Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorgoodevans
    • CommentTimeAug 23rd 2020 edited
     
    Posted By: bhommelsAnother question regarding cooling using an ASHP - blissfully unaware of the setup you have:
    Most ASHPs have a buffer tank that also serves for DHW, for example to provide hot water for a shower in the morning. How would this be compatible with your overnight active cooling scheme? How to avoid spending money on temperature cycling a buffer tank?
    I did not see the point of a buffer tank - I have a DHW cylinder - 250 litre with a 3m2 coil that the ASHP pumps water through once a day. And the UFH circuit which it pumps water through for heating and occasional cooling. By the time the water has passed through the UFH pipes it is no more than 0.5 deg C above the slab temp (when heating).

    The ASHP suppliers wanted to put in either a) a low loss header or b) a buffer tank (which is in effect a big low loss header) or c) a heat exchanger to separate the water in the ASHP circuit from the water in the ufh/dhw circuit. I ignored the advice and the ASHP is directly coupled the the UFH and DHW coil.

    This means I have one pump, and one circuit (with zone valves) - I have no need for a separate buffer tank - the DHW cylinder is its own buffer tank and the UFH takes so long to heat up it is the equivalent to a buffer tank of approx 4m3 of water. The ASHP moduates it heat output if necessary - It can supply as much as 9kW of heating (15 l/min at delta T of 8.5 degrees c) down to as little as around 1.9kW (9l/min at delta T of 3 deg C). The pump pumps less through the UFH than through the DHW coil.

    The downside is that either alot of glycol is required (option c avoids this) - or you rely on the frost protection of the ASHP system (I did the latter). If there is a power cut during freezing conditions I will have to power the pump via a leisure inverter and a car battery to ensure the residual heat in the slab will keep the ASHP from bursting its internal heat exchanger.
  1.  
    Posted By: goodevansIf there is a power cut during freezing conditions I will have to power the pump via a leisure inverter and a car battery to ensure the residual heat in the slab will keep the ASHP from bursting its internal heat exchanger.

    Caution is needed using a 'leisure inverter' as many have a wave form that is not good for motors (too 'square' or chopped wave form) There are (more expensive) inverters that have a good sine wave form suitable for motors. Also car batteries are not designed for deep discharge and will be quickly wrecked when used for deep discharge cycles. Unfortunately lead acid batteries suitable for deep discharge are quite a bit more expensive than car batteries. Lithium batteries are an option but again cost is a factor.

    Are you intending to have a battery and inverter on the shelf as insurance or do a panic buy if the situation looks imminent?

    Will the battery back up be on a uninterruptible power supply or will it be manual change over? I guess that depends on the expected frequency of outages, duration and the length of time the ASHP can survive without power. Of course power outages will always happen when most inconvenient e.g. 02:00. Not too expensive to have a battery powered loss of power alarm to wake you up!

    What happens if you go away for a period?

    Is frost damage due to power failure an insurable event (without the insurance co. insisting on antifreeze)
  2.  
    Our Ashp had its own inverters, in the variable speed drives for the compressor and the circ pump, it would be neat if you could feed external DC into those! But unlikely to be easy or warrantied.

    As you only need a slow trickle circulation of the CH water through the ashp and the slab or DHW tank, maybe a tiny DC pump inside the house could do that? Or just a few W of DC heater, inserted into the ashp casing - a car lightbulb?

    Our ASHP died when the heat exchanger got a hairline crack and started leaking refrigerant. It wasn't caused by frost. The exchanger was mounted right down at the back of the case, and the labour cost was prohibitive to remove all the other components to access it.
    • CommentAuthorEd Davies
    • CommentTimeAug 23rd 2020
     
    Posted By: Peter_in_HungaryAlso car batteries are not designed for deep discharge and will be quickly wrecked when used for deep discharge cycles.
    Indeed, but if they're left in the car with the engine ticking over that needn't be a problem, assuming you have a car with an engine. Not the sort of thing you want to make a habit of but quite acceptable for a once-in-a-decade emergency.

