			<![CDATA[<blockquote ><cite >Posted By: SteamyTea</cite>DJH<br />Was a simple polystyrene box with a roof tile on top.  I then added different insulation under the tile and measured the temperatures as the solar input varied.  Disregard Solar Shiny and Solar Matt as they are left over from a previous test.<br /></blockquote><br />How was the side of the box sealed to the foil and/or insulation? A photo/diagram would help me build a similar box.<br /><br /><blockquote >As for oocalc not reading it have you tried Find and Replace,</blockquote><br />Ah, that worked. Thanks for that excellent idea <img src="/newforum/extensions/Vanillacons/smilies/standard/bigsmile.gif" alt=":bigsmile:" title=":bigsmile:" /><br /><br /><blockquote >or a copy of Excel, there are enough versions floating around.</blockquote><br />Wash your mouth out! <img src="/newforum/extensions/Vanillacons/smilies/standard/devil.gif" alt=":devil:" title=":devil:" /> I don't have any M$ licences for anything.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83216#Comment_83216</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83216#Comment_83216</guid>
		<pubDate>Sat, 29 May 2010 23:01:14 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[Ok here's my view of the conventional building science for foam insulation, as near as I can make out the history.<br /><br />Back in the mid-80s, people were measuring conductivities for foams that were significantly worse than predicted by theory. The mainstream presumption was that the extra losses were caused by inadequate allowance for radiation in the models.<br /><br />It's a bit difficult to check references because many papers from that time are not online, and others require subscriptions that I don't have. The best reference I can find is from 1984 [1] and the authors clearly recognize the importance of radiation within the material. You'll notice that one author is an engineer at a major insulation company. The other author is a scientist at MIT. He later became Professor of Building Technology & Mechanical Engineering and seems [2] to have made a significant contribution to energy-efficiency and sustainability. So I hardly think it is credible to hold the idea that mainstream science and corporates ignore the separate issues of conduction, convection and radiation. They appear to be precisely the people developing that depth of understanding.<br /><br />By the early 90s there was research underway to improve the performance of foam by (a) reducing cell size and (b) altering the transmissivity to thermal radiation. Glicksman was supervising two MSc theses on these subjects [3], [4]. At the same time, there was also work to remove the CFC blowing agent, and the removal would make performance worse. MIT wasn't the only place doing such research; [5] is an example from Germany.<br /><br />By 1995, BASF had a patent for Neopor.<br /><br />So the history as I see it is what I would expect, no big mysteries or conspiracies to be accounted for.<br /><br />Cheers, Dave<br /><br />[1] Schuetz, M.A., Glicksman, L.R. (1984) Journal of Cellular Plastics, 20 (2), pp. 114-121<br />BASIC STUDY OF HEAT TRANSFER THROUGH FOAM INSULATION.<br /><br />The first page is available at <a href="http://cel.sagepub.com/cgi/pdf_extract/20/2/114" target="_self" rel="nofollow">http://cel.sagepub.com/cgi/pdf_extract/20/2/114</a><br /><br />[2] <a href="http://architecture.mit.edu/people/profiles/prglicks.html" target="_self" rel="nofollow">http://architecture.mit.edu/people/profiles/prglicks.html</a><br /><br />[3] <a href="http://dspace.mit.edu/bitstream/handle/1721.1/26816/23885591.pdf?sequence=1" target="_self" rel="nofollow">http://dspace.mit.edu/bitstream/handle/1721.1/26816/23885591.pdf?sequence=1</a><br /><br />[4] <a href="http://dspace.mit.edu/bitstream/handle/1721.1/26827/24882071.pdf?sequence=1" target="_self" rel="nofollow">http://dspace.mit.edu/bitstream/handle/1721.1/26827/24882071.pdf?sequence=1</a><br /><br />[5] <a href="http://dx.doi.org/10.1016/0017-9310" target="_self" rel="nofollow">http://dx.doi.org/10.1016/0017-9310</a>(92)90150-Q]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83217#Comment_83217</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83217#Comment_83217</guid>
		<pubDate>Sun, 30 May 2010 07:55:34 +0100</pubDate>
		<author>SteamyTea</author>
		<description>
			<![CDATA[Dave<br /><br />The box is made from 50mm thick expanded polystyrene.<br />External measurements: 340L, 340W, 150H<br />Internal measurements: 240L, 240W, 100H<br />A roof tile was put on top with different 'finishes' under the tile.<br /><br />There are some pictures of my original tests at, they were for trying out different finishes on the outside:<br /><a href="http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=5643&page=2" target="_self" rel="nofollow">http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=5643&page=2</a><br /><br />And here is a screen capture of a very bad drawing:]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83218#Comment_83218</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83218#Comment_83218</guid>
