<?xml version="1.0" encoding="utf-8"?>
	<rss version="2.0">
		<channel>
			<title>Green Building Forum - Price of solar storage batteries</title>
			<lastBuildDate>Sat, 18 Apr 2026 10:47:08 +0100</lastBuildDate>
			<link>https://www.greenbuildingforum.co.uk/newforum/</link>
			<description></description>
			<generator>Lussumo Vanilla 1.0.3</generator>
			<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284255#Comment_284255</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284255#Comment_284255</guid>
		<pubDate>Sun, 01 Nov 2020 15:46:04 +0000</pubDate>
		<author>revor</author>
		<description>
			<![CDATA[As someone who is set on installing a battery for PV storage I cannot fathom out why these batteries are so expensive compared to those in cars. I recently read on a motoring site that a replacement 40kw battery for a Nissan leaf is Â£5k.  40 KW worth  of solar battery would set me back in the region of  Â£12K to Â£15K at least. A mini car from China Baojun 300  you can have for ca $9000 complete with 17kw battery. Can't think anything much to do with sales volume the cells are typically the same in EV and solar pv batteries.]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284256#Comment_284256</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284256#Comment_284256</guid>
		<pubDate>Sun, 01 Nov 2020 16:20:55 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[The Â£5k price you have seen is I believe a replacement price. i.e. You give them your old battery pack and they give you a new one to replace it. The article I found was dated 2014 so I don't know what the current price is. And the price may or may not be subsidised of course, since it's only for captive customers who own a Leaf.]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284257#Comment_284257</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284257#Comment_284257</guid>
		<pubDate>Sun, 01 Nov 2020 16:33:27 +0000</pubDate>
		<author>jamesingram</author>
		<description>
			<![CDATA[for ref approx Â£5k ex will get you 3.5kW- 17.6kWh HV system, at trade]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284258#Comment_284258</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284258#Comment_284258</guid>
		<pubDate>Sun, 01 Nov 2020 16:36:50 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[The batteries in a Powerwall AFAIK are those very same post-vehicle batteries getting a second life in the kinder regime of a domestic installation.]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284263#Comment_284263</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284263#Comment_284263</guid>
		<pubDate>Sun, 01 Nov 2020 17:31:50 +0000</pubDate>
		<author>Ed Davies</author>
		<description>
			<![CDATA[Posted By: fostertom: â€œThe batteries in a Powerwall AFAIK are those very same post-vehicle batteries getting a second life in the kinder regime of a domestic installation.â€<br /><br />This article corresponds with what I thought I'd heard elsewhere, that the cells in the Powerwall are a different chemistry from the Tesla vehicle batteries and so definitely not post-vehicle ones. Apart from anything else, I doubt there are that many Tesla vehicle batteries that have reached end of road life yet.<br /><br /><a href="https://electrek.co/2017/05/04/tesla-battery-researcher-chemistry-lifcycle/" target="_self" rel="nofollow">https://electrek.co/2017/05/04/tesla-battery-researcher-chemistry-lifcycle/</a><br /><br />â€œInterestingly, Tesla currently uses nickel cobalt aluminum (NCA) battery cells for its vehicles. For its stationary energy storage products, like the Powerwall and Powerpack, the company uses nickel manganese cobalt oxide (NMC) cells, which typically have a longer cycle life, but less energy density.â€]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284264#Comment_284264</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284264#Comment_284264</guid>
		<pubDate>Sun, 01 Nov 2020 17:32:26 +0000</pubDate>
		<author>Ed Davies</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: jamesingram</cite>for ref approx Â£5k ex will get you 3.5kW- 17.6kWh HV system, at trade</blockquote>â€œHVâ€?]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284265#Comment_284265</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284265#Comment_284265</guid>
		<pubDate>Sun, 01 Nov 2020 17:40:11 +0000</pubDate>
		<author>Ed Davies</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: revor</cite>â€¦a replacement 40kw batteryâ€¦</blockquote>Obligatory kWh <img src="/newforum/extensions/Vanillacons/smilies/standard/devil.gif" alt=":devil:" title=":devil:" />]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284268#Comment_284268</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284268#Comment_284268</guid>
		<pubDate>Sun, 01 Nov 2020 18:39:33 +0000</pubDate>
		<author>jamesingram</author>
		<description>
