    I was interested to examine the relative running costs associated air source and ground source heat pumps. To look at this question I started with a rather simple two season model.
    The broad implications may be best described by considering the two extreme situations:
    Where summer and winter temperatures are constant (but less than the desired indoor temperature) there would be no advantage to be gained from the additional costs of a ground based system. (Intuitively, ground source systems utilise the stabilising effect of the ground as a thermal sink. Where air temperature is constant, there is no need for an additional stabiliser, so that money spent on it is wasted.)
    Where summer and winter temperatures differ widely, the ground source heat pump is likely to be more economical, particularly if summer temperatures are high and a combined air conditioning unit is required.
    In practice, these extremes are not to be found in the UK, but situations approaching the extremes, may tip the balance in favour of either air source or ground source.
    The rather crude modelling that I have done suggests, for example, that the North-East coastal areas of Scotland, with its climate moderated by the North Sea and ‘enjoying’ cool summers (mean July temp 58 degrees F) and ‘relatively’ mild winters (mean January temp 38 degrees F), shifts the balance towards air source heat pumps. The model suggests that they are only slightly more expensive to operate, so that the additional capital costs of ground source heat pumps may not be justified. Other parameters included in the simple two season model are as follows:
    Proportion of year as Summer 0.5
    Desired indoor temp 70
    COP in Winter of an air source heat pump 2.3
    COP in Summer of an air source heat pump 3.3
    COP in Winter & Summer of a ground source heat pump 2.8

    Using these parameters, I calculate the ratio of air source energy use to ground source energy use to be: 1.1

    I’d be grateful for comments, particularly on the COP parameters that I’ve used. Getting reliable data on this crucial variable seems to be somewhat problematic!!

    Ken
    • CommentAuthorDantenz
    • CommentTimeFeb 15th 2008
     
    Kenbuckingham wrote
    (Intuitively, ground source systems utilise the stabilising effect of the ground as a thermal sink. Where air temperature is constant, there is no need for an additional stabiliser, so that money spent on it is wasted.)

    I disagree, the ground temperatures below 15 metres are a resultant of the average annual air temperature. If the annual air temp was held constant then the ground temperature would reflect this annual temperature, there would be difference.

    I agree with however, the statement that the additional capital costs of installing a GSHP may not be justified. For the most part of the UK we do not experience large temperature swings between summer and winter to the extent that external air temperatures in winter have a signifcant effect on an ASHP COP. ASHP's inherantly, have more parasitic losses than a GSHP so, even if the source temperature was the same for both, an ASHP would always come off slightly worse. That said, ASHP's are far more likely to be the systems of the future compared to GSHP.
  2.  
    Posted By: DantenzASHP's inherantly, have more parasitic losses than a GSHP so, even if the source temperature was the same for both, an ASHP would always come off slightly worse.


    I don't think there is anything in this. An ASHP has the outdoor unit (with a fan) and the GSHP has a circulation pump. Both probably use about the same power.

    The UK is an ideal climate for an ASHP since it is almost always above 0C. In this case, an ASHP would not have to enter defrost mode (where it loses efficiency).

    Since ASHPs have a much larger market than GSHPs, they are always likely to be more efficient for a given operating temperature - and cheaper too. However, most of that (worldwide) market is for reversible units - something which the UK seems to be averse to - probably because A/C is rarely required.

    The main disadvantage of an ASHP is that the outdoor unit makes noise, whereas as GSHP is quieter because it doesn't have a fan for the equivalent of the outdoor unit.

    Paul in Montreal.
    • CommentAuthorDantenz
    • CommentTimeFeb 15th 2008
     
    Paul wrote
    The UK is an ideal climate for an ASHP since it is almost always above 0C. In this case, an ASHP would not have to enter defrost mode (where it loses efficiency).

    The source temperature, be it air or ground, is not what determines the lowest operational temperatures within the machine; it's the refrigerant. The refrigeration cycle always works with sub-zero tempeartures within the closed refrigerant loop. Refrigerant, by nature ,is cold. This is why the ground collector heat transfer fluid on A GSHP (loop, slinky, borehole etc) is filled with an anti-freeze. It has nothing to do with possible freezing temperatures in the ground ( unlikey with a borehole drill depth of 180 m) it is all to do with temperatures within the fridge circuit. So, even with zero or above ambient air temps with an ASHP, the refrigerant will still chill the evaporator and form ice. This is where the de-frost operation comes into play and it is this function that lowers the COP of an ASHP.
    • CommentAuthorEd Davies
    • CommentTimeFeb 16th 2008
     
    Anybody have any thoughts on or experience with using solar-air-heating panels on the input side to an ASHP?
  3.  
    Very many thanks to all of you who responded to my posting. Probably you will have already realised what I needed the model to tell me, ie that the relative advantage of ground source heat pumps is dramatically affected by low summer time temperatures. It became obvious when I thought about it. If summer temperatures are below the desired indoor temperature, then a ground source heat pump would be extracting heat from the relatively cold ground rather than from the warmer air. So, in crude terms, if Winter temperature is 30F, Summer temperature is 60F, the average temperature is then 45F which we can use to approximate ground temperature. An air source pump would be using a source at 60F to obtain an indoor temperature of 70F, while a ground source heat pump would be using a source at 45F to obtain an indoor temperature of 70F. This can substantially reduce the advantage that ground source pumps have in Winter.

