Posted By: Mike1The Passivhaus Institute provide a database of independently tested units at https://database.passivehouse.com/en/components/list/ventilation_small - and personally I'd choose one of those.
Posted By: Artiglioeven more to look into
Posted By: Simon StillThere's really not much in these units - I'm guessing they're all basically the same construction
Looking at the materials they're staggeringly expensive (the Senintal is about £1k)
Posted By: WillInAberdeenit seems like the market is charging whatever the market will bear to pay
Posted By: jms452Nuaire have sub 1k units with a metal box and up to 95% efficiency.
Posted By: djh- I didn't spot anything that says how the frost protection works, which makes my cynical mind suspect it's not a separate pre-heater as required by PHI, nor reflected in test results I think, so that's another thing to considerThe installation manual says:
5.6 Frost ProtectionI.e., overwhelm any frost by blasting it with greater quantities of extract air so sucking more air in through any other leakage in the house.
In the event of the intake air temperature at the unit dropping below the predetermined set point (-5°C as standard) the supply fan will reduce to minimum speed, once the temperature rises above the set point the fan will return to its commissioned speed.
Posted By: djh- I would definitely recommend getting the AB models (auto summer bypass) that's very useful.Depends where you live.
Posted By: Ed DaviesI.e., overwhelm any frost by blasting it with greater quantities of extract air so sucking more air in through any other leakage in the house.
Depends where you live.Maximum outside air temperature here last year was 21°C.
Posted By: djhA few thoughts on those models:
- I would definitely recommend getting the AB models (auto summer bypass) that's very useful.
- before buying I would check that it's possible to fit better than G3 filters. G3 is very basic. We use G3 on the exhaust just to protet the heat exchanger from house dust. We use a G4 and a G3 on the intake - the G3 catches large crap such as carne flies in season and the G4 filters smaller crap a bit. Both fit in the slot together. Pollen filters are about the same thickness as a G4 if you need/want to use those.
Posted By: WillInAberdeenBit left field, but could you reduce the humidity locally in the cupboard, by making a tiny hole in the duct that carries warmed fresh outdoor air from the mhrv to the house. This dry air will leak into the cupboard and surround the cold duct, which is at or above the dewpoint of the outdoors air. Eventually the dry air will leak out of the cupboard into the room, where it will help with the ventilation and then be recycled back to the mhrv
Posted By: bhommelsWell worth the extra power consumption and a recalibration of the flow rates that fitting finer filