Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    •  
      CommentAuthordjh
    • CommentTimeSep 7th 2019
     
    Some recent discussions have reminded me how cheap small ASHPs can be. It got me to reconsidering whether it might be appropriate for our house, and I'd appreciate any thoughts anybody has.

    We currently use electrical resistance heating for our space heating and our water heating and have an E7 meter. For most of the year, we don't need any space heating and our water heating is provided by PV diversion. April through September, our grid consumption is between 4 and 7 kWh/day. November through February is our heating season. March and October are transitional. Daytime usage during the heating season is about 8 kWh/day and nighttime E7 usage, which is when the DHW heating and most of the space heating occur, is around 20 kWh/day. Heat diverted to water is typically maybe 6 kWh/day when PV is heating it, so I suppose about the same or maybe a bit less is provided from the grid during the winter. Which leaves about 14 kWh/day as the space heating demand. Times say 150 days is 2100 kWh per year, which at 7p /kWh is £147 per year.

    So what are the costs of a small ASHP? Purchase? Installation? Maintenance? Electrical running costs? These are numbers that anybody with an ASHP probably knows a lot more about than me!
    • CommentAuthortony
    • CommentTimeSep 7th 2019
     
    How long a period do you want to cost it over?

    Professional installed a single typical single split ASHP can cost £5k, there are diy ones available for between 500 and 1000.

    Assume a 3.5 CoP so

    Your 7p per kWh looks too low

    On that basis you could save £100 p/a but I would double the cost of electricity

    I would install solar thermal and a shower timer and take the pain.

    On my calcs over 20 years — savings of £ 200p/a cost say 1000 on diy basis payback 5 years, ROI = huge

    Up side is you gain air cooling
    •  
      CommentAuthordjh
    • CommentTimeSep 7th 2019
     
    Posted By: tonyHow long a period do you want to cost it over?

    I'm looking for advice from people with knowledge of what is sensible. What is the guaranteed and expected lifetime of the devices you are talking about?

    Professional installed a single typical single split ASHP can cost £5k, there are diy ones available for between 500 and 1000.

    What specifically?

    Assume a 3.5 CoP so

    I ass U me. No, I would rather have people's actual experience.

    Your 7p per kWh looks too low

    You're right. It's 7.6p

    I would install solar thermal and a shower timer and take the pain.

    What would the solar thermal do that the PV doesn't? Why would I want all the extra complication?
    Why would I want a shower timer? I don't want to compromise our experience (wear a hair shirt).

    Up side is you gain air cooling

    Agreed, but that rather contradicts your hair shirt suggestion and cost basis.
  1.  
    What's your objective? You won't save much money compared to a smart-meter tariff, but you could reduce some CO2 by avoiding resistance heating and PV diversion.

    Your heat demand (1-2kWth) is of course much less than most heating systems are intended for.

    IIRC you do not have a wet heating network or UFH pipework (?) which you would require for a 'typical' multi-kW air-water ashp install, and the cost of retrofit is disproportionate to the benefits.

    You mentioned using over-ventilation to distribute electric heat, there could be knockon advantages in reducing this.

    You could look at a very small air conditioning unit in your main room. Somebody here installed one diy as an air-air heatpump, with a high spf, but these are quite unusual so don't expect very much crowd-sourced knowhow... Edit: the one I meant was prior to Owlman's recent install. Was it Ringi's perhaps?

    Our (much larger) ashp's 5-year warranty was conditional on us taking out an expensive service contract, you'd want to avoid that.

    RHI is based on heat demand as stated on the EPC, which I imagine is low for your place, and is not available for air-air ashps or DIY.

    For an appliance like a heat pump with lots of moving parts, I'd plan around a ten years lifetime. Edit: our big one lasted faultlessly for 8 years, then kaput.
    • CommentAuthorowlman
    • CommentTimeSep 8th 2019
     
    Are you looking at Air to Water or Air to Air? I'm guessing the latter.
    • CommentAuthorJeff B
    • CommentTimeSep 8th 2019
     
    Will the ban on the installation of gas boilers in new builds from 2025 accelerate the development of more efficient ASHP's? An ASHP will be no good unless the new houses are very well insulated, so this ban should also provide an incentive to do just that.

    https://www.thetimes.co.uk/article/gas-boilers-will-be-banned-in-new-homes-from-2025-s7kbtb6jq

    Doesn't help those of us living in existing housing stock of course! I would very much like to go over to ASHP but it's a non-starter sadly.
    •  
      CommentAuthordjh
    • CommentTimeSep 8th 2019 edited
     
    Posted By: Jeff BWill the ban on the installation of gas boilers in new builds from 2025 accelerate the development of more efficient ASHP's?

