			<![CDATA[I had planned to build my roof from 300mm Finn I joists, hip roof, no purlins, two mtr ridge, osb lined inside for racking and vapour barrier, full fill with 300 mm batt insulation, felt, battens, slates etc. I have been told this is incalculable for the roof by the I beam suppliers! They are talking ( to my builder who I trust) about a raised tie truss roof battened out to 300 for insulation and using a glulam ridge beam or even needing steels in some way.<br /> <br />With regard the glulam ridge beam ( which I cannot see the need for) I have had this discussion before, with a pitched roof the ridge beam simply ties the two sets of rafters together and carries no weight as such. If ( like a loft conversion) one pitch was removed then yes a beam, steel or glulam is needed to carry the weight of the slope retained but with equal and opposite slopes surely this is not required.<br /> <br />Surely 300mm I joists over a 5 mtr span at an angle of 35 degrees is not rocket science to calculate ( I<br /> wish I had become a SE or at least learnt the theory before I started this project). We are also getting into the realms of paying for an S.E. to make these calculations which obviously I would like to avoid. <br /> <br />So, am I barking up the wrong tree?, am I trying to be too simplistic?, I cannot for the life of me see the requirement for steels.<br /> <br />HELP]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252685#Comment_252685</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252685#Comment_252685</guid>
		<pubDate>Mon, 09 Jan 2017 21:36:38 +0000</pubDate>
		<author>owlman</author>
		<description>
			<![CDATA[Maybe they are altogether unhappy at using the I joists as rafters, 'cos they think they may not be best suited to some aspect of roof loading?]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252687#Comment_252687</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252687#Comment_252687</guid>
		<pubDate>Mon, 09 Jan 2017 21:56:26 +0000</pubDate>
		<author>Peter_in_Hungary</author>
		<description>
			<![CDATA[You could find that the I beam suppliers are unhappy about the use of their product outside of its normal use. They won't want to approve any nonstandard application (liability insurance etc.).<br /><br />You might find that in the end you will need an SE (with professional liability insurance) to calculate and assure the design. Such things happen when you step out of the 'deemed to satisfy' or the standard loading tables areas of building design]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252689#Comment_252689</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252689#Comment_252689</guid>
		<pubDate>Mon, 09 Jan 2017 22:22:38 +0000</pubDate>
		<author>tychwarel</author>
		<description>
			<![CDATA[My roof is a 30 degree hipped roof 5 metre span 9 metres length, so very similar to yours and done in 300mm finn frame joists, if I can remember how to I will put some photos up]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252691#Comment_252691</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252691#Comment_252691</guid>
		<pubDate>Mon, 09 Jan 2017 22:35:46 +0000</pubDate>
		<author>tychwarel</author>
		<description>
			<![CDATA[[URL=<a href="http://s1214.photobucket.com/user/nantcoly/media/Ty%20chwarel%20build%20blog/roof%20structure/008.jpg.html][IMG]http://i1214.photobucket.com/albums/cc492/nantcoly/Ty%20chwarel%20build%20blog/roof%20structure/008.jpg[/IMG][/URL]" target="_self" rel="nofollow">http://s1214.photobucket.com/user/nantcoly/media/Ty%20chwarel%20build%20blog/roof%20structure/008.jpg.html][IMG]http://i1214.photobucket.com/albums/cc492/nantcoly/Ty%20chwarel%20build%20blog/roof%20structure/008.jpg[/IMG][/URL]</a><br /><br />[URL=<a href="http://s1214.photobucket.com/user/nantcoly/media/Ty%20chwarel%20build%20blog/roof%20structure/008.jpg.html][IMG]http://i1214.photobucket.com/albums/cc492/nantcoly/Ty%20chwarel%20build%20blog/roof%20structure/008.jpg[/IMG][/URL]" target="_self" rel="nofollow">http://s1214.photobucket.com/user/nantcoly/media/Ty%20chwarel%20build%20blog/roof%20structure/008.jpg.html][IMG]http://i1214.photobucket.com/albums/cc492/nantcoly/Ty%20chwarel%20build%20blog/roof%20structure/008.jpg[/IMG][/URL]</a>]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252692#Comment_252692</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252692#Comment_252692</guid>
		<pubDate>Mon, 09 Jan 2017 22:40:46 +0000</pubDate>
		<author>tychwarel</author>
		<description>
			<![CDATA[<a href="http://s1214.photobucket.com/user/nantcoly/media/Ty%20chwarel%20build%20blog/roof%20structure/008.jpg.html" target="_self" rel="nofollow">http://s1214.photobucket.com/user/nantcoly/media/Ty%20chwarel%20build%20blog/roof%20structure/008.jpg.html</a>]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252697#Comment_252697</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252697#Comment_252697</guid>
		<pubDate>Tue, 10 Jan 2017 07:47:30 +0000</pubDate>
