		<description>
			<![CDATA[Hi all,<br /><br />Attached is an extract from a document called "Calculating potential freedom from structural damage of thermal insulation structures in timber built systems", produved by Pro clima. Catchy title I know! <br /><br />The text is specifically for timber frame details in the Scottish Highlands.<br /><br />The document goes on to say that the only other acceptable way to avoid the issue, is to use the equivalent quantity of insulation outboard of the timber frame as is contained within it. <br /><br />Grateful to hear what anyone thinks about this.]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273319#Comment_273319</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273319#Comment_273319</guid>
		<pubDate>Sat, 13 Apr 2019 11:38:11 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Tullich</cite>the only other acceptable way to avoid the issue, is to use the equivalent quantity of insulation outboard of the timber frame as is contained within it</blockquote>Absolutely - that's the answer.<br /><br />Otherwise, the outer board, be it OSB or soft board, is inevitably exactly where the zone of condensation begins, and maybe spreads inwards. That may happen at least momentarily in any cool climate - the key question is how long it will stay wet before re-drying. 'Next summer' seems to be good enough. But in some climates/conditions it may never fully re-dry before next winter, then the board gets steadily wetter and wetter year by year. This can be seen graphically in WUFI simulations. Do we trust that bituminous softboard outer sheathing, recommended as the answer, is really immune forever to decay in that case?<br /><br />The cure is to put substantial non-organic insulation outboard of the studwork and its outer sheathing, then any condensation happens in non-organic non-structural zone, and OSB outer sheathing is fine.<br /><br />Anyway, studwork with insulation between is prime thermal bridge - really poor practice. A substantial layer of insulation across either the inner or outer face of the sheathed studwork easily cures the bridging. Best on the outboard face, for reason given above.]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273322#Comment_273322</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273322#Comment_273322</guid>
		<pubDate>Sat, 13 Apr 2019 11:58:49 +0100</pubDate>
		<author>Tullich</author>
		<description>
			<![CDATA[Thanks Tom.<br /><br />If using an airtightness layer on the internal side of the timber frame (OSB or equivalent) would this not also serve to provide racking restraint? Could the exterior structural sheathing board then be substituted for an insulation board (woodfibre from Pavatex, Steico, etc) instead?]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273323#Comment_273323</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273323#Comment_273323</guid>
		<pubDate>Sat, 13 Apr 2019 12:08:27 +0100</pubDate>
		<author>Tullich</author>
		<description>
			<![CDATA[I'm guessing not as it doesn't meet the "inorganic" criteria?<br /><br />In Swedish TF's do they not just use an external membrane in place of external racking resistant boards, and have an internal air tightness / racking make up as described above?]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273325#Comment_273325</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273325#Comment_273325</guid>
		<pubDate>Sat, 13 Apr 2019 12:57:47 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Trouble with airtightness layer on the inside is ... trouble! It's inevitably multi-punctured by everything from joist ends to services, all having to be sealed with 100% precision even where inaccessible. Sticky tapes - last forever? Plastic membrane - never ever punctured?<br /><br />To me, better to put the airtightness layer on the outside of the studwork - an uninterupted tea-cosy dropped over the whole. Make it of OSB gapfilling glue-and-screwed to the studwork - foolproof, easy for chippies, durable, easily repaired. OSB doesn't have declared airtightness yet according to PH Certifier Peter Warm, I've heard him say that he's never seen a PH fail airtightness due to using OSB. If OSB airtightness is slightly suspect, it can be backed up with blown-in cellulose insulation between the studs, which has quite good airtightness, as well as other valuable characteristics. The two together offer robust in-depth airtightness, worlds away from plastic sheet and sticky tape fragility and exquisite worknanship requirement.<br /><br />Having sheathed the exterior with OSB, is v easy to EWI over it externally. Note, no internal vapour or airtightness layer, no need for battened service void, just plasterboard straight onto the studwork, electricians free to make holes in it as convenient.]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273327#Comment_273327</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273327#Comment_273327</guid>
