Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.

The AECB accepts no responsibility or liability for any errors or omissions in the content of this site. Views given in posts are not necessarily the views of the AECB.



    • CommentAuthorgravelld
    • CommentTimeAug 6th 2015 edited
     
    I have three electrical cables (not flex - running to an immersion) tied together and run through joists in my loft space. I want to insulate between the joists.

    I know it is not a good idea to bury cables, particularly of a high rating. But it would be costly in terms of time and money to re-route the cables.

    Is is acceptable to run the cables in some sort of conduit or sheathing to maintain an air gap between the cable and the insulation?
  1.  
    The air gap makes little difference to the calculation because they're still buried in insulation, from what I remember.

    What size are the cables (2.5mm^2 ?) and what rating of fuse or breaker are they fed from?

    EDIT are the cables PVC twin&earth or singles?
    •  
      CommentAuthorfostertom
    • CommentTimeAug 6th 2015
     
    The point is, can they cool, or the resistance heat they produce just builds up? Oversizing within insulation is to reduce the resistance to design load, hence reduce the heat produced.
    •  
      CommentAuthordjh
    • CommentTimeAug 6th 2015
     
    Posted By: gravelldBut it would be costly in terms of time and money to re-route the cables.

    Is is acceptable to run the cables in some sort of conduit or sheathing

    Isn't threading them through conduit about as time consuming as laying them on top of the insulation?
  2.  
    Posted By: djh
    Isn't threading them through conduit about as time consuming as laying them on top of the insulation?

    I was assuming that wouldn't be easy since they currently go through the joists, and that the conduit might be something like sections of the trunking with a removable side?

    As to how that affects the calculations, IANAE...
    •  
      CommentAuthorSteamyTea
    • CommentTimeAug 6th 2015
     
    I think this is notifiable work, so you need to be Part P certified or get someone in that is.
    • CommentAuthorgravelld
    • CommentTimeAug 6th 2015
     
    Yes, they go through the joists. The joists are about 150mm deep and they go right through the middle.

    Sorry, I am not an electrician hence my trepidation re. the immersion coil. If they were just going to downlighters I would re-wire myself but I'm not so sure about this.

    Posted By: Andrew_Doran
    What size are the cables (2.5mm^2 ?) and what rating of fuse or breaker are they fed from?

    EDIT are the cables PVC twin&earth or singles?

    Sorry but I can only give a layman's description. They are 10mm wide, flat, grey. At least one of them goes into an MCB with B20 on it - that means 20A?
    • CommentAuthorgravelld
    • CommentTimeAug 6th 2015
     
    Would another option be to run something like chicken wire (hear me out) in an "n" shape over the cable so there's no insulation below the cable, just the plasterboard ceiling below. Then a 20-odd mm gap above (somehow)?
    • CommentAuthorgravelld
    • CommentTimeAug 6th 2015
     
    Posted By: SteamyTeaI think this is notifiable work, so you need to be Part P certified or get someone in that is.
    Even if there's no re-wiring?
    • CommentAuthorEd Davies
    • CommentTimeAug 6th 2015
     
    Would it be feasible to stuff some insulation under the wire (e.g., foil-faced PUR) but leave them freely in contact with the air above? Ie, break the mineral wool or whatever main insulation say 75 mm each side of the cables but make up for the gap with a bit of higher-grade insulation under.
    •  
      CommentAuthorSteamyTea
    • CommentTimeAug 6th 2015 edited
     
    Possibly, there are 'installation methods' to take into account.

    I also think that if you disconnect and reconnect a water heater then it is classed as major work. Not 100% sure on that though (I did my Part P a few years back and it has changed since).

    Quite simply you are going to struggle without rerouting what sounds like twin and earth.
    • CommentAuthorgravelld
    • CommentTimeAug 6th 2015 edited
     
    Posted By: Ed DaviesWould it be feasible to stuff some insulation under the wire (e.g., foil-faced PUR) but leave them freely in contact with the air above? Ie, break the mineral wool or whatever main insulation say 75 mm each side of the cables but make up for the gap with a bit of higher-grade insulation under.
    Yes, definitely feasible. But 75mm! That's quite the 'bridge... If cables were run inside an IWI wall would there be as much as 75mm required either side?

    There's about 70mm underneath the cable.
    • CommentAuthorgravelld
    • CommentTimeAug 6th 2015
     
    Posted By: SteamyTeaPossibly, there are 'installation methods' to take into account.

