Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




  1.  
    Hello everyone,

    First post here - hoping to get some feedback on our thoughts about replacing a >30 year old oil boiler with an ASHP/GSHP in the house we're prospectively buying (a couple of weeks from exchanging).

    Firstly, a little about us - we're a young family (my wife and I and two children, 3 and 1) and although being cost efficient is important, the most important thing for us is going to be a balance of comfort and convenience. I want to try and avoid the inevitable arguments in the years to come about where to set the thermostat, which has led us to AS/GSHP because we love the idea of keeping the house at a steady temperature year round with constant heat. I've been doing a lot of research on the subject but I'm still struggling a little with viability.

    We are buying an old house which we believe the oldest part is likely to be 18th century, with 0.5m thick stone wall construction. I understand that stone walls aren't good insulators but are good heat sinks, so the last thing we want to be doing is trying to heat the house up in a hurry. It's a 5 bed detatched, approx. 180 m2. It needs more loft insulation which will be the first job when we move in (sheeps wool looking most likely) up to 300mm. The house is double glazed and although not a hugely drafty house, it's not that airtight either and we're likely to improve the ventilation.

    Doing some calculations on the heat loss calculator (https://www.resurgence.org/resources/heac.html) seems to indicate that the total heat lost during a typical year might be in the region of 35,000 kWh, and that the peak power output required of a heating system would be c12-14kW. Using the 'rule of thumb' on this resource https://synergyboreholes.co.uk/information/calculations/ seems to indicate that more like 22kW of power output would be required in the coldest periods to maintain 20 degrees in the house. There's a massive discrepancy here and the last thing we want to do is under-spec a system. 12kW looks to be achievable for ground source or for air source.

    For a ground source system, we'd have to look at either one very deep (~200m) or two shallower (~100m) boreholes (using 35w/m of collector) which would probably be feasible, but more than two boreholes would be difficult from a logistical and cost perspective. We would prefer ground source for potentially higher COP and higher RHI payments to offset the higher cost of installation.

    For air source, there seems to be a decent amount of choice at the 12kW-14kW including Ecodan which appear to be highly rated and we wouldn't have the same space concerns.

    The property has solid floors and is slightly split level, but I've assumed we could probably fit wet underfloor heating next year to take advantage of low-temperature heat, but currently the house has decent size (but not 'oversized') radiators in all rooms.

    All this to say does anyone have experience with ground source or air source for a similar property? Can anyone offer insight on whether 12-14kW is likely to be sufficient, paired initially with radiators then subsequently with underfloor heating?

    Thanks in advance for reading this.
    • CommentAuthorrevor
    • CommentTimeOct 14th 2020
     
    If it was my house before start thinking about heating systems I would see how best I could insulate the walls. Regardless of how efficient HP are, they still use energy which needs paying for despite RHI payment. The smaller your HP needed the better. Bore holes are expensive ASHP noisy if not sited properly. What scope have you to insulate the walls internally or externally and what about the floors. I think to take a fabric first approach (Insulation, elimination of cold bridges and elimination of air leakage) is where I would start. Spending money on these areas is there for ever, a once off cost, whereas any heating system requires repair, maintenance etc and the smaller and simpler the better. Once you have worked out what you can achieve with this approach go back to the calculation to see how much energy is needed to heat the house.
  2.  
    Wot revor said +1
    I have put external wall insulation (EWI) on my stonewalled houses (2 with 50cm basalt rock and earth construction) with great success. After the insulation the effect was a lack of mould in the corners and on north facing wall and a much more comfortable living space. The EWI was 10cm thick.

    If your house is rendered then there should be no issues with planning however if you have facing stone externally then talk to the planning people.
    •  
      CommentAuthordjh
    • CommentTimeOct 14th 2020
     
    Posted By: lookseehearDoing some calculations on the heat loss calculator ( https://www.resurgence.org/resources/heac.html ) seems to indicate that the total heat lost during a typical year might be in the region of 35,000 kWh

    Hmm, that calculator says the heat loss from my house is 14,888 kWh per year. PHPP says it is a maximum of 2,160 kWh, and it's much closer to the truth. I was pleasantly surprised that it allowed me to say my house was built from straw bales :bigsmile: but not so pleased by its reluctance to let me enter triple glazing, or underfloor insulation or even 450 mm of roof insulation. So I'd take everything it says with a big pinch of salt.

