Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthorsune
    • CommentTimeJul 9th 2013 edited
     
    Hello everyone - I bet someone here can help: we have been considering using Sarket sarking board, mostly because we know of it. However I would much rather use something made in the UK. Can anyone suggest a type of sarking board that is made here, is water resistant and vapour permeable? Thanks.
    • CommentAuthorSprocket
    • CommentTimeJul 9th 2013
     
    •  
      CommentAuthorfostertom
    • CommentTimeJul 9th 2013
     
    Discovered that Smartply OSB3 (no added formaldehyde) is v much more vapour permeable than 'typical' OSB, presumably being less impregnated with glue. That's good - been using it - but the worry now is that it may also be much less airtight (figures hard to get).
    • CommentAuthorsune
    • CommentTimeJul 10th 2013
     
    Thanks - I knew someone would have a bright idea I will check out OSB3. An advantage of the Sarket was that you can use it uncovered for a fair while and without a membrane, so hopefully the obs3 is the same. : )
    •  
      CommentAuthorfostertom
    • CommentTimeJul 10th 2013
     
    No, shouldn't leave OSB exposed for long.
  1.  
    One minor point to mention is that SmartPly is manufactured in Clonmel Ireland rather than the UK.

    Depends what the OP's motivation is, if it is consideration of carbon miles then depending on the delivery address in the UK the impact may be smaller than from a manufacturing plant that is in the UK perhaps for example in highland Scotland.

    If the motivation is to support UK jobs then SmartPly do at least have a considerable workforce post manufacturing in the UK and the Irish will be grateful of the input to their economy.
    •  
      CommentAuthorfostertom
    • CommentTimeJul 10th 2013
     
    I was wondering where Smartply came from. Aren't most other OSBs either European origin or even far east/US? Isn't Smartply almost as homegrown as any? Clonmel is strategically closer to UK pop centres than Highland Scotland - and ships are pretty good on air-miles!
    • CommentAuthorTimSmall
    • CommentTimeJul 11th 2013
     
    Posted By: fostertomworry now is that it may also be much less airtight


    I found in my informal test (single sample, side-by-side same building - we switched suppliers part way through due to short stock) that 18mm Smartply was as airtight as 18mm Norbord Sterlingboard, and that both had good airtightness (towards the top of the experimental range in the University of Leuven study).
    • CommentAuthorTimSmall
    • CommentTimeJul 11th 2013
     
    BTW, I believe that Sterlingboard is produced in both Inverness and Belgium (the stuff I bought in Brighton came from Belgium ISTR).
    •  
      CommentAuthorSteamyTea
    • CommentTimeJul 11th 2013
     
    The motivation is an interesting question.
    If it is to support British Industry, you may do more good by buy cheap imports and spending the saving on something that has a direct impact at home, say a food bank or a homelessness charity.
    Just like 'carbon miles', lots of research is needed.:wink:
    •  
      CommentAuthorfostertom
    • CommentTimeJul 11th 2013
     
    V gd info Tim - thanks.
    ST as controversial lateral-thinking as usual!
    •  
      CommentAuthorSteamyTea
    • CommentTimeJul 11th 2013
     
    Posted By: fostertomST as controversial lateral-thinking as usual!
    How you get change :bigsmile:
    • CommentAuthorCWatters
    • CommentTimeJul 11th 2013
     
    Aside: Some parts of England are closer to Belguim than they are to other parts of England. It's funny how the the English Channel is still seen as a barrier to trade. When we lived in Belgium we had a great problem getting British companies to ship stuff to us. In one case was easier to get the item from Australia!

    Although consumers have the right to buy from anywhere in the EU, sellers aren't obliged to sell to everywhere in the EU. It appeared that companies in the UK frequently only had the distribution rights for the UK, whereas companies the other side of the channel tended to have had the distribution rights for Europe (excluding the UK). I've no idea if that's legal but it's certainly the impression we got.
    •  
      CommentAuthorfostertom
    • CommentTimeJul 11th 2013 edited
     
    Posted By: TimSmallI found in my informal test (single sample, side-by-side same building - we switched suppliers part way through due to short stock) that 18mm Smartply was as airtight as 18mm Norbord Sterlingboard, and that both had good airtightness (towards the top of the experimental range in the University of Leuven study).
    How did you test, and how did you calibrate to get actual figures i.e. 'top end of Leuven'?

