Posted By: fostertomthe P/A floor reistance method in EN 13370
Posted By: fostertomThe perimeter heat loss is proportional to delta-t - the temp difference between inside and out.
But what is the temp difference to apply to the straight-down heat loss? What is the temp, and at what depth in the subsoil, that heat is being lost straight-down to?
Posted By: TimberI have a copy of that standard you mention so I can check and see if it actually gives a formula.The end-result formula itself is readily available - U = 0.05 + 1.65P/A - 0.6(P/A)^2
Posted By: TimberI also have an excel spreadsheet that I got on the AECB therm course many years ago which allows you to calc the PSI value of a solid ground floor to wall junction based on the PA calc.That'll be the one(s) in http://www.peterwarm.co.uk/?dl_id=2 ? I agree with yr 2nd para comment.
I know that definitely makes all sorts of assumptions that may or may not accurately reflect the real building - those may be same as the official U-Value software I use for floors.
Posted By: Ed DaviesFor any who've not heard the obvious caveat before: water. Specifically, the highest water table for the year.I've been thinking about that, and wonder whether it's an exagerated threat.
Posted By: ringiRemember you are also trying to stop condensation on the floor in summer.Say more?
Posted By: fostertomunder open ground at depth of 1.5 to 3m (varies depending on local subsoil density (or rather, volumetric thermal capacity) and conductivity), the steady year-round temp will equilibriate at the annual average air temp aboveThat, I realise, is wrong - more like 10-12m deep. At 1-2m, it's diurnal fluctuations that disappear
Posted By: fostertomThe end-result formula itself is readily available - U = 0.05 + 1.65P/A - 0.6(P/A)^2
Posted By: fostertomI've been thinking about that, and wonder whether it's an exagerated threat.Interesting link, thanks. Rest of the site looks worth a read, too - bookmarked.
http://www.homeintheearth.com/tech_notes/basics-of-earthsheltering/earth/soil-properties/soil-temperature-experiment
Actually it's not just vertical rise and fall of water table that could carry stored heat away, but also horizontal flow of underground water.Absolutely - that's mostly what I'd worry about.
How to guess what's happening with water in the subsoil beneath your site?Well, if it pisses out of the ground on the downhill side of your house and runs across the road that's a bit of a hint.

Posted By: mike7Shome mishtake shurley? The units don't work, and where is the ground conductivity?I think you have to pretend that the constants have units appropriate to conversion of 1/m or 1/m² to W/m²·K. If you measure P in feet and A in square feet then you have to use different constants. If you measure P in metres and A in square feet you're on your own.
Posted By: fostertomwhat is the rainwater's thermal capacity, totalled over the heating season? How many inches of water? A fraction of the vertical height of the subsoil block that we're interested in. Even allowing that water has 5(?)x the volumetric specific heat of subsoil, by how much will percolating rainfall actually cool the subsoil?If rainwater's not that cold, and doesdn't cool the ground that much, then what makes it supposedly colder than the ground it's in, once it's joined the water table and/or is flowing horizontally underground?
Posted By: fostertomOnce water is deep in the subsoil, the stuff of underground horizontal flow and water table vertical movement, why should its temp be any different from the soil it's in? The deeper its source and the longer in the ground, the warmer it should be - it's horribly hot down a mine!
Posted By: Ed DaviesPosted By: mike7Shome mishtake shurley? The units don't work, and where is the ground conductivity?I think you have to pretend that the constants have units appropriate to conversion of 1/m or 1/m² to W/m²·K. If you measure P in feet and A in square feet then you have to use different constants. If you measure P in metres and A in square feet you're on your own.
Posted By: mike7a conductivity of 1W/mKNot so far off correct.
Posted By: fostertomOnce water is deep in the subsoil, the stuff of underground horizontal flow and water table vertical movement, why should its temp be any different from the soil it's in? The deeper its source and the longer in the ground, the warmer it should be - it's horribly hot down a mine!
Posted By: mike7but the constant adjustment to sort out the watts bit would need to be ..er .. the conductivity. Otherwise it would be a formula only for a conductivity of 1W/mK - woodnit?Aren't they just assuming the conductivity of the ground, which might be 1 W/mK or might be something else; it's buried in with all the other assumptions leading to those magic numbers?