    IMHO, a better approach would be to ask the vendor for a copy of their heating bills, and some idea of how warm they keep the house. Given the time of year and where you are in the house-move cycle, I would suggest the following plan:

    (1) Get to completion on the transaction and move in
    (2) Try to enjoy Christmas
    (3) Sort out whatever turn out to be the most urgent deficiencies of the house
    (3a) Hopefully not the oil heating :bigsmile:
    (4) Subscribe to PH+ magazine - the current issue has a good Enerphit refurb

    Meanwhile, and while waiting for an end to the covid confusion:
    (1) Get or make some accurate floor plans and elevations of the house and make several copies
    (2) Decide on how you will plan to install some ventilation (preferably MVHR)
    (3) Decide on your airtightness strategy
    (4) You can start on the MVHR and airtightness anytime after this
    (5) Decide on your goal (PH, Enerphit, AECB Gold, Silver etc etc)
    (6) Decide details of your insulation plan
    (7) Only after the previous step will you be able to work out how much heat you will need and start to think about how you might obtain it
    (8) Decide how to implement all the plans
    (9) Do it
  3.  
    Welcome! I agree with revor - insulate, insulate, insulate (but make sure it's as air-tight as you can get it too). Edit: Agree with P-in-H and djh too, but we were typing at the same time!

    If it were me would not be taking on a house with no wall insulation (other than that inherent in the building material). If we assume that half the reason you bought it is because you like the stone (correct me if I am wrong), then suggestions that you externally insulate might go down like a lead balloon. If you have to insulate internally I would recommend a lime parge-coat (which at least in part may be the existing plaster unless it's been messed with and replaced with gypsum), then, following an interstitial condensation risk assessment, perhaps 80-100mm of rigid wood-fibre or cork on a toothed coat of lime plaster, fixed with plastic or stainless mechanical fixings and finished with lime plaster. pull back ceilings and floors so that the insulation runs seamlessly from room to room. Don't forget to parge and tape around joist ends. The recommendation re thickness should see a U value of around 0.35-ish, which is not quite on the Part L button but close enough to satisfy most BCOs in buildings like this. Only if the building is very exposed would you perhaps consider a lesser thickness.

    Breathability (water vapour permeability) is imprortant for such constructions.

    I'll leave it there for now - running out of grunt!

    And finally, don't be overwhelmed! There's loads of good help on here.
  4.  
    Hi all,

    Thank you so much for all your input so far. I'm definitely getting that insulation is preferable, there are a few reasons why we aren't massively keen which I'll try to set out below, but they focus around the fact that this is an old house (here it is https://www.rightmove.co.uk/property-for-sale/property-84497702.html).

    From what I've read about internally insulating stone houses, by creating a warm box inside a cold house, the external walls are much less likely to dry out properly after cold wet weather, and that can cause accelerated damage to the fabric of the walls (freeze/thaw when sub zero and the walls have no chance to dry out between wet weather) and also damp issues (regardless of breathable materials). I can't remember the source for this, but I remember reading that you are encouraged to use the walls as a heat sink in order to help the drying out process. Also, unless we are going to internally insulate everywhere, we'll end up with some very comfortable rooms and some very cold rooms. Insulating all rooms internally would be a huge disruption to family life, so I expect it wouldn't be something we would 'get around to' in the first year or two.

    External insulation seems to be the 'right' thing to do to drastically improve the performance of a building. There are a few issues with this. The main one is altering the appearance (see Rightmove link above). It isn't the most beautiful building in the world, but we're quite keen on the natural stone as well as the foliage (although currently it needs some work cutting back and tidying up). The next issue again relates to the breathability of the walls, as we're quite nervous about getting this right in terms of using sensitive materials and preventing damp, both from inside the house and soaking up into the walls from the ground. I know that external insulation is also an expensive option with no RHI to help pay for it (and it doesn't look like many people are having much luck with the GHG either - I wouldn't be confident in finding a contractor and getting the works booked in before it expires in March next year). Also this link (https://www.engineshed.scot/building-advice/common-problems/how-to-insulate-stone-walls/#external-wall-insulation) seems to indicate that EWI might only be suitable for a harled or rendered finish, as well as the need for planning permission.

    The final reason why we've invested a lot of time researching ground source/air source heat pumps is that the boiler needs replacing relatively soon. It may be an old workhorse that will continue to function, but the vendors (who have been looking after the house for nearly two years - sadly it's a probate sale) told us that the boiler is 'intermittent' despite recently being serviced with comments from the engineer that it's functioning well at the moment. It's also not a condensing boiler, so less efficient than newer models. We know that given the size and structure of the house we won't be able to heat it up in an hour or two if it's a cold evening, so we're expecting to be keeping the heating on pretty consistently over winter.

    We're quite desperate not to put in another oil boiler. If we do that we know it's likely to be in there for the next 20 years or more and we have an opportunity to do a good thing and avoid burning a lot of oil. We know that either way we look at it, it isn't going to be a cheap house to heat, but a heat pump and a green electricity supplier will put our conscience to rest at least.

