			<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82818#Comment_82818</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82818#Comment_82818</guid>
		<pubDate>Fri, 21 May 2010 08:38:21 +0100</pubDate>
		<author>CWatters</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: fostertom</cite><blockquote ><cite >Posted By: CWatters</cite>tin is opaque to IR energy so ALL the heat passing through the thin layer of tin plate must travel through it by conduction</blockquote>Absolutely true - solid metal, unlike just about all other building materials, has no micro-pores (or does it, at the inter-molecular level?) so indeed, all transmission through it is classic conduction. The exception that proves the rule, amongst building materials.</blockquote><br /><br />How about roof slate? Again I'm not suggesting a slate roof doesn't  benifit from a radiant barrier in it somewhere but that appears to be the implication of the "60% is by radiation" argument. (eg a slate roof transports 100% of the heat through the slate itself by conduction so a radiant barrier is usless?). <br /><br />I'm still convinced you need to block all methods of heat transport.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82821#Comment_82821</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82821#Comment_82821</guid>
		<pubDate>Fri, 21 May 2010 08:53:04 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: CWatters</cite>So whats the best insulation to use on the inside of a hot tin roof? One that blocks radiant heat or both radiant and conducted?<br /><br />The point is I don't see how the dominant transport mechanisim in the existing uninsulated structure effects the choice of insulation type being added.</blockquote>Agree. How the heat was transmitted through the thickness of the tin, or any other material, doesn't determine what mix of conduction/convection/radiation is emitted from its under-surface.<br /><br />It could have been a sheet of Onduline (sawdust bound with bitumen, with lots of micro-pores within the wood fibre and maybe the bitumen too) or slate (also full of micro-pores, I'd guess) whose under-surface gets almost equally hot. The tin would have purely conducted, but I'd say that radiation would dominate within the interstices of the Onduline.<br /><br />What mix of conduction/convection/radiation is emitted from the under-surface of either of them, is determined by what happens below it - e.g. is the sheet 'looking at' an airspace, of what thickness, or is it in contact with a substrate. Irrespective of whether it's tin or anything else above.<br /><br /><blockquote ><cite >Posted By: CWatters</cite>that appears to be the implication of the "60% is by radiation" argument. (eg a slate roof transports 100% of the heat through the slate itself by conduction so a radiant barrier is usless?).</blockquote>I'm not saying that at all. I'm talking about the mechanisms of heat transport within the thickness of an insulant (or most other building materials), which make its behaviour different, in real life, from what's conventionally assumed/understood/got from artificially steady-state testing.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82823#Comment_82823</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82823#Comment_82823</guid>
		<pubDate>Fri, 21 May 2010 09:04:26 +0100</pubDate>
		<author>SteamyTea</author>
		<description>
			<![CDATA[Tom<br /><br />I can feel an experiment coming on.  Shall see if I can find some think polystyrene and set it up as it looks like we are in for a few days of sun at long last.<br /><br />A tile with tinfoil on the inside, a tile with just thin insulation and one with the same insulation but with that insulation foiled both sides should do it.  What do we think?]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82825#Comment_82825</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82825#Comment_82825</guid>
		<pubDate>Fri, 21 May 2010 09:53:59 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: SteamyTea</cite>Physicists approximate from their data quite a bit, much of it because of the accuracy of the equipment used</blockquote>That's fine as long as the results so obtained are useful and correspond with reality. In the slide-rule era, concepts and theories had to be pragmatically simplified, eliminating much complexity, in order to be practically calculable. In the number-crunching computer era, that's no longer so necessary - tho there's always further areas of complexity that have to ignored, even by super-computers.