		<pubDate>Sun, 30 May 2010 08:42:35 +0100</pubDate>
		<author>marktime</author>
		<description>
			<![CDATA[Dave, how dare you pollute this thread with good science! Tut!Tut!]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83219#Comment_83219</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83219#Comment_83219</guid>
		<pubDate>Sun, 30 May 2010 09:31:40 +0100</pubDate>
		<author>SteamyTea</author>
		<description>
			<![CDATA[Derrick<br /><br />No good will ever come of science, we have all we will ever need]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83220#Comment_83220</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83220#Comment_83220</guid>
		<pubDate>Sun, 30 May 2010 09:40:06 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: djh</cite>the authors clearly recognize the importance of radiation within the material</blockquote><blockquote ><cite >Posted By: djh</cite>I hardly think it is credible to hold the idea that mainstream science and corporates ignore the separate issues of conduction, convection and radiation. They appear to be precisely the people developing that depth of understanding.</blockquote>Jolly good - I'm glad they agree with me. What we (them and me) want to know is, where did the many people (incl 'scientists') on this forum get their strong belief that radiation is insignificant?]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83221#Comment_83221</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83221#Comment_83221</guid>
		<pubDate>Sun, 30 May 2010 09:53:05 +0100</pubDate>
		<author>SteamyTea</author>
		<description>
			<![CDATA[Tom<br /><br />I suspect from anecdotal observations, temperature differences, misunderstanding of the systems, the initial question, inability to collect/analysers data, differences in opinions, teasing a signal from data.  I am sure the 'scientists' on here will go and research and synthesis what data is available and draw conclusions without the red herrings of cost, practicality of installation, other influential factors etc.<br /><br />Have you had your simulation results back yet for your heat transfer design?]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83234#Comment_83234</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83234#Comment_83234</guid>
		<pubDate>Sun, 30 May 2010 20:29:35 +0100</pubDate>
		<author>biffvernon</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: fostertom</cite>where did the many people (incl 'scientists') on this forum get their strong belief that radiation is insignificant?</blockquote>Others will speak for themselves but I don't think I've ever thought that radiation is insignificant - just that after the first shiny layer there's a strong law of diminishing returns for succeeding layers in non-vacuum mutifoils making them bad value for money.<br /><br />Is anyone making a foil-faced areogel board?]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83243#Comment_83243</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83243#Comment_83243</guid>
		<pubDate>Sun, 30 May 2010 23:00:51 +0100</pubDate>
		<author>Saint</author>
		<description>
			<![CDATA[Biff, there would be no point. The reflective surfaces work only in combination with air gaps so as an installed insulation solution it would simply be a case of making what is currently the most effective thinnest passive insulation available into a thick one displaying an average "R" value<br />The effect of radiation is not refuted its just not as significant as some people would like us to believe. Carbon black added to EPS improves its thermal conductivity by about 5 milliwatts depending on the density of the EPS. With XPS the improvement is nearer 2 miliwatts, changing the density and cell size have more dramatic effects impacting on conduction and convection respectively]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83249#Comment_83249</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83249#Comment_83249</guid>
		<pubDate>Mon, 31 May 2010 00:56:37 +0100</pubDate>
		<author>bot de paille</author>
		<description>
			<![CDATA["The effect of radiation is not refuted its just not as significant as some people would like us to us believe."<br /><br />Exactly, and still no one has be able to point to any academic research that says otherwise...]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83260#Comment_83260</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83260#Comment_83260</guid>
		<pubDate>Mon, 31 May 2010 13:43:18 +0100</pubDate>
		<author>biffvernon</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Saint</cite>Biff, there would be no point. The reflective surfaces work only in combination with air gaps</blockquote>I think a common misconception is the size of air gap needed.  It is of the order of magnitude of the wavelength of infra-red light, i.e. not very much and so of approximately zero consequence.<br /><br />Endlessly repeating the false assertion that a wide air gap is required above multifoils does not alter physics.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83264#Comment_83264</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83264#Comment_83264</guid>