    All this said, I'm leaning towards DJH's suggestion of getting in and acquainted with the house before doing anything significant (boiler-allowing). We have a few other priorities (levels are too high, so french drains required on the perimeter and repointing of stonework in hot lime mortar to correct previous cementicious pointing applied, as well as aformentioned loft insulation).
  5.  
    Oh and I'm also keen to put in internal wooden shutters - the windows are double glazed but I think this will definitely make a significant difference to the feel of the rooms.
    • CommentAuthorrevor
    • CommentTimeOct 16th 2020
     
    It is a very nice looking house plenty of character so can understand why you would not want to mess around too much with it. I note it has a poor EPC is there a requirement to have a good EPC rating for RHI ? I do not know much about HP and RHI but I know you needed a C for FIT for solar PV.
  6.  
    I think ther requirement for RHI is to have adequate loft insulation and cavity wall (if you can, but not a possibility here). I don't think there's any requirement for internal or external insulation.
    •  
      CommentAuthorfostertom
    • CommentTimeOct 16th 2020 edited
     
    I know Carlingcott, lived in Peasedown, architected around Bath for years, and IMHO would not hesitate to EWI this house.

    As you say "It isn't the most beautiful building in the world" but could become so because EWI is a great opportunity to modify elevational appearence, get rid of what's crude, improve window design/material/proportions and end up with a seriously handsome house, such as the attached (rear elevation, farmhouse nr Glasto, v beautiful Georgian front, crude Victorian rear).

    Of course this is a major project, new windows, extending the eaves/verges, but after thorough insulation incl roof you'd barely need a heating system, maybe let the old boiler struggle on, for the few days it's needed, feeding a few retained rads. You woudn't need to disturb the ground floor to insulate it, if the EWI is carried down into the ground, to base of founds if modern, or as a horizontal sub-surface 'wing' if founds are shallow (or on bedrock), forming a 'coffer dam' of insulation around the ground floor perimeter. The building fabric will thrive, mould disappear, any rising damp too, with good EWI.
      Wick.JPG
  7.  
    I didn't ever get around to thanking you for your response @fostertom. We moved in 3 and a bit years ago and are now getting our act together with our works. We're expecting a response to our planning application on Monday which is to include a ground floor extension, a first floor extension and adding an office space above the garage (this part may have to wait some time or may never happen depending on the cost of the rest of the works).

    We have also included in the planning application for change of the appearance to allow for EWI and increase to roof height to allow for a warm roof with vaulted ceilings upstairs as well as enlarging some windows (we expect to replace all the windows anyway). The idea is to go 'upside down' and have a large open plan living/kitchen/dining space on the first floor where we can have higher ceilings, roof lights and a first floor deck leading out to the garden.

    The bit that's causing me the biggest headache currently just to get my head around is the EWI. I've heard various suggestions that thick solid stone walls are actually pretty good insulators if kept dry, and that if we repoint with non-hydraulic lime mortar and address all gypsum plaster/modern paints particularly on external walls then there would not be a need to put in EWI, because it won't pay for itself in energy savings and the house will feel warm providing the walls are dry. I've been searching on here and have seen your suggestion to install the new windows in a 'picture frame' onto the outside wall of the house, and insulate over the frames, but if we do this then there really isn't a route back without replacing all the windows again, and at probably £70k+ for windows and EWI this is quite a terrifying thought if the EWI was to fail short of the expected lifespan.

    The thing I keep coming back to is whether a good compromise is to install new triple glazed windows and more efficient doors all around, put in the new warm roof construction, and maybe replace the current solid floors with a slab sat on glapor foamed glass with UFH, as well as leaning into the breathability of the existing stone walls to make sure they remain dry (maybe to include french drains as the levels are a bit off in places).

    It just feels like EWI on an old house like this is a huge investment which won't pay itself off, but more importantly is tricky to do well and to find installers who will do a good job with the right materials that the house needs. It just feels perhaps like there's too much complexity for it to be the right decision when the rest of the project is complex enough. I'd welcome thoughts on any of the above!
  8.  
    Apart from loft insulation there isn't much insulation / thermal improvements that actually have a decent ROI. I would still go for EWI if you can. The improvements to the internal thermal stability both summer and winter - especially with stone walls are a great advantage and v. difficult to put a monetary value on that advantage. And of course any chance of mould in corners or behind wardrobes will be banished. In fact wot fostertom said above +1.

    Think carefully about changing to an upside down house. It might sound appealing but the amount of times you will be going up and down the stairs will IMO soon get tiring and everything needed for living (shopping etc.) needs to be carried upstairs. Do a proper count of how often you all go in and out of the front / back door (which will mean an up and down the stairs) especially now the kids are 6 and 3 and want to play outside and have friends around and for a few years yet they will need a level of supervision when in the garden, difficult when you are 'upstairs'