			<![CDATA[HV = High voltage , PV (DC-DC) direct to battery (100-400v)<br />rather than LV (48v) DC-AC-DC double inversion more common with retro fit battery systems]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284274#Comment_284274</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284274#Comment_284274</guid>
		<pubDate>Sun, 01 Nov 2020 19:47:44 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[Any brand names, and what's the ratio of trade to retail prices?<br /><br />edit: And Tesla are just starting to use Li-ion phosphate batteries on cars produced in China, I believe.]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284276#Comment_284276</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284276#Comment_284276</guid>
		<pubDate>Sun, 01 Nov 2020 20:30:33 +0000</pubDate>
		<author>jamesingram</author>
		<description>
			<![CDATA[thats for a SolaX triple power <br />LGchem  HV are more expensive <br />Pylontech LV a bit cheaper.<br />not sure what mark ups other people are charging , <br />theyre pretty expensive already. I work on the standard builders 15%ish for most stuff , but it all a bit variable, (quick nose around and its probably 20-25%) <br />since the internet was invented the list and discount pricing seems very dated. I still find it funny the old school builder merchants think theyre doing you a favor giving you 60% discount whilst still charging twice what anyone can get things delivered to their door next day for 10am for]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284288#Comment_284288</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284288#Comment_284288</guid>
		<pubDate>Mon, 02 Nov 2020 11:46:47 +0000</pubDate>
		<author>dereke</author>
		<description>
			<![CDATA[I've just started looking into building a battery (to better take advantage of octopus agile).<br />You can get LifePo4 cells from china (check alibaba) very cheap - around Â£750 for 10kWh (+shipping)<br />Then you need a hybrid inverter, a reputable one (you want a good one from what I can tell) is around Â£1,500.<br />I haven' figured out if there is much else needed, possibly a BMS if the inverter doesn't have one.<br />But less than Â£3k for a 10kWh is quite good value I think!]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284291#Comment_284291</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284291#Comment_284291</guid>
		<pubDate>Mon, 02 Nov 2020 13:06:18 +0000</pubDate>
		<author>revor</author>
		<description>
			<![CDATA[For many reasons collected over many years I do not want my money to go to China.It is very difficult to find other sources but they are around. I am able to source a German designed and assembled battery made from cells manufactured in Korea. It is actually quite difficult to find out where battery components come from. In enquiring from one EV manufacturer where the batteries were made, as I was considering one of their models they would not divulge where the cells came from but would state where they were assembled.]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284292#Comment_284292</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284292#Comment_284292</guid>
		<pubDate>Mon, 02 Nov 2020 14:09:30 +0000</pubDate>
		<author>dereke</author>
		<description>
			<![CDATA[fair enough - where do you look for non china sourced batteries?]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284297#Comment_284297</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284297#Comment_284297</guid>
		<pubDate>Mon, 02 Nov 2020 16:57:43 +0000</pubDate>
		<author>revor</author>
		<description>
			<![CDATA[You ask the manufacturer. Some will tell you others won't. Asked recently a British manufacturer who gave me quite a bit of technical info but did not reply when I asked where the cells came from. The British distributor of the German battery told me it was all made in Germany but when I asked the actual manufacturer where the cells came from they told me. I do not believe one is told deliberate untruths it is more in the realms that they think they know but don't know that really, they don't know. I wanted non Chinese solar panels asked UK sales office which models came from Korea was told ordered they came made in China. Took a while to get them exchanged but they came good in the end. Often you have to be like a dog with a bone keep checking and cross checking until it all adds up. Been caught out too often. Needed solar cable checked spec on sellers website was suspicious checked the manufactures website it was different. Emailed them was told no one in UK sourced cable from them. Back to UK seller they checked up on their supplier of the cable, they had switched source and not told the seller. So spec on website was wrong. It is a minefield all down to lack of attention to detail just like the rest of the building industry.]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284358#Comment_284358</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284358#Comment_284358</guid>