    If true, makes Smartply a remarkably useful product - high(ish) airtightness plus low(ish) vapour resistance (much lower than 'generic' OSB3) - and as untoxic, formaldehyde-wise, as natural timber - and almost home-grown. A real alternative to expensive woodfibre sheathing.

    Viking House also confirms v gd measured whole-house airtightness using 18 T&G OSB3, joints mastic'd. My method has been 9 or 11 square edged OSB3 bubble glued and screwed to continuous support, all edges. In a way even more durably gap-filling, but maybe less airtight in that thickness. However I couple it with blown-in Warmcel between the studs, which has fair airtightness itself. So I think I get airtightness robustly in-depth, especially free from the slow-leak pinhole/hairline faults inevitable with tapes/membranes, which WUFI identifies as disastrous condensation-wise (strangely, bigger leaks are no prob, condensation-wise, because the air channel gets warmed above dew point).

    All contrary to conventional wisdom about OSB airtightness (and about 'breathability' too). Of course it's got to be kept dry, otherwise Weetabix and destruction of all attributes!
    • CommentAuthorTimSmall
    • CommentTimeJul 11th 2013
     
    Posted By: fostertomHow did you test, and how did you calibrate to get actual figures i.e. 'top end of Leuven'?


    I put the building under (~250 pa if I remember correctly) negative pressure (measured the pressure with a slightly iffy micromanometer - but good enough for ball park). I used some decorator's acrylic to seal a square of clear polythene onto the surface of both boards, and timed how long it took them to 'blow up'.

    I then did a back-of-envelope calc, and took at look at the U Leuven numbers (which were for a thinner OSB I think - 14mm?), and reckoned they were both roughly equiv to the best results from Leuven (which spanned about a factor of 10x if I remember correctly between the best and the worse results - I'd guess my results had an error factor of circa 3).

    So, not massively brilliant methodology, but at the time I satisfied myself that I didn't need to try and seal the face of the board with anything.
    • CommentAuthorSprocket
    • CommentTimeJul 12th 2013 edited
     
    > So, not massively brilliant methodology,

    Not daft though. I'm pretty impressed.
    I've not detected any pseudoscience yet. Awareness of the weaknesses looks pretty good too.
    So far you could pass for yer actual scientist!
    (well, to me anyway)

    You sure you didn't wave any crystals about or blindly believe some PR tripe from products on that internet?

    Blimey though... 250 Pa... lucky you didn't blow (suck?) the windows in. The standard 50Pa air tightness test is sometimes enough to pop taped joints in membranes.
    • CommentAuthorEd Davies
    • CommentTimeJul 12th 2013
     
    Posted By: SprocketThe standard 50Pa air tightness test is sometimes enough to pop taped joints in membranes.
    To put it in context, 50 Pa is about the pressure difference between the ground floor floor and the first floor ceiling. It's the dynamic pressure you get from 9 m/s wind (force 5, fresh breeze). 250 Pa corresponds to 20 m/s (force 8, fresh gale). If your house can't stand that you really want to know earlier rather than later.
    • CommentAuthorSprocket
    • CommentTimeJul 12th 2013
     
    > 250 Pa corresponds to 20 m/s (force 8, fresh gale).

    Blimey. That makes me think...

    Our rubble walls next layer in before internal insulation was a heavy Solitex membrane intended to stop wind coming through. It had a blue fabric finish and looked fine in principle but as we finished working with it we realised that the Tescon tape (as recommended) did not bond it anything like as well as with the internal membranes. Hearing that this layer could see something like 250 Pa (and after seeing effect of 50Pa on internal membranes before internal boards fitted) is quite alarming :-/

    I suppose, thinking about it... 250Pa is 250 N/m2 and 250N is not much - only the downward force from 25Kg
    If that could suck your windows in then those windows would have to be pretty poorly made :-)
    •  
      CommentAuthordjh
    • CommentTimeJul 12th 2013
     
    Posted By: SprocketIf that could suck your windows in then those windows would have to be pretty poorly made :-)

    More likely poorly installed. I have heard of windows in a tall building installed using small screws. One popped and after the engineer did some calcs, the screws were replaced with M14 bolts.
    • CommentAuthorEd Davies
    • CommentTimeJul 12th 2013
     
    Posted By: SprocketBlimey. That makes me think...
    Yep, that's one reason why it would be fun to do some airtightness testing on 5 year old houses, rather than just a week after construction and before the first windy winter.

