Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorgohuwgo
    • CommentTimeMay 18th 2016
     
    I’m after advice for a wall thermostat to maximise the use we make of the solar heat we generate from our thermal panels. Here’s the issue:-
    In an Alpine climate, on sunny days, our solar system generates lots of lovely hot water. However, production stops when we run out of cold water to heat, and when this happens I’d like to use the excess to start the UFH, using the wall thermostats connecting to the bottom of the water store tank. We can already achieve the same manually when at the building by looking at the temperature stats on the water store, but we’re often not there so would like to do this automatically, and be able to monitor over wifi.

    Currently we have 3 (non wifi) thermostats over the building (one on each of the 3 floors), and they are set to start the heating when the building is used most of the time (post 4pm, and pre 9am). On cloudy / foggy / snowy days I want to keep the heat in the tank, so it’s ready for night time heating / DHW, when it’s needed most. Note the DHW and UFH comes from the same tank – see below.
    I’d like to find a Wifi connected smart wall thermostat that connects to our Akvatherm 1000ltr water store, so we can:-
    1) Control Wall Thermostat remotely via Wifi, and be able to set rules such as: if temp > 35 degs at bottom of tank between 10am and 5pm then direct heat to UFH.
    2) Control the immersion heaters on the water store remotely (the Akvatherm water store has 2 immersion heaters, 6kw each – one for DHW, and the other for heating backup), and check they are working properly.

    I looked at the Nest system, but not sure if this will work for what I want to do (but maybe it does…). There seems so many thermostat variants out there, and am very confused which one would work for our situation. HELP!

    Description of system & environment
    French Alpine chalet for 12 pax (170m2 – 6 bedrooms), situated at 1350 meters. Heating & DHW load required early morning and post skiing (post 4pm). Usually most people are out in the day. Some weeks have zero occupancy, so much reduced DHW load – in these weeks, we have very little cold water to heat for the solar panels to heat.
    Power generation: Solar array of 17.5m2; woodburning fire (16 KW); 2x 6KW immersion heater electric backup for DHW & heating
    Heat Storage: water storage tank (Akvaterm 1000 ltr) plus thermodynamic store of 250ltr acting as a pre heater. The Akvaterm supplies DHW from the top of the tank, and feeds building UFH from the middle of the tank (as per manufacturer’s spec)
    Other: x3 wall thermostats to control UFH. Currently set to times when heating is most required (morning / evening, with lower temps in the day). No direct link from thermostats to water stores, but it would be good to have this.
    •  
      CommentAuthorSteamyTea
    • CommentTimeMay 18th 2016 edited
     
    Posted By: gohuwgoNote the DHW and UFH comes from the same tank – see below.
    In my view that is the problem.
    DHW and Space Heating do different things, at different temperatures and at different times.

    Any way you can separate the two easily and cheaply.
    • CommentAuthorgyrogear
    • CommentTimeMay 18th 2016
     
    S.T. = +1

    sounds like OP needs a three-way temperature-controlled diverting valve, on a stub in the bottom of the DHW cylinder. When the latter gets up to temp, the valve switches and sends the solar feed to a separate thermal store for the UFH.

    or something...

    http://cgproducts.johnsoncontrols.com/met_pdf/977320.pdf

    gg
    • CommentAuthorEd Davies
    • CommentTimeMay 18th 2016
     
    Posted By: gohuwgoI’d like to find a Wifi connected smart wall thermostat…
    You've already got three thermostats. It seems to me that what you want is not a smart thermostat as such but rather a suitable controller to go next to the heat store. Sorry, no particular suggestions but maybe thinking about it a bit differently will help you find something.

    Personally, I'd use a little Linux board like a Raspberry Pi or similar but that might not the the sort of game you want to play - particularly if there are other people staying so you'd have to wrap it up and hide it well to stop people fiddling.

    I can't really see the problem that ST and gg are worrying about as the stratification in the heat store should be enough to keep things apart suitably. Still, two irrelevant questions: what's the water in the Akvatherm? Is it heating water which flows through the UFH (presumably with a blending valve, I imagine) with a heat exchanger to DHW or is it a DHW store with a heat exchanger to the UFH?

