		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=248952#Comment_248952</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=248952#Comment_248952</guid>
		<pubDate>Thu, 27 Oct 2016 10:31:41 +0100</pubDate>
		<author>delprado</author>
		<description>
			<![CDATA[Is there a calculator for this? I have the original holes from my 1920s house, but I am not convinced it is enough.]]>
		</description>
	</item>
	<item>
		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=248966#Comment_248966</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=248966#Comment_248966</guid>
		<pubDate>Thu, 27 Oct 2016 12:25:53 +0100</pubDate>
		<author>CWatters</author>
		<description>
			<![CDATA[Approved Doc C says the free area should be...<br /><br />"1500mm^2/m run of external wall or 500mm^2/m^2 of floor area whichever is the greater"<br /><br />Page 26 - 4.14b<br /><br /><a href="https://www.gov.uk/government/uploads/system/uploads/attachment_data/file/431943/BR_PDF_AD_C_2013.pdf" target="_self" rel="nofollow">https://www.gov.uk/government/uploads/system/uploads/attachment_data/file/431943/BR_PDF_AD_C_2013.pdf</a><br /><br />I think the NHBC recommend the vents are distributed on 2m centres.]]>
		</description>
	</item>
	<item>
		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=248973#Comment_248973</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=248973#Comment_248973</guid>
		<pubDate>Thu, 27 Oct 2016 14:52:53 +0100</pubDate>
		<author>delprado</author>
		<description>
			<![CDATA[Yeah I saw this, but like every building reg I don't trust it at first sight and wondered if there was any wisdom here that means I should do something else?]]>
		</description>
	</item>
	<item>
		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=248991#Comment_248991</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=248991#Comment_248991</guid>
		<pubDate>Thu, 27 Oct 2016 22:58:26 +0100</pubDate>
		<author>gyrogear</author>
		<description>
			<![CDATA[(1) What are the joists made of ?<br />(2) Where is the ventilation air coming from (and going to...).<br /><br />gg]]>
		</description>
	</item>
	<item>
		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=248997#Comment_248997</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=248997#Comment_248997</guid>
		<pubDate>Fri, 28 Oct 2016 07:11:02 +0100</pubDate>
		<author>delprado</author>
		<description>
			<![CDATA[Joists are timber. Diagram shows ventilation pattern here:<br /><br /><a href="http://s10.postimg.org/kpgkttc6x/plan.jpg" target="_self" rel="nofollow">http://s10.postimg.org/kpgkttc6x/plan.jpg</a>]]>
		</description>
	</item>
	<item>
		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249001#Comment_249001</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249001#Comment_249001</guid>
		<pubDate>Fri, 28 Oct 2016 08:24:10 +0100</pubDate>
		<author>Victorianeco</author>
		<description>
			<![CDATA[Block them up and pump with EPS?]]>
		</description>
	</item>
	<item>
		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249004#Comment_249004</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249004#Comment_249004</guid>
		<pubDate>Fri, 28 Oct 2016 08:53:36 +0100</pubDate>
		<author>Sprocket</author>
		<description>
			<![CDATA[I'm sure I remember someone in here suggesting Leca (or something like that) for this purpose many years ago.<br />Can anyone comment on pros and cons?]]>
		</description>
	</item>
	<item>
		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249005#Comment_249005</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249005#Comment_249005</guid>
		<pubDate>Fri, 28 Oct 2016 08:59:19 +0100</pubDate>
		<author>Nick Parsons</author>
		<description>
			<![CDATA['' I have the original holes from my 1920s house, but I am not convinced it is enough.''<br /><br />Are you convinced it's *not* enough? (And if so, by what symptoms?)<br /><br />Since I note your subsequent post re u/floor insulation you are definitely right to question the amount and flow of ventilation air. I (and others - viz a lot of discussion in AECB) find that under-floor insulation applications don't always behave as one might expect them to.]]>
		</description>
	</item>
	<item>
		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249009#Comment_249009</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249009#Comment_249009</guid>
		<pubDate>Fri, 28 Oct 2016 10:13:11 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Sprocket</cite>someone in here suggesting Leca</blockquote>This one?<br />Not so legible as a jpg - click fostertom and tell me yr email and I'll send you the pdf.]]>