    Beaufort force 11 (strong gale, just short of hurricane) could be around 30 m/s. ½ρv² = 0.5 * 1.2 * 900 = 540 Pa. That's the pressure increase on the upwind side and the decrease on the downwind side - open a door or window or something on the downwind side so the inside of the house equalizes with that and the pressure difference across the upwind side becomes 1080 Pa. And that's assuming nice smooth air, not the buffeting pressure caused by gusting.
    •  
      CommentAuthorfostertom
    • CommentTimeJul 12th 2013
     
    Posted By: Ed Davies50 Pa is about the pressure difference between the ground floor floor and the first floor ceiling. It's the dynamic pressure you get from 9 m/s wind
    Surely Ed, that buoyancy effect is too great by a factor of 10?
    • CommentAuthorskyewright
    • CommentTimeJul 12th 2013 edited
     
    Posted By: Ed DaviesThat's the pressure increase on the upwind side and the decrease on the downwind side - open a door or window or something on the downwind side so the inside of the house equalizes with that and the pressure difference across the upwind side becomes 1080 Pa. And that's assuming nice smooth air, not the buffeting pressure caused by gusting.

    On a breezy (& gusty) day in Broadford a few years ago I opened the driver's side car door, heard a pop & felt something fly past. What I'd felt was some of the granules that were all that was left of the rear passenger window which had shattered in response to the sudden change in pressure distribution. :shocked:
    I try to be very careful about opening doors (both car & house) gently on windy days now...
    •  
      CommentAuthorfostertom
    • CommentTimeJul 12th 2013 edited
     
    Amazingly, Fraunhoffer's (WUFI) tests have shown that constant, weak buoyancy completely dominates actual airchange effects, long-term; breezes/winds/gales they recommend to simply ignore, because intermittent - and also reversible.
    (However their perspective is mainly moisture effects - heat loss effects prob a bit more affected by wind - but nothing like you'd imagine).

    Means that exposed windy sites have negligible effect on actual air change, long-term!

    The stack-effect height's effect on that buoyancy is very strong - so a 3-storey building has pro-rata much higher actual airchange, than a 1-storey, for same standard of airtighting in construction. Even a bungalow whose stack-effect height is up to ridge height, fares worse than a flat-roof bungalow, or a bungalow with airtight ceiling. Flats off a stairwell - depends on how effective the entrance/lobby doors are at airtight compartmentation.

    Am currently dealing with a 2-storey maisonette above shop, with front door at street level - has stack-effect height 3-storeys plus up to ridge!

    Anyway, typical ach performance figures measured at say 50Pa, i.e. 0.6ach @ 50Pa being v gd, are just for airtightness comparison. Doesn't mean that actual long-run airchange is anywhere near that figure, because constant stack-effect buoyancy is much weaker than that.
    • CommentAuthorEd Davies
    • CommentTimeJul 12th 2013
     
    Posted By: fostertomSurely Ed, that buoyancy effect is too great by a factor of 10?
    Take a 1 m² horizontal-area column up through the house. 2.4 metres per storey so 4.8 metres tall. The density of air is about 1.2 kg/m³ so the column has a mass of 5.76 kg. Force of gravity is 9.81 N/kg so the weight of the column is 56.5056 N so the pressure at the bottom is 56.5056 Pa greater than that at the top.

    Note, this isn't buoyancy (due to different temperature or humidity) but simple pressure difference.