    If you have a car with a big battery and a motor, it'll presumably have a 12V battery for lights, accessories, etc. Will it keep that charged off the big battery just sitting there?
    • CommentAuthorgoodevans
    • CommentTimeAug 23rd 2020
     
    we do not have many power cuts - and i'm not away from home that much - I have elected to take the risk of not being in at the wrong time.

    Given the infrequency of power cuts here I intend to have a manual cut over. Plug the pump into the inverter or ups when required. A mains off alarm is a good idea.

    The pump draws something like 27 watts an needs to run for say 5 minutes per hour. In the event of a power cut I can dial the pump down to minimum so it will probably draw less than 10w.

    My main fear is not maintaining good battery health - most systems require a discharge, charge cycle every 3 months or so which I don't trust myself to do - so I was thinking of using my actual car batteries - they always charged and known working and shouldn't take more than 10 minutes to disconnect. It will take hours to discharge the battery. because the power requirement is so low I may be able to use the cigarette lighter and not disconnect the battery.

    The pump has an EC motor - so I strongly suspect that unlike traditional AC motors so long as the inverter doesn't mangle the mains facing electronics the pump will be fine.

    I intend to buy the inverter and have it on the shelf (but have not done so yet - so a panic buy may happen this winter!).
  3.  
    I remember my granddad lashing up something similar from the alternator of his tractor, to run the milking machine.

    I'm sure you'll be careful, but for others reading in future, the supply from the car to the inverter to the pump must never be allowed to back-feed into the house and the mains supply...
    • CommentAuthorgoodevans
    • CommentTimeAug 23rd 2020
     
    Posted By: WillInAberdeenI'm sure you'll be careful, but for others reading in future, the supply from the car to the inverter to the pump must never be allowed to back-feed into the house and the mains supply...
    Yes - that why I have the pump on a 13amp plug - it will either be plugged into the inverter, or into the mains. Keeping the two systems separate.
    • CommentAuthorward32
    • CommentTimeFeb 13th 2021
     
    I'm in the same position as some others whereby in times of heatwave the inside temperatures become uncomfortable after a few days. The thermal mass of the extension (at least EnerPHit) is great for holding the inside temperature comfortable for several days but when it does eventually rise it can take days to come back down. Summer of 2020 we had about 5-7 days when the inside temperature was over 26C.

    I was wondering if anyone had tried using the ground under the slab/insulation as a heat dump. I am renovating our original bungalow (EnerPHit) and could put UFH pipes on the original oversite before concrete-insulation-screed (with UFH). When required I could circulate water from below (insulation) to the above UFH pipes to extract heat, excess heat would then dissipate in to the ground under the house. No heat pumps involved as the soil under the floor should be around 12C. I imagine it will work in the short term but not sure for prolonged periods, is it really worth considering?
    • CommentAuthorSimonD
    • CommentTimeFeb 13th 2021
     
    Posted By: ward32

    I was wondering if anyone had tried using the ground under the slab/insulation as a heat dump. I am renovating our original bungalow (EnerPHit) and could put UFH pipes on the original oversite before concrete-insulation-screed (with UFH). When required I could circulate water from below (insulation) to the above UFH pipes to extract heat, excess heat would then dissipate in to the ground under the house. No heat pumps involved as the soil under the floor should be around 12C. I imagine it will work in the short term but not sure for prolonged periods, is it really worth considering?


    I have a book published sometime mid to late 1800s that has a similar design though it uses air as opposed to liquid to provide cooled ventilation. Long winding ducts below ground and under floor. Obviously doesn't work as a heat sink.

