It is set up with bypass valves to control the return temperature to the" boiler" which should be hotter than the return temperature of the u/f heating loops but in my case it is not as the return to the store is the same temperature as the loops.
Posted By: GreenPaddyAnyway, the reason that adding a second pump in series, but upstream of the mixing valve is a problem, is as you described above, ie. the signal to run the new/additional pump would come from the actuator valves being in the open position. These valves can be in the open position, but the mixing valve is on full recirc from the cold loop returns, with NO water coming from the Thermal Store, and so NO water being pumped by the new/additional pump, even though it's being told to run...ie. the pump is dead-ended.