		<pubDate>Sat, 13 Apr 2019 13:25:00 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Tullich</cite>If using an airtightness layer on the internal side of the timber frame (OSB or equivalent) would this not also serve to provide racking restraint? Could the exterior structural sheathing board then be substituted for an insulation board (woodfibre from Pavatex, Steico, etc) instead?</blockquote><br />I don't see why not, but I would ask Pro Clima (via Ecological Building Systems) to confirm it.<br /><br />PS. Here's the rest of the text of that section that you quoted above:<br /><br />"If the OSB boards are to be installed<br />externally they have alternatively to be<br />insulated additionally on the external<br />side. In this way the dew point is<br />abated. The thickness of insulation apart<br />from the OSB boards should be as high<br />as the insulation between the posts.<br /><br />"Concrete masonry and quarrystone<br />masonry should be insulated externally.<br />An internal insulation should only be an<br />additional insulation in connection with<br />an external insulation."<br /><br />The documents are available from https://proclima.com/service/downloads<br />Thanks for drawing attention to them.]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273328#Comment_273328</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273328#Comment_273328</guid>
		<pubDate>Sat, 13 Apr 2019 13:33:44 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: fostertom</cite>Trouble with airtightness layer on the inside is ... trouble! It's inevitably multi-punctured by everything from joist ends to services, all having to be sealed with 100% precision even where inaccessible. Sticky tapes - last forever? Plastic membrane - never ever punctured?</blockquote><br />Our airtightness layer is on the inside, because of all the trouble I heard of people building with it on the outside!<br /><br />I don't think there's trouble likely with ours, or I wouldn't have done it, but it's true it influenced some decisions. There are no ceiling-mounted light fittings on the first floor, for example, and no switches or sockets on the exterior walls (although I've now discovered wire and battery-free switches that just stick to the wall so that could change a bit if I wanted).]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273329#Comment_273329</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273329#Comment_273329</guid>
		<pubDate>Sat, 13 Apr 2019 14:00:42 +0100</pubDate>
		<author>Tullich</author>
		<description>
			<![CDATA[Thanks Tom and djh.<br /><br />To give a little more background to the build....<br /><br />I'm determined to only use materials available from local builders merchants. I'm in the Scottish Highlands and don't want to risk delays in supply or to pay extortionate delivery costs. I've settled then on stick timber and Rockwool, which are both self build friendly materials for a hands on construction.<br /><br />I costed blown cellulose at the outset, but per 100mm thickness it's Â£19/m2 @ 60kg/m3 density. Rockwool is less than Â£8 for the equivalent thickness.<br /><br />Aside from materials the other constraint is the need to get the build to wind and watertight as quickly and cost effectively as possible. I'd hoped to avoid any genuine external insulation and to rely instead on the stud/counterstud frame approach to increase available depth for insulation.]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273330#Comment_273330</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273330#Comment_273330</guid>
		<pubDate>Sat, 13 Apr 2019 14:40:04 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[There's a lot more information in the New Zealand version of that study. I haven't read it all but it might be worth looking in there for alternative possibilities. Canadian building practice is also worth looking at.]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273374#Comment_273374</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273374#Comment_273374</guid>
		<pubDate>Tue, 16 Apr 2019 12:32:49 +0100</pubDate>
		<author>GreenPaddy</author>
		<description>
			<![CDATA[Hi Tullich,<br /><br />my first thoughts are that wanting to get weather tight quickly, will probably mean the OSB skin on the on the outside, as we traditionally do with timber frames here in the highlands.<br /><br />That lets you insulate with non-waterproof insulation in the dry from the inside, but of course doesn't stop you adding a layer of rigid board over the outside, which I've done on some occasions, including over the roof, for the very good reasons pointed out above.<br /><br />Consider how you'll demonstrate to building control as regards vapour control, for your building warrant. I'm not giving any direction on this, by making the comment, but if you're not using a proprietary wall build up, which has been tested, and it sounds like you're going for stick build, then the responsibility will be on you to demonstrate no (or virtually no) interstitial condensation. Good design, and use of cond modelling software would do this.]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273376#Comment_273376</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273376#Comment_273376</guid>
		<pubDate>Tue, 16 Apr 2019 13:03:27 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Spot on]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273383#Comment_273383</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273383#Comment_273383</guid>
		<pubDate>Tue, 16 Apr 2019 20:12:00 +0100</pubDate>
		<author>borpin</author>
		<description>
			<![CDATA[Totally agree with Tom.<br /><br />If you put enough insulation outboard, then the timer is always on the warm side of any condensation. If it did by some remote chance get wet, it would then dry.<br /><br />Also agree that the easiest way is to make a tea cosy of OSB and then insulate over. I would though use Icynene insulation between the studs as that helps with the air tightness and yet lets vapour out.<br /><br />I built with a metal frame from U-Roof <a href="http://www.u-roof.com," target="_self" rel="nofollow">http://www.u-roof.com,</a> created a tea cosy of Insulation and then sprayed Icynene inside.  Worked perfectly!  The metal frame has it's own challenges when finishing inside, but the roof is self racking so less requirement for purlins etc.<br /><br />No wood, nothing to rot!<br /><br /><a href="https://www.borpin.co.uk/2012/09/07/the-u-roof-frame-is-up/" target="_self" rel="nofollow">https://www.borpin.co.uk/2012/09/07/the-u-roof-frame-is-up/</a>]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273395#Comment_273395</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273395#Comment_273395</guid>
		<pubDate>Wed, 17 Apr 2019 12:41:13 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[A few links about vapour barriers and building in very cold climates:<br /><br /><a href="http://www.cchrc.org/sites/default/files/docs/Exterior_Insulation_Envelope_Retrofits.pdf" target="_self" rel="nofollow">http://www.cchrc.org/sites/default/files/docs/Exterior_Insulation_Envelope_Retrofits.pdf</a><br /><br /><a href="https://www.buildingscience.com/documents/insights/bsi-031-building-in-extreme-cold" target="_self" rel="nofollow">https://www.buildingscience.com/documents/insights/bsi-031-building-in-extreme-cold</a><br /><br /><a href="https://www.researchgate.net/publication/238747123_The_Influence_of_Low-Permeance_Vapor_Barriers_on_Roof_and_Wall_Performance" target="_self" rel="nofollow">https://www.researchgate.net/publication/238747123_The_Influence_of_Low-Permeance_Vapor_Barriers_on_Roof_and_Wall_Performance</a><br /><br /><a href="https://www.nrel.gov/docs/fy13osti/56145.pdf" target="_self" rel="nofollow">https://www.nrel.gov/docs/fy13osti/56145.pdf</a><br /><br />As ever, I like John Straube's best <img src="/newforum/extensions/Vanillacons/smilies/standard/bigsmile.gif" alt=":bigsmile:" title=":bigsmile:" /><br /><br />His point about using higher permeability boards on the outside of the studs is germane.]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273425#Comment_273425</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273425#Comment_273425</guid>
		<pubDate>Fri, 19 Apr 2019 16:06:49 +0100</pubDate>
		<author>Tullich</author>
		<description>
			<![CDATA[Really appreciate your input so far, and the links suggested. Thanks.<br /><br />I'm familiar with the REMOTE wall concept, and the excellent video series produced by the Cold Climate Housing Research Centre. I've often wondered why nobody produces a t & g profiled sheet (as seen on external woodfibre boards etc) which could be installed in one thickness to save layering sheets and the additional labour costs? <br /><br />With EPS100 being the default material for EWI the issue is availability of materials locally again. Any number of retailers will sell me EPS70, but EPS100 is a special order item and the delivery costs are eyewatering. Is EPS70 a safe (albeit lower density) substitute?<br /><br />Icynene's not a self install option in much the same way as cellulose isn't, your steel frame looks amazimg and terrifying in equal measures though borpin! <br /><br />If I were to bite the bullet on an externally air tightened timber frame option, the next step would be to figure out how this can be integrated with a suspended timber floor. I'm already feeling a little bit like i'm selling out by considering EPS options, I really don't want to pour a slab....]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273427#Comment_273427</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273427#Comment_273427</guid>
		<pubDate>Fri, 19 Apr 2019 18:28:37 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Tullich</cite>With EPS100 being the default material for EWI the issue is availability of materials locally again. Any number of retailers will sell me EPS70, but EPS100 is a special order item and the delivery costs are eyewatering. Is EPS70 a safe (albeit lower density) substitute?</blockquote><br />AFAIK, the difference is the load-carrying ability of the material, which is pretty much irrelevant for EWI. But then I've never investigated EWI in any detail, so I may be ignoring something.<br /><br /><blockquote >If I were to bite the bullet on an externally air tightened timber frame option, the next step would be to figure out how this can be integrated with a suspended timber floor. I'm already feeling a little bit like i'm selling out by considering EPS options, I really don't want to pour a slab....</blockquote><br />The way I thought was that investing oil-derived materials in the fabric of a building is one of the best uses for oil. Far better than burning it; although I do admit that leaving it in the ground is better. I think the same goes for heat-processed materials like lime or cement. So I'm relatively content that I have EPS and concrete under my straw bales. A suspended-timber floor with piles underneath and PH performance proved too difficult to organize for me.<br /><br />The Murricans and Canucks have a lot of experience with suspended timber floors in a lot of different climates, so I'd look there for good practice.]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273433#Comment_273433</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273433#Comment_273433</guid>
		<pubDate>Fri, 19 Apr 2019 22:41:52 +0100</pubDate>
		<author>borpin</author>
		<description>
			<![CDATA[EPS under a raft<br /><br /><a href="http://www.isoquick.co.uk" target="_self" rel="nofollow">http://www.isoquick.co.uk</a>]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273434#Comment_273434</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273434#Comment_273434</guid>
		<pubDate>Fri, 19 Apr 2019 22:43:07 +0100</pubDate>
		<author>borpin</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Tullich</cite>Icynene's not a self install option in much the same way as cellulose isn't</blockquote>True, but it is quick and improves air tightness to boot.]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273465#Comment_273465</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273465#Comment_273465</guid>
		<pubDate>Tue, 23 Apr 2019 08:34:46 +0100</pubDate>
		<author>goodevans</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Tullich</cite>Is EPS70 a safe (albeit lower density) substitute?</blockquote> I think EPS70 is ok - I'm using it at the moment for my EWI.  The data sheets for my adhesive and render system states EPS70 is also OK.<br /><br />If you do use EPS as the rot-proof outer insulation layer of the timber frame ensure you have a higher density sound attenuating insulation layer inboard - wool batts, cellulose or spray foam.]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273483#Comment_273483</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=273483#Comment_273483</guid>
		<pubDate>Fri, 26 Apr 2019 15:30:52 +0100</pubDate>
		<author>GreenPaddy</author>
		<description>
			<![CDATA[EPS70 is fine for EWI, having used it, and no issues after several years.<br /><br />If you get the 2.4x1.2 sheets, it can tend to have a slight bow sometimes, which makes flush fitting a bit more time consuming.<br /><br />It is softer than EPS100 or XPS of course, but when the undercoat is applied, it goes rock hard on the surface. The the render coats helps too.<br /><br />Clearly, it won't take any fixings (though neither do any of the polys), and if thumped with a hammer or a car bumper, it will "puncture"...make sure that doesn't happen!]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275091#Comment_275091</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275091#Comment_275091</guid>
		<pubDate>Fri, 16 Aug 2019 20:50:26 +0100</pubDate>
		<author>Tullich</author>
		<description>
			<![CDATA[So, things have moved on a fair bit since April....<br /><br />Against all the advice i've recieved from local builders, other self builders, my draughtsman, etc i've decided after a lot of reading and head scratching to go with the REMOTE wall model as discussed here previously. This decision is mainly based on buildability as this is a hands on self build. I understand the construction type and feel I can achieve it. My planning permission's been granted, so things are heading in the right direction.<br /><br />The wall make up now looking like:<br />12.5mm platerboard, taped and filled<br />145mm timber frame<br />140mm Rockwool in stud bays<br />OSB3 racking layer, screwed and glued<br />EWI type and thickness tbc (see below)<br />Weather barrier <br />Batten<br />Larch cladding<br /><br />There are two design issues i'm still wrestling with: floor construction and which type and thickness of foam material to spec for the ewi aspect of the walls. So, I have a couple more questions.... <br /><br />Firstly, has anybody here successfully self installed a non proprietary EPS insulated raft type foundation? Sticking to the principle of "only building with materials off the local builders yard", I can source EPS sheets but not the edge profiles. I don't want to spring for the full Kore or similar package - it's serious money that I don't have. <br /><br />Secondly, i've read as much as I can find around the topic of which type external insulation to use outside of the timber frame in a REMOTE type system. The standard approach of layering EPS sheets with staggered board joints make sense. However, I have a note somewhere to the effect that 38mm of EPS = 23mm of PIR? I've been thinking about using 120mm of PIR therefore in lieu of 200mm of EPS. Would it be feasible to then use just one layer, with the edges intentionally gapped, say 5mm, and foam filled after the fact? I know PIR loses to EPS in respect of breathability but does that matter in this example? Would 140mm Rockwool Flexi in stud bays internally and 120mm PIR externally cut it on a condensation risk analysis? <br /><br />Ha! I guess i've got more to figure out still than I thought!]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275094#Comment_275094</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275094#Comment_275094</guid>
		<pubDate>Sat, 17 Aug 2019 10:21:24 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Tullich</cite>Firstly, has anybody here successfully self installed a non proprietary EPS insulated raft type foundation? Sticking to the principle of "only building with materials off the local builders yard", I can source EPS sheets but not the edge profiles. I don't want to spring for the full Kore or similar package - it's serious money that I don't have.</blockquote><br />I do have a Kore system, as opposed to a DIY one. It was built by my groundworks contractors but I didn't see anything I couldn't have done myself if I'd been so inclined. There are a few points about the system that might be worth noting.<br /><br />Firstly, decide how you are going to make the 'bucket' of EPS strong enough to contain the concrete. Perhaps best is to pile up lots of gravel or earth against the outside of the EPS. Note that the edge profiles are EPS300 or thereabouts, not the regular EPS material, to make them stronger. How do you plan to achive the bucket shape?<br /><br />Secondly, will you not need to get the design signed of by an engineer, for building control? You may find some difficulty finding an engineer willing to do that for a one-off DIY system. I suppose Hilliard Tanner might just be up for the challenge if you can get him interested.<br /><br />The majority of the cost of my insulation was for the flat sheets; they cost about double the fancy-shaped bits. And I had quite a lot of fancy bits because of the complex nature of my ring beam. Transport was also fairly hefty, about Â£1000. If you were able to purchase the sheets from your local builders' merchant and maybe collect the shaped pieces from Kore, it wouldn't work out as expensive as you think, perhaps.]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275100#Comment_275100</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275100#Comment_275100</guid>
		<pubDate>Sat, 17 Aug 2019 13:52:26 +0100</pubDate>
		<author>GreenPaddy</author>
		<description>
			<![CDATA[Hi Tulloch, very happy for you to ignore my comments, if you're already past this point, with supporting calcs <img src="/newforum/extensions/Vanillacons/smilies/standard/cool.gif" alt=":cool:" title=":cool:" /><br /><br />Stating the obvious, but you do need to nail all this down for your building warrant, and get a struct engineer to sign off the design with an SER. You'll need interstitial condensation calcs for all the structural elements too. This insulation info will also be required by the SAP calculation guys...apologies if you're aware of all this.<br /><br />I've done several timber frames with the insulation on the external OSB face, so no big deal really.<br /><br />I don't see a vapour control layer between pboard and the frame? Have you considered a service cavity under the pboard, so you don't puncture the VCL, or have services squashed into the insulation, or have to drill out all the studs and dwangs?<br /><br />You seem to be talking about very large thicknesses of the sheet insulation externally.<br /><br />What's the lambda value of the rockwool between studs? If you improve this, say with a frametherm 35 or even 32, you will be able to reduce the external board thickness. Why? well it makes life a bit trickier fixing your battens through the sheet insulation into the timber frame, and also issues with future &quot;sag&quot; due to the vert loading of the timber cladding. Compressive strength of the chosen insulation boards also comes into play. It's all do-able in various ways, but some are a bit more tricky than others.<br /><br />Just as examples:<br /><br />frametherm 32 between studs, with 50mm PUr board = Uval 0.15 W/m2K<br /><br />rockwool/other 44 between studs, with 100mm EPS boar = Uval 0.16 W/m2K<br /><br />compressive str of EPS70 (usual, easily avail) is half that of PUR boards (kingspan type stuff)<br /><br /><br />Ground Bearing Slab...<br /><br />I see you're building a raft, rather than strip foundations with typical block underbuild. I usually stick to the strip type, not that that means anything. I've done lots of slabs with EPS70 underneath. In one case, it was cheaper to add a 3rd layer of EPS70, rather than build up the solum level with crushed stone. The edge detail can be dealt with in various successful ways, but afraid I can't help with details for full raft under foundations. &quot;Viking House&quot; of this forum is the king of raft slabs from what I've seen. Has your struct engineer confirmed the bearing strength of your soil conditions for this or any other type of foundation?]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275106#Comment_275106</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275106#Comment_275106</guid>
		<pubDate>Sat, 17 Aug 2019 23:15:11 +0100</pubDate>
		<author>Tullich</author>
		<description>
			<![CDATA[djh<br />Interesting that you used the Kore system and feel it could be diyable. Those transport costs are one of my main worries about off the peg components. In terms of forming an EPS bucket, i'd been wondering if the following would be feasible:<br />Follow the standard below ground process of compacting sub base material, blinding, etc. Then lay out flat EPS sheets to the slab size, install a timber shutter at the perimeter as per a conventional slab, pour the slab and install a vertical EPS element afterwards to bridge the sub slab EPS to the EWI. <br /><br />I was looking for a way to avoid any specialist edge components, and this is what I came to. It uses off the shelf EPS sheets, but doesn't use the  EPS itself to contain the slab during pouring. Needless to say the idea has had zero input from a SE as yet....<br /><br />GreenPaddy<br />I've no plans to ignore anything I hear on the forum! Collectively you've provided the best advice i've received to date!<br /><br />So, i've got both a SE on and a SAP calculator on side, who's also looking at the condensation risk analysis.<br /><br />Ref the lack of VCL, is this needed in an externally air tightened wall assembly? Other threads on here don't seem to think so.<br /><br />140mm Rockwool flexi is 0.035 W/mk<br /><br />Ref the raft, this isn't really something I actually want to even do to be honest! The SE input would need to come from someone other than who's certifying the frame. I said at the outset that I didn't want to pour a slab of any kind, but I haven't managed to come up with a suspended timber alternative that isn't either full of cold bridges or a huge damp trap. No ground bearing assessments have been made, i'm just spitballing before I commit.<br /><br />Grateful to you both for your replies.]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275107#Comment_275107</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275107#Comment_275107</guid>
