Posted By: Jeff BI have a 400 litre vented thermal store with 3 coils – upper coil for C/H, middle coil input from wood pellet boiler, and lower coil, input from solar thermal. (The middle coil may be partially contained within the upper coil – I’m not sure).
The C/H system works well enough but the heat transfer is not brilliant i.e. whilst the input from the boiler is approx 72C, the flow to the radiators is approx 48C at best. I suspect the surface area of the coil is just not man enough.
Hence I am considering a suitable PHE, set up as per attached sketch. (The upper coil is labelled spare coil, which it will be if we install a PHE). I realise this set up will probably destroy the stratification within the TS but might that not be a bad thing in that the entire store will be at a uniform temperature?
Any comments welcome.
PHE schematic.pdf
Posted By: revorWhat is the potential output of the boiler?
Posted By: Jeff B(4.1kW is the minimum setting; the rated max output is 25kW)
Posted By: revorhow much distance is there between the 2
Posted By: Jeff Bthe distance (about 12 metres)
Posted By: dereke@JeffB excuse me if I am being daft - but if you are struggling to get enough heat out of the rads at 50C wouldn't you be best off replacing them higher output rads? This might also put you in a better place for switching to a heatpump when your pellet boiler reaches end of life.
Posted By: Peter_in_HungaryJeff B - you said that the CH was direct from the TS but was changed to indirect to solve air problems in the CH. Would a cheaper option be to investigate the reasons for the air problems and then revert to CH direct from the TS? (or put a AAV in the CH where the air accumulates).
I have found in the past where there is an expansion tank on top of the main tank with little pipe distance between the 2 tanks that air has been drawn into the main tank pipe work via the connection between the 2 tanks. The solution has been to put a loop of pipe in to the expansion pipe, down to the bottom of the main tank then back to the expansion tank giving a longer column of water between the 2 tanks which has solved the problem.
Posted By: revor@jeffb. Looks like your pipework is man enough although never been a fan of microbore. Have you tried
A. Speeding up the CH circ pump.
B. Isolating as many of the rads that you can so you are feeding fewer rads to see what happens.
Posted By: revorThe pump I am referring to is the pump that circulates the water through the rads loops. A certain volume of water at a given temperature will contain a certain quantity of heat increase that volume at the same temperature will take more heat to the rads and therefore heat up quicker that is off course if your boiler and coil can keep up and deliver that heat to the system. What can happen in this situation is the level of noise increases as the velocity of water increases. There are tables available (in the book I have mentioned) that give recommendation as to pipe size to deliver the quantity of heat needed and avoiding noise due to friction of the water in the pipe.
Just another thought do you have a bleed valve on your the entry to your TS boiler coil. Could be an air lock.
Posted By: GreenPaddyI'm at a loss as to what the thermal store is doing for you? It's not even acting as a buffer, if the boiler is running all day.
What is the most efficient point of operation of the boiler? I suspect it is not at the 4kW output, and also not at 75oC.
Can you tell us the type of pellet boiler, as I'd be surprised if it is not condensing?
I think you're asking the wrong question, as regards using a PHX. Clarify the logic of your system (to yourself if no one else), and then go about simplifying the system to make it work. Taking into account your previous posts on here, I sense your frustration, but I suspect that's as a result of having a system that doesn't quite make sense, and so are forever trying to patch symptoms rather than resolving the cause. If I'm wrong, my badhttp:///newforum/extensions/Vanillacons/smilies/standard/shamed.gif" alt="
" title="
" >
I've designed loads of systems with thermal stores plus log boilers, pellet boilers, GSHP, oil and gas inputs, and most combinations there of, and almost always open vented, but I just don't quite get what your system is doing. Heating a TS continuously, but only achieving 50oC in the thermal store, and drawing off half way up for CH only. Eh??