		<pubDate>Wed, 04 Nov 2020 15:07:58 +0000</pubDate>
		<author>revor</author>
		<description>
			<![CDATA[Came across this<br /> <a href="https://www.bing.com/videos/search?q=using+EV+battery+to+power+house&docid=608007712599048600&mid=E7AA33AA8741674D3DBAE7AA33AA8741674D3DBA&view=detail&FORM=VIRE" target="_self" rel="nofollow">https://www.bing.com/videos/search?q=using+EV+battery+to+power+house&docid=608007712599048600&mid=E7AA33AA8741674D3DBAE7AA33AA8741674D3DBA&view=detail&FORM=VIRE</a><br /> Bit long winded but useful look see how Tesla car batteries are installed. Guy bought battery from Tesla write off and used it in an off grid situation replacing lead acid ones. Worth just skipping through for the interesting bits if you ever wondered what is under the floor of a Tesla EV.]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284361#Comment_284361</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284361#Comment_284361</guid>
		<pubDate>Wed, 04 Nov 2020 18:06:26 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[Are there any plug-an-play systems that also providing islanding in the event of a power cut? i.e. act as a UPS? We've had 3 brief power cuts in the past month and lots since we moved in. Given that we have a new underground connection, I find that somewhat annoying and would like to fix the problem.]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284362#Comment_284362</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284362#Comment_284362</guid>
		<pubDate>Wed, 04 Nov 2020 18:27:59 +0000</pubDate>
		<author>revor</author>
		<description>
			<![CDATA[What I have come across so far apart from the expensive Tesla battery and gateway unit is a Delios inverter which has the switching built in to isolate from the grid and connect to the battery. There is a delay of about 30 secs before battery start powering. The inverter can also turn on a generator set as well. The only other one I have stumbled on is the Powervault 3 which in Jan 2021 will have an UPS facility. Think this one will integrate easily to an existing solar PV system. I too have outages sometimes just a couple of seconds so there is no advantage having UPS in this situation and there is no way I think one will get a step less system do to the requirement to disconnect from the grid. I also think that one needs to separate some of the circuits from the consumer unit into a second one so that the battery powers this second one, powering the essential low power consumption loads .]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284370#Comment_284370</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284370#Comment_284370</guid>
		<pubDate>Wed, 04 Nov 2020 22:37:41 +0000</pubDate>
		<author>borpin</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: djh</cite>Are there any plug-an-play systems that also providing islanding in the event of a power cut? i.e. act as a UPS? We've had 3 brief power cuts in the past month and lots since we moved in.</blockquote>Your issue will be that the power in the house should disconnect from the supply when there is a power cut so when they come to fix it, the line is not live (from your end). A UPS just supplies onward power i.e. everything goes through the UPS. Whatever you had would need to be on the supply side of your consumer unit.<br /><br />This was one of the issues when there was the large power outage a while back. The strike on the sub station caused the disconnection of something like half a MW of embedded generation.]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284371#Comment_284371</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284371#Comment_284371</guid>
		<pubDate>Wed, 04 Nov 2020 23:38:23 +0000</pubDate>
		<author>Jecop</author>
		<description>
			<![CDATA[SMA Sunny Boy Storage (SBS) has an optional automatic transfer switch that will disconnect the home from the grid in case of grid failure. It allows the solar inverters as well as the battery inverter to keep providing energy during blackouts. Takes about 5s to switch.  <br />https://www.sma-sunny.com/en/backup-options-with-sunny-boy-storage/]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284376#Comment_284376</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284376#Comment_284376</guid>
		<pubDate>Thu, 05 Nov 2020 11:21:26 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: revor</cite>I too have outages sometimes just a couple of seconds so there is no advantage having UPS in this situation</blockquote><br />That's exactly the situation I want to protect against. And that's what UPS do protect against, among other things.<br /><br />I suspect most of the failures we get are switching transients where the DNO automatically reroutes around some crappy piece of their overhead wire somewhere. But that's enough to reboot my PC, wipe the clocks on all the kitchen devices so they need to be reset, stop the PVR in the middle of recording and sometimes take down some of my pi and make them fail to reboot. So any interruption at all is very annoying.]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284377#Comment_284377</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284377#Comment_284377</guid>
