Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorLoftDIY87
    • CommentTimeDec 4th 2019
     
    Had a builder do the shell/structure of my loft conversion earlier this year and I'm DIYing the rest.

    Whilst putting insulation in I've discovered he hasn't left ventilation at either end of the cold dormer roof. It's felt on top, with 150mm (145mm) ceiling joists, plus firrings. Am using 120mm Celotex in between joists, with 25mm Celotex underneath. Taking the firrings and 120mm Celotex into account, the ventilation gap (between top of insulation and bottom of roof OSB) spans from 63mm at one end to 33mm the other end - I know, a little less than the recommended 50mm ventilation gap, but that particular detail is the least of my worries at the moment! Because...

    I've already discovered severe condensation when I removed one of the roof insulation boards and found the dormer roof OSB wet to the touch! The top of the ridge beam is also wet to the touch.

    I know it will be (relatively) easy enough to vent at the far end of the dormer roof - using soffit or fascia vents. However I know I need the air to circulate i.e. vented at both the 'far' dormer soffit end, as well as the ridge end. Am toying with the idea of mushroom vents on top of the dormer roof, but there are 13 openings and obviously I don't want 13 mushroom vents on my dormer roof! (would need one for each opening as there's currently no way for the air to circulate between them)

    I'm also thinking I could notch and drill holes in each and every joist to the maximum regulations permitted, that would create some sort of airflow in between joists, and possibly result in needing far less mushroom vents? (could I get away with just 3 - one in the middle and one at each end?) I've attached a diagram showing joist holes and notches I've calculated. I'd have to batten 44mm x 44mm timber to the bottoms of the joists and bring the 120mm Celotex down to that level to allow for 30mm holes to still have the required 50mm height clearance from the hole to the top of the joist.

    Also concerned about the roof leaking if I get a roofer to put mushroom vents into a felt roof, whether it's 1, 3 or 14...

    Any other solutions to provide ventilation?
      IMG-20191203-WA00002.jpg
    • CommentAuthorLoftDIY87
    • CommentTimeDec 4th 2019
     
    Ridge beam touching underside of roof decking, blocking flow of ventilation:
      Top of ridge beam touching underside of roof OSB2.jpg
    • CommentAuthorLoftDIY87
    • CommentTimeDec 4th 2019
     
    Pic of what I could potentially do to create cross ventilation between joist openings
      Loft joist holes and notches for ventilation2.png
  1.  
    .I've been edited!

    Welcome to GBF!

    You are not alone! I spent many happy hours trying to un-knit loft-conversion-related issues (via e-mail and phone) for a client last year.

    (On the other hand I may be a bit stupid, but I can't interpret your sketch. Are the holes and notches 'either/or'?)

    Cancel that, I think! It's a plan, rather than an elevation - yes? The black-hatched line is the top of the joist? If I have got that right surely the 30mm holes at the 'shallow end' are right at the top of the joists, so they are effectively 'short notches'?

    So let me get it clear in my head - you are planning to put fascia vents above the window? That's the 'in', but because the back of the dormer is at ridge level, there's no 'out'. Is that correct? So you are planning to allow air to flow at 90 degrees to the front-to-rear path, via holes and notches? So where's the 'out'? Can you vent out at the top of the cheeks?

    Air-flow can be pretty lazy, so if you offer a series of 'ins' at the fascia, and a series of holes/notches 100mm or so away, I reckon you will get lots of short-circuiting and not a lot of cross-ventilation.

    On the (more positive) other other hand...

    You don't have a VCL yet. I am a cynic when it comes to 100%-tight VCLs, but (in conjunction with *cross-* ventilation) if you had, say, Intello below the bottom layer of PIR things might get a lot less moist. Probably more thoughts later.

    ...and one more now... The cross-sectional area of the round fascia vents is a lot less than you'd think. I'll see if I can find the sketch I did last year showing more vent than fascia.
  2.  
    Found it! See a few posts below.
    •  
      CommentAuthordjh
    • CommentTimeDec 4th 2019 edited
     
    "Please repost the lost image Nick - Ed"

    That is nothing like what I wrote!