		<author>SteamyTea</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: joe90</cite>I wish I had become a SE or at least learnt the theory before I started this project</blockquote>Never too late<br /><br />http://web.mit.edu/4.441/1_lectures/1_lecture5/1_lecture5.html]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252707#Comment_252707</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252707#Comment_252707</guid>
		<pubDate>Tue, 10 Jan 2017 11:13:48 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[In my experience the suppliers employ the structural engineers who do the calculations for the beam structure and sign it off. So it might be worth trying some other suppliers since they will employ different engineers.<br /><br />Tychwarel, as well as photos, can you remember who supplied your roof?<br /><br />It might also be worth contacting one or two manufacturers (Metsa etc) to see if they can help.]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252709#Comment_252709</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252709#Comment_252709</guid>
		<pubDate>Tue, 10 Jan 2017 11:23:43 +0000</pubDate>
		<author>joe90</author>
		<description>
			<![CDATA[Tychwarel, thanks for that, very informative and yours looks more complicated than ours and needed a ridge beam ( but I understand why from your pics) I would like to know of anyone who has had a design done for a similar I beam roof as I am convincinced there is a fairly easy solution to this problem.<br /><br />Nick, yes never too late and I would be interested to learn just wish I had done it already to get me out of this mess.]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252717#Comment_252717</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252717#Comment_252717</guid>
		<pubDate>Tue, 10 Jan 2017 13:04:43 +0000</pubDate>
		<author>Ed Davies</author>
		<description>
			<![CDATA[My SE and potential suppliers (will order some time next month) for roof rafters were both quite happy with JJI (from James Jones) I-beams for rafters. SE specified the basics, supplier the details of the blocking.<br /><br />Mine will have a ridge beam but it's not that heavy - slices of ply staggered and bolted together.<br /><br />Starting from scratch I think the big thing I'd want to learn a lot more about is structural engineering. My house would eventually need an SE sign off anyway but having a detailed plan which was generally plausible but just needed a few tweaks would have saved me a bit of hassle and left me with a design I was happier with the construction of, I think.]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252738#Comment_252738</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252738#Comment_252738</guid>
		<pubDate>Tue, 10 Jan 2017 18:47:19 +0000</pubDate>
		<author>ringi</author>
		<description>
			<![CDATA[I wish there were architects that understood structural engineering and â€œbuildabilityâ€, it seems that architects donâ€™t care how hard it is to build, or what size beams will be needed for their nice shapes, structural engineering donâ€™t think about how beams will be moved etc, and builders donâ€™t understand the â€œwhyâ€ of most of what they doâ€¦.]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252740#Comment_252740</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252740#Comment_252740</guid>
		<pubDate>Tue, 10 Jan 2017 18:56:54 +0000</pubDate>
		<author>Fred56</author>
		<description>
			<![CDATA["Nick, yes never too late and I would be interested to learn just wish I had done it already to get me out of this mess."<br /><br />Try OU T357, introduces the basics and a good understanding.<br /><br />Bits of it are free through the OpenLearn portal.]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252742#Comment_252742</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252742#Comment_252742</guid>
		<pubDate>Tue, 10 Jan 2017 19:13:51 +0000</pubDate>
		<author>Peter_in_Hungary</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: ringi</cite>I wish there were architects that understood structural engineering and â€œbuildabilityâ€, it seems that architects donâ€™t care how hard it is to build, or what size beams will be needed for their nice shapes</blockquote><br />Architects have the dreams, the SEs job is make sure the dreams don't fall down..........Daughter-in-law an architect, Son-in-law a SE.<img src="/newforum/extensions/Vanillacons/smilies/standard/cool.gif" alt=":cool:" title=":cool:" /><img src="/newforum/extensions/Vanillacons/smilies/standard/cool.gif" alt=":cool:" title=":cool:" />]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252744#Comment_252744</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252744#Comment_252744</guid>
		<pubDate>Tue, 10 Jan 2017 19:59:48 +0000</pubDate>
		<author>joe90</author>
		<description>