    I doubt it. I don't think the UK market has much influence on ASHP development. Places like Asia and America where there is a lot more demand for air-con have a lot more influence.

    I don't think banning gas boilers, if it happens, will have much influence on insulation either, sad to say. I don't think mass builders will go beyond what they're required to by building regs etc and the SAP/EPC system is not fit for purpose in measuring heat requirements either, IMHO.

    @owlman, I would guess A-A as well, but that's the kind of thing I hope and expect other people to know better than me.

    @will, yes lack of return was why I didn't really consider ASHP when we built but there do seem to be some cheaper small units around now, or maybe I missed them 5-10 years ago. There's lots of brands I've never heard of as well as a few like Mitsubishi & Daikin that I know of but don't know much about. So I'm hoping somebody might be able to give me a few pointers.

    I don't expect I'd qualify for any subsidies, and our low demand means we would need to minimise standing costs, so knowledge of which brands if any don't require maintenance contracts etc would be useful.

    Our space heating is by heating the ventilation air and by a radiant heater in the hall. Basically as long as they dissipate enough heat energy somewhere in the building each day, the temperature stays fairly constant and reasonably evenly distributed (the inside walls are less well insulated than the exterior walls and internal doors are normally open). There might be a bit of a conflict between heating and cooling with an ASHP. I put the radiant heater in the hall because its on the north side of the building and the space has immediate access to both floors, so there's a reasonable chance of the heat getting distributed some useful. So that would be a good place for the inside unit for heating. But equally, it's the south side of the building that gets hottest in summer - the living room and dining room specifically, so there would be better for an inside unit for cooling.

    To some extent the need for cooling is self-inflicted and is very marginal in any case. I still haven't built the pergola I plan to use as the brise soleil shown on the plans shading those two rooms, so they get more solar gain than was designed. It's not been a serious problem because we both like it warm, and my wife is concerned that plants on a pergola will attract mosquitos etc.
    • CommentAuthorcar-mark
    • CommentTimeSep 8th 2019 edited
     
    Hi there
    You asked for real life usage, well here it is.
    My wife is disabled with need of a wheelchair for moving about the house. So what you say why mention when this is about heating. Her internal thermostat is somewhat ruined thus we need room temperatures in the day of about 23C.
    We have used individual AtoA heat exchangers in the bedroom, Kitchen diner and conservatory. (Note not green in the conservatory but with solar PV net no cost to us in the summer.) A little less to the grid.

    1 The bedroom unit worked for about 7 years before death (ebay self install) New unit 3 years in and still working, again self install. About £400 all in.
    2 Kitchen unit Mitsubishi ceiling cassette unit, 3.5kW £200 S/H ebay, again self install 10 years on and still working well
    3 Conservatory 5kW Fujitsu self install ebay £450 7 years ago.

    You may have noticed the common elements, S/H and ebay plus self install no probs.
    Get reversible units as you never know when cooling may be needed. (If temperature gets too high in the house I need the cooling function otherwise all hell breaks loose from the non functioning body temperature control.)

    The Air con units are problematic in the wet shoulder months, using more energy than they should due to deicing.

    Will post more if required
    •  
      CommentAuthordjh
    • CommentTimeSep 8th 2019
     
    Many thanks, Mark. That's very helpful. Sorry to hear of your wife's problems. It's amazing how much difference to comfort even a single degree can make in some circumstances.
    • CommentAuthorJeff B
    • CommentTimeSep 8th 2019
     
    Car-Mark, I presume each of these units that you own each have their own external unit?
    • CommentAuthorcar-mark
    • CommentTimeSep 10th 2019
     
    Yes I have used separate installations, I feel multi output single base unit would not suit retrofit.

    An added bonus of the separate units is providing some sort of control to the rest of the heating which is storage heaters and wood stove
    • CommentAuthorJeff B
    • CommentTimeSep 11th 2019 edited
     
    Car-mark - thanks for your reply. I am looking at various options for the future as my wife and I are not getting any younger; she is worried if I go first then she would not be able to manage our complicated wood pellet fired heating system!