		<pubDate>Sat, 17 Aug 2019 23:30:43 +0100</pubDate>
		<author>Tullich</author>
		<description>
			<![CDATA[What do you think about my idea for the EWI install? <br /><br />Intentionally gapped PIR boards with joints spray foamed afterwards?<br /><br />It reduces the overall thickness of the EWI, avoids the need to install two layers, and from what GP has said above has a better compressive strength to install battens and timber cladding over afterwards.<br /><br />Is the lack of breathability an issue?<br /><br />If using 140mm Rockwool flexi in the stud bays, what thickness would I need over the frame to hit 0.1 W/mk?<br /><br />Lastly, bearing in mind this thread started out with a quote from Pro Clima about condensation risk, would any of this pass?]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275108#Comment_275108</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275108#Comment_275108</guid>
		<pubDate>Sun, 18 Aug 2019 08:09:57 +0100</pubDate>
		<author>GreenPaddy</author>
		<description>
			<![CDATA[Why do want (I assume you mean) a Uvalue in W/m2K of 0.1 ? You are well past the point of diminishing returns, as our friends in Passiv Haus have reliably demonstrated - their benchmark is around 0.15W/m2K. I tend to target 0.12, as being in the highlands, we tend not to get the sunny days in winter, cold and driech. Not suggesting you are wrong with this, just interested in your logic?<br /><br />With 140mm wool35, you'd need 125mm PIR on the outside to get down to 0.1 Uval. That includes a silver/lowE face to internal and external cavities. No interstit cond with or without VCL, but gets closer to hitting dew point in the rigid board without the VCL. If you go thinner with the ext insul, interstit cond becomes more likely at the OSB interface, as it obviously gets colder.<br /><br />Air tightness method? Also think about detailing at the wall head and DPC, that's where it can start to unravel, with insulation continuity, vermin prevention, etc.<br /><br />I'd expect you'd need edge thickening for the raft, where the load bearing walls land, which may be internally as well as the external perimeter, so flat sheets prob won't do it, unless you start building a lego base, with trenches formed in the insulation sheets.<br /><br />Why would a suspended timber floor, with say JJI's to minimise cold bridging, not work for you. I've done that, where I couldn't get site access for concrete wagons, and works fine, and yes I am anal about cold bridging, air tightness, etc, etc. However, given the choice, I'd stick with a poured slab every time...lower profile versus ext ground level, easier for UFH, less insulation required as it's ground bearing not open to cold air, much more solid for tiling on etc.]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275109#Comment_275109</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275109#Comment_275109</guid>
		<pubDate>Sun, 18 Aug 2019 08:19:58 +0100</pubDate>
		<author>Peter_in_Hungary</author>
		<description>
			<![CDATA[over here EPS is the cheapest form of slab insulation and whilst for a given U value it is thicker than others if you are doing a new build I would not have thought that a couple of inches extra thickness would matter. If you are doing a timber frame with OSB boards I would have thought that the result would (should) be flat enough to put up the slab insulation without the need to leave gaps to be foam filled later. <br /><br />If you don't build off the slab but use strip foundations then depending upon the required depth you can insulate down to the bottom of the foundation wall and avoid the need to insulate the floor slab but if you need to go that deep an insulated slab might cheaper / easier.<br /><br />For your thoughts about the DIY slab edge insulation a problem could be the internal part of the edge profile. Usually the slab edge is thicker than the center so an internal downstand is needed, this will need to be supported to take the strain of the concrete pour without moving. One way around this is to pace the internal downstand EPS in place, brace it on the outside edge and then back fill with a weak concrete mix to stop the concrete pour displacing the EPS<br /><br />The plan for the outside edge of the slab as a post fit up to the EWI sounds OK, although you could pre-install the  EPS inside the shuttering and pour into an ESP box supported on 3 sides]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275111#Comment_275111</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275111#Comment_275111</guid>
		<pubDate>Sun, 18 Aug 2019 11:31:33 +0100</pubDate>