    What's a “thermodynamic store” and what does it do?
    •  
      CommentAuthorSteamyTea
    • CommentTimeMay 18th 2016 edited
     
    Posted By: Ed DaviesI can't really see the problem that ST and gg are worrying about as the stratification in the heat store should be enough to keep things apart suitably.
    If we change 'stratification' to 'gradient', then you need quite a large gradient, around 40°C I would think. This probably does not happen unless the vessel is very tall. Would have to try and model it to see if what I mean makes sense.

    Do you know your DHW usage? i.e. how much water at 50 or 60° do you take out of the vessel every day.
    • CommentAuthorgohuwgo
    • CommentTimeMay 18th 2016
     
    Thank you so much for your comments.
    One thing I should probably add is: I have to change one wall thermostat anyway, because the LCD screen has gone, so we can't make any changes to the controller. I was hoping to kill 2 birds with one stone, by buying a new wall (smart) thermostat that I could remotely see the temperature at the bottom of the tank, and (ideally) set an IFTTT rule to start the heating if the temperature was sufficiently high at the bottom of the tank. I wasn't sure if the 3rd generation of Nest could do this (or similar product) - its not clear to me.

    To answer your questions: when we have guests at the chalet, they use around 400-500 litres per day at 40 degs+ (an estimate). Bear in mind the incoming water is very cold. The Akvaterm is about 8ft tall, with the bottom used mainly for solar, and the top for DHW. There are 2 immersion heaters - one for the DHW (higher in the tank) and the other for the UFH (lower in the tank).
    The thermodynamic store is another phrase for a water store with an air pump, but is also linked up to the solar thermal panels, and solar gets priority. This pre heat tank is quite useful because its always hot post ski time, and when guests shower/bath, this feeds in low into the Akvaterm raising the temperature, helping the UFH demands early evening.

    The answer to the question: "What's the water in the Akvaterm" - wood boiler stove feeding hot water at the top, with solar and 2x electric backup lower down. The UFH comes from the middle of the tank and is blended if the temp is too hot. DHW comes from the top, and is always the hottest. Stratification works well.
    • CommentAuthorgyrogear
    • CommentTimeMay 18th 2016 edited
     
    Posted By: Ed DaviesI can't really see the problem that (...) gg (is) worrying about as the stratification in the heat store should be enough to keep things apart suitably


    Well, apparently not, since OP says :

    Posted By: gohuwgoproduction stops when we run out of cold water to heat, and when this happens I’d like to use the excess to start the UFH, using the wall thermostats connecting to the bottom of the water store tank.


    To me (neophyte...) this suggests that the capacity of the thermal storage (or more to the point, the upstream SHW tank feeding into the thermal storage) is too low, for OP's solar thermal potential...

    Whence my agreement with ST's proposition of needing a second storage to separate the DHW from the heating...

    (at the time of my suggestion, I had not devined that OP *was* actually using a second storage for his solar HW)

    gg
    • CommentAuthorgyrogear
    • CommentTimeMay 18th 2016
     
    Posted By: gohuwgoHowever, production stops when we run out of cold water to heat,


    gohuwgo,

    Does "Alpine climate," mean France by any chance ?

    I note you have a
    Posted By: gohuwgoSolar array of 17.5m2;


    Is this a hot-air collector, feeding your heat-pump water tank, or a hot-water collector ? (or both ?)

    Any idea of the output (in kWh) of solar collector ?
    What is the capacity of the "ballon thermodynamique" ? (in kWh)
    Otherwise, angle of inclination and azimuth of collector ?

    gg
  1.  
    Posted By: gohuwgoIn an Alpine climate, on sunny days, our solar system generates lots of lovely hot water. However, production stops when we run out of cold water to heat, and when this happens I’d like to use the excess to start the UFH, using the wall thermostats connecting to the bottom of the water store tank.
    This can probably more easily be achieved using the solar controller. Most have a heat "dump" or "diverter" function which can be activated when the main thermal store is satisfied. This output could be used to start the UFH, overriding the heating controller &/or room thermostats. Although you would need to think about how to avoid over-heating.

