Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




  1.  
    We are collecting rain water in a large header tank. It's very satisfying! One issue is manually filling it when the weather is dry for a long time. I'd like some kind of ball valve that only fills up the bottom 10% of the tank to prevent it running dry. Normally ball valves keep the tank topped right up.

    Any ideas on how to achieve this?

    Comments gratefully received.
    • CommentAuthortony
    • CommentTimeOct 14th 2018
     
    What I did was to fit a second mains fed ball valve 150mm above the rainwater one with a bespoke longer arm, the float sits below the normal water level of the rain water controlled by its own ball valve, the cistern refills once a day from my underground rain tank pump. When rainwater is exhausted the mains fills the cistern about half full til it rains again then does nothing more till the next drought
  2.  
    Thanks Tony, that's asking the lines I was thinking. There's quite a big difference between the levels though, so a bespoke arm might be a bit contorted.
    • CommentAuthormike7
    • CommentTimeOct 15th 2018 edited
     
    Assuming the 2nd ball valve has to be at the top of the tank so you can get at it, I'd remove the ball from the valve arm, fix it to one end of a rod with the other end pinned to the arm, the rod being of such a length that the ball dangles down close to the bottom of the tank. The rod would need a running guide of some sort near the ball to keep it roughly vertical.
    As the ball will spend most of its life completely immersed its buoyancy will exert much more force on the valve lever than would normally be the case, so it might be a good idea to pin the vertical rod to the valve arm nearer to the valve body to reduce the leverage on the valve. Doing so would also make the valve open and close with a smaller range of level change, which might be useful.
    •  
      CommentAuthordjh
    • CommentTimeOct 15th 2018
     
    Posted By: mike7Assuming the 2nd ball valve has to be at the top of the tank so you can get at it

    The mains ball-valve has to be 150 mm above the rainwater one as Tony said for reasons of the water regs say there has to be an airgap. Very reasonable in this case, IMHO.

    A cranked arm, perhaps bespoke as Tony suggests, sounds simpler to my mind than a pin joint.
    • CommentAuthorCWatters
    • CommentTimeOct 21st 2018
     
    +1 to cranked arm.

    If that doesn't work out.. I suppose you could fit a submerged level sensor connected to a motorised valve higher up?
    • CommentAuthorbxman
    • CommentTimeOct 22nd 2018
     
    Assuming you are pumping into the header tank you could use a diaphram switch as used on most washing machines to switch the pump on and off when required
  3.  
    Posted By: bxmanAssuming you are pumping into the header tank you could use a diaphram switch as used on most washing machines to switch the pump on and off when required

    Except the OP is talking about a back up mains water connection filling only the bottom 10% of the tank in the event of prolonged dry weather.