			<![CDATA[Well I think I have sort out my problem without an S.E., I found a supplier that has a very good web site that lists with diagrams what is achievable and yes with a smallish ridge beam I can achieve what I want. Tomorrow I will be doing drawings and referring to this site and ask the builder to forward it onto his supplier. If it's successful I will post what I propose/found for others who may have similar problems.<br /><br />Thanks guys]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252758#Comment_252758</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252758#Comment_252758</guid>
		<pubDate>Wed, 11 Jan 2017 14:42:37 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Joe, sounds like you have basically a monocoque shape (if you can assume it's 'closed' at floor level) which should be calculable as such by a SE - the sheathing doing most of the work - but then would you need I-beams when all you really need is to connect the sheet edges together and make sure they don't sag too much between those edges?]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252760#Comment_252760</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252760#Comment_252760</guid>
		<pubDate>Wed, 11 Jan 2017 16:02:54 +0000</pubDate>
		<author>joe90</author>
		<description>
			<![CDATA[Ft, I agree with you and have ( as above) found a website ( BBA approved) that spells this out, I have sent it to my builder to hopefully get the nod. I have spent money on an S.E before when in my opinion it was not really required ( once bitted twice shy).<br /><br />Main reason for I beams as rafters is they give me 300mm depth for insulation without massive timbers ( warm roof)I will report back, wish me luck.]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252765#Comment_252765</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252765#Comment_252765</guid>
		<pubDate>Wed, 11 Jan 2017 21:33:29 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Anywhere near Devon Joe? My favourite SE is brilliant, quick to understand, does minimal paperwork knowing that I like to do the drawing-up, earns every penny.]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252767#Comment_252767</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252767#Comment_252767</guid>
		<pubDate>Wed, 11 Jan 2017 22:30:25 +0000</pubDate>
		<author>Ed Davies</author>
		<description>
			<![CDATA[Stunningly, he's actually put his location in his profile. Nearish Devon - at least seen from this distance. <img src="/newforum/extensions/Vanillacons/smilies/standard/wink.gif" alt=":wink:" title=":wink:" />]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252769#Comment_252769</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252769#Comment_252769</guid>
		<pubDate>Thu, 12 Jan 2017 07:09:49 +0000</pubDate>
		<author>SteamyTea</author>
		<description>
			<![CDATA[Joe90 can smell the pasties where he is.  On the wrong side of the border though as far as the planning department is concerned.]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252771#Comment_252771</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252771#Comment_252771</guid>
		<pubDate>Thu, 12 Jan 2017 08:51:29 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Not exacly from Bristol, unless the pasties have got there on a Ginsters truck! I've PM'd Joe, recommending <a href="http://pasquibbs.co.uk" target="_self" rel="nofollow">http://pasquibbs.co.uk</a>]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252772#Comment_252772</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252772#Comment_252772</guid>
		<pubDate>Thu, 12 Jan 2017 09:26:42 +0000</pubDate>
		<author>SteamyTea</author>
		<description>
			<![CDATA[Careful Tom, you will be putting the jam and cream on the wrong way on your scone if you are not careful.<br />That is then a very slippery slope.<br />If anyone is interested, and I doubt if they are.  It is pronounced scone (with a capital O) before it is eaten, and scone (as in gone) once eaten.]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252774#Comment_252774</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252774#Comment_252774</guid>
		<pubDate>Thu, 12 Jan 2017 10:08:28 +0000</pubDate>
		<author>joe90</author>
		<description>
			<![CDATA[For anybody else that needs help with I beams here is a very good site that describes what can be done and how.<br /><br /><a href="http://www.donnybrooktimberframes.co.uk/files/I-Joists%20-%20Boise%20UK%20Technical%20Guide.pdf" target="_self" rel="nofollow">http://www.donnybrooktimberframes.co.uk/files/I-Joists%20-%20Boise%20UK%20Technical%20Guide.pdf</a><br /><br />I am hoping this will sort my problem out, if not I will be in touch with the S.E. that ft recommends.]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252777#Comment_252777</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252777#Comment_252777</guid>
		<pubDate>Thu, 12 Jan 2017 10:57:46 +0000</pubDate>
		<author>dickster</author>
		<description>