    Thanks again
    Ken
    • CommentAuthorDantenz
    • CommentTimeFeb 16th 2008
     
    It's the other way round, you only want space heating in the winter. So, the average of 45'C would is what the GSHP would operate off and 30'C the ASHP.
  4.  
    I think that you might have missed my point Dantez. If the summer temperature is below your desired temperature, you may well want space heating in summer.
    Best
    Ken
    • CommentAuthorEd Davies
    • CommentTimeFeb 16th 2008
     
    Also, you still want hot water in summer.
    • CommentAuthorDantenz
    • CommentTimeFeb 17th 2008
     
    I see your point Ken however, if there were only 10F difference between the summer outdoor temp and the required indoor temp then it is unlikely the ASHP would need operate in heating mode due to the self heating gains within the house.
  5.  
    Posted By: DantenzThe refrigeration cycle always works with sub-zero tempeartures within the closed refrigerant loop. Refrigerant, by nature ,is cold. This is why the ground collector heat transfer fluid on A GSHP (loop, slinky, borehole etc) is filled with an anti-freeze. It has nothing to do with possible freezing temperatures in the ground ( unlikey with a borehole drill depth of 180 m) it is all to do with temperatures within the fridge circuit.


    This is just not true. Refrigerant is not "cold". It simply has the capacity to absorb and release heat through phase change and compression. The refrigerant can never be colder than the coldest part of the evaporator. In the case of a water source (i.e. GSHP) heat pump, this is determined by the input temperature of the working fluid and the flow rate. I know that in my case in Montreal, the input temperature can be as cold as 2C towards the end of winter and then the return temperature is around -3C at the flow rate we have - so the refrigerant is also at -3C at that point too. Places with higher ground temperatures do not need antifreeze in the circulating fluid in the ground. My heat pump has jumpers to select whether the ground loop has antifreeze or not as there is a temperature sensor which shuts down the heatpump in case the ground loop temperature is too low (i.e. would freeze) - the jumper is configurable for -12C and -1C.

    In Ken's case, an ASHP would be more efficient in summer - but then the heat load is lower (since there's less differential between inside and outside) but this would be offset by the ASHP being less efficient in winter and with a lower output capacity. So if his ASHP was sized for winter heating, it would be oversized for summer (of course). A GSHP would end up being less oversized for summer operation and would be more efficient in winter. All that said, an ASHP would be much cheaper to install than a GSHP for his climate and probably be the better solution. As for internal gains being sufficient in summer, that depends on how well the house is insulated. It could be that internal gains are sufficient, but a Scottish cool and damp 60F can be pretty dismal :wink: And, as it has been pointed out, hot water is still needed.

    Paul in Montreal
    • CommentAuthorDantenz
    • CommentTimeFeb 19th 2008
     
    "Refrigerant is not "cold". It simply has the capacity to absorb and release heat through phase change and compression. The refrigerant can never be colder than the coldest part of the evaporator".

    Paul, with respect, I beg to differ.

    As I understand it the basic rules of physics of the vapour compression cycle are:

    Rule 1. Heat flows from hot to cold

    Rule 2. Energy (in the form of heat) is required to change a substance from a liquid to a gas (ie boil or evaporate). When this happens the liquid absorbs large amounts of heat.

    Rule 3. Energy is given out by a substance changing from a gas into a liquid (ie liquefying or condensing).

    Rule 4. The boiling temperature and the condensing temperature change if the pressure changes.

    In the evaporator the temperature of the refrigerant is kept lower (suction line from the compressor) than the temperature of the heat source (ground/air) causing heat to flow from the heat source to the refrigerant and the refrigerant evaporates. Rule 1.

    If the source temperature = refrigerant temp = evaporator temp. then rule 1 cannot happen.
  6.  
    You didn't read what I wrote. The refrigerant temperature is the post evaporator temp. In my GSHP, there is a 7F differential between the input and output water temps. This, multiplied by the mass flow rate determines the amount of heat absorbed by the refrigerant. There is no temperature change to go from liquid to gas if the latent heat of evaporation is supplied. I didn't say the source temp = refrigerant temp - it's the post heat-extraction temp of the now chilled source. All your rules are correct - rule number 1 isn't relevant for rule number 2 as the boiling point of the refrigerant is much lower than the source (evaporator) temperature - around -41C for R22 and -26C for R410a - both much lower than the input to the evaporator of a GSHP or and ASHP.

    Paul in Montreal.
    • CommentAuthormbartosik
    • CommentTimeFeb 20th 2008
     
    Find out your ground water temp, for me in New York it is 55F.
    Get specs from manufacturer, for me this is Florida Heat Pump, and find out the COP at that temp. They have a table. The COP improves for heating cycle as the heat source temp (water for gshp) increases. Indeed it appears that additional BTU or KWH available due to higher temp of water almost gets extracted for free above about 55F.

    Do similar for air source, using maybe an average air temp for winter.

    One thing to watch out for is energy to pump fluid is no always included in GSHP tables. My system requires about 400W to pump at 7 GPM (depth of well 56 ft).