Posted By: Nick ParsonsI assume the cavity is ventilated, for the 'health' of the timber frame. I share your concern, but perhaps the problem could be mitigated if the dpc were glued to the TF opening. Not normal practice, I know, but pragmatic.
I might be equally concerned about the depth of the external reveal. I feel that the tendency for windows and doors to be fitted with only a slight reveal can put timber windows at risk. Are yours alu clad? That would reduce the risk.
Posted By: djhIdeally the windows shouldn't be fitted in the outer blocks, since that means both the inner and outer surfaces of the frame are cold, making a thermal bridge that will encourage condensation in the corners of the windows.
The best arrangement is to mount the windows in the plane of the insulation. In that case it is obvious to seal the outside of the frame to the cold side of the insulation, and the inside of the frame to the warm side of the insulation.
One surface should be the main airtightness barrier. In your case with a vapour barrier behind a service cavity, I presume (you haven't stated) that is your primary airtightness barrier. Clearly that should be connected to the inside of the frame.
The outer surface should also be airtight but especially watertight, although ideally breathable. Are your breather membrane and/or your OSB airtight? Drainage also needs to be incorporated below the outer edge of the frame.
If your windows project outward beyond the insulation, you will need to provide both airtightness and insulation alongside the window somehow. Insulated, airtight cavity closers, perhaps?
If there's anything else the builders can be doing I would stop them installing the windows, work out the best solution first and get it properly drawn up for clarity.
Posted By: FJWHi There,
Ideally the window should be connected both wind tight externally to your tf200 breather membrane and airtight internally to your vc foil airtight layer.
As you say, sealing the dpc around the reveal prior to sealing the air barrier to your window is a very good idea - otherwise a bypass of air from cavity to the internal is quite likely.
You can peel back the folded vc foil and tape the dpc to the timber surround at the reveal, head and cill timbers.
Once you have sealed this, the vc foil internally can be folded back into reveals. Cut four corner pieces approx 200-250mm and apply 100-125 to each side of corner around reveal and tape back to foil already installed. you should also consider releasing slightly the battens installed nearest the cill level to allow you to get a good air tight seal with the tape here. externally depending on access tape between the window frame and tf200 breather using an airtight tape also.
good luck