		</description>
	</item>
	<item>
		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249017#Comment_249017</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249017#Comment_249017</guid>
		<pubDate>Fri, 28 Oct 2016 11:24:08 +0100</pubDate>
		<author>gyrogear</author>
		<description>
			<![CDATA[I blocked mine up (interestingly, they are / were the exact size as stated in the (so-called...) "guidance").<br /><br />Could not understand why they were there: admitting cold air in winter so UFH was working overtime to warm the crawlspace !  and warm air in the summer, rusting up my plumbing and condensing on the (muck) floor !<br /><br />So insulated CS walls & house has been *much* warmer & THE CS MUCH dryer ever since !<br />(Am now concreting the CS floor...)<br /><br />gg<br /><br />edited : it is the *CS* that is much dryer (not the house!) (the house has always been dry !) <img src="/newforum/extensions/Vanillacons/smilies/standard/shocked.gif" alt=":shocked:" title=":shocked:" />]]>
		</description>
	</item>
	<item>
		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249019#Comment_249019</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249019#Comment_249019</guid>
		<pubDate>Fri, 28 Oct 2016 11:52:44 +0100</pubDate>
		<author>Ed Davies</author>
		<description>
			<![CDATA[gg, have you been monitoring the humidity in your crawlspace?]]>
		</description>
	</item>
	<item>
		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249040#Comment_249040</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249040#Comment_249040</guid>
		<pubDate>Fri, 28 Oct 2016 23:07:55 +0100</pubDate>
		<author>gyrogear</author>
		<description>
			<![CDATA[Yes, Ed, although I am not sure how well, or what it all means !<br /><br />For past year or more, I have had a weather station (base) in the kitchen, with temp and RH, and a slave transmitter for temp and RH, down in the CS.<br />I don't (yet) have a data logger, so my method is to take occasional photos, then copy these to my PC; I then file them by Month, and by Day.  I have started grabbing them into an XL file, it is very laborious !<br /><br />My aim is to establish a one-year record.<br />However, as I see it, the weak point is, I do not have the external RH of the day, against which to compare - for that, I have to visit the local weather station via internet. For example, today our local RH was 84%, and the CS is currently at 83%...<br /><br />========= <br />Otherwise:<br /><br />Lowest CS RH observed = 74% (12 OCT 2016) (Lounge RH = 38% = a very dry & sunny autumn afternoon).<br /><br />Highest RH observed = 98% (after 10 daysâ€™ absence, no heating on) at 30th Dec. 2015 @ 6 p.m. (Lounge at 16Â°C and 62% RH, CS at 15Â°C and 98% RH) (we went on holiday and the house was not heated).<br /><br />Prior to blocking the vents, I have no idea what the CS RH was - it was certainly smelly, moist and very uninviting... <br />====================<br />I have to confess that my main point of interest is the CS *temperature*, not the RH...<br />(I don't live down there !)<br /><br />gg]]>
		</description>
	</item>
	<item>
		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249057#Comment_249057</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249057#Comment_249057</guid>
		<pubDate>Sat, 29 Oct 2016 13:14:13 +0100</pubDate>
		<author>Ed Davies</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: gyrogear</cite>Lowest CS RH observed = 74%</blockquote>That's not ideal but<br /><br /><blockquote >Highest RH observed = 98%</blockquote>that's truly scary if it lasts long.<br /><br /><blockquote >(I don't live down there !)</blockquote>Yet.<br /><br />Remembering my father's leg going through the floor of my ground floor bedroom when I was about 6 or 7 due to the joists rotting away after a water leak. The flowing water wasn't directly in contact with the joists (just flowing across the ground) but must have been pushing the RH way up.]]>
		</description>
	</item>
	<item>
		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249063#Comment_249063</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249063#Comment_249063</guid>
		<pubDate>Sat, 29 Oct 2016 17:34:53 +0100</pubDate>
		<author>gyrogear</author>
		<description>
			<![CDATA[LOL !<br /><br />Actually, I have *concrete* joists !<br /><br />gg]]>
		</description>
	</item>
	<item>
		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249066#Comment_249066</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249066#Comment_249066</guid>