    I also think that if you disconnect and reconnect a water heater then it is classed as major work. Not 100% sure on that though (I did my Part P a few years back and it has changed since).
    Thanks. Part P or not I don't fancy it!
    • CommentAuthorgravelld
    • CommentTimeAug 6th 2015 edited
     
    http://electrical.theiet.org/wiring-matters/15/current-ratings.cfm?type=pdf

    So what do these current ratings mean? Given a 10mm cable and my target of 400mm+ of loft roll, does this mean the current rating is 35-60A if installed at the bottom of a joist? What does that mean, something goes boom if you demand more than that for "enough" time?

    In fullness, the cables run through joists, or along them at the top of the vertical face of the joist.
    •  
      CommentAuthorjoe90
    • CommentTimeAug 6th 2015
     
    Posted By: Ed DaviesWould it be feasible to stuff some insulation under the wire (e.g., foil-faced PUR) but leave them freely in contact with the air above? Ie, break the mineral wool or whatever main insulation say 75 mm each side of the cables but make up for the gap with a bit of higher-grade insulation under.


    I am with Ed on this one, just put 75mm pir/pur under the wires say 100mm wide and leave above free to air, fill all other voids with wool as described. No touching electrics, no part P, no problem.😀
    • CommentAuthorEd Davies
    • CommentTimeAug 6th 2015
     
    Posted By: gravelldThere's about 70mm underneath the cable.
    So 50 or 60 mm of PUR would leave the cable pretty much in free air and provide enough insulation that it wouldn't be such a terrible cold bridge. Dunno, 75 mm was just the first number I thought of; you just want to make sure that the air round the cable has enough room to convect properly.
    •  
      CommentAuthorcrosbie
    • CommentTimeAug 6th 2015
     
    There's probably a calculation one can do for the vacuum temperature of a conductor of a particular material of a particular diameter carrying a particular current. If this is within tolerable limits then greater losses caused by contact with insulation material would lower the temperature - even if convection provides greater losses.

    Another approach could be to bung a couple of temperature sensors in hot spots along the cable (the most insulated places), either for monitoring or even connecting them to a thermal cut-out of the immersion. You can stress test the cable (immersion on for 6 hours during a hot summer's day in a cold tank) and if it never rises more than 20C above ambient then perhaps that's safe enough?
    • CommentAuthorgravelld
    • CommentTimeAug 6th 2015
     
    I like the idea of testing it. Can anyone suggest some sensors? Would be good to integrate with a rPi or Sheeva Plug or similar.
    • CommentAuthorCWatters
    • CommentTimeAug 6th 2015
     
    Posted By: gravelldhttp://electrical.theiet.org/wiring-matters/15/current-ratings.cfm?type=pdf" rel="nofollow" >http://electrical.theiet.org/wiring-matters/15/current-ratings.cfm?type=pdf

    So what do these current ratings mean? Given a 10mm cable...


    You misunderstand. The data in that link refers to the cross sectional area of the copper cores (in mm^2) not the size of the outer grey insulation. You need to find out exactly what the wires are.

    In a typical house you might find 1 or 1.5mm^2 wire used for lighting and 2.5mm^2 for ring mains. You might also find 6, 10, or 16mm^2 feeding something like a cooker or shower. Perhaps also cables for a PV array.

    Many of these wires are capable of carrying more current than they are actually used for. For example I think a 2.5mm^2 wire can carry up 27A or 54A in a ring without insulation. However that document says if the wire is on top of a joist and under 440mm of insulation it should be derated to carry around 16A or 32A for a ring. However many rings are protected by a 32A breaker in the consumer unit so the current is already limited to 32A. In which case no action is required when covering that ring with insulation.

    Other sizes of cable may need to be derated by changing the breaker to a smaller one. Sometimes that's not possible. For example a 12kW shower draws 52A. If it was on a 16mm^2 wire the depth of insulation might mean limiting the current to 45A. If you fitted a 45A breaker the 52A shower would probably trip it.
    • CommentAuthorEd Davies
    • CommentTimeAug 6th 2015 edited
     
    IANAL or E, either, but I do have a copy of the Electrician's Guide to the 17th Edition… by John Whitfield. There are various exceptions (e.g., in kitchens and bathrooms, ELV lighting, small-scale generators) but the two that seem likely relevant here are:


    3 providing mechanical protection to existing installation items (Note B)
    4 replacing or refixing enclosures of existing installation items (Note C)

    Note B Only if the circuit's protective measures are not affected.
    Note C Only if added thermal insulation has no effect on the current carrying capacity and on circuit electrical protection (fuses or circuit breakers).
    In other words, if the insulation affects the current carrying capacity of the cable (whether that capacity is actually used or not and whether it's still more than the circuit protection allows) then the work is technically notifiable.
    • CommentAuthorgravelld
    • CommentTimeAug 6th 2015 edited
     
    Posted By: CWatters
    You misunderstand. The data in that link refers to the cross sectional area of the copper cores (in mm^2) not the size of the outer grey insulation. You need to find out exactly what the wires are.