		<pubDate>Thu, 05 Nov 2020 11:22:31 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: borpin</cite>Your issue will be that the power in the house should disconnect from the supply when there is a power cut so when they come to fix it, the line is not live (from your end).</blockquote><br />Yes, clearly. I don't want to be powering the entire neighbourhood!]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284379#Comment_284379</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284379#Comment_284379</guid>
		<pubDate>Thu, 05 Nov 2020 11:38:27 +0000</pubDate>
		<author>dereke</author>
		<description>
			<![CDATA[from what I can tell you want to get a hybrid inverter, it handles grid disconnections (as far as I am aware but I haven't completely confirmed this yet, you may need an additional piece of equipment) and can supply power immediately when the grid goes down<br /><br />Something like this - <a href="https://www.victronenergy.com/inverters-chargers/multiplus-12v-24v-48v-800va-3kva" target="_self" rel="nofollow">https://www.victronenergy.com/inverters-chargers/multiplus-12v-24v-48v-800va-3kva</a>]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284382#Comment_284382</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284382#Comment_284382</guid>
		<pubDate>Thu, 05 Nov 2020 12:34:10 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: dereke</cite>from what I can tell you want to get a hybrid inverter, it handles grid disconnections (as far as I am aware but I haven't completely confirmed this yet, you may need an additional piece of equipment) and can supply power immediately when the grid goes down<br /><br />Something like this https://www.victronenergy.com/inverters-chargers/multiplus-12v-24v-48v-800va-3kva </blockquote><br />Thanks, that looks like exactly the kind of thing. Apart from the cost I suppose the problem will be what happens if the power cut occurs whilst the kettle is on or we're cooking dinner, or in the middle of the night when the heating is on. I guess I would have to buy a bunch more smart control gear to immediately switch those off when there was a power cut.]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284383#Comment_284383</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284383#Comment_284383</guid>
		<pubDate>Thu, 05 Nov 2020 13:09:37 +0000</pubDate>
		<author>revor</author>
		<description>
			<![CDATA[From what I can make out there are very few hybrid inverters that handles auto grid disconnects. The Tessla system as mentioned has the box called gateway that handles the switch over this is covered in one of the fully charged you tube videos. But this takes a few seconds despite its expense. I think if it was immediate they would have done it. The difference between a UPS and a battery I guess is that an UPS e.g.that powers the computer the UPS does not feed into the grid at 230 volts it powers the equipment it is protecting.<br /><br /><a href="https://www.youtube.com/watch?v=gP51JjnWvLo&list=PLzD0K2OhbVfEaxtwOfUmiDE17pf__Ialo&index=7&t=80s" target="_self" rel="nofollow">https://www.youtube.com/watch?v=gP51JjnWvLo&list=PLzD0K2OhbVfEaxtwOfUmiDE17pf__Ialo&index=7&t=80s</a><br /> <br />One of the popular hybrid inverters Solax and its accompanying battery does not switch over automatically it can be configured so that you have a manual switch which disconnects you from the grid and over to the battery. It seems the hybrid systems are geared up to help you manage usage and store your excess solar production and store cheap night energy but needs a feed from the grid. The Delios is the only one I have found so far that will switch over automatically but that is not to say there are others. I have the same issue as DJH get a power dip  have to go round resetting clocks very frustrating on ovens that have cost Â£1000 which are in themselves programmable. It might be worth exploring the Powervault3 as in their brochure they use the term UPS. Available next January. The only way, certainly currently to avoid dips and disruption to  supply, is go off grid.]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284398#Comment_284398</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=284398#Comment_284398</guid>
		<pubDate>Thu, 05 Nov 2020 19:38:41 +0000</pubDate>
		<author>WillInAberdeen</author>
		<description>
			<![CDATA[UPS 'hats' are available for RPi]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=289001#Comment_289001</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=289001#Comment_289001</guid>