			<![CDATA[Hi Joe 90,<br /><br />We have an I beam roof (walls and floor) with 300mm insulation. Look for Little Dockens build part 2 (?) video on Youtube, Might be of help]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252778#Comment_252778</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252778#Comment_252778</guid>
		<pubDate>Thu, 12 Jan 2017 11:42:34 +0000</pubDate>
		<author>joe90</author>
		<description>
			<![CDATA[Hi dickster, thanks, will look at that closely.ðŸ‘]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252782#Comment_252782</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252782#Comment_252782</guid>
		<pubDate>Thu, 12 Jan 2017 12:23:54 +0000</pubDate>
		<author>Greenfish</author>
		<description>
			<![CDATA[Another design suggestion for you Joe, use a "parallel chord scissor truss".  We used such a thing in part of our new build to gain an attic room, 400mm deep space for insulation etc. and the truss companies can do the stress calc for roofs. I had to ring around a bit before I found a couple of truss companies prepared to try the calcs (not totally standard so had to do more than press one button), but they both said that the result was surprizingly good.]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252785#Comment_252785</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252785#Comment_252785</guid>
		<pubDate>Thu, 12 Jan 2017 13:33:06 +0000</pubDate>
		<author>joe90</author>
		<description>
			<![CDATA[Sorry guys but this is bugging me so I needed to do a drawing, now from my very simplistic drawing I fail to understand why "W" needs support from below<br />1/.  flex is the bend within the rafter and it depends on the weight and depth of the timber/ijoist<br />2/. Spread is the tension in the ceiling joists created by the weight of the whole roof ( I admit this could be less if a ridge beam were installed)<br />3/. W1 is the equal weight on both wall plates of the whole roof ( unless a ridge beam is installed)<br />4/. W2 is the equal and opposite weight both sides of the roof create by resting on one another ( think of house of cards) <br /> <br />The various pressures are dependant on angle a.<br /> <br />therefore if all the above is adequate there is no need for W to be supported I.e. No ridge beam.]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252786#Comment_252786</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252786#Comment_252786</guid>
		<pubDate>Thu, 12 Jan 2017 13:34:18 +0000</pubDate>
		<author>joe90</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: joe90</cite>Sorry guys but this is bugging me so I needed to do a drawing, now from my very simplistic drawing I fail to understand why "W" needs support from below<br />1/.  flex is the bend within the rafter and it depends on the weight and depth of the timber/ijoist<br />2/. Spread is the tension in the ceiling joists created by the weight of the whole roof ( I admit this could be less if a ridge beam were installed)<br />3/. W1 is the equal weight on both wall plates of the whole roof ( unless a ridge beam is installed)<br />4/. W2 is the equal and opposite weight both sides of the roof create by resting on one another ( think of house of cards)<br /><br />The various pressures are dependant on angle a.<br /><br />therefore if all the above is adequate there is no need for W to be supported I.e. No ridge beam.</blockquote><br /><br /><br />Oops unable to load diagram it says it's too big! ( I think this is an iPad problem)]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252787#Comment_252787</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252787#Comment_252787</guid>
		<pubDate>Thu, 12 Jan 2017 13:48:48 +0000</pubDate>
		<author>SteamyTea</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: joe90</cite>I think this is an iPad problem</blockquote>Probably just the image too big.<br />But there is an "i" in Sh!t <img src="/newforum/extensions/Vanillacons/smilies/standard/wink.gif" alt=":wink:" title=":wink:" />]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252799#Comment_252799</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252799#Comment_252799</guid>
		<pubDate>Thu, 12 Jan 2017 15:51:38 +0000</pubDate>
		<author>joe90</author>
		<description>
			<![CDATA[Yes ST, problem is I drew it and took a photo, I don't know how to make the photo smaller in data terms.]]>
		</description>
	</item>
	<item>
		<title>Help needed with I beam roofing design</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252800#Comment_252800</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=14821&amp;Focus=252800#Comment_252800</guid>
		<pubDate>Thu, 12 Jan 2017 15:56:42 +0000</pubDate>
		<author>SteamyTea</author>
		<description>
			<![CDATA[It is all do to with the width and height and colour depth.<br />Generally a 800pixel by 600pixel will be small enough.<br />There should be an option to resize and save the image on the iCant Do It somewhere.<br /><br /><a href="http://www.iosappweekly.com/resize-photos-iphone-ipad/" target="_self" rel="nofollow">http://www.iosappweekly.com/resize-photos-iphone-ipad/</a>]]>