    Posted By: gohuwgoWe can already achieve the same manually when at the building by looking at the temperature stats on the water store, but we’re often not there so would like to do this automatically, and be able to monitor over wifi.
    Remote monitoring is a lot easier than remote control. Do you really need remote control? Do you really want to be sat there waiting for the tank temperature to get to the right point before remotely throwing the switch? What happens if you're at work, on holiday, ill, etc?

    From a technological point of view, remote control over the internet is almost trivial. The problem is integrating all the different pieces of hardware with different electrical interfaces, voltages, polarities, etc and controlling this from a common software platform. You either do it yourself as Ed describes or pay a lot of money for someone else to do it. In the latter case you will likely be forced to change a lot of the hardware to make it compatible with their software!

    And watch out for them removing support at a later date. Product life cycles in consumer electronics are a lot shorter than those in houses & heating systems.

    David
    •  
      CommentAuthordjh
    • CommentTimeMay 19th 2016 edited
     
    davidfreeborough advised: "watch out for them removing support at a later date. Product life cycles in consumer electronics are a lot shorter than those in houses & heating systems."

    Infamously
    https://www.theguardian.com/technology/2016/apr/05/revolv-devices-bricked-google-nest-smart-home

    Note also that security is an issue with any remote access and especially so for remote control.

    Edit: link corrected.
    • CommentAuthorEd Davies
    • CommentTimeMay 19th 2016
     
    Posted By: gyrogear: “To me (neophyte...) this suggests that the capacity of the thermal storage (or more to the point, the upstream SHW tank feeding into the thermal storage) is too low, for OP's solar thermal potential...”

    If the store is large enough to deal with the evening and next morning's DHW and UFH needs, or whatever the criteria are, then it's large enough. Making it larger just to store more heat because it's available is pointless - much better to move the excess available heat to storage elsewhere like in the floor slab, walls, etc, where it's more useful. That's the control problem which the OP is asking about.

    Posted By: davidfreeborough: ”You either do it yourself as Ed describes or pay a lot of money for someone else to do it. In the latter case you will likely be forced to change a lot of the hardware to make it compatible with their software!”

    If a completely DIY solution is too much then maybe something can be done using:

    https://openenergymonitor.org/emon/

    I haven't yet explored what they do properly yet but they do do some control functions. I think MQQT (which they use) integrates with IFTTT somehow.

    I share DavidF's scepticism of basing the system around some web service that could go away any time. I feel this sort of thing ought to be able to run autonomously, without an internet connection, in a reasonably sensible manner and that any connection is just used for monitoring and tuning. Having a third party involved is a potential source of headache but sort-of handy to get round the hassles with IPv4 and NAT, etc. Beyond that I don't see the point.
    • CommentAuthorEd Davies
    • CommentTimeMay 19th 2016
     
    DJH, is that the right link?
    •  
      CommentAuthordjh
    • CommentTimeMay 19th 2016
     
    Posted By: Ed DaviesIf a completely DIY solution is too much then maybe something can be done using:

    https://openenergymonitor.org/emon/

    I haven't yet explored what they do properly yet but they do do some control functions. I think MQQT (which they use) integrates with IFTTT somehow.

    Thanks for that posting, Ed. They didn't do much in the way of control as far as I knew so your post prompted me to check. Things appear to have moved on. As well as the MQQT interface they also seem to interface to Lightwave RF - https://guide.openenergymonitor.org/integrations/lightwaverf/ - which may well mean emon etc could be used to meet the OP's requirements.
    • CommentAuthorgyrogear
    • CommentTimeMay 19th 2016
     
    Posted By: Ed Daviesmuch better to move the excess available heat to storage elsewhere like in the floor slab, walls, etc, where it's more useful. That's the control problem which the OP is asking about.


    Thanks, Ed, I get your point.

    gg