    Also, in Europe there's a growing supply of both ceiling and wall radiant heat elements that, because they're just like wet UFH elements, they're also used to provide summer cooling, if not in some places primarily so. I think this approach may make more sense as it can absorb excess heat as it's conducted through the fabric as opposed to the floor that works once it's already absorbed by the fabric.
    • CommentAuthortony
    • CommentTimeFeb 13th 2021
     
    Better to dump the heat either deep in the ground or under the garage. Danger is that if you heat up under the floor slab, the room may overheat more badly and for longer
    • CommentAuthorward32
    • CommentTimeFeb 14th 2021
     
    Thanks for the comments. I was thinking that the worst that could happen was the ground bearing slab under the insulation could rise to the same temperature as the room screed, and hopefully would eventually dissipate in to the soil. With an insulation U=0.11 very little heat would permeate upwards to the room screed. I would estimate getting a week or two of cooling before the ground got too hot (23-24c) and no more heat was transferred. Probably enough for UK heatwaves. The hardware will cost less than a decent aircon unit so I will give it a go and report back in a couple of years.
    •  
      CommentAuthordjh
    • CommentTimeFeb 14th 2021
     
    Posted By: ward32With an insulation U=0.11 very little heat would permeate upwards to the room screed.

    That may be true, but without this scheme heat would be percolating down, so just stopping that downward flow of heat will lead to increased temperatures in the room, even without any heat flowing upwards.

    I will give it a go and report back in a couple of years.

    I look forward to reading how it goes :bigsmile:
    • CommentAuthortony
    • CommentTimeFeb 14th 2021
     
    Will be interested to hear the result, other options are nighttime cooling and shading the glazing especially west facing glass
  4.  
    Hi Ward32, out of interest, why is the slab going underneath the insulation and not the other way around? Would it help to regulate the temperature if the thermal mass of the slab is inside the insulated envelope?
    • CommentAuthorward32
    • CommentTimeFeb 16th 2021
     
    I'm replacing the existing suspended timber floor with a ground bearing buildup and BC require me to start with a min 100mm of concrete on top of the original oversite (about50mm concrete). I will put the UFH pipes under this bottom layer of concrete. Then 200mm of insulation and the top layer of liquid screed with UFH pipes.

    I have made provision to fit external louver shading on south and west aspects as and when necessary.
    •  
      CommentAuthordjh
    • CommentTimeFeb 16th 2021
     
    Posted By: ward32I'm replacing the existing suspended timber floor with a ground bearing buildup and BC require me to start with a min 100mm of concrete on top of the original oversite (about50mm concrete). I will put the UFH pipes under this bottom layer of concrete. Then 200mm of insulation and the top layer of liquid screed with UFH pipes.

    Find a new BCO! 100 mm concrete over 200 mm insulation is called a passive slab. Or near enough anyway. Or take out the oversite and dig down a bit to put more insulation in and make the slab a bit deeper/stronger.
    •  
      CommentAuthordjh
    • CommentTimeFeb 16th 2021
     
    Posted By: Paul in MontrealThe Wattisham example a6 23.6C has a humidex of 23.6C so there's essentially no humidity ... the dewpoint is at -1.4C so it's very dry!

    Sorry, only just noticed this. I didn't know what a humidex is so I just looked it up - seems like a useful idea. But what Paul says is wrong. What I said was:
    Posted By: djh19:00 32.9% 23.6°C

    And the 32.9% is the RH of course, so it isn't/wasn't 'very dry'! It's on the dry edge of comfortable. The corresponding dewpoint is actually something like 6°C. Dunno where the -1.4°C came from.
  5.  
    Posted By: djh
    Posted By: Paul in MontrealThe Wattisham example a6 23.6C has a humidex of 23.6C so there's essentially no humidity ... the dewpoint is at -1.4C so it's very dry!

    Sorry, only just noticed this. I didn't know what a humidex is so I just looked it up - seems like a useful idea. But what Paul says is wrong. What I said was:
    Posted By: djh19:00 32.9% 23.6°C

    And the 32.9% is the RH of course, so it isn't/wasn't 'very dry'! It's on the dry edge of comfortable. The corresponding dewpoint is actually something like 6°C. Dunno where the -1.4°C came from.


    Indeed, the -1.4C dewpoint was completely wrong - it is 6.34C - but with those figures fed into the https://memory.psych.mun.ca/tech/js/humidex/ calculator, it comes out with a humidex of 23.4C - i.e. no discomfort at all and no feeling of humidity. So it's still "dry" and "comfortable" :)

    Paul in Montreal where the temperature is currently a relatively warm -6.5C with a dewpoint at -9.1C (giving a humidity of 82%) and it's snowing gently