<br /><br />The problem comes when those approximations are revealed to be inadequate, when new combinations of materials or new uses place novel emphases on the assumed/glossed-over parts of the theory. As in radiation-blocking insulants, or the opposite, carbon-blacked/radiation-absorbing insulants (aerogel, 'Platinum' EPS). Does the scientific community then promptly review its assumptions and readily correct course? No way - the old assumptions are gospel and challengers are heretics. The scorn and fury of the defence is a sure sign of emotional crutches of routine and security being kicked away, jobs and reputations threatened by new thinking.<br /><br />It's not true that experimenters are careful not to influence results to fit their expectations. For example the outrageously biassed investigation by the hack 'scientists' of NPL into multifoils. By using the very testing methods that CMM (Confed of Multifoil Manufs) was showing as inadequate and misleading, they 'proved' that multifoils don't work, exactly as they expected. As a sop to CMM, they allowed hotbox temps to vary, and still got neg results. But, in studied ignorance of the physical principles and mechanisms that CMM were suggesting, the rate-of-change of said 'variation' was so glacial, that it amounted to steady-state. They didn't check with CMM as to what 'dynamically varying' (i.e. just like real life) should mean, to be relevant. In general, the hotbox is a way of carefully selecting/eliminating parameters so as to produce results that still correspond with the 60yr old slide-rule-era assumptions and approximations of building science, upon which BRE's reputation was built (and then squandered by Mrs T).<br /><br />Most recently, those troublesome experimental anomalies and 'inaccuracies' that had to be approximated or statistic'd out, have been discovered to be due to the fundamental non-deterministic chaotic behaviour of systems, in all areas (except, apparently, building physics) - and behind that the unpredictabilities of quantum behaviour. Everything around us is in perpetual chaotic ferment, even with no apparent perturbative input to set it going. Accepting this, new ways have been developed to understand the semi-predictable nett 'patterns' that emerge from that chaos. That offers exciting new potential to control, manipulate or take advantage of sophisticated kinds of physical behaviour newly revealed, and the development of new physical theories couched on the 'pattern' level (rather that classic Newtonian 'billiard-ball' level), which incorporate and reproduce the results of traditional/approximated theories (like building science's versions of heat-transmission theory) but are equipped to manipulate strange but useful behaviours that have been traditionally eliminated as anomalies.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82826#Comment_82826</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82826#Comment_82826</guid>
		<pubDate>Fri, 21 May 2010 09:56:49 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: SteamyTea</cite>I can feel an experiment coming on</blockquote>Say more - what will that prove?]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82827#Comment_82827</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82827#Comment_82827</guid>
		<pubDate>Fri, 21 May 2010 10:22:05 +0100</pubDate>
		<author>SteamyTea</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: fostertom</cite>results so obtained are useful and correspond with reality</blockquote><br />Case of whose reality really.<br /><br /><blockquote ><cite >Posted By: fostertom</cite>promptly review its assumptions and readily correct course?</blockquote><br />Yes, generally they do, called the peer review process.<br /><br /><blockquote ><cite >Posted By: fostertom</cite>outrageously biassed investigation by the hack 'scientists' of NPL into multifoils</blockquote><br />I don't know these report but would be interested in reading them.<br /><br /><br /><blockquote ><cite >Posted By: fostertom</cite>approximated or statistic'd out</blockquote><br />Very powerful tools as long as everyone is clear exactly what was done and the reasons why.  An example being a typical repeatable train journey, the statistics over many months will say what the mean speed was, it can also tell you what the excepts where.<br /><br /><blockquote ><cite >Posted By: fostertom</cite>potential to control</blockquote><br />This is the area that has really changed, we know have much better control of over things since moving away from the analogue to the digital (price had plummeted as well).  A bi-metallic thermostat is a good example, a cheap one probably had a 5 deg window, an expensive one possibly 0.5, now a cheap microprocessor can measure and control hundreds of temperatures easily to a much finer resolution.  I still wonder why they are not used more.<br /><br /><br />Philosophy of science is an interesting area, not one I really wish to enter, but the basic theories are valid and applied.<br /><br /><br />Well I have put some tests out and I suspect that the order will be Tile the hottest, followed by just tinfoil, insulation(if it is not swamped, this may need investigation) then tin foil with insulation wedged in between.<br />That is the hypothesis, the data will show if it is correct.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82828#Comment_82828</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82828#Comment_82828</guid>