    In a typical house you might find 1 or 1.5mm^2 wire used for lighting and 2.5mm^2 for ring mains. You might also find 6, 10, or 16mm^2 feeding something like a cooker or shower. Perhaps also cables for a PV array.

    Many of these wires are capable of carrying more current than they are actually used for. For example I think a 2.5mm^2 wire can carry up 27A or 54A in a ring without insulation. However that document says if the wire is on top of a joist and under 440mm of insulation it should be derated to carry around 16A or 32A for a ring. However many rings are protected by a 32A breaker in the consumer unit so the current is already limited to 32A. In which case no action is required when covering that ring with insulation.

    Other sizes of cable may need to be derated by changing the breaker to a smaller one. Sometimes that's not possible. For example a 12kW shower draws 52A. If it was on a 16mm^2 wire the depth of insulation might mean limiting the current to 45A. If you fitted a 45A breaker the 52A shower would probably trip it.
    Thanks for that.

    So is the upshot of that that I need to check the wire is 2.5mm (twin)? And if so, and if the breakers are 16A or 32A I would be OK to cover? As above it looks to be 20A but will check all cables with my voltage tester pen thing, turning off the MCBs and testing if they are still live.
    •  
      CommentAuthordjh
    • CommentTimeAug 6th 2015
     
    Posted By: gravelldI like the idea of testing it.

    Indeed, it sounds sensible, but unfortunately I don't think it gets you anywhere with the regs.

    Given your lack of confidence, I'd suggest that you really do need to get a qualified electrician to have a look and sign off whatever you end up doing.
    • CommentAuthorEd Davies
    • CommentTimeAug 7th 2015 edited
     
    Posted By: gravelldSo is the upshot of that that I need to check the wire is 2.5mm (twin)?
    mm². The squared bit is important but unfortunately electricians habitually leave it out leaving the rest of us not quite sure what is being talked about in odd cases. E.g., are connectors which are not typically used in domestic situations being specified for wire sizes in mm (diameter) or really mm² (cross-sectional area).

    It'll almost certainly be twin and earth. Live (phase) and neutral wires, each of the specified cross-sectional area, in their own coloured insulation with a bare copper earth wire (usually slightly smaller cross-section, I think) all wrapped in an outer PVC layer of insulation.
    •  
      CommentAuthorSteamyTea
    • CommentTimeAug 7th 2015
     
    I seem to remember that the Neutral is part of the live circuit (why we have double pole switching) and should be treated as a such.
    The Earth is grounded and is not switched.
    This all gets a bit confusing when the Neutral and the Earth are joined together (they usually are somewhere).
    But they do different jobs at different times.

    Never treat a Neutral as zero voltage/current.
    • CommentAuthorgravelld
    • CommentTimeAug 7th 2015 edited
     
    Posted By: djhGiven your lack of confidence, I'd suggest that you really do need to get a qualified electrician to have a look and sign off whatever you end up doing.
    Right. To be clear: my lack of confidence is in my inexperience to perform wiring on a high draw appliance. If I see credible evidence that leads to a solution to this however, I would have confidence in that.
    •  
      CommentAuthorjoe90
    • CommentTimeAug 7th 2015
     
    That's why Ed and I suggested insulating below the cables and leaving air around them to continue to work as they did in the past without any need to touch the cables.
    • CommentAuthorgravelld
    • CommentTimeAug 7th 2015
     
    Sure, thanks to you all for advice. I think I'll do that. I might see if I can construct something with EPS (not touching cable) to keep the loft roll back.
    •  
      CommentAuthorjoe90
    • CommentTimeAug 7th 2015
     
    I do like the simple approach to most thing (kiss), no point in making it more complicated than it needs to be!
    •  
      CommentAuthorcrosbie
    • CommentTimeAug 7th 2015
     
    Frankly, if a mains wire is generating so much heat that it requires convection cooling to avoid a fire hazard, then it's undersized in the first place.
    • CommentAuthorbarney
    • CommentTimeAug 7th 2015
     
    It doesn't take much increase in "heat" to get PVC insulation nice and soft, the conductors migrating, a short circuit occurring but with some impedance and the whole lot to runaway into a fire in the attic

    The safest thing to do is get the cables tight to either the plasterboard ceiling or a joist - it's a good heat sink

    The next best is to get it exposed to air on one side - as suggested above

    If it's surrounded by insulation the current carrying capacity will be degraded by about 50%

    The current carrying capacity of any cable is determined from the internal heating effect (I2R) and the method by which that internal heat can be dissipated - the actual numbers depend on the insulation type and the installation method

    It's all about respecting the thermal limit of the insulation

    Regards

    Barney
   