    For thermal calculations I use https://www.ubakus.de/en/r-value-calculator/?
    My 500mm basalt walls come in at a u value of 3. With 100mm of EPS EWI the u value goes to 0.31 and the difference to the internal environment summer and winter has been worth the expense.
  9.  
    We've been over and over the upside down argument between us because we've been challenged by friends, family and architects many times over, but we think it still makes sense for quite a few reasons:
    * We live on a hill, so steps up and down are just part of our daily life. To access the garden currently we have to walk up 4-5 steps to get into the garden from a slightly sunk patio, which we would trade for walking down maybe 8 steps from the first floor deck.
    * The views are much better from the first floor and we'd like to take advantage of these from our living space not from the bedrooms
    * The walls are thick and taking walls out to create a more open plan space would be logistically a lot more difficult downstairs (or maybe impossible within our budget)
    * Headroom is quite limited downstairs because of level changes, and natural light is poor in the kitchen in the morning and poor in the dining room in the afternoon/evening. If we go upstairs we can vault the ceilings and put in velux windows to bring in much more natural light for more of the day.
    * Our garden wraps around the back 2/3 of the house, and because we're sunk into the hill a little, the visibility of the kids in the garden will be much better from the first floor than it is currently where we can't see 80% of the garden from the kitchen.
    * I don't mind going up and down stairs for things like bringing in shopping, doing the bins etc. My wife and I both do fairly sedentary jobs and aren't seeking this kind of convenience. I'm a firm believer that going up and down stairs is good for you. If we wanted to be step-free at our house it would take far more changes, as getting to either front or back door from the drive is 4-5 steps up, so in the event any of us had reduced mobility in the future we'd likely be looking at moving.

    Thanks for sharing your experience with EWI. From SPAB's report on solid wall U-values they suggest that a 500mm thick limestone wall could have a u-value in the range of 1-1.5 and that a lot of sources overestimate the u values for solid walls, but I'm definitely no expert here. I'd definitely be nervous about putting EPS on a solid stone wall due to the lack of breathability but every system seems to have compromises. I've seen Udireco as a two part wood fibre EWI system which would also allow for our uneven wall surfaces. I've also heard of lime based products like Diathonite which I think would provide a more appealing look than the hard edges and reveals we'd get with EPS or wood fibre boards.

    Here's the planning app with elevations and floor plans if you're interested: https://www.bathnes.gov.uk/webforms/planning/details.html?refval=24%2F00515%2FFUL
  10.  
    Your edges do not have to be that hard even with rigid boards. You can rasp reveals etc instead of using angle beads, and you can wrestle thinner boards round curves and build them up. Have a look at luneretrofit.com for sprayed Diathonite (though not sure if that was internal).

    Udireco is good for uneven walls, as you say.
    • CommentAuthorMike1
    • CommentTimeApr 5th 2024 edited
     
    Posted By: lookseehearI've heard various suggestions that thick solid stone walls are actually pretty good insulators if kept dry
    It's true that the insulation value of solid stone walls is often too pessimistic. That's often because a U-Value for the type of stone has been used, ignoring the contribution of the lime mortar, or using a low proportion of mortar - it could be up to 40% of the wall (see Historic Scotland's Technical Paper 10, for example)

    Never-the-less, a stone wall can't be considered a 'good' insulator.

    Posted By: lookseehearI'd definitely be nervous about putting EPS on a solid stone wall due to the lack of breathability
    So would I. Fortunately there are much more vapour-permiable insulations available, particularly wood fibre and cork (or hemp, if anyone's producing it in the UK), but there's also mineral wool. I'd be looking to insulate with one of those.
    •  
      CommentAuthorfostertom
    • CommentTimeApr 6th 2024 edited
     
    Thanks LSH
    Posted By: lookseeheardue to the lack of breathability
    No no - only the cellular plastic insulations are unbreatheable; EPS, wood fibre etc are fully breatheable.

    Stone may be underestimated for insulation, but 1-1.5 is stiil v poor (whereas cob BTW is about 0.7 or better, even in RdSAP). Any room that's not strongly heated (e.g. turned off when not occupied) soon feels stone-cold clammy - it's all the cold radiation.
    • CommentAuthorrevor
    • CommentTimeApr 6th 2024
     
    I have insulated a stone wall with Kingspan 100mm K50 and not had any issues. The internal of the wall is lime plastered and finished in clay paint. However being belts and braces chap there is a cavity between the insulation and the external cedar cladding ensuring the insulation does not get wet. We are very pleased with how it has worked out that room was very damp when we bought the property the external wall was cement rendered and pebble dashed and the internal wall cement rendered and plastered over. Interestingly the previous owners were funded by the LA to make the improvements that they did. Who on earth specified how the renovation was to be done heaven knows.

    The posters comment re living upstairs makes a sound argument and can see why. We once stayed at a B&B in Scotland that overlooked the loch and with living and dining upstairs and bedrooms on ground floor. That was built into a slope with the main entrance from above. The vies weere glorious and we spied deer and pine marten in the garden below.
    • CommentAuthorMike1
    • CommentTimeApr 6th 2024
     
    Posted By: fostertomNo no... EPS... [is] fully breatheable.
    No No it isn't.

    A typical water vapour diffusion resistance coefficient (µ-value) for EPS is around 60 (though it can be significantly more or less, depending on density). Which is certainly better than XPS (typically around 150)

    For comparison:
    solid wood - around 50;
    expanded cork - around 25 (but can vary significantly by brand);
    wood fibre insulation - around 10 (similar to plasterboard);
    mineral wool - 1.