    So that must mean you have several outdoor units scattered around your house. I presume you have plenty of space and you can place them not too near your neighbours' properties?
    • CommentAuthorcar-mark
    • CommentTimeSep 12th 2019
     
    Hi there

    I feel that is a jump to conclusions, I would not use the term scattered, More placed carefully and with full appreciation of the surroundings, others less inclined to give the benefit of the doubt may use the term scattered.

    Now I have had experience of some cheap units in France and one of these was of the piston variety. I can understand why people would be upset with operating within 50 m of a property.
    Our best unit is a 3.5kw unit Mitsubishi slim jim. This was my best purchase at <£200 I collected at 70 miles and he added a condensate pump for free. Still working 10 years later. I defy anybody to hear this style working at 10ft that is inverter scroll type very quite and neighbors do not hear it.

    Now this unit has a wall controlled thermostat controller. With care this can be set up like a central heating unit with no added control by yourselves. I use this to give me overall control of a kitchen/diner temperature.
    These are 2 rooms of about 6m*4m in an L shape with storage heater in the dining room and the air-con in ceiling of the kitchen. This gives me control of the temp which storage radiators are incapable of doing.
    enough for now
    Mark
    • CommentAuthormarktime
    • CommentTimeSep 12th 2019 edited
     
    I live in the north of Tenerife in the Canary Islands. As Tom has pointed out elsewhere, one becomes physiologically acclimatised to the local ambient temperature and as our seasonal variations are relatively minor we only feel the chill when the outside temp. falls to 15º C or so which is rare. Hopefully Dave, you are still with me and the point is we have an a nominal 1kW ASHP which is only ever employed as a heat pump with, as you might imagine, a decent CoP. It works adequately to take the chill off the lounge but because it pumps out warm air at ceiling height, you do notice that your feet remain cold. It's a real bugger!
    • CommentAuthorJeff B
    • CommentTimeSep 13th 2019
     
    Car-Mark: thanks for your response. Re: "scattered" - by this I meant (as per dictionary definition) "occurring or found at intervals or various locations rather than all together" and not in any derogatory sense! I asked the question because I do not have much choice where I could put three outside units in my property without one or two being rather near the neighbours' boundaries and this would influence any choices I would have to make.

    I can concur with your comment about the Mitsubishi external unit - we have two at our chapel and they are very quiet, as indeed are the four indoor units (critical in a church environment).
    • CommentAuthorowlman
    • CommentTimeSep 13th 2019
     
    @ Jeff B; You could stack them using cantilever brackets.
    • CommentAuthorcar-mark
    • CommentTimeSep 13th 2019
     
    Been there got the T shirt
  2.  
    Posted By: WillInAberdeenFor an appliance like a heat pump with lots of moving parts, I'd plan around a ten years lifetime. Edit: our big one lasted faultlessly for 8 years, then kaput.


    A heatpump has only 3 moving parts - the compressor, the fan and the reversing valve. Well potentially 4 as the TXV has parts that move, but they move automatically. As the compressor and fan are electric motors, the start/run capacitors can fail. TXVs do break, but can be replaced, as can the reversing valves - though, as in everything, the labour costs may make it unfeasible. Other parts can leak refrigerant ... which can make the machine kaput in the end.

    Paul in Montreal.
  3.  
    Ours also had an inverter-driven circulation pump for the hot water, and a motorised ch/dhw diverter valve, both uniquely made with fancy electronics to match. It was also an oddity with two compressors. But (as you guessed!), it was a non-moving part that killed it - the main heat exchanger developed a tiny crack and lost refrigerant, and as it was mounted underneath everything else in the box, the labour costs to remove/replace everything were uneconomic.

    Sadly the useful lifetime of many similar appliances seems to be more like 10years rather than 20 years now - thinking of fridges, freezers, washing machines, gas boilers etc - and kettles/toasters/computers/phones last even less, with no moving parts!
    •  
      CommentAuthordjh
    • CommentTimeSep 14th 2019
     
    Posted By: marktimeHopefully Dave, you are still with me and the point is we have an a nominal 1kW ASHP which is only ever employed as a heat pump with, as you might imagine, a decent CoP. It works adequately to take the chill off the lounge but because it pumps out warm air at ceiling height, you do notice that your feet remain cold. It's a real bugger!