		<pubDate>Mon, 31 May 2010 14:47:51 +0100</pubDate>
		<author>Mike George</author>
		<description>
			<![CDATA[Biff, you may want to look at this BBA <a href="http://www.bbacerts.co.uk/PDF/4543i1_web.pdf" target="_self" rel="nofollow">http://www.bbacerts.co.uk/PDF/4543i1_web.pdf</a> <br /><br />Note the thermal resistance of the multifoil virtually doubles from 0.97m2K/W to 1.9M2k/W [page 4] with a minimum airgap of 20mm [page 8]<br /><br />Seems they think the air gap is pretty important.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83265#Comment_83265</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83265#Comment_83265</guid>
		<pubDate>Mon, 31 May 2010 15:16:08 +0100</pubDate>
		<author>Paul in Montreal</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Mike George</cite>Note the thermal resistance of the multifoil virtually doubles from 0.97m2K/W to 1.9M2k/W [page 4] with a minimum airgap of 20mm [page 8]</blockquote> Maybe because that's the insulating property of that thickness of airgap. Up to a cetain point, air does insulate - but if the gap is too wide, convection currents reduce its effectiveness. Exactly the same mechanism as double/triple glazing. Which, if you think of it, is just like a multifoil (if the glass is coated). So any multifoil that claims better performance than triple-glazing is dubious to say the least.<br /><br />Paul in Montreal.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83266#Comment_83266</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83266#Comment_83266</guid>
		<pubDate>Mon, 31 May 2010 15:24:24 +0100</pubDate>
		<author>Mike George</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Paul in Montreal</cite><blockquote ><cite >Posted By: Mike George</cite>Note the thermal resistance of the multifoil virtually doubles from 0.97m2K/W to 1.9M2k/W [page 4] with a minimum airgap of 20mm [page 8]</blockquote>Maybe because that's the insulating property of that thickness of airgap. Up to a cetain point, air does insulate - but if the gap is too wide, convection currents reduce its effectiveness. Exactly the same mechanism as double/triple glazing. Which, if you think of it, is just like a multifoil (if the glass is coated). So any multifoil that claims better performance than triple-glazing is dubious to say the least.<br /><br />Paul in Montreal.</blockquote><br /><br />I don't think they are claiming better performance than tripple glazing, and I didn't say that they were. They are only claiming that the air gap is necessary to achieve the tested themal resistance of 1.9m2K/W.<br /><br />Biff seems to contradict the worthiness of such an airgap in his post. Unless I am misunderstanding him, Biff?]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83267#Comment_83267</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83267#Comment_83267</guid>
		<pubDate>Mon, 31 May 2010 16:19:22 +0100</pubDate>
		<author>biffvernon</author>
		<description>
			<![CDATA[Of course, as Paul points out, air is a good insulator.  My point is that the air gap (after the first few nanometres) makes zero difference to the radiation related properties of a foil surface.  The out going infra-red radiation does not 'know' how wide the air gap is beyond the first wavelength.  (That's how low-e coatings work - the coating is half a wavelength thick so radiation leaving from the glass surface cancels out with that leaving form the outer side of the coating.)]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83268#Comment_83268</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83268#Comment_83268</guid>
		<pubDate>Mon, 31 May 2010 16:36:47 +0100</pubDate>
		<author>Mike George</author>
		<description>
			<![CDATA[So are you saying that the mulifoil in the BBA will achieve 1.9m2K/W irrespective of whether the airgap is 20mm or a 'few nanaometere'?]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83269#Comment_83269</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83269#Comment_83269</guid>
		<pubDate>Mon, 31 May 2010 17:08:47 +0100</pubDate>
		<author>Saint</author>
		<description>
			<![CDATA[Biff, I'd follow the guidelines from the BRE Convention for U value calculations<br /><a href="http://www.bre.co.uk/filelibrary/pdf/rpts/BR_443_" target="_self" rel="nofollow">http://www.bre.co.uk/filelibrary/pdf/rpts/BR_443_</a>(2006_Edition).pdf<br />para 4.8.2 recommends an air gap of at least 25mm and lets face it what's the most commonly used spacer, a batten.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83270#Comment_83270</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83270#Comment_83270</guid>
		<pubDate>Mon, 31 May 2010 17:19:51 +0100</pubDate>