    Personally I'd consider EPS adequately breathable in new build, but would avoid it for insulating an old stone-walled building.

    All values are from my own notes...
    •  
      CommentAuthorfostertom
    • CommentTimeApr 6th 2024 edited
     
    Posted By: Mike1I'd consider EPS adequately breathable in new build, but would avoid it for insulating an old stone-walled building
    Maybe - that's a fair nuance. At any rate, tho close to a dividing line, EPS is on the right side of it, where XPS is not.

    As I see it, 'adequately breatheable' is good enough - no great advantage in going for super-permeable things like Panelvent.
  11.  
    All I can do is recount my own experience.

    I have a stone wall property, 500mm basalt stone with rubble infill with no render on the outside. The property is 36M long and 6M wide, single story with built in attic. During renovation the internal plaster was removed and I was horrified to see / feel the amount of air movement coming through the wall. Once the restoration was complete part of the property was rented.

    The tenants used the lounge a couple of weekday evenings and at weekends. Once the cold weather arrived they turned down the rad in the lounge and used the wood burner when the lounge was in use - so for most of the time the heating was low and the room colder than the rest of the flat. After a few weeks they complained that there was black mould on the NE facing wall of the lounge which they had to clean weekly. When they washed the wall with bleach then it lasted 10 or so days before the mould returned.

    I put 10cm of EPS EWI on the affected lounge wall, oversailing the lounge area by a meter or so. Problem solved!! The next spring I put EWI on the whole NE side of the property and a couple of years later I did the rest of the property (all with 10cm EPS) That was 10 years ago and there have been no problems since and no mould has returned. The property is much better thermally both summer and winter. That is a more stable temperature.

    When putting on the EWI the builders wanted to render the wall first to get a uniform flat surface which was going to put up the cost tremendously. Instead of that I told them to put a thick bead of adhesive around the edge of each slab of EPS with 3 or 4 doughnuts in the centre and press the slab on to the wall. This they did (reluctantly) There were no mechanical fixings used as drilling the basalt stone proved impossible without causing significant damage to the EPS due to the drill skating around the stone before biting in.

    10 years on there have been no problems with either the EWI or the wall with no damp apparent on the walls. The internal render was sand lime cement mix and the building has concrete floors.
  12.  
    My understanding is that to be 'breathable' a material must be
    * Vapour permeable
    * Capillary open
    * Hygroscopic
    EPS appears to have some vapour permeability but isn't capillary open or hygroscopic. I also wonder about how breathable the adhesives and renders are, because that's another interface to consider. All in all I'm nervous about what kind of materials to use. If you spend any time on any of the 'old house' type groups, particularly on facebook you get shot for suggesting that any modern materials are used, and any attempt to google it results in a range of different answers (https://ewistore.co.uk/external-wall-insulation-on-heritage-properties/ suggests that only wood-fibre type boards should be used as an example).

    Our house has quite a lot of repointing in cementitious mortar, which I assumed we should be replacing with a non-hydraulic lime mortar before adding EWI. It also is very uneven on the outside, with probably 30-50mm gaps in places if you put a straight edge across the stone faces. Peter's suggestion to just glue the outer edges seems a radical one, as does not using mechanical fixings, but it does appear to yield good results.

    We seem to have gypsum plaster on some of the walls at least. Ideally we'd replaster all internal walls with a lime based mortar, which I assume would mitigate some of the impact of having 'less' breathable EWI like EPS if we paired lime plaster internally with MVHR.
  13.  
    Posted By: lookseehearPeter's suggestion to just glue the outer edges seems a radical one, as does not using mechanical fixings, but it does appear to yield good results.

    It is not 'just glue around the edges,

    Posted By: Peter_in_Hungaryput a thick bead of adhesive around the edge of each slab of EPS with 3 or 4 doughnuts in the centre and press the slab on to the wall.

    The thickness of the bead and the doughnuts has to vary to take account of the lumps and unevenness of the wall. I have found that this method uses more adhesive than the usual method of a toothed float as used on a flat surface but still way cheaper than rendering the wall flat first.
    The lack of mechanical fixings is because it was impossible to put them into the basalt rock from which the walls are built. Over here mechanical fixings are not recommended on all types of walls used in new build. e.g. Ytong type blocks don't use fixings and others only recommend mechanical fixings in exposed locations.

    With regards to breathability my walls being basalt rock the only breathable bit would be the earth between the rocks, that said I have a bit of a problem with a statement from the link

    Quote
    Because heritage properties are typically made of porous materials such as sandstone and limestone, they rely on the breathability of these materials to allow moisture to escape from their structures.
    End quote.

    If EWI is put on properly this provides a weather screen on the outside which will prevent any precipitation going into the wall, and if during renovation proper ventilation is addressed which will control moisture (condensation) from the inside then what moisture is left that needs to escape through the walls to the outside?