    I object to brazen rewriting of what I write.
  3.  
    Coming soon!
    • CommentAuthortony
    • CommentTimeDec 4th 2019 edited
     
    There are flat roof vents, I dislike flat roofs, but near the highest point these, or similar, could save a load of hassle.

    https://www.roofingsuperstore.co.uk/browse/ventilation/flat-roof-vents-extraction.html?gclid=Cj0KCQiAz53vBRCpARIsAPPsz8VYPMcylDAzGTmSeVMcLqb_nqXbUBSOpfQ2vHwB79S42BTyWuRFfVgaAksEEALw_wcB
  4.  
    Vents sketch
      DSCF6650 - Copy2.JPG
  5.  
    Ignore the trade name. I am not advertising for them. It's just the first vent I found when looking for dimensions for my client.
    • CommentAuthorLoftDIY87
    • CommentTimeDec 4th 2019
     
    Thanks for replies guys.

    Nick - sorry I've just looked at the diagram I drew - not very clear is it! I've redrawn so it's a little more clear - yes you were right when you said it's plans, not just elevations. Hopefully second drawing will make more sense.

    And yes those holes and notches would just be there to have cross flow ventilation between the joists. It's just an idea I have at the moment, as I can't think of any other way to provide a flow of air between the joists...and don't want vents in each joist opening as that will be 13 vents on my roof!

    I'd still need to have an 'in' and 'out' you're correct. The 'in' I'm thinking is through the soffit or fascia vents, and the 'out' I guess would have to be through the flat roof mushroom vents like the ones you've posted Tony.

    I don't really want to put those mushroom vents on the flat roof as I'm not sure how well they can be retrofitted to a felt roof? Would they not be prone to leaking? If it was GRP I guess it would make things a lot simpler but unfortunately it is what it is now!
      Loft joist holes and notches for ventilation 3.png
    • CommentAuthorLoftDIY87
    • CommentTimeDec 4th 2019 edited
     
    Re: vents sketch - I've actually discovered that the builder did put a vented soffit in on the outside...but on the inside it's blocked with timber?!
      Timber blocking soffit vent.jpg
      IMG-20191203-WA0010.jpg
      Soffit vents on outside 2.jpg
    •  
      CommentAuthordjh
    • CommentTimeDec 4th 2019
     
    I'd just chop sections out of the firring near the ridge, rather than make 18 mm notches. You can always put a metal strap over the top if anybody insists, but since you won't have touched the joist I don't see why there would be any problem.
    • CommentAuthorLoftDIY87
    • CommentTimeDec 4th 2019
     
    djh - that actually does make more sense. Plus the firrings are about 38mm at their highest point, so much larger gaps.

    However, I've been advised on another forum to push the existing 120mm Celotex all the way up to the underside of the decking, and put more insulation underneath until it's flush with the bottom of the joists...i.e. fill each and every joist opening with insulation, so there is no void at all for air to condense. And then cover with a further 25mm beneath the joists, vapour barrier, then plasterboard.

    And leave both ends (soffit and ridge end) closed so no air can comes in.

    Anyone have any experience/knowledge on this option? Seems a better way if it's scientifically correct and BCO agree? I haven't come across this option in 2 days of Googling flat roof ventilation...but if it does solve my problem it makes sense to do it - would be a lot cheaper too! (although would mean cutting and fitting even more insulation and a bit of difficulty getting it all flush because of the firrings)...just when I thought I was seeing the light at the end of the tunnel of all that dust)
  6.  
    Gosh, you must be busy just reading all the forum replies!

    One of the posters on the diynot forum, in suggesting the full-fill lay-up, suggests that the water vapour won't get there *because of the VCL*. He/she must have more faith in VCLs than I do. I believe that it is rare for a VCL to be installed 100% tight. Therefore, in your position I would have a VCL ('for what it's worth' - don't get me wrong - I'd do my damnedest to get it tight) *and* a well-ventilated gap.

    The full-fill option is not a common one, as far as I know.

    Ventilate that gap! (And next time you do a flat roof you'll do a warm roof anyway, so you won't have any of this fuss!).