		<author>Paul in Montreal</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Mike George</cite>So are you saying that the mulifoil in the BBA will achieve 1.9m2K/W irrespective of whether the airgap is 20mm or a 'few nanaometere'?</blockquote><br /><br />Of course not. Most of the performance is from that 20mm airgap. Any more than that and convection would reduce the effectiveness, any less than that and there would be less insulative effect of the air itself. It's just like double glazing: you compromise the performance if the airgap is too wide or too narrow (depends on the gas of course).<br /><br />Seems to me that about half of the performance is due to the air gap - if one used a conventional insulation with the same thickness as the Gen-X foil and the 20mm airgap, I suspect the performance would be at least as good - maybe even better as that 20mm airgap seems to have the same performance as 33mm of multi-foil. Note the BBA certificate makes a note about the airgap being well sealed against air leakage.<br /><br />Paul in Montreal.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83272#Comment_83272</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83272#Comment_83272</guid>
		<pubDate>Mon, 31 May 2010 17:39:43 +0100</pubDate>
		<author>bot de paille</author>
		<description>
			<![CDATA[Some very interesting points made that go a  along way to making things clearer re the insitu performance of mf. Home made double glazing for the walls and roof, plus air barrier. Finaly, radiation takes third place in importance in a typical mf installation.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83273#Comment_83273</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83273#Comment_83273</guid>
		<pubDate>Mon, 31 May 2010 17:51:45 +0100</pubDate>
		<author>Mike George</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Paul in Montreal</cite><blockquote ><cite >Posted By: Mike George</cite>So are you saying that the multifoil in the BBA will achieve 1.9m2K/W irrespective of whether the air-gap is 20mm or a 'few nanometer'?</blockquote><br /><br />Of course not. <br />Paul in Montreal.</blockquote><br /><br />Thanks Paul, I understand you are not saying that. <img src="/newforum/extensions/Vanillacons/smilies/standard/bigsmile.gif" alt=":bigsmile:" title=":bigsmile:" />I should have made it clearer that the question was put to  Biff.<br /><br />Regarding the BBA, I have not seen any others which attribute such a thermal performance to air. And more importantly allow u-value calculations to be based on it.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83274#Comment_83274</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83274#Comment_83274</guid>
		<pubDate>Mon, 31 May 2010 17:57:46 +0100</pubDate>
		<author>James Norton</author>
		<description>
			<![CDATA[Just like to say that I've not really read a lot of this latest stuff but thoroughly approve of the surge in this thread, 750 not too far away now which really puts that magic 1000 well on the horizon!<br /><br />Well done chaps, keep up the good work!<br /><br />J<br /><br />(Keith any possibility of some stats on this amazing thread; no. of posters, no. of words etc...? - [only if you have an idle moment <img src="/newforum/extensions/Vanillacons/smilies/standard/wink.gif" alt=":wink:" title=":wink:" />...])]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83277#Comment_83277</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83277#Comment_83277</guid>
		<pubDate>Mon, 31 May 2010 19:40:00 +0100</pubDate>
		<author>CWatters</author>
		<description>
			<![CDATA[Deleted as already discussed.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83279#Comment_83279</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83279#Comment_83279</guid>
		<pubDate>Mon, 31 May 2010 21:10:31 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[As soon as the radiative component of overall heat transfer becomes (or is admitted to be) significant, then so also does frequency and amplitude of variation of the delta-t that is driving the transfer.<br />Radiant is at a minimum under steady-state delta-t (the unnatural state established at great effort in the hotbox), at a maximum under turbulent (real-life) delta-t.<br />I'm not sure that the v interesting pieces of research put up by djh on 22 May and 30 May ('1 day ago') have grasped that.<br /><br />Note that in saying "frequency and amplitude of variation of the delta-t" we're not talking about the kind of slow variation that can be achieved by varying temps in a hotbox - that's so slow as to count as near enough steady-state. That was the ridiculous 'error' made in the infamous NPL study that was commissioned to discredit multifoils.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83280#Comment_83280</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83280#Comment_83280</guid>
		<pubDate>Mon, 31 May 2010 21:53:43 +0100</pubDate>
		<author>Paul in Montreal</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: fostertom</cite>Radiant is at a minimum under steady-state delta-t (the unnatural state established at great effort in the hotbox), at a maximum under turbulent (real-life) delta-t.</blockquote> All that matters is the delta-t - the rate of change makes no difference as the absolute power of the radiative component is fixed by Stefan's law. No amount of handwaving about "real world" conditions can change that maximum. Sorry.<br /><br />Paul in Montreal.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83281#Comment_83281</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83281#Comment_83281</guid>