		<pubDate>Sat, 29 Oct 2016 19:24:04 +0100</pubDate>
		<author>Ed Davies</author>
		<description>
			<![CDATA[So, helpful advice to somebody with timber joists to say you blocked your vents up without mentioning that your joists are concrete. <img src="/newforum/extensions/Vanillacons/smilies/standard/devil.gif" alt=":devil:" title=":devil:" />]]>
		</description>
	</item>
	<item>
		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249075#Comment_249075</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249075#Comment_249075</guid>
		<pubDate>Sat, 29 Oct 2016 22:47:06 +0100</pubDate>
		<author>gyrogear</author>
		<description>
			<![CDATA[yes, admittedly, My Bad<br /><br />Severe apologies for that...<br /><img src="/newforum/extensions/Vanillacons/smilies/standard/shamed.gif" alt=":shamed:" title=":shamed:" /><br /><br />However, that admittedly belated parameter does not prevent the OP from consdering blocking *HIS* - depends on how humid his conditions are...<br /><br />If the underfloor is an accessible crawlspace, it could be conditioned, by blocking the vents; encapsulating the floor; and insulating the periphery walls, to make a conditioned crawl...<br /><br />Air could then be drawn in from the heated volume, and expelled through one of the blocked vents - <br /><br />I found this on a blog: http://www.energyvanguard.com/blog-building-science-HERS-BPI/bid/70974/What-Is-the-Best-Way-to-Deal-with-Crawl-Space-Air<br /> <br />"continuously operated mechanical exhaust ventilation at a rate equal to 1 cfm for each 50 square feet of crawl space floor area.â€ <br />(The makeup air entering the crawl space is conditioned air from the house upstairs; since this conditioned air is drier than outdoor air, it doesn't lead to condensation problems.)<br /><br />Hope this helps some, and goes some way towards correcting my earlier concrete (non-abstract...) omission <img src="/newforum/extensions/Vanillacons/smilies/standard/sad.gif" alt=":sad:" title=":sad:" /><br /><br />gg]]>
		</description>
	</item>
	<item>
		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249079#Comment_249079</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249079#Comment_249079</guid>
		<pubDate>Sun, 30 Oct 2016 06:55:51 +0000</pubDate>
		<author>delprado</author>
		<description>
			<![CDATA[Thanks for your thoughts. I am wondering if there is any benefit of laying limecrete along the mud floor in the void]]>
		</description>
	</item>
	<item>
		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249083#Comment_249083</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249083#Comment_249083</guid>
		<pubDate>Sun, 30 Oct 2016 11:25:50 +0000</pubDate>
		<author>gyrogear</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: delprado</cite>if there is any benefit of laying limecrete along the mud floor</blockquote><br /><br />well, that is what I am currently engaged in !<br /><br />http://voices.yahoo.com/how-rid-moisture-crawl-space-6367824.html?cat=6<br /><br />QUOTE<br />â€œFor those that have concrete surface spaces, consider yourselves fortunate. These finished crawl spaces have sealed protection against unwanted water and create much appreciated surface area to stow away several items as storage".<br /><br />I suspect that even lime-stabilization would be better than nothing...<br /><br />gg]]>
		</description>
	</item>
	<item>
		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249092#Comment_249092</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249092#Comment_249092</guid>
		<pubDate>Sun, 30 Oct 2016 16:30:23 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: gyrogear</cite>http://voices.yahoo.com/how-rid-moisture-crawl-space-6367824.html?cat=6</blockquote><br />That redirects to a generic yahoo front page for me. So I don't have any information except what you posted.<br /><br />Neither concrete nor limecrete provide a barrier against damp, so unless there's a damp proof course somewhere I doubt it will reduce humidity much.]]>
		</description>
	</item>
	<item>
		<title>How much underfloor ventilation is needed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249119#Comment_249119</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14655&amp;Focus=249119#Comment_249119</guid>
		<pubDate>Mon, 31 Oct 2016 12:29:29 +0000</pubDate>
		<author>gyrogear</author>
		<description>
			<![CDATA[Hmmm....  apologies for the bad link, I ended up contramoggrifying it with a keyword search - here is a fresh link...<br /><br />http://itchyfish.com/how-to-get-rid-of-moisture-in-a-crawl-space/<br /><br />gg]]>
		</description>
	</item>
	