    I do not subscribe to the notion that modern materials should not be used on old buildings. Typically 'traditional' materials were used because that was all that was available. Building materials were what was available locally within transport distance by horse and cart, which is why my building are basalt stone, 30km away the buildings are red sand stone in one direction and adobe 30 km in the other direction. Material choice should be based on performance and characteristics and not because that was what was used back in the day.
    • CommentAuthorrevor
    • CommentTimeApr 8th 2024
     
    <blockquote><cite>Posted By: Peter_in_Hungary</cite>Material choice should be based on performance and characteristics and not because that was what was used back in the day.</blockquote>

    Totally agree except when what was used in the day is more appropriate or where original based materials are specified in a historic or listed building renovation or alteration work.
    •  
      CommentAuthordjh
    • CommentTimeApr 8th 2024
     
    Posted By: lookseehearMy understanding is that to be 'breathable' a material must be
    * Vapour permeable
    * Capillary open
    * Hygroscopic
    I don't think so. I think breathability generally just refers to the vapour permeability. There are roof membranes that claim to be both breathable and waterproof for example. Hygroscopicity is often a useful property found usually in organic materials, but is sometimes a nuisance. So:
    * breathable = vapour permeable
    * capillary open = transports liquids, usually water
    * hygroscopic = capable of storing liquids by absorbtion

    As you say there are a lot of potential sources of information. Some are biased by commercial interests; others by well-meaning misunderstandings, and yet more by pure prejudice. Some places are better than others. It's very confusing sadly.

    Posted By: Peter_in_HungaryIf EWI is put on properly this provides a weather screen on the outside which will prevent any precipitation going into the wall, and if during renovation proper ventilation is addressed which will control moisture (condensation) from the inside then what moisture is left that needs to escape through the walls to the outside?
    It's best to think of waterproofing as an external layer outside EWI. Weather screening is provided by the render or cladding and drainage plane membrane rather than by the EWI itself.

    Proper ventilation doesn't mean there's no moisture in a house. There's as much moisture in internal air brought in from outside as there is in external air (measured by absolute humidity) plus there's moisture emitted by human activity inside (transpiration of plants, animal and humans; cokking; washing etc). The RH may be lower because it's warmer inside but that doesn't make molecules disappear. Most excess moisture is carried outside by the ventilation system along with the 'used' air and indeed preventing a moisture build up is one of the main reasons for ventilation rates. But there can still be vapour pressure driving moisture into the walls from inside. (or from outside if the inside is artificially cooled).
    •  
      CommentAuthorfostertom
    • CommentTimeApr 8th 2024
     
    Posted By: Peter_in_HungaryIf EWI is put on properly this provides a weather screen on the outside which will prevent any precipitation going into the wall, and if during renovation proper ventilation is addressed which will control moisture (condensation) from the inside then what moisture is left that needs to escape through the walls to the outside?
    AFAIK there's constant traffic of moisture alternating in both directions, tho mostly from inside to out, depending mainly on changing weather/time of year, only slightly on internal moisture generation. It seems best to allow this, not to intentionally or accidentally obstruct it - provided that the configuration of the 'sandwich' checks out well in WUFI or equivalent - or is known from experience and custom to be OK.

    So, having adjusted my prefered 'sandwich' in WUFI many years ago when I had access to it, I tried it with and without an internal vapour barrier - and it performed much worse with the barrier. Over a range of sandwich-variants, right-through breatheability was considerably best. I understand this is due to the vital ability of a sandwich to re-dry as quicly as poss, when conditions change. Drying inward is just as important as outward, and cutting off one direction or the other, by an intentional or accidental vapour barrier, hits re-drying ability hard. This didn't require or prefer super-permability - just 'fair' (like EPS) was plenty good enough.

    Nowadays, conventioal wisdom still wants an internal vapour barrier, tho I understand that the latest (or soon forthcoming) revision of BS5250 has big changes, due to developing understanding - principally realising that the main (or only) source of any interstitial condensation is not internally-generated, as has seemed 'common sense' hitherto, but atmospheric (varying in direction and quantity with weather/time of year), so needing that ASAP re-drying in both directions, inward as well as outward. Hence no obvious call for internal vapour barrier, in new BS5250.

    But the manufacturers and Bldg Regs still presume internal vapour barrier, or otherwise some Certification to justify no vapour barrier. And this stipulation has greatly tightened recently, so e.g. Warmcel won't allow their distributors to supply the stuff without such Certification. Which mainly doesn't exist, so looks like I for one will have to get myself WUFI, to provide the documentation.