		<pubDate>Fri, 21 May 2010 10:31:39 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Paul in Montreal</cite>test houses have been built which use conventional and multi-foil insulation and their actual energy usage monitored over a period of months or years. If "conventional insulation science" was so far off the mark then the measured figures would be far away from theoretical, yet they're not.</blockquote>AFAIK, the grand-daddy of such 'twin shacks'  tests showed that multifoils worked, and that data was accepted by BBA in their approval of multifoils. That was withdrawn, after pressure to the effect that 'these emprical results count for nothing because hotbox theory says they're impossible (and because it'd put the conventional insulation manufs out of business)'.<br /><br /><blockquote ><cite >Posted By: Paul in Montreal</cite>In my own case, the hot2000 model of my house has been close to measured performance over 5 years now</blockquote>Yes, the power of Intentionality is a wonderful thing! Or maybe it's because Hot2000 (and PHPP which produces similiarly accurate results based on traditional building-physics assumptions) do not actually model laws of physics, right or wrong, but are pragmatic spreadsheets that have been tweaked into reliability, within the range of variables of a typical house, such as yours is, I think.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82835#Comment_82835</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82835#Comment_82835</guid>
		<pubDate>Fri, 21 May 2010 11:24:56 +0100</pubDate>
		<author>CWatters</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: SteamyTea</cite> A tile with tinfoil on the inside, a tile with just thin insulation and one with the same insulation but with that insulation foiled both sides should do it. What do we think?</blockquote><br /><br />Woud be interesting to compare three tiles, one with a layer of foil underneath and the other a layer of newspaper and a control. Repeat with tiles swapped around unless the tiles are similar colour.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82839#Comment_82839</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82839#Comment_82839</guid>
		<pubDate>Fri, 21 May 2010 12:39:23 +0100</pubDate>
		<author>SteamyTea</author>
		<description>
			<![CDATA[Colin<br /><br />Have done that.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82891#Comment_82891</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82891#Comment_82891</guid>
		<pubDate>Sat, 22 May 2010 13:21:45 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[There's been a bunch of speculation and ill-informed rumour-mongering in this thread about how science lags behind reality and ignores new facts that arise. I was finally stung into doing a little digging to show the facts. So I was investigating the history of foam insulation - and I'll come back to that in another message, because it's a longer story - and I came across a paper about multifoils that I couldn't resist.<br /><br />A while ago I dug around and discovered that multifoils are excellent when used for insulation IN VACUUM. They're used on spacecraft and they're used in high-vacuum cryogenic equipment. But their performance drops off as pressure is increased and there's a trade-off so foam insulation is better at atmospheric pressure. Google "multilayer insulation" and perhaps "cryogenic" to find lots of information. But this time I found a paper that makes it clear that DYNAMIC considerations are also fully considered ...<br /><br /><a href="http://accelconf.web.cern.ch/AccelConf/e00/PAPERS/TUP5A13.pdf" target="_self" rel="nofollow">http://accelconf.web.cern.ch/AccelConf/e00/PAPERS/TUP5A13.pdf</a><br /><br />... because the entire measurement technique is based on the dynamic response!<br /><br />I'll paraphrase the method in the hope of making it easier to understand but please read the paper before declaring it's rubbish.<br /><br />The basic idea is that you take a piece of insulation and keep it at a fixed temperature (20 C in this case). Then you shine a light at a small part of the 'front' surface (one watt in this case) and vary the intensity of the light sinusoidally. Then you measure the slight sinusoidal variation in temperature that appears on the 'back' surface of the insulation. By comparing the magnitude and timing of the variation on the back and comparing it with that of the variable light on the front, you can work out the physical properties of the insulation.