		<pubDate>Wed, 21 Apr 2021 08:26:05 +0100</pubDate>
		<author>RobinB</author>
		<description>
			<![CDATA[Somewhat tempted by the Powervaul home batteries so I thought I'd ask for the wisdom of the crowd.  Price list in Revor's link above. Looks like one version recycles car batteries. I wonder if there is any chance of them paying back in the lifetime. Any thoughts?]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=289007#Comment_289007</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=289007#Comment_289007</guid>
		<pubDate>Wed, 21 Apr 2021 12:38:36 +0100</pubDate>
		<author>revor</author>
		<description>
			<![CDATA[I now have my system installed all wired up which I did myself but waiting for electrician to connect me to the grid so I can have an MCS certificate but 4 attempts to get him here have failed so might revert to doing it myself and forego MCS. I would need to sell on 7000 Kwh to get the MCS fee back so not very cost effective. Anyway the battery I ended up with is a 10 kw BMZ made in Germany from cells from Korea it is extremely well engineered. It seems the way to look at the cost benefit of a battery is over its  life time expressed as the cost per unit of electricity . Mine is predicted to be 12p / Kwh so basically you are buying in advance at this rate. The company who supplied it in the UK is Ace-On  they are battery specialists and I have had excellent support from them in sharing their knowledge to a newbie like me. It is coupled to a Delios inverter which has all the gubbins to manage the battery and also do an auto changeover to battery in event of grid power cut after 30 seconds.<br /><br /><a href="https://www.aceongroup.com/energy-storage/battery-energy-storage/why-choose-bmz-ess/" target="_self" rel="nofollow">https://www.aceongroup.com/energy-storage/battery-energy-storage/why-choose-bmz-ess/</a><br /><br />A battery might be cheap but if not properly engineered and manged by the management system and the inverter you won't get the life out of it.]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=289012#Comment_289012</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=289012#Comment_289012</guid>
		<pubDate>Wed, 21 Apr 2021 18:33:35 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: revor</cite>an auto changeover to battery in event of grid power cut after 30 seconds</blockquote><br />I'm not sure I understand that. You mean the power has to go down for thirty seconds and then the battery brings it back? I'm not sure I see the point of that since everything will still reboot then surely? What happens when the mains comes back?]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=289015#Comment_289015</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=289015#Comment_289015</guid>
		<pubDate>Wed, 21 Apr 2021 22:14:46 +0100</pubDate>
		<author>philedge</author>
		<description>
			<![CDATA[I think the auto changeover switches the house system between grid connected and off grid modes. If you didnt do that you have a battery powered inverter trying to push 240vac down the grid and power the neighbours as well as trying to shock any linesmen working on the grid! Same principle as a grid connected PV inverter has to shut down when it looses the grid connection.]]>
		</description>
	</item>
	<item>
		<title>Price of solar storage batteries</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=289016#Comment_289016</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=16775&amp;Focus=289016#Comment_289016</guid>
		<pubDate>Wed, 21 Apr 2021 22:46:47 +0100</pubDate>
		<author>WillInAberdeen</author>
		<description>
			<![CDATA[Think the delay is something to do with forcing all the loads to shutdown and motors to run down to a stop, so that when the inverter starts in off-grid mode, it doesn't have to synchronise. If there was an interruption of mains supply, and then the inverter quickly started up but was not synchronised with the spinning loads or potentially any other inverters in the house, then could be damaging/dangerous.  Would imagine it does the same when reconnecting to the grid, there's some stuff in G83 about it. <br /><br />The grid usually comes back on within a few seconds, so no point switching to off-grid mode until you are sure that the grid is going to be down for a while.<br /><br />Shhh, not a sparky....<br /><br />Robin, I suspect the answer to your question is 'no'... The peak price period on a smart meter tariff is now only a few hours eg 4-7pm. Mornings and early afternoons are off-peak. Unless for some reason you must use a vast amount of power between 4-7pm, won't be worth buying a battery to store up power for that short period.<br /><br /> You can effectively 'store' off-peak power for free, by shifting your usage to when power is cheap, eg EV charging or immersion heaters etc.]]>
		</description>
	</item>
	
		</channel>