    Or give in, and specify internal vapour barrier, but the expensive self-regulating kind, which 'disappears' (as far as vapour resistance) when it senses high RH. Which seems an expensive way of leaving the vapour barrier out!
    • CommentAuthorMike1
    • CommentTimeApr 8th 2024 edited
     
    Posted By: fostertom
    Posted By: Peter_in_HungaryIf EWI is put on properly this provides a weather screen on the outside which will prevent any precipitation going into the wall, and if during renovation proper ventilation is addressed which will control moisture (condensation) from the inside then what moisture is left that needs to escape through the walls to the outside?
    AFAIK there's constant traffic of moisture alternating in both directions, tho mostly from inside to out, depending mainly on changing weather/time of year, only slightly on internal moisture generation. It seems best to allow this, not to intentionally or accidentally obstruct it - provided that the configuration of the 'sandwich' checks out well in WUFI or equivalent - or is known from experience and custom to be OK.
    Agreed. And if there is no DPC, then moisture from the ground may also be a consideration; more so if the original floor has been replaced with concrete + DPM.

    Posted By: fostertomHence no obvious call for internal vapour barrier, in new BS5250.
    Logical and, as you probably know, UK Government advice for IWI (Retrofit Internal Wall Insulation Guide to Best Practice) is already to drop the vapour barrier, while stressing the need for an air barrier.

    Posted By: fostertomspecify internal vapour barrier, but the expensive self-regulating kind, which 'disappears' (as far as vapour resistance) when it senses high RH. Which seems an expensive way of leaving the vapour barrier out!
    At least according to Pro Clima's explanation, it's the difference between internal and external temperature (rather than RH) that changes the vapour resistance; hotter outside than in and the resistance drops. But yes, I'm not convinced that they make a big difference, though I'd like to read more on the topic.

    Posted By: djhHygroscopicity is often a useful property found usually in organic materials, but is sometimes a nuisance
    The ability to absorb and desorb moisture is a very useful property for IWI & cold-roof insulation. A considerable quantity of moisture can be safely buffered within the cell walls of the material, rather than condensing out. One of the reasons that I'm using hemp-based insulation on my current refurb.

    And on that topic, if anyone knows of study into hemp insulation in an unventilated cold roof in the presence of MVHR, I'd be very interested!
  14.  
    We're commencing works to our house next week and are starting to think about heating. I'd written this as a new post but I can't seem to create one as my membership expired and it wouldn't let me renew for some reason.

    As a reminder, our house consists of two C1800 miners cottages knocked together and extended to the rear and one end in the 1970s. The original buildings are ~500mm rubble filled limestone walls and the extensions are two skins of breeze blocks with a 50mm cavity and faced with limestone to match the original structure.

    The house is perfectly liveable at the moment, but is poorly insulated and drafty, and the aluminium DGUs have mostly blown and are slim and provide a significant cold bridge. At some point in the past the roof tiles were removed on the older section of the house, and multifoil insulation has been put in between the rafters and the felt/tiles, but there is also 30-50mm of mineral wool between the ceiling joists, and I believe the eaves have been blocked by mineral wool too, so we have some kind of hybrid warm/cold loft space. Due to the low pitch of the roof there's not much space up there (~1m at the ridge or a little more).

    We discussed EWI above and have planning permission for a rendered finish but have decided to hold off on this. We are planning to replace the roof so that we can vault the ceilings and insulate properly, as well as install solar panels and put in roof lights (existing rafters are only 70mm deep), as well as replace all windows and doors and fairly aggressively renovate and reorganise inside. Once we have done this, we'll assess whether or not to EWI in the future, based on costs and likelihood of payback, and any green initiatives that come along. We would consider EPS bead cavity fill in the 1970s extension (any thoughts or experience with a 50mm cavity?).

    Additionally we're adding a first floor extension which will be built to modern standards. We'll be moving the living space to the first floor which will be mostly open plan other than a snug/TV room, a utility and attached WC, and will have a large deck (over the new extension) with access to garden. Bedrooms/bathrooms will all be downstairs.

    For our heating strategy here's what I'm currently thinking, but I'd love to hear some thoughts/opinions on this.

    We had to replace the 30 year old oil boiler because it dropped dead, so we currently have a 3 year old external oil boiler and unvented cylinder. The new extension is going to have wet underfloor heating, and I would ideally like to put this throughout the ground floor, ideally driven by an ASHP. We're not certain whether there's insulation in any of the existing floors, so would potentially be looking at slim overlay type systems.

    For the first floor, due to it being open plan with vaulted ceilings I like the idea of putting in an MVHR assisted by an air to air heat pump so we can both heat and cool. I believe there are combined units available but haven't put a lot of time into researching this yet. My thinking is that warm air would be collected from near the ridge of the vaulted ceiling and distributed to bedrooms to supplement the underfloor. It seems elegant in my head due to the lack of radiators and ability to cool in the summer if needed. Having two systems could also make it easier to balance bedrooms downstairs vs open plan space upstairs.

