Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthordaserra
    • CommentTimeMar 7th 2014
     
    You put it so elegantly :bigsmile:
    •  
      CommentAuthordjh
    • CommentTimeMar 8th 2014
     
    Indeed, but elegance doesn't change the facts. Boundary layer effects are nowhere near as important as the effects I described.
  1.  
    So what evidence do you have for that statement, djh? What meaning do you attach to 'importance' ? Heat loss? Comfort? Building deterioration? Moisture penetration and air infiltration should be eliminated by good design detailing, and are unrelated to thermal mass. The thread topic raised was about thermal mass effects. That inter-relates with wind chill (bigger mass, lower cooling rate).
    •  
      CommentAuthordjh
    • CommentTimeMar 9th 2014
     
    Remember that we are discussing your assertion that "That's why our forebears chose sheltered locations for their homes", not modern building practice. Drafts have been a major problem even until now, but in previous times were even more significant.
    • CommentAuthordickster
    • CommentTimeMar 10th 2014
     
    Steamy,

    sunny Hampshire.
    •  
      CommentAuthorSteamyTea
    • CommentTimeMar 10th 2014
     
    Coastal or no?
    • CommentAuthorMikel
    • CommentTimeMar 28th 2014
     
    We are taking part in a DECC funded trial of control systems for heat pumps. The company conducting the trial for our system is Passiv Systems Ltd.

    I have their agreement to post their graph showing the temperature changes in our house whilst we were away for six days last week.

    In order to understand this graph, some background information:

    Our house is a hybrid house, part timber frame built about 1984 and part modern block built 2006/7. Passiv Systems have installed temperature sensors in the rooms:

    Zone 1 (A): Lounge (blue line) orientation NW, windows on NE, NW and SW, modern block
    Sensor 1 :Old hall (blue line) interior, timber frame
    Sensor 2 : New Hall (lime line)interior, modern block
    Sensor 3 : Master bedroom (pink line) small window on NE, main window SW timber frame
    Sensor 4: Guest bedroom (light blue line) window on NW timber frame

    Apologies for the two different blue lines, which make it a bit harder to separate.

    It does look like the modern block part loses heat more slowly and heats up more slowly and the timber frame part responds more rapidly to heating.


    We are just over two months into this trial and have only been running the new control system since the end of February. So it is far too early to draw any definitive conclusions. However, I have found it easy dealing with Passiv Systems and their staff are very approachable and responsive. They will be looking for further triallists next year, so I will be happy to provide feedback to anyone thinking of volunteering.
    •  
      CommentAuthorSteamyTea
    • CommentTimeMar 28th 2014
     
    Bit hard to tell, and not got the time to look at the solar data for that period (we can sit in a cafe and do that).
    may be worth comparing all the dimensions and orientations of the rooms and the accuracy of the measuring equipment. If they are using the Dallas stuff it is only good to within a degree, though that should not affect the response time.

    Is the very lowest line the ambient temp and the higher two lines something to do with the HP?
    • CommentAuthorMikel
    • CommentTimeMar 28th 2014
     
    I'll have the solar data from the PV, it is quite a good proxy. Sunday Mar 23rd PV peaked at over 3.3 kW and generated over 19 kWh for our 3.84 kW array. Best day for the year so far for PV.

    Yes, the grey line is the external temp taken from the local Met Office (I think), there isn't an outside sensor. The bottom yellow blips are the heat pump cycling and the top two lines are the measured flow and return temps for the heat pump. The temp sensors record to two decimal places, what they are accurate to is a different question.
  2.  
    Posted By: funcrusherA point almost universally ignored is the critical factor of radiation. Mammals are far more sensitive to radiant heat than to air temperature

    I agree radiant heat is not considered as often as it ought to be, and that we have an obsession with air temperature.
    Why do you say far more sensitive? My understanding is that our sensation of thermal comfort comes approximately 50% from each of these two.
    Peter
    • CommentAuthorArchmoco
    • CommentTimeApr 1st 2014
     
    My view would be in a traditional blockwork house there is too much thermal mass. I've just finished a build and went with a 300mm blockwork construction with full fill insulation, but I also insulated the outside of the building with a batten and sheeted exterior finish. Inside I dry lined all the external walls. The theory being that I would still have the interior blockwork walls for the thermal mass.