    I hope it goes well.
    • CommentAuthorGreenPaddy
    • CommentTimeDec 5th 2019 edited
     
    Pretty sure it doesn't matter if there is an air gap or tight to the OSB, you will still get condensation. You have to either stop any moisture getting up there from the house (impenetrable VCL) which is near impossible to do, or you have to remove the moisture once it's up there.

    A high quality VCL continuously across the area will help a lot (something like profoil 861, whch has a vapour resistance of around 45,000 MNs/g, plus ventilation. Taking chunks of the firring out (as per DJH) would be a smart way to enhance cross joist air movement.

    Can you get in with a right-angled drill, and core out the flat timbers that are blocking the soffit vents? Or a multi tool to zip through them.

    Then add the 3 roof vents you mentioned earlier.

    A combination of good vapour check, and soffit-to-roof/ridge ventilation, with firrings notched for cross flow.

    Your ridge steel will still be cold, so think about how you insulate to keep the bottom flange outside the thermal envelope.
    •  
      CommentAuthordjh
    • CommentTimeDec 5th 2019 edited
     
    Posted By: LoftDIY87However, I've been advised on another forum to push the existing 120mm Celotex all the way up to the underside of the decking, and put more insulation underneath until it's flush with the bottom of the joists...i.e. fill each and every joist opening with insulation, so there is no void at all for air to condense. And then cover with a further 25mm beneath the joists, vapour barrier, then plasterboard.

    Seems a better way if it's scientifically correct and BCO agree?

    I think the last little bit is the key. Whether the BCO agrees. When I did my roofs, regs said ventilation was required except for a true warm/inverted roof (I.e. no material that can rot on the cold side). I suppose that may have changed.

    So I did my conservatory roof in the standard way ventilated with insulation underneath and a VCL at the bottom, much like your original scheme although I do have ventilation at both ends.

    My house roof is not ventilated. It has (bottom up) skimmed plasterboard, VCL, panelvent, 450 mm warmcel in crossed rafters and purlins, 18 mm ply, 'metal' breather membrane and standing seam aluminium. My BCO (actually a private building inspector) accepted it on the basis of a condensation analysis done by the membrane supplier, who also warranted it for my benefit. To me the important differences from your proposal are: my insulation is hygroscopic and will buffer any moisture; the 'metal' breather membrane forms a small gap above the ply and below the aluminium to allow moisture to escape. Particularly with non-absorbent foam insulation and felt directly on top I'd be very concerned about condensation and mould in your OSB.
  7.  
    GreenPaddy said: ''Your ridge steel will still be cold, so think about how you insulate to keep the bottom flange outside the thermal envelope.''

    In a recent scheme I was involved with, with very limited headroom at the ridge beam, 10mm aerogel with a 3mm MgO board attached was to be used on the bottom flange.
    • CommentAuthorLoftDIY87
    • CommentTimeDec 5th 2019
     
    Thanks all, appreciate the assistance here - although am now even more concerned after having BCO round for a site visit today! Re: vapour barrier, I will certainly be putting this under the insulation either way to help stop moisture getting in the void, but I'm aware they can't be 100% effective and would only help to a certain degree.

    Discussed options to solve this issue with the BCO...bottom line he wasn't too pleased with the way the builder had done it! He said the steel should have been lower so air could flow on top of it.

    We discussed all the options, including:
    - Mushroom vents: he said it was an option to put 3 on top, but then even if I drilled holes between joists the cross ventilation wouldn't be great so not an ideal solution
    - Full filling the void: he said Celotex themselves don't like hybrid roofs and he didn't agree to this option at all
    - Getting back on the roof and adding 50mm of insulation on top of the felt, then refelting on top of that...i.e. making it a warm roof. However he thinks this would then result in a height smaller than the required 150mm between top of ridge tile and top of flat dormer roof, so that option was also ruled out

    He then called his manager (private BCO firm) who advised him to call a company called GlideVale, who specialise in roof venting products. BCO called them and they advised to get back on the roof and fit an 'FV250' vent all across the ridge, and open the soffit vents up on the other end too.

