Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorhairydude
    • CommentTimeOct 15th 2013
     
    Hi All,

    After various planning and mortgage (dont talk to me about banks!) issues, our self-build is moving forward apace and I'm looking for some collective wisdom re MVHR systems / costs.

    Our house is well-insulated (although not PH levels) around 270m2 FA and I've been quoted £5.5K + VAT supply only for a Sentinel Kinetic Plus system (2 MVHR units, controllers and ductwork (uninsulated at this stage). Installation / commissioning quoted at a further £3K + VAT.

    Can anyone who has installed or is considering this system comment on these costs - the company is very helpful but the price seemed a bit steamy - my other option is to self-install and get it commissioned for £300 so comments on viability of this would be welcomed also. (Suggestions on alternative system which are worth a look would also be welcomed).

    Thanks in advance folks, I'm off to get my wellies on to get the foundations in today:bigsmile:
    • CommentAuthorPugliese
    • CommentTimeOct 15th 2013
     
    To get some meaningful comments, suggest you post the plan showing how many rooms, size of duct runs, where the duct runs will be. Has the house been designed to accommodate ducting? This will all have a bearing on the costs and ease for a self install.
    What I did find was that of the half a dozen quotes I got, the cheaper ones just concentrated on as short a runs as possible and would have led to an inferior ventilation system,whereas the more expensive ones concentrated on getting the airflows right - the old adage - you get what you pay for
    • CommentAuthorhairydude
    • CommentTimeOct 15th 2013
     
    thanks, I'll try to post some plans later. the house has been designed to accommodate ducts but there will be some long runs to get around some vaulted ceilings, etc and to ensure the correct flow to defeat rooms.

    sounds like you're saying those costs don't seem ridiculous?
  1.  
    I'm not familiar with the prices of this model so can't comment on that, but the installation costs seem rather high.

    You seem to be indicating that all the materials are included in the supply price of £5,500 so you are looking at £2,700 for labour only to install the system. Assuming a labour cost of £60 an hour that's 50 hours work, 6 days or so.

    My experience of installing my own MVHR system was that it certainly didn't take that long but I didn't do it all in one hit so couldn't give you an accurate time, but all together probably 3 days or so.

    I would have thought that an experienced fitter should be able to do it inside 2 days.

    Once you are following a professionally designed duct layout for your house then I found that the actual installation work very straightforward.

    Whatever you decide I would advise to install your duct early in the build before plumbers and electricians come on site and start putting obstacles in the intended path of the ducts, then seal up all the ends so you don't get any dust into them and leave it like that and commission the system when all building work is complete. We commissioned our system the day before we moved in. If the system has been designed well then commissioning should be a fairly simple task, ours took less than an hour and the cost was approx. £120 including travel time.
    • CommentAuthorsnyggapa
    • CommentTimeOct 15th 2013
     
    the guys did my sentinel MVHR - they did design, supply, "installation training" and certification as myself & my builder installed it. they also will install if required. http://www.thebuiltenvironment.co.uk/

    I think you can send them your plans, may be worth a second opinion (assuming it's not them you are already looking at :)

    -Steve

    P.S. make sure you get it vat zero rated if this is a new build! A copy of the planning permission should be enough for the supplier to 0 rate the works.
    • CommentAuthorPeterW
    • CommentTimeOct 15th 2013 edited
     
    Any idea why they want to spec two MHRV units..? Are they both under a single controller..?

    I looked at a few, and to be honest a lot of what they offer now in components are just standard items that are repurposed. For example, Airflows Zero Leakage ducting is pretty much identical to this http://www.drainageonline.co.uk/Ducting.htm if you look at it. Most of this stuff is contract moulded so copies and similar products will be very common as manufacturers want to get the most out of tooling prices and production runs.

    I'd be interested to see what the thoughts on using some of the smaller (read cheaper..) units is in parallel as this seems to be where they have added cost in the past in significant jumps in pricing. Also, have they given a breakdown on what is the unit, what is controller costs etc..?