<br /><br />It sounds like magic; the temperature variations being measured are around 10 microkelvins and they're extracted from the normal random fluctuations using a box of electronics called a 'lock-in' amplifier. But the technique is real and the amplifiers can achieve performance like this. I've used them myself to measure other small things.<br /><br />So far from science ignoring dynamic radiative effects; they're a fundamental basis of the techniques used to measure the static properties!]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82895#Comment_82895</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82895#Comment_82895</guid>
		<pubDate>Sat, 22 May 2010 15:49:47 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Very interesting - I think - because unfortunately much of it, esp the Conclusions and Outlook, is beyond me. Anyone translate, please?<br />At least they're using real-chaotic-life-like higher frequencies of input variation - 0.03Hz (= period 33 secs - still much too slow) to 20 Hz (prob more like it), unlike the glacially-slow variation that the NPL guys could get their hotbox to do.<br />As I understand it, multifoils are a really crude, unoptimised way of approaching insulation by means of resistance to radiation. The voids are unnecessarily large, therefore few in number, and only function in one of the three axes - i.e. perp to the layers, not up-down or side-to-side in the plane of the layers. Something like aero-bar insulation with the interior surfaces of the bubbles chrome-plated - or going more micro, micro-pore-riddled 'solid' materials with emission-resistant pore surfaces, would have multiple interrupts, at which slow conductive transport would convert to instantaneous radiant, and thereby get left behind, and would function equally in all axes.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82900#Comment_82900</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82900#Comment_82900</guid>
		<pubDate>Sat, 22 May 2010 19:01:58 +0100</pubDate>
		<author>CWatters</author>
		<description>
			<![CDATA[Apparently the insulation used on existing space suits will have to be redesigned for a mars trip because they rely the vacuum of space removing gas from between the layers and reducing the conductance. Article here..<br /><br /><a href="http://www.bme.utexas.edu/docs/kd/220.pdf" target="_self" rel="nofollow">http://www.bme.utexas.edu/docs/kd/220.pdf</a><br /><br />says the "..heat lost trough the current insulation is expected to be intolerable at Mars pressures.The presence of interstitial gases compromises the insulating properties of multilayer materials that were designed for use in a radiation dominated environment."<br /><br />"The target thermal conductivity to provide adequate insulative properties for the suit is 0.005W/mK."<br /><br />Given that insulation on current suits is only about 0.1" thick and has to be flexible that sounds challenging.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82901#Comment_82901</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82901#Comment_82901</guid>
		<pubDate>Sat, 22 May 2010 19:55:34 +0100</pubDate>
		<author>DamonHD</author>
		<description>
			<![CDATA[Sounds like a call for an aerogel variant!<br /><br />Rgds<br /><br />Damon]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82906#Comment_82906</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82906#Comment_82906</guid>
		<pubDate>Sat, 22 May 2010 22:01:27 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Indeed - aerogel, 'platinum' EPS and multifoils are all playing similar games. Both aerogel and multifoil give 'impossible' results in the hotbox - in opposite directions.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82909#Comment_82909</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82909#Comment_82909</guid>
		<pubDate>Sun, 23 May 2010 09:32:08 +0100</pubDate>
		<author>biffvernon</author>
		<description>
			<![CDATA[Nice contribution, djh.  We seem to be getting back to close to where we started in March 2006.  Multifoils are useful in vacuum cryogenics and in space but keep them out of our houses.  Remember my coffee got cold quicker when when wrapped in mutilfoil.<br /><br /><a href="http://www.greenbuildingforum.co.uk/forum/index2.php?DATEIN=tpc_wlpssdlpg_1142805843&showpage=1" target="_self" rel="nofollow">http://www.greenbuildingforum.co.uk/forum/index2.php?DATEIN=tpc_wlpssdlpg_1142805843&showpage=1</a>]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82913#Comment_82913</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82913#Comment_82913</guid>