		<pubDate>Mon, 31 May 2010 22:16:10 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Paul, in a mix of radiant, conductive and convective, when there's a disturbance in the delta-t, across a void space, it has to be re-equilibriated. The radiant component starts delivering energy instantly to the suddenly-colder end of the couple, whereas there's a time-lag before conductive and convective get there. By then the radiant component may have already done much or all of the transfer necessary to complete the re-equilibriation. The delta-t driver for the conductive and convective may even peter out before they get there.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83282#Comment_83282</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83282#Comment_83282</guid>
		<pubDate>Mon, 31 May 2010 23:22:31 +0100</pubDate>
		<author>Saint</author>
		<description>
			<![CDATA[Withdrawn]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83299#Comment_83299</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83299#Comment_83299</guid>
		<pubDate>Tue, 01 Jun 2010 13:46:22 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: fostertom</cite>As soon as the radiative component of overall heat transfer becomes (or is admitted to be) significant, then so also does frequency and amplitude of variation of the delta-t that is driving the transfer.<br />Radiant is at a minimum under steady-state delta-t (the unnatural state established at great effort in the hotbox), at a maximum under turbulent (real-life) delta-t.</blockquote><br /><br /><blockquote ><cite >Posted By: fostertom</cite>in a mix of radiant, conductive and convective, when there's a disturbance in the delta-t, across a void space, it has to be re-equilibriated. The radiant component starts delivering energy instantly to the suddenly-colder end of the couple, whereas there's a time-lag before conductive and convective get there. By then the radiant component may have already done much or all of the transfer necessary to complete the re-equilibriation. The delta-t driver for the conductive and convective may even peter out before they get there.</blockquote><br />Tom, I agree with some parts of what you say here. But I'm not so sure about other parts, such as "significant" in the context of variations. Remember that some of the experiments measure diffusivity directly. Rather than get into another sterile debate, I suppose you must have a basis for your belief, so could you post the references so we can all read them.<br /><br />Thanks, Dave]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83310#Comment_83310</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83310#Comment_83310</guid>
		<pubDate>Tue, 01 Jun 2010 16:55:22 +0100</pubDate>
		<author>Paul in Montreal</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: fostertom</cite>Paul, in a mix of radiant, conductive and convective, when there's a disturbance in the delta-t, across a void space, it has to be re-equilibriated.</blockquote><br /><br />Tom, there's two flaws in your argument above. First of all, you talk of a void space. In real-world materials, there is no void space, it is filled with something - most likely air or another gas. The second flaw is your "re-equilibrated" statement. Heat flow through a material is already a dynamic equilibrium - you talk as if an external change suddenly causes the radiative transfer of energy to be activated: this is most certainly not the case - all components of your insulation are radiating energy (google "prevost's theory of exchanges"). The rest of the energy transfer in materials is via momentum transfer - this is the mechanism of the transfer of energy that occurs in conduction and convection. These are statistical processes that the laws of thermodynamics describe very well. Your "chaotic changes in delta-T" are already described by these statistical processes and you can't just wave your hands and say radiant transfer dominates. Of course, in materials like aerogels, the bubble sizes are on the nano-scale in order to minimize the momentum-transfer processes - in this case reducing the radiant transfer does make a difference since the other transfer processes have been reduced to a smaller level than in typical materials. If your assertions were correct then a thermally massive but pore-ridden material like brick would behave quite differently than is observed. In your case, sunlight shining on a brick wall would be transferred through very quickly since, by your own argument, radiation dominates - and I'll grant that the delta-T on a sunlight illuminated wall is very high (after all, 100% of the heat we receive from the sun starts out as radiation). But it is commonly observed that brick is rather slow at reacting to temperature fluctuations which, I posit, is because of the dominance of the momentum-transfer mechanism of heat transfer. A brick wall that's facing north will receive almost all it's delta-T changes from momentum transfer from the air layer in front of it.<br /><br />Hope this helps clarify your misconceptions.<br /><br />Paul in Montreal.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83317#Comment_83317</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83317#Comment_83317</guid>