    Cheers

    Peter
    • CommentAuthorsnyggapa
    • CommentTimeOct 15th 2013
     
    yes, I must confess to have been staggered by the costs of ducting.

    what looked like simple injection moulded plastic fittings which should have cost 1p to make being sold for £28 each - my experience was that the ducting cost as much as the unit - I'm not sure if that is typical but our unit cost about £1,000 and the ducting the same again. (88m2 floor plan, 18 months ago)
    • CommentAuthorPeterW
    • CommentTimeOct 15th 2013
     
    It does worry me when ducting bends and tees are around £6-8 each, exhaust valves at less than £10, and 50m of duct is £120 that suppliers can soon get north of £1000 with cheap and cheerful plastic bits. Of all the exhaust valves I've seen, I think only 1 hasn't been based upon a threaded bolt in the centre of the fitting. The cost difference has been huge - from £6 for no name, to £11 for Lindab and up to £30 from a 'green eco store' for what was essentially a badge on a no badge unit !

    Cost of being green, or just a market that's finding its watermark for pricing..? And how ethical is it to take a suppliers drawings and 'DIY' the system from the web for a third of the price..?

    Cheers

    Peter
    • CommentAuthorPugliese
    • CommentTimeOct 15th 2013 edited
     
    Posted By: hairydude

    sounds like you're saying those costs don't seem ridiculous?


    No, my gut feeling is that it is expensive but without knowing more about the install, it is difficult to say it is for definite.

    Mine is a 200sqm house so one unit was sufficient but my unit, ducting and paying for the commissioning was £3.5k. I did the instal along with the builder and it took less than a week but we had easijoists and did a lot of planning
    • CommentAuthorborpin
    • CommentTimeOct 15th 2013
     
    Bit more than I paid for similar size building. I used the flexible (semi rigid) ducting so easily installed myself. I over specced the unit so it usually runs at less than 50% capacity - Helios EC 500 pro (IIRC). Just ordered a flow meter to set it up myself (not balanced yet and in Scotland you can do it yourself) but it seems to work pretty well 'as is'. No noticeable noise.
    • CommentAuthornbwilding
    • CommentTimeOct 15th 2013
     
    We paid £5.3k+VAT last year for a Vent-Axia Sentinel Kinetic Plus B, plastic ducting (insulated), installation and commissioning in our 180m^2 1980s house. Took 3 guys about 3 days to install and commission. No noticeable noise in the bedrooms, though you can hear it a bit in the kitchen. We runs it at about 20%.
    • CommentAuthorhairydude
    • CommentTimeOct 16th 2013
     
    Thanks everyone,

    Our house design is fairly long and linear (I know - not the most thermally or economically efficient shape but dictated by plot shape and orientation!) resulting in fairly long duct runs - Google gives me indicative prices for the MVHR units and controller so from the comments above I think it is the ducting costs which are surprising me (i thought to myself "basic plastic fittings - how expensive can they be?").

    2 MVHR units have been spec'd because of the duct lengths (allows the duct sectional size to be kept manageable to fit with pre-planned service voids inboard of VCL/airtightness layer). I understand that this also means that units are each working at low capacity which is desirable from a noise perspective.

    I'm more or less certain I'll go down the self-install route with some assistance from the trades already on site (at these install costs I may give up my day job and do this full-time!).
    • CommentAuthorfinny
    • CommentTimeOct 16th 2013
     
    Unless you have had a site visit from your quoting installer, they will assume worst case scenario, this might add 15 or 20% to the quote. Getting someone in to quote might help. There aren't that many qualified installers out there so travel, accomodation etc.for a team soon adds up too. Having installed a few systems myself (genvex units lindab steel ducting) , they are invariably more complex to install well than envisaged on paper. I would advise not giving up the day job just yet :cry: oh and always 160 mm ducting, T ing to 125mm and attenuators extract and supply, every time.
    • CommentAuthoradi
    • CommentTimeOct 20th 2013
     
    Ducting cost me about £1500(inc vat) for the property I'm renovating. The ducting was directly from lindab and it was there safe system (worth the extra money as it makes getting an air tight duct system easy).

    Floor area is approximately 145m2 (using PHPP measuring standard) and system consisted of 5 supply vents and 3 extract vents along with several silencers. Ducting size was 160mm , 125mm and 100mm. I designed the system myself and I'm relatively happy so far. I also installed the system with my father helping and it probably took us about 2 days in total.

