', but preferrable IMHO to an industry-standard non-'breathing' construction with inboard full VCL.<br /><br />Having said that, are we sure about<blockquote ><cite >Posted By: Saint</cite>Its not a special grade of EPS, its just made in smaller board sizes to fit in a cavity.</blockquote>My prev researches held up Springvale's Neopor EPS as having particularly low resistance, 50 I think, not 145, i.e. even lower (because Neopor) than the 100-750 range given in http://www.natural-building.co.uk/images/downloads/Breathability_in_buildings.pdf .]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171133#Comment_171133</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171133#Comment_171133</guid>
		<pubDate>Thu, 21 Mar 2013 10:00:20 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[I'm really sceptical about any closed-cell (aero bar) plastic solid having low water vapour resistance, compared to EPS which is flakes of stuff clumped together. The former is an imperforate solid, albeit with separated air bubbles within, while the latter has numerous free-air passages right through. Explanation needed, before I'll believe.]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171139#Comment_171139</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171139#Comment_171139</guid>
		<pubDate>Thu, 21 Mar 2013 10:43:15 +0000</pubDate>
		<author>Saint</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Shevek</cite>So it seems to me there's no winner on item 5 (vapour permeability). Both PIR and EPS are increasing the risk of interstitial condensation by similar degrees.</blockquote><br />If you want vapour permeable you'll need to look at mineral fibre, Rockwool etc. <br />No plastic foam is particularly vapour permeable. Kingspan who bought Springvale as part of the CRH acquisition insulation and then let them Springvale go (they didn't want EPS) get very shirty about the whole idea of breathability...well they would do...http://www.kingspaninsulation.co.uk/Knowledge-Base/Breathability-1.aspx]]>
		</description>
	</item>
	<item>
		<title>EPS vs. PIR</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171143#Comment_171143</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=10318&amp;Focus=171143#Comment_171143</guid>
		<pubDate>Thu, 21 Mar 2013 10:47:59 +0000</pubDate>
		<author>Shevek</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Saint</cite>If you want vapour permeable you'll need to look at mineral fibre, Rockwool etc.</blockquote><br />That's a thought. Much more expensive though right? Perhaps, however, we could use a strip of it at the base of the existing wall above ground level to improve the risk of rising damp not being able to escape outside?]]>
		</description>
	</item>
	