Posted By: GotanewlifeUK regsAin't no such thing - I think you're probably thinking of English regs.
bedrooms at 3AC/HSounds an awful lot to me. Values like 0.5 AC/h seem more reasonable.
Posted By: barneyStart with the basics - for a single person in sleeping accomodation, you would want about 10 litres/second for a good air quality index
Posted By: GotanewlifeNow what sort of extraction rate should I be aiming for in single occupancy bedrooms of about 40m^3?
Posted By: barney…and come out at around 1ACH (which is generous as Ed points out)1 AC/h for each of the bedrooms would be 0.5 AC/h for the whole flat if each bedroom was a quarter of the overall volume. So probably roughly consistent depending on what you're measuring the AC rate over. Perhaps I should have been clearer that I was thinking of typical overall AC rates and assuming inlets in the bedrooms and exhausts in the kitchen and bathroom.
Posted By: barneysupply and extract to the bedroomsDo you mean one or 2 HR100s, if one, you mean T off so both supply and extract ducts go to both bedrooms?
Posted By: barneyrig a set of controlls to allow extract onlyas these don't have summer bypass do you mean blanking off the external inlet and leaving the fan to pull against a dead head?
Posted By: barneyrevese the supply fan as wellI like that idea, just a bit of work twice a year but do you know that is always feasible with a HR Unit?
Posted By: barneyFor the lounge, I'd put supply into the lounge and take dirty extract from the kitchen and bathroomyou mean with another HR 100 unit - except I cannot run ducting in the lounge at all. I can extract and supply from the kitchen and shower-room but only through the wall into the storage room; the only mechanical option in the lounge is a Single Room through wall unit built into a cupboard sound proofed and with careful separation of flows and returns - feasible but with a bigger unit as per my diagram I wouldn't need to do that.
Posted By: barneyor is it truly continental and is a hollow pot floor onto which a render and set finish is applied to form a truly solid ceiling ?Got it in one - concrete beams, hollow blocks dropped on top with base of block level with base of beam and rendered/plastered directly - same throughout my house it is just that in the lounge kitchen area I need all the height I can get whereas in the bedroom area there will be suspended plasterboard ceiling 120 lower as place is full of services for my kitchen above and the floor has previously been dug out a bit.