    Only item I couldn't buy from lindab was an extract air valve with filter which i wanted for the Kitchen.
  2.  
    Any reason not to use pvc drainage pipes ? OK it's pvc ' the devils sputum' according to any self respecting yogurt weaver , but it's going to be reusable at end of life same as metal.
    • CommentAuthoradi
    • CommentTimeOct 20th 2013
     
    I would assume the cost saving isn't worth the hassle as there would be a far smaller range of fittings and sizes available. Also you would have to deal with adapting from PVC to the sound attenuators and then back to PVC, along with adapting from PVC pipe to the supply and extract valves.

    I also think you might struggle using drainage pipe unless you have very large void/area to run pipes as even simple things like bends are available in a much tighter bend radius for proper duct systems.

    I spent £1500 on lindab ducts but looking at the cost of PVC drainage I doubt you would save more than £500 as you still need to buy the sound attenuators and air valves. So is £500 worth saving worth all the issues of trying to mate too different systems together and all the extra time it might take along with the chances that it might not be possible!

    I'm all for saving money but that's why I chose a quality duct system and installed it myself as this was cheaper than getting certain lesser quality systems installed by professionals!
    • CommentAuthorborpin
    • CommentTimeOct 20th 2013
     
    Used Lindab guttering - quality system even if the fitting of the gullies is slightly odd :)
    • CommentAuthorPeterW
    • CommentTimeOct 21st 2013
     
    On ducting... Anyone know if the 'ban' on flexible ducting for SAP Q includes short lengths of the convoluted aluminium tube to allow for slight offsets..?

    Cheers

    Peter
    • CommentAuthorDarylP
    • CommentTimeOct 22nd 2013
     
    App. Q currently allows for 'rigid' or 'semi-rigid' as far as I know. So, NO convoluted of any kind.
    The pressure drop across that stuff is significant compared to the smooth-walled....

    Good luck:smile:
  3.  
    The twin wall 'semi-rigid' ducting seems to be a no-brainer. Airflow market it as https://www.airflow.com/zeroleakageducting and http://www.allergyplus.co.uk/ also sell it.

    I'm trying to work out the difference between the ducting they sell and the stuff from http://www.drainageonline.co.uk/Ducting.htm

    The airflow ducting is 75/63 outer inner and that size doesn't seem easy to find elsewhere
  4.  
    Simon,

    I think the difference is 'love'! By that I mean cable ducting exists and even their manifolds, but you need time, care, attention and patience: you have to make it with love (as the Italians say). I feel sure a good DIYer could use the alternatives you mention but, as was pointed out, you are going to face challenges at every junction and you may need some bits fabricated - I will find out myself next year as getting the 'proper' stuff here is impossible so i have bought the adjustable vents, attenuators etc and will 'find a way' to make it work - fortunately over here bespoke fabrication is still normal, easily accessible and labour rates are cheap. :wink:
  5.  
    My point was actually that the 75/63 sold as MVHR duct should be available elsewhere cutting out a middleman and saving a chunk of cost.
  6.  
    simon , any point using 63/50 at a 3 to 2 ratio or would the cost benefit be lost ?
    • CommentAuthorPeterW
    • CommentTimeOct 22nd 2013 edited
     
    Simon - think I found that stuff as well, the bigger issue is getting them to sell you just the terminals without a whacking premium !

    I also found converters to do 125mm valves to 63mm pipe - may have to see if they would work out more economical. The plenum is easy to build as its just a box although I did consider sticking 4 of the hoses as tight as possible into the end of a 160mm duct and foaming them in !

    Cheers

    Peter
    • CommentAuthorborpin
    • CommentTimeOct 27th 2013
     
    There are a number of threads on A+ and I would take care with them.
    • CommentAuthorRobinB
    • CommentTimeOct 28th 2013
     
    Maybe worth pricing up a system at http://www.dealec.co.uk/acatalog/vent_axia_sentinel_kinetic_e.html

    Have bought stuff there in the past including recirulating cooker hood. Found them good but no other connection.
  7.  
    A potential issue with using alternatives such as pvc instead of purpose made ducting is that you may encourage dust build up in your extract lines due to static build up. Internal supply lines would be less affected as the air going through them has been filtered.