Posted By: philedgeHaving a pipe stat on the flow pipe that inhibits the pump when the boiler is cold, is Dunsleys recommended way of wiring things. Unless youve got problems with excess soot in the fire or flue then I woulnt worry about minimum stove temperatures, so long as the stat setting is correct!
Posted By: GreenPaddyP
Anyway, that's by the by. Ben your diagram is very helpful. All heat inputs and outputs are from the main body of TS water, so no issues with undersized coils. There is the issue with crud being able to get to all parts of the system, and choking flow rates. Your gas boiler at 30kW could charge your store from cold in about 30 mins. With full CH demand (16kW I think you said) it would take the boiler an hour.
So the heat is neither getting from the gas boiler to the TS, nor from the TS to the rads. That's either because the gas boiler is being told not to run, or because the flow rate is insufficient. Big coincidence that the flow rate could be insufficient in both the boiler AND CH circuits (ignoring the stove for the moment as it's less predictable). The only common link between gas boiler and the CH circuits should be the shared water (and any bits floating in it). You have all the right bits and pieces, they just are not being allowed to do their job.
Posted By: GreenPaddyIf you can hold the pipe, it's not much above 50oC.
Posted By: Pile-o-StoneWe have a thermal store and its temperature plummets when the central heating is turned on, due to the hot water being pushed into the rads and pipework and the cold water coming from them. The thermal store heats up a bit once the radiators get hot, but the water is always losing heat (that's what radiators are for), so we never get a hot TS.
We also have an issue with the radiators not getting hot enough. Our plumber thinks we need a larger gas boiler as the house is quite large and over 3 levels. We have about 16 radiators and a 350l thermal store to heat and the boiler maybe isn't up to the job.
Posted By: Pile-o-StoneWe have a thermal store and its temperature plummets when the central heating is turned on, due to the hot water being pushed into the rads and pipework and the cold water coming from them. The thermal store heats up a bit once the radiators get hot, but the water is always losing heat (that's what radiators are for), so we never get a hot TS.
We also have an issue with the radiators not getting hot enough. Our plumber thinks we need a larger gas boiler as the house is quite large and over 3 levels. We have about 16 radiators and a 350l thermal store to heat and the boiler maybe isn't up to the job.
Posted By: Benm85Can’t really understand why flow temp would drop like that
Posted By: Benm85Definite issue with the boiler. The 65c temp on the boiler flow reading earlier (no CH on) then dropped to 58c when the CH had been on about 45 mins.
Posted By: Benm85You can audibly hear the click when you turn the dial of the thermostat to get a rough reading on tank temp, so it's working.
Posted By: Benm85So the the flow from the boiler (at the boiler) was reading 65c. The flow from the boiler at the tank was also measure 65c. This is pretty odd as it is set to 85c. Don't think it coincidence that it struggles to get beyond 60c if it's only getting 65c from the boiler. Oddly, the boiler is knocking off as it gets to 65c, like it thinks the tank set to that temp. But the control stat is at 75c on the TS.
Posted By: Benm85Definite issue with the boiler. The 65c temp on the boiler flow reading earlier (no CH on) then dropped to 58c when the CH had been on about 45 mins.
Posted By: GreenPaddyPhiledge - when linked to a thermal store, unless you blend stove flow into the return, you will always be drawing cool water from the base of the TS, until the whole TS starts to get hot to the base, which for a 350 litre store like Ben's could take hours, all the while drawing the cool water into the stove. It may be recommended by some people, but as I said, it's not a way of controlling the temperature of feed water to the stove. That is something that is not good practice.
Also, as the stove starts to cool, having heated the TS to a temp above the fixed pump stat temp, there's a chance you could have a continuous run of the pump, as it pumps hot water from the TS, through the stove to the stat, self perpetuating. Also not clever.
Posted By: Benm85
I’ll take a look at a wiring diagram later when the kids are in bed.
Posted By: Peter_in_HungaryI think that you need to get a thermometer that gives an accurate reading of the pipes.
Posted By: Peter_in_HungaryIs the boiler CH controlled by the internal boiler thermostat or the thermostat on the TS,it seems you are mentioning two thermostats, one at 75 and the other at 85.
I would also expect an over temp. thermostat on the boiler to cut it off if the temp. is too high - this is also a potential fault point cutting the boiler out at 65deg. regardless of the set temp.
Whilst the diagram of the TS is helpful it could be misleading. Your TS (having had a quick look online) has the optional extra of a coil for the boiler, do you know if this has been fitted?
Posted By: Peter_in_HungaryIf there was a blockage in the boiler to TS pipework I would expect to see the boiler temp. at the set temp, but the return at TS return temp.. I would also expect to see the boiler short cycling.
Posted By: philedgen the photo you posted there are 5 pipes showing in the cupboard next to the boiler which I assume are hooked up to the boiler. Could you update the pipework schematic to show where these are connected to save guessing. The stove pump also seems to be missing!
Posted By: Benm85Apologies, I should have been clearer on where the temps are set. The TS control thermostat is set at 75c. The boiler on it's control panel (i.e. on the front of the boiler) is set at 85c.
Posted By: Benm85When I was at the boiler, I noticed it does turn on and off, even though the TS is not at the 75c set on the control thermostat. Not sure if that is called short cycling, just an observation.
Posted By: Peter_in_HungarySo what does the 75c TS thermostat control and what does the 85c boiler thermostat control
Posted By: Peter_in_HungaryI would suggest one of those is turning the boiler off at 65deg.
I presume you are also having problems with the hot water not being hot enough
Edit to ask - Where abouts on the TS is the thermostat located?
Posted By: GreenPaddy- has the gas boiler been set to "Heat Only" in the service set up parameters. One would assume it has been, but worth checking that (section 10.3 Parameters in the installation manual). Check the other settings whilst your about it, to see they are as per the manual.
Posted By: GreenPaddy- so why is the boiler shutting off at 65oC? You've described the TS stat appears to be functioning, and knocking off the gas boiler. The stat "shows" 75oC, but is that really 75oC. As a very simple test, turn the the TS which controls the boiler up as far as it will go. That should ensure the gas boiler continues running for longer. If that's the case, then the stat may be incorrectly set (maybe someone put the knob on the wrong position. Maybe it has an internal "off-set" that has been set incorrectly). That can be sorted. First is to confirm is that stat is really what is switching the boiler off/on.
- when you do get your thermometer, you can perhaps verify the temps you think you're seeing. Then we need to be clear about where the temp stats are positioned on the TS. That will clearly affect the temp values in the TS.
Posted By: philedgeBefore you make any changes to the boiler config/settings I suggest you isolate the boiler from the TS controls to prove that the boiler is working properly, or not!
Posted By: BenMThe stat is located on the tank approximately in the middle (half way up and in the centre).
Posted By: philedgeIf youd happily fit a new doorbell, this is no different. Take a photo before you start. Switch the power off as a general safety precaution, not because the terminal are dangerous as the manual says they are only at 24volts.