    I'm still here, Derrick, and thanks for this. Do you mean 1 kW electric input or heat output? I'm hoping that if I used a wall-mounted indoor unit, then I could have it blow at the ceiling in summer and more towards the floor in winter.
    • CommentAuthorJeff B
    • CommentTimeSep 14th 2019
     
    <blockquote><cite>Posted By: owlman</cite>@ Jeff B; You could stack them using cantilever brackets.</blockquote>

    The problem with that is that we have a large-ish bungalow and having multiple external units in one place would mean having impractical long runs of refrigerant pipework. Any idea what the longest permissible run would be?
    • CommentAuthormarktime
    • CommentTimeSep 15th 2019
     
    My unit is a Panasonic rated at 1 kW so in theory I get 3 kW of heating. Although it has controllable ventilation louvres the difference in air density means that most of the warm air doesn't get to foot level. In real life that results in cold feet when sitting on the sofa watching TV. The ideal situation would be vents at skirting level but as I imagine the overall design consideration for ASHP is for cold air conditioning, that is impractical. Something to bear in mind if your primary goal is a heat source.
    • CommentAuthorowlman
    • CommentTimeSep 15th 2019
     
    Posted By: Jeff B
    Posted By: owlman@ Jeff B; You could stack them using cantilever brackets.


    The problem with that is that we have a large-ish bungalow and having multiple external units in one place would mean having impractical long runs of refrigerant pipework. Any idea what the longest permissible run would be?




    I think it's variable, dependent on manufacturer, unit size, etc., but 50M is not unusual, some bigger units go up to 75M, some smaller ones 30M
  4.  
    Aren't these indoor units just the functional equivalent of a radiator, with refrigerant flowing through and a big fan blowing over it? Somebody should be able to build them in other shapes, like a skirting radiator or even a UFH pipe grid, like the grid on the back of a fridge, has anyone seen products like this?
    •  
      CommentAuthordjh
    • CommentTimeSep 15th 2019
     
    You can get skirting units I believe, but usually the option if the situation needs something different is to go for an air-to-water heat pump and use conventional wet radiators etc. You want refrigerant pipework and heat/cold emitters to be easily accessible for maintenance as far as possible.
  5.  
    Why would an underfloor grid of refrigerant pipes need different maintenance than the equivalent grid of hot water pipes?

    Just curious, never seen it done so guess there must be a catch, but can't see why not. Air-to-water heat pumps have to run hotter in the refrigerant circuit than air-to-air ones, hence the better efficiency of air-to-air. 'Air-to-floor' pumps could run even cooler and more efficiently, in theory...
    • CommentAuthorowlman
    • CommentTimeSep 15th 2019
     
    Posted By: WillInAberdeenWhy would an underfloor grid of refrigerant pipes need different maintenance than the equivalent grid of hot water pipes?

    Just curious, never seen it done so guess there must be a catch, but can't see why not. Air-to-water heat pumps have to run hotter in the refrigerant circuit than air-to-air ones, hence the better efficiency of air-to-air. 'Air-to-floor' pumps could run even cooler and more efficiently, in theory...


    The testing pressure for soft copper refrigerant pipes is much higher than standard UFH so maybe problem number one, and I guess the total pipe length would preclude any such use as you describe.
    • CommentAuthorJeff B
    • CommentTimeSep 15th 2019 edited
     
    Thanks Owlman. I had no idea that you could have such long runs! I'm still pinning my hopes on some new super-duper ASHP being developed so I can simply take out my existing C/H boiler and replace it directly with an ASHP.

    There is nothing currently available that would do my C/H and DHW at a sensible cost.
    • CommentAuthorowlman
    • CommentTimeSep 15th 2019
     
    Hi Jeff,
    You mentioned you live in a bungalow, assuming loft space is unused can't you utilise that for your refrigerant pipe runs? Then simply separate your CH from your DHW; a good plan anyway IMO, and there's choice there.
    • CommentAuthorJeff B
    • CommentTimeSep 16th 2019
     
    <blockquote><cite>Posted By: owlman</cite>Hi Jeff,
    You mentioned you live in a bungalow, assuming loft space is unused can't you utilise that for your refrigerant pipe runs? Then simply separate your CH from your DHW; a good plan anyway IMO, and there's choice there.</blockquote>

    Yes, I could do, especially as you say the possible lengths of refrigerant pipe are much more than I had imagined. Certainly food for thought. I have been put off a bit by the comment about poor heat distribution - cold air near the floor, cold feet etc!