		<pubDate>Sun, 23 May 2010 10:25:36 +0100</pubDate>
		<author>SteamyTea</author>
		<description>
			<![CDATA[Biff<br /><br />Fits in with the cooling law nicely by the looks of it, just as it should <img src="/newforum/extensions/Vanillacons/smilies/standard/bigsmile.gif" alt=":bigsmile:" title=":bigsmile:" />]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82927#Comment_82927</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=82927#Comment_82927</guid>
		<pubDate>Sun, 23 May 2010 21:50:02 +0100</pubDate>
		<author>bot de paille</author>
		<description>
			<![CDATA[Thank you djh, that is the sort of thing I had in mind. It seems that unless the MF  supporters can come up with something similar it appears the debate is over... mf just isnt that good here on earth compared to insulation against conduction and convection.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83003#Comment_83003</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83003#Comment_83003</guid>
		<pubDate>Tue, 25 May 2010 11:45:56 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Well' I've tried v hard but I don't understand what Chapters 3, 4 and 5 mean, so am not throwing in the towel yet!Is anyone up for a bit of correspondence, to help me understand the terminology of these chapters?]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83123#Comment_83123</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83123#Comment_83123</guid>
		<pubDate>Thu, 27 May 2010 08:42:41 +0100</pubDate>
		<author>SteamyTea</author>
		<description>
			<![CDATA[Just to put a spanner in the works here are the results from my tests.  They were not what I was expecting, now I could, in the best scientific way, explain them away to suit my hypothesis but I won't.<br />It boils down to a Standard tiles getting hottest at 58.5 C (the temperature in the void under the tile), then the Insulated tile (-2 C), then the Foiled Tile (-11.5 C) and finally the Insulated and Foiled tile (-13 C).  I expected the Insulated tile to be cooler than the Foiled tile but the results are the results even allowing for instrument variation of 0.5 C it seems that 1 layer of tin foil under a tile is better than 3 layers of J-Cloth sandwiched between foil Layers.<br /><br />The Solar Shiny and Solar Matt temperatures are two sensors on the horizontal and are really a secondary test and do not give the ambient temperature (goes back to Painting Roof Tiles White) and unfortunately my Solar Power Sensor Logger (also on the Horizontal) decided to only log two days worth (24th and 25th May 2010).  The tests still go into shade at about 1PM and there is some shading before 8AM.<br /><br />More analysis of of the data could tease out better statistics but I don't think that the results would change much.  I may try later when I have a couple of spare hours but I have posted the full data if others wish to play about with it.  It is a Winzip file but to upload it I have renamed the extension to rar so that it can be uploaded.  Rename the last 3 letter (after the full stop to zip) or just open with Winzip or similar.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83172#Comment_83172</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83172#Comment_83172</guid>
		<pubDate>Fri, 28 May 2010 08:37:39 +0100</pubDate>
		<author>Mike (Up North)</author>
		<description>
			<![CDATA[Hi could you re save that as a Zip file or something else.<br />Cant download somehting to open with as a) have to pay, b) work computor<br />thanks<br />Cheers<br />Mike up North]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83173#Comment_83173</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83173#Comment_83173</guid>
		<pubDate>Fri, 28 May 2010 09:04:48 +0100</pubDate>
		<author>SteamyTea</author>
		<description>
			<![CDATA[I cant upload it as a zip file, thats the problem, had to rename the zip file as an rar, change the last 3 letters to zip.  Cant really help in the Excel format as it is over 500kb.  Peazip is freeware, that will open it.<br />Actually I think of XP/Vista/7 will open ZIP files, download it, rename it and then right click on it and see if the option is there.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83175#Comment_83175</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83175#Comment_83175</guid>
		<pubDate>Fri, 28 May 2010 10:14:35 +0100</pubDate>
		<author>Mike (Up North)</author>
		<description>
			<![CDATA[Nope nothing<br />error - cannot find source directory??<br /><br />Keep trying]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83176#Comment_83176</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83176#Comment_83176</guid>