		<pubDate>Tue, 01 Jun 2010 20:37:00 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Thanks. Paul, for engaging with what Iâ€™ve been saying for a couple or three years â€“ no one else has, on this forum (and I donâ€™t think Iâ€™ve said it anywhere else).<br /><br /><blockquote ><cite >Posted By: Paul in Montreal</cite>you talk of a void space. In real-world materials, there is no void space, it is filled with something - most likely air or another gas</blockquote>Yes, that's what I meant, not a vacuum.<br />So when, after a period of steady-state transfer across plus around the perimeter of such a gas-filled void, one 'shore' of the void changes in temp because a temp wave has reached it via the solid material 'inland' (I'm going into a flat-earth analogy here), delta-t across the void increases and a new equilibrium has to be established.<br />The total rate of heat transfer across plus around the perimeter of the void will increase and eventually as a result the far 'shore' will also rise in temp, until a new steady-state equilibrium is established.<br />That transfer will be by convection thro the gas that fills the void;<br />by conduction thro the gas that fills the void and also thro the solid material that surrounds the void;<br />and by radiation across the void.<br />The radiant mode gets transferring instantly; the convective and conductive modes take time to have any effect on the far 'shore'.<br />By the time they do, the radiant mode will have already done much or all of the work of re-equilibriation, and may even have wiped out the temporarily raised delta-t that was driving the conductive and convective transfer.<br /><br /><blockquote ><cite >Posted By: Paul in Montreal</cite>you talk as if an external change suddenly causes the radiative transfer of energy to be activated</blockquote>All three modes were already activated; the external change causes all three modes to increase equally, more or less pro rata.<br />The point is that the increase of the radiant component then gets there sooner than the increase of the convective and conductive components, hence the radiant does much or all of the work of re-equilibriation neither helped nor hindered by the tardy convection and radiation.<br />This 'gets there sooner' advantage only applies to the increased portion of the transfer, attributable to the suddenly increased delta-t;<br />the 'base load' portion of the transfer, attributable to the pre-existing steady-state, ploughs on unchanged.<br /><br />Thus the radiant component trumps the other two only in respect of the increased portion of the transfer, and that increased portion only exists when delta-t is suddenly disturbed, from the pre-existing steady-state.<br /><br />So under steady-state I donâ€™t doubt that radiant does play its significant but minority role, as calcd by the conventionally understood physics of convection (tricky), conduction (simple) and radiation (simple).<br /><br />When a new isolated temp wave comes through, disturbing the steady-state, that variant portion is effectively handled by the radiant component (where there are voids and pores - obviously not within the solid), until re-equilibriation. This is superimposed on the ongoing steady-state regime (which again prevails after re-equilibriation), so you might say is interesting but insignificant.<br /><br />But when new temp waves are coming through constantly, steady-state hardly exists, so a high proportion of the constant re-equilibriation is handled by the radiation component, while the convective and conductive are reduced to impotence, constantly setting off in a new direction but never getting there, before a new disequilibrium arises.<br /><br />Donâ€™t ask for my sources â€“ this is all out of my head. Itâ€™s like â€“ I donâ€™t need a peer reviewed research project to tell me that if A is faster than B, then A gets there sooner.]]>
		</description>
	</item>
	<item>
		<title>Multifoil Insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83318#Comment_83318</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=125&amp;Focus=83318#Comment_83318</guid>
		<pubDate>Tue, 01 Jun 2010 20:55:18 +0100</pubDate>
		<author>biffvernon</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Mike George</cite>So are you saying that the mulifoil in the BBA will achieve 1.9m2K/W irrespective of whether the airgap is 20mm or a 'few nanaometere'?</blockquote>Paul answered that very well.<br /><br />Doubtless the 20mm of air adds a lot of insulation.  And the air costs nothing other than the space it occupies.  The bit you are paying over the odds for, the foil, doesn't care whether there is an air gap there or not.  It's performance will not be affected by the air gap.  It's a shame that the BBA and the BRE do not make clear the operation of pretty basic physics.<br /><br />The purveyors of thermal vests don't say this garment may only be worn in conjunction with a shirt and woolly jumper if you want to stay warm on a cold day.]]>
		</description>
	</item>
	
		</channel>
	</rss>