    The living spaces are all open plan with large quantities of South and west facing triple glazing and the passive solar works great. During the winter with the lower sun these spaces do not require any heating during the day, during the evening the spaces would rarely drop lower than 19 degrees. During the daytime with a good sunny day the space would heat up to 25 degrees, with the rooms 23-24 during the evening
    • CommentAuthorEd Davies
    • CommentTimeApr 1st 2014
     
    Posted By: Peter ClarkWhy do you say far more sensitive? My understanding is that our sensation of thermal comfort comes approximately 50% from each of these two.
    It's my understanding, too. Thought there was a chart showing this in the Green Building Bible but couldn't find it in my copy (3rd edition) or in Sue Roaf's Ecohouse 2 which is another likely source for this sort of thing.

    Still Wikipedia seems to think so, too:

    https://en.wikipedia.org/wiki/Operative_temperature

    It is also acceptable to approximate this relationship for occupants engaged in near sedentary physical activity (with metabolic rates between 1.0 met and 1.3 met), not in direct sunlight, and not exposed to air velocities greater than 0.20 m/s (40 fpm). [6]

    to = (ta + tmr) / 2
    Where to is the operative temperature, ta the air temperature and tmr the mean radiant temperature.

    Previous discussion: http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=11659
    • CommentAuthorEd Davies
    • CommentTimeApr 1st 2014
     
    Posted By: ArchmocoMy view would be in a traditional blockwork house there is too much thermal mass.
    What makes you take that view?

    If you only want to heat the house for a few hours in the evening then you could have too much thermal mass but is there any other reason?
    • CommentAuthortony
    • CommentTimeApr 2nd 2014
     
    Too much thermal mass = thermal comfort, very slow temperature changes, maximum ability to store solar gains......
    •  
      CommentAuthorSteamyTea
    • CommentTimeApr 28th 2014 edited
     
    Just spent the last week logging some temperatures in my thermal mass experiment.
    It is two identical polystyrene boxes with two identical double glazed lids (fish boxes and small fridge doors). One has two bricks in it, the other does not. I covered the bricks in tin foil to reduce the amount of direct sunlight hitting them (test 3 may be without tin foil)
    Have stuck them in the garden were they can catch the sun until 1PM. There is a bit of a difference as the sun goes into shadow on one box first.
    I have since re-setup to correct some inconsistencies (added to fake bricks to the non thermal mass box so that the volumes are the same) and moved the temperature sensors to the same position in each box. Not sure how much difference it will make but last Saturday I dislodged a probe and got very high readings (have taken that day out of the data).
    The boxes are .55m x .32m x .115 m, the window aperture .55m by .32m. The bricks are .21m x .08m x .1m and .2m x .08m .1m and 3.23kg and 3.83kg respectively.
    I also put a temp sensor in my shed, and one on the shed wall (have since put these in a better position too).

    It is worth pointing out the the 1Wire sensors are really only accurate to 0.5°C and often give misreadings (which I filter out).
    I have averaged the data into half hour blocks, and charted this over the last few days, I have also added some solar and temperature data from a local weather station. This makes for a cluttered chart but shows that my data correlated well with someone else's.