		<pubDate>Fri, 28 May 2010 10:47:16 +0100</pubDate>
		<author>SteamyTea</author>
		<description>
			<![CDATA[Mike<br /><br />Have you managed to download it ok?]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83178#Comment_83178</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83178#Comment_83178</guid>
		<pubDate>Fri, 28 May 2010 11:41:13 +0100</pubDate>
		<author>Mike (Up North)</author>
		<description>
			<![CDATA[Yes it downloads. using rar extension  you get the usual option to find the prog to open it with and changing ext to zip it is recoognised as a zip, but on opening gives the error message. This is winzip v10.<br /><br />I will try it on another machine<br /><br />Cheers]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83180#Comment_83180</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83180#Comment_83180</guid>
		<pubDate>Fri, 28 May 2010 12:28:51 +0100</pubDate>
		<author>Paul in Montreal</author>
		<description>
			<![CDATA[<a href="http://www.7-zip.org" target="_self" rel="nofollow">http://www.7-zip.org</a> opens it fine, even with the rar extension and then the xlsx file in there opens fine for me  - though you need office2007 or later to open files of this type.<br /><br />Paul in Montreal.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83183#Comment_83183</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83183#Comment_83183</guid>
		<pubDate>Fri, 28 May 2010 14:40:39 +0100</pubDate>
		<author>SteamyTea</author>
		<description>
			<![CDATA[Paul<br /><br />I re saved it as an 2003 but it went from about 700k to over 2.1mb, know idea why that happened, sometimes technology is a mystery to me.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83187#Comment_83187</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83187#Comment_83187</guid>
		<pubDate>Fri, 28 May 2010 16:02:44 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: SteamyTea</cite>Just to put a spanner in the works here are the results from my tests.  They were not what I was expecting, now I could, in the best scientific way, explain them away to suit my hypothesis but I won't.<br />It boils down to a Standard tiles getting hottest at 58.5 C (the temperature in the void under the tile), then the Insulated tile (-2 C), then the Foiled Tile (-11.5 C) and finally the Insulated and Foiled tile (-13 C).  I expected the Insulated tile to be cooler than the Foiled tile but the results are the results even allowing for instrument variation of 0.5 C it seems that 1 layer of tin foil under a tile is better than 3 layers of J-Cloth sandwiched between foil Layers.</blockquote><br />I don't understand what the arrangement is. Is there a diagram somewhere?<br /><br />Also, I can download the file, I can open it in oocalc but it doesn't work because all the cross-sheet references are in the wrong format. They use ! whereas oocalc is expecting .]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83188#Comment_83188</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83188#Comment_83188</guid>
		<pubDate>Fri, 28 May 2010 16:16:09 +0100</pubDate>
		<author>SteamyTea</author>
		<description>
			<![CDATA[DJH<br /><br />Was a simple polystyrene box with a roof tile on top.  I then added different insulation under the tile and measured the temperatures as the solar input varied.  Disregard Solar Shiny and Solar Matt as they are left over from a previous test.<br /><br />As for oocalc not reading it have you tried Find and Replace, or a copy of Excel, there are enough versions floating around.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83198#Comment_83198</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83198#Comment_83198</guid>
		<pubDate>Sat, 29 May 2010 09:40:56 +0100</pubDate>
		<author>marktime</author>
		<description>
			<![CDATA[I haven't opened the file either but the results seems extraordinary, especially the drop in temperature resulting from a sandwich of tile, foil and insulation. I assume ambient temperature was the same throughout? Your file would show that but it seems to be beyond me. <img src="/newforum/extensions/Vanillacons/smilies/standard/sad.gif" alt=":sad:" title=":sad:" />]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83201#Comment_83201</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83201#Comment_83201</guid>
		<pubDate>Sat, 29 May 2010 12:36:32 +0100</pubDate>
		<author>SteamyTea</author>
		<description>
			<![CDATA[Derrick<br /><br />All the test were done side by side.  The temp drops are from maximums, mean temperatures are not so impressing with means of:<br /><br />Standard Tile=21.8<br />Foiled Tile=20.2<br />Insulated Tile=20.6<br />Foiled Insulated=19.2]]>