    The house is currently roughly 200 sqm and will be ~250sqm by the time the extension is done. I suspect what I need to do is find someone to spec a system but I'm not sure if I'm overcomplicating it.
  15.  
    Are you talking a combined MVHR/ExhaustASHP (I am not sure if 'assisted by' means 'integrated with')? I have not looked at such systems for nearly 10 years but, IIRC, they would only have been much use with almost Passive-House levels of insulation and air-tightness. Maybe bigger systems exist but I'd have thought that the inherent slow speed air-shifting of an MVHR would militate against this. If you think of the almost silent running of an MVHR and the fairly loud 'rush' of an air-con external unit on 'full chat' it may give you an idea of the different volumes. (But I am definitely not an expert on this - I usually concentrate on insulation and air-tightness and getting the heat-load down really low, then whatever heating system you end up with is probably the smallest it can be. Others with more knowledge of ASHP and particularly EAHP/MVHR may be along soon.

    I am more worried about the heat-loss (and 'comfort-loss') from the walls, though if you try to calculate pure payback I daresay it would 'tell you' not to do EWI. I doubt my EWI will pay back till after I am dead, but I am wholly satisfied that it's the right thing to do.

    Unless the roof void to which you refer is entirely un-ventilated (not the norm) I would question whether the multifoil is doing anything. Therefore I feel your 'radical' roof works are likely to be a good idea.

    It sounds like you have come a long way since your earlier posts, and I hope the next stages go well.

    You say ''I'd written this as a new post but I can't seem to create one as my membership expired and it wouldn't let me renew for some reason.''.

    It may be worth trying again. Have a look at Keith's post (dated 2009 or 2007, I think) at the top of the 'menu'. Strictly the forum is closed to new members but there are at least a couple recently (welcome, all!) who have succeeded in posting.
  16.  
    <blockquote><cite>Posted By: Nick Parsons</cite>Are you talking a combined MVHR/ExhaustASHP (I am not sure if 'assisted by' means 'integrated with')? I have not looked at such systems for nearly 10 years but, IIRC, they would only have been much use with almost Passive-House levels of insulation and air-tightness. Maybe bigger systems exist but I'd have thought that the inherent slow speed air-shifting of an MVHR would militate against this. If you think of the almost silent running of an MVHR and the fairly loud 'rush' of an air-con external unit on 'full chat' it may give you an idea of the different volumes. (But I am definitely not an expert on this - I usually concentrate on insulation and air-tightness and getting the heat-load down really low, then whatever heating system you end up with is probably the smallest it can be. Others with more knowledge of ASHP and particularly EAHP/MVHR may be along soon.</blockquote>

    I'm thinking along the lines of the Genvex Premium Preheat. The smallest one provides up to 2.5kW of heating added to incoming air post heat-exchanger in the MVHR. The idea is that this would just be to heat the main living space (70m2 or so) and to redistribute heat from other rooms where heat is supplied by wet underfloor heating. The expectation is that heat would rise through the house from the UFH downstairs, so the air to air system wouldn't have to work as hard.

    <blockquote><cite>Posted By: Nick Parsons</cite>
    I am more worried about the heat-loss (and 'comfort-loss') from the walls, though if you try to calculate pure payback I daresay it would 'tell you' not to do EWI. I doubt my EWI will pay back till after I am dead, but I am wholly satisfied that it's the right thing to do.</blockquote>

    We had a rough estimate from an architect of £30k to complete EWI works, plus the structural changes to roof etc to allow for this. We asked ourselves why we wanted to do EWI, and the main reasons were environmental and comfort. If we move to heat-pump based heating and are on a green electricity tariff and supplemented by some solar then we have ticked the environmental box, and comfort can be achieved through improvements we're already making (windows/doors/roof/UFH etc) albeit with higher energy spend, but then we're onto the subject of payback. My intention isn't to create a debate about the pros and cons, just that it feels like we can't fit EWI into our budget, along with the added complication and risks associated with it being a relatively immature industry. It's a bonus that we can keep the stone look of the house which we've become fairly fond of.

    <blockquote><cite>Posted By: Nick Parsons</cite>Unless the roof void to which you refer is entirely un-ventilated (not the norm) I would question whether the multifoil is doing anything. Therefore I feel your 'radical' roof works are likely to be a good idea.</blockquote>

    I agree. Best case is that it's not doing anything, worst case is that there is risk of moisture issues from having an unventilated loft space.
    •  
      CommentAuthordjh
    • CommentTimeSep 12th 2024
     
    I just took a look at the Genvex Premium Preheat 250 details. I'd be concerned about noise levels - some of the number look quite high. As Nick said, an MVHR is limited in how much heat it can supply by the low speed air used. I have a 1.8 kW post heater attached to my MVHR, but at the normal level of ventilation it limits itself to about 1.2 kW because there isn't enough air flow for it to use full power. Our internal volume is 414 m³.

    So if I were to think about buying one of these units, I'd want to see some pretty convincing evidence of it in use somewhere else first and be able to ask about noise levels, power output and such like.
   
The Ecobuilding Buzz