    Below are the basic average results:

    Temp,Box,Box with ,Ambient,Shed
    Mean Temp /°C,12.2,12.3,10.0,12.2
    Standard Deviation /°C,6.4,4.2,2.2,2.9
    Count,2478,2472,2465,2478
    Standard Error/ °C,0.1,0.1,0.0,0.1
    T Test (1st 6 days),0.36

    And as a couple of charts, two as time series and the other a correlation.
    There is more analysis to do, but seems with this set up that it limits the maximum temp, but makes little difference to the overall temperature over a day.
    • CommentAuthortony
    • CommentTimeApr 28th 2014
     
    OK then can I conclude that living in a high thermal mass box will be more comfortable and not get as cold or as hot as a box with no mass would?
    •  
      CommentAuthorSteamyTea
    • CommentTimeApr 28th 2014 edited
     
    I wouldn't, as the variations is not so different, especially when the temperatures are within normal house ranges i.e not 40°C plus or below 15°C (this is a problem with small scale models).
    I will try and filter out the extremes and see what we are left with. But if you look at the correlation chart there is little difference at the 'normal' temps.

    As I said, I do need to do some more analysis (night times, daytimes, shaded, non shaded, radiation levels...).
    This is just a simple analysis and this not really looking at typical data (it was sunny in Cornwall!!)
  3.  
    I would think that covering the thermal mass with tin foil would act directly against they way its intended to be used. To absorbe sunlight and ambiante heat, and then release heat during the night.
    •  
      CommentAuthorSteamyTea
    • CommentTimeApr 28th 2014
     
    I did that so I get an initial baseline. There are more tests to be done, one will be with only one brick (the thermal mass to air ration is huge at the moment), another will be with a smaller window aperture, another will be with uncovered bricks, another with gravel instead of bricks.
    It is way too easy to jump to a quick conclusion without having data. I am trying to provide data and a test methodology that gives meaningful results (within the limits of what I can do).
    • CommentAuthorEd Davies
    • CommentTimeApr 28th 2014
     
    The “RC” time constant of a little box like this will be much shorter than that of a house-sized thing. You need to move to an asteroid with a rotation period of, I'm guessing, an hour or less to scale things properly. Maybe just put it on the outside of the ISS with 50 minute days and 45 minute nights would work and be less hassle.
    •  
      CommentAuthorSteamyTea
    • CommentTimeApr 28th 2014
     
    Posted By: Ed DaviesMaybe just put it on the outside of the ISS with 50 minute days and 45 minute nights would work and be less hassle.
    Or get people with high and low mass houses to supply temperature data. Get enough places and the means will be, umm, meaningful. :wink:
  4.  
    Ed hits the nail on the head,a point that has been raised before about trying to simulate real life conditions with small scale models.

    One could also look through the 60+ years of academic research that has been carried out on the usefulness of thermal mass in building design :wink:
    •  
      CommentAuthorSteamyTea
    • CommentTimeApr 28th 2014
     
    Posted By: bot de pailleOne could also look through the 60+ years of academic research that has been carried out on the usefulness of thermal mass in building design
    Show me the UK research about the UK climate, I really want to see it.
  5.  
    Posted By: SteamyTea
    Posted By: bot de pailleOne could also look through the 60+ years of academic research that has been carried out on the usefulness of thermal mass in building design
    Show me the UK research about the UK climate, I really want to see it.



    Type "research paper thermal mass building britain" into Google and you will find lots of research papers on the benefts of using thermal mass in the UK climate!
  6.  
    http://etheses.nottingham.ac.uk/1872/2/PhD_Thesis_-_Lucelia_Taranto_Rodrigues_Single_Side.pdf
  7.  
    "New evidence indicates thermal mass solutions, such as Insulating Concrete Form (ICF) walls, have a more significant effect on indoor temperatures and comfort conditions than is commonly predicted. It has also been found that the concrete core of the ICF wall is not as thermally isolated as might be conventionally expected. This is an important phenomenon to investigate as it suggests standard calculations and building design modelling software is based on inaccurate data and buildings may be over or under designed as a result. Hence, the need exists to investigate the physical behaviour of high thermal mass and derive lessons from new datasets to create a validated evidence base of robust information on low energy, high mass structures."

    http://www.lboro.ac.uk/departments/civil-building/research/projects/developingan.html
    • CommentAuthorbella
    • CommentTimeApr 29th 2014
     
    Posted By: tonyOK then can I conclude that living in a high thermal mass box will be more comfortable and not get as cold or as hot as a box with no mass would?