    Posted By: fostertomAmazingly, Fraunhoffer's (WUFI) tests have shown that constant, weak buoyancy completely dominates actual airchange effects, long-term; breezes/winds/gales they recommend to simply ignore, because intermittent - and also reversible.
    Yeah, but is unsticking tape reversible?
    •  
      CommentAuthorfostertom
    • CommentTimeJul 12th 2013 edited
     
    Too right - it's endless reversal that yanks and works flexible-material seams apart and fatigues adhesives, when steady pressure and/or rigid materials wouldn't. So don't use tapes and membranes!

    Posted By: Ed DaviesNote, this isn't buoyancy (due to different temperature or humidity) but simple pressure difference.
    Ah I misunderstood - so not talking here of pressure that wd drive air change, inside to out. You got me worried, just when I thought I'd got straight the scale of actual airchange and forces driving same!

    Because I got a shock when I saw in WUFI, to enter Air Exchange Rate, as default, 2 alternatives - standard construction 0.2ach; airtight construction 0.1ach. These were so much smaller than I'd thought - maybe it meant something else - but it's right apparently.

    I was so fixated on 'is it 0.6ach (I wish) or more like 1.5ach (with these slapdash chippies)' that I've been using such figures in home-made heat-loss spreadsheet - forgetting they're @ 50Pa - which it's nothing like, most of the time.
    • CommentAuthorsune
    • CommentTimeJul 13th 2013
     
    Hi all - thanks for the ideas and comments.

    If all is equal then I would rather support UK businesses and help to develop the UK timber industry at the same time. For example the struc. eng had specified C24 for floor joists when C16 would have been, and are, perfectly adequate. So I have changed to C16 and we are now able to source these from the UK. The rest of the wood is from the UK, the floor boards are from just down the road - well half an hour, etc.

    It looks like osb is on the cards - just got to double check a few details as there seem to be quite a few different figures for vapour permeability knocking about for osb3.
    Sterlingboards figures seem a little confusing.

    They say:

    The water vapour resistance factor (μ) of OSB, as given in BS EN 13986 : 2004, should be either taken as
    the design value given in BS EN 12524 : 2000 [30 (wet cup), 50 (dry cup)] ***so this agrees with what we found out so far

    ....or determined in accordance with
    BS EN ISO 12572 : 2001. Such values may be used in any interstitial condensation calculations to BS 5250 :
    2002. Experimental values determined in accordance with BS EN ISO 12572 : 2001 (wet cup) for Sterling OSB/3
    are given in Table 1.

    Table 1 Water resistance factor (μ)
    Panel thickness (mm) Water resistance factor (μ)
    9mm 219
    15mm 147
    23mm 107

    So the experimental factors would appear to be very different.

    Make any sense to anyone?

    : )

    Sune
    •  
      CommentAuthorfostertom
    • CommentTimeJul 14th 2013
     
    Oh blimey so that [30 (wet cup), 50 (dry cup)] in Smartply data sheet may be just parroted from suspect generic figure in BS EN 13986 : 2004. Will have to ring em up.
    •  
      CommentAuthordjh
    • CommentTimeJul 15th 2013
     
    Posted By: fostertomMeans that exposed windy sites have negligible effect on actual air change, long-term!

    I don't think it does. If the wind blows from the west and changes the air once, then blows from the east and changes the air again, the result is two changes of air not none! Lovely and fresh and freezing cold.

    Granted you may be able to net out moisture flows to some degree, but not air changes.
    •  
      CommentAuthorfostertom
    • CommentTimeJul 15th 2013
     
    You're at least partly right djh - this insight from Fraunhofer is predominantly about moisture, which indeed nets out; whereas any airflow direction causes heat loss and isn't netted. However, the bit about the 24/7 nature of stack effect outweighing the intermittency of wind, still holds.
    • CommentAuthorskyewright
    • CommentTimeJul 16th 2013
     
    Posted By: fostertomwhereas any airflow direction causes heat loss and isn't netted. However, the bit about the 24/7 nature of stack effect outweighing the intermittency of wind, still holds.

    Wind is more intermittent in some places that others.
    It seems reasonable to guess that the relevance of wind will also vary with the exposure of the property? A terrace in London & a detached property on an exposed hillside or coastline are very different things surely?
   