		<author>Tullich</author>
		<description>
			<![CDATA[GreenPaddy<br /><br />Sorry, one day i'll get my units right.... <br />I'm not necessarily aiming for a 0.1 Uvalue for the wall assembly, I was just trying to stimulate a bit of chat about what could be possible. Seamus's wall sections on the Viking House site show 140mm mineral wool in stud bays + 200mm EPS as EWI for a 0.1 Uvalue wall. I'm guessing this passes a CRA. This has been the point of reference since April because it's the best example of a REMOTE wall being used in practice that I can find.<br /><br />Air tightness detailing in the form of foamimg glue, a shame we can't get our hands on some if the clever mastik products used in the US. <br /><br />Ref the raft, the house is a small single storey bungalow. There's a vaulted ceiling over the living area and a loft for storage over the two bedrooms. The porch and bathroom are in lean to ext to the rear, so it's only really one room deep. Traditional Highland form factor except with a 30 degree roof pitch. Total floor area of just over 90 m2. Construction methods as discussed so far are all at the lighter weight end of the scale, except maybe the timber cladding. What any of this means in terms of raft construction I don't know, and there are so few people who can advise. More reasons really to look to strip founds and iJoists as you suggest! I've been waiting for Pat Munro's guys to come and scope the access for concrete wagons for weeks....]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275112#Comment_275112</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275112#Comment_275112</guid>
		<pubDate>Sun, 18 Aug 2019 11:36:19 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Tullich</cite>Then lay out flat EPS sheets to the slab size, install a timber shutter at the perimeter as per a conventional slab, pour the slab and install a vertical EPS element afterwards to bridge the sub slab EPS to the EWI.</blockquote><br />It might work. I don't have the knowledge to judge. Bear in mind that the outer edge of the slab is a lot deeper than a normal floor slab. Ours is 400 mm, though I think 200-300 mm is more normal. Hence the loads on the shuttering are greater than for a normal floor slab. Apart from that, I think the main issue might be any gap between the EPS and the shuttering, perhaps due to movement of the latter, will result in concrete filling the gap.<br /><br />I looked at a suspended timber floor on piles as an alternative, but that seemed a lot more complicated and probably more expensive, plus gave issues with the height of the floor above ground. Passive slab seems very simple by comparison.]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275113#Comment_275113</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275113#Comment_275113</guid>
		<pubDate>Sun, 18 Aug 2019 11:40:42 +0100</pubDate>
		<author>Tullich</author>
		<description>
			<![CDATA[Peter_in_Hungary<br />Thanks for the feedback about the EWI, and you're right about the possibility of including EPS within a timber shutter for pouring the slab.<br /><br />I'm trying to picture your description of the alternative floor construction. Would you have time to explain a liitle more? <br /><br />Thanks both. <br /><br />Does anyone think it would be worthwhile splitting this into two threads, one for floor construction and one for wall construction? I'm thinking this is being missed by most due to being in a thread that started in April about condensation in walls? <br /><br />In terms of the potential need for a ringbeam, I guess that's wher any rule of thumb gets binned and a SE is needed.]]>
		</description>
	</item>
	<item>
		<title>Timber frame wall construction / potential condensation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275114#Comment_275114</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16097&amp;Focus=275114#Comment_275114</guid>
		<pubDate>Sun, 18 Aug 2019 11:51:08 +0100</pubDate>
		<author>Tullich</author>
		<description>
			<![CDATA[djh<br />Your last sentence sums it up for me. A passive slab seems simple compared to any alternative. I started out planning to build off of a series of pillars and a ringbeam, with a cassette type floor over the top. This later became iJoists over a stem wall which still needed a concrete solum and didn't cost out well, and so I finally arrived at the raft/slab idea. The main difficulty with which is finding someone to engineer it quickly so I can get my warrant application in. SE's work anything but quickly for good reason, but the weather window for building up here is narrowing daily....]]>