    I asked BCO who was responsible and he said builder should have done it correctly from the start, and he'll be writing an enforcement letter saying it needs to be corrected within 90 days! Just called the builder who wasn't too pleased with BCO comments and will be coming round tomorrow...he thinks he could just drill into the steel ridge beam to provide airflow but I'm sure that would compromise it's integrity surely?!

    Anyway just Googled the FV250 vent and looks like it's an over fascia vent so have no idea how it can be the solution, or how it can be fitted at the ridge tiles to provide ventilation to a flat roof! Product is here: https://www.roofingsuperstore.co.uk/product/glidevale-over-fascia-ventilator-25-000mm-airflow-1m-pack-12.html
    • CommentAuthorLoftDIY87
    • CommentTimeDec 5th 2019
     
    Have just received this drawing from BCO, detailing this ridge vent.

    Would also need to make an opening on the inside to allow the air to escape, which would then need lead flashing to seal back up again.

    A lot of extra work and not budgeted for... Hoping builder will sort it out of his own pocket as really don't want to drag it to courts!
      Screenshot_20191205-151650_Drive.jpg
  8.  
    I often sit in my office, complaining about BSO's, and the system we have here in Scotland, whereby you have do prepare all the drawings, including sectional details like the one your BSO provided for you (very helpful of him), and get it audited/signed off before starting on site.

    However, it makes total sense to have every junction/interface/fixing/etc detail fully thought through, put on paper, agreed with client/builder/BSO, before you start any work, and might have avoided this vent detail, and poss steel beam issue, and been clear as to what SHOULD have been provided by the builder and costs for correction.

    Won't stop me sitting here cursing them though!!

    When the client & builder get in a huddle, and decide they want to alter the design, and build it in a way that I know will be an issue, I usually tell them that's great, there's no problem doing it, and they are now assuming design responsibility for the project, and absolving me from any future issues. Usually gets the desired response :devil:

    Trying to be helpful for a moment, your builder does have to comply with building regs, so if he has chosen to build it in contravention of building regs, he can have as many goes as he likes at his own expense, but it ultimately has to comply (and regs are just a minimum). Your BSO's sketch might also solve the the steel beam condensation issue, by venting around it. Just insulating a bit under the bottom flange, won't stop it sweating, and so likely to get water staining on the ceiling (which people often think is a roof leak, and spend months chasing rain ingress).
    • CommentAuthorLoftDIY87
    • CommentTime7 days ago
     
    Apologies for reviving an old thread but builder only just came round to get this sorted today, after months of me calling!

    The roofer said we couldn't do the ridge vent idea as it would change the profile of the ridge itself and since it's a terraced house, that's not possible.

    So gone for 70mm fascia vents in every joist opening, and 70mm mushroom vents in every OTHER joist opening.

    However I'm concerned this may not be adequate?

    I've sketched a diagram of what the builder has done.

    Roofer i coming round this afternoon to get on the roof and fit the mushroom vents.

    However I'm thinking of going out and buying 100mm vents, redrilling 100mm holes myself and getting him to fit those instead. Even still I'm wondering if it will be enough? Building control (private) seem satisfied with the 70mm setup, but being a new build with excess heat, I'm still concerned.
      loft drawing.png
    • CommentAuthortony
    • CommentTime7 days ago
     
    Looks fine to me but you have to convince building control
    • CommentAuthorLoftDIY87
    • CommentTime6 days ago
     
    I ended up changing the holes to 100mm and buying 100mm mushroom vents for the roofer to fit.

    Have attached a pic of the 100mm hole below, and showing notches in the firings.

    As the mushroom vents will only be every other joist, will it be beneficial or detrimental to create larger notches / holes in the joist?

    Building control guy thinks this would be enough as the vents will suck the air up, however a couple of people mentioned air is lazy and doesn't like to flow sideways, so I'm not sure if whether creating larger openings between the joists/firrings will help or not
      IMG_20200520_184900-min (1).jpg
  9.  
    Just a though..apart from it being a pain, is there any reason you can't make more openings in the "firrings", along the length of each rafter?

    It's not structural, just a spacer. If you drilled every let's say 150mm, or even 100mm? Youy might hit the odd fixing nail, but just stop, and move over.