Posted By: gravelldBut it would be costly in terms of time and money to re-route the cables.
Is is acceptable to run the cables in some sort of conduit or sheathing
Posted By: djh
Isn't threading them through conduit about as time consuming as laying them on top of the insulation?
Posted By: Andrew_Doran
What size are the cables (2.5mm^2 ?) and what rating of fuse or breaker are they fed from?
EDIT are the cables PVC twin&earth or singles?
Posted By: SteamyTeaI think this is notifiable work, so you need to be Part P certified or get someone in that is.Even if there's no re-wiring?
Posted By: Ed DaviesWould it be feasible to stuff some insulation under the wire (e.g., foil-faced PUR) but leave them freely in contact with the air above? Ie, break the mineral wool or whatever main insulation say 75 mm each side of the cables but make up for the gap with a bit of higher-grade insulation under.Yes, definitely feasible. But 75mm! That's quite the 'bridge... If cables were run inside an IWI wall would there be as much as 75mm required either side?
Posted By: SteamyTeaPossibly, there are 'installation methods' to take into account.Thanks. Part P or not I don't fancy it!
I also think that if you disconnect and reconnect a water heater then it is classed as major work. Not 100% sure on that though (I did my Part P a few years back and it has changed since).
Posted By: Ed DaviesWould it be feasible to stuff some insulation under the wire (e.g., foil-faced PUR) but leave them freely in contact with the air above? Ie, break the mineral wool or whatever main insulation say 75 mm each side of the cables but make up for the gap with a bit of higher-grade insulation under.
Posted By: gravelldThere's about 70mm underneath the cable.So 50 or 60 mm of PUR would leave the cable pretty much in free air and provide enough insulation that it wouldn't be such a terrible cold bridge. Dunno, 75 mm was just the first number I thought of; you just want to make sure that the air round the cable has enough room to convect properly.
Posted By: gravelldhttp://electrical.theiet.org/wiring-matters/15/current-ratings.cfm?type=pdf" rel="nofollow" >http://electrical.theiet.org/wiring-matters/15/current-ratings.cfm?type=pdf
So what do these current ratings mean? Given a 10mm cable...
In other words, if the insulation affects the current carrying capacity of the cable (whether that capacity is actually used or not and whether it's still more than the circuit protection allows) then the work is technically notifiable.
3 providing mechanical protection to existing installation items (Note B)
4 replacing or refixing enclosures of existing installation items (Note C)
Note B Only if the circuit's protective measures are not affected.
Note C Only if added thermal insulation has no effect on the current carrying capacity and on circuit electrical protection (fuses or circuit breakers).
Posted By: CWattersThanks for that.
You misunderstand. The data in that link refers to the cross sectional area of the copper cores (in mm^2) not the size of the outer grey insulation. You need to find out exactly what the wires are.
In a typical house you might find 1 or 1.5mm^2 wire used for lighting and 2.5mm^2 for ring mains. You might also find 6, 10, or 16mm^2 feeding something like a cooker or shower. Perhaps also cables for a PV array.
Many of these wires are capable of carrying more current than they are actually used for. For example I think a 2.5mm^2 wire can carry up 27A or 54A in a ring without insulation. However that document says if the wire is on top of a joist and under 440mm of insulation it should be derated to carry around 16A or 32A for a ring. However many rings are protected by a 32A breaker in the consumer unit so the current is already limited to 32A. In which case no action is required when covering that ring with insulation.
Other sizes of cable may need to be derated by changing the breaker to a smaller one. Sometimes that's not possible. For example a 12kW shower draws 52A. If it was on a 16mm^2 wire the depth of insulation might mean limiting the current to 45A. If you fitted a 45A breaker the 52A shower would probably trip it.
Posted By: gravelldI like the idea of testing it.
Posted By: gravelldSo is the upshot of that that I need to check the wire is 2.5mm (twin)?mm². The squared bit is important but unfortunately electricians habitually leave it out leaving the rest of us not quite sure what is being talked about in odd cases. E.g., are connectors which are not typically used in domestic situations being specified for wire sizes in mm (diameter) or really mm² (cross-sectional area).
Posted By: djhGiven your lack of confidence, I'd suggest that you really do need to get a qualified electrician to have a look and sign off whatever you end up doing.Right. To be clear: my lack of confidence is in my inexperience to perform wiring on a high draw appliance. If I see credible evidence that leads to a solution to this however, I would have confidence in that.