    To a simple biologist it does look from the second and third plots as if you have demostrated rather nicely the difference between light-weight (1) and heavy-weight (2) buildings ie that 1 heats up rather faster and to a higher level that 2. And given your experiement why wouldn't you.

    It may not be quite right to assume the relation between the temperatures in the two boxes is linear. Could you modify the third plot slightly by giving the x and y axes equal scales? The eye is good at detecting non-linear relationships but has trouble adjusting for scaling differences.
    •  
      CommentAuthorSteamyTea
    • CommentTimeApr 29th 2014 edited
     
    Posted By: bellaThe eye is good at detecting non-linear relationships but has trouble adjusting for scaling differences.
    Do you mean make the y-axis go to 55°C like the x-axis.

    Initially I thought that the relationship would be exponential or logarithmic, but then realised that they are two separate systems and not one heating the other (which would hit a return limit).

    When I used the temperature ranges from the normal box to work out the mean corresponding temperatures in the box with mass, the trend line then follows a power law with very good correlation.
    • CommentAuthorbella
    • CommentTimeApr 30th 2014
     
    Posted By: SteamyTeaDo you mean make the y-axis go to 55°C like the x-axis.

    Not quite, something simpler - I was suggesting that your third graph be modified by plotting those temperatures using the same intervals (spatially) on each axis so that the eye does not need to correct for the wider intervals along the x axis. I assumed that each point represented a pair of measurements taken at the same time - correct? Does the graph show that the high mass box stays as lower temperatures for the same solar input?

    One would expect the two sets of data to be closely correlated (both boxes exposed to the same powerful stimuli under similar conditions - overnight low temperatures followed by day time sun and high temperatures). Is the question whether from a baseline (early morning lowest temperatures) the rates of temperature change deviate in a useful way? Graph 2 suggests they do, the high mass box moderating the rate of rise and fall. So a high mass building with a low cost heat source (sun on south facing windows or a porch or some other solar collector (or Economy 7 electricity come to that) doesn't need to "dispose" of heat but can retain it for the time when only a higher cost heat source is available? This is sounding obvious - have I missed something?
    •  
      CommentAuthorSteamyTea
    • CommentTimeApr 30th 2014
     
    Posted By: bellaI was suggesting that your third graph be modified by plotting those temperatures using the same intervals (spatially) on each axis
    Ah, see what you mean. Would not make much difference in this case as the line almost follows Y= MX+C.

    Posted By: bellaI assumed that each point represented a pair of measurements taken at the same time - correct?
    Yes, paired datapoints.

    Posted By: bellaOne would expect the two sets of data to be closely correlated
    In my initial test (this one was really to get a baseline and some idea of what is happening), there is a very good correlation. Bit too good, which is always a reason to investigate more.

    Posted By: bellaIs the question whether from a baseline (early morning lowest temperatures) the rates of temperature change deviate in a useful way?
    Yes, and if they do is it real or an illusion (or can you actually use the stored heat)

    Posted By: bellaSo a high mass building with a low cost heat source (sun on south facing windows or a porch or some other solar collector (or Economy 7 electricity come to that) doesn't need to "dispose" of heat but can retain it for the time when only a higher cost heat source is available?
    Yes, that is the idea, but my thinking is that the thermal mass rarely gets hot enough and is often acting as a heat sink, meaning you need extra heating energy (this is for the UK climate, not a mile high at 40°N)

    What I do have to do is try and calculate the lead and lag of each box, and how often the box with mass has a temperature that is greater or lesser than the box without mass. Then, because of the small scale create a coefficient to scale it. Interestingly my shed has a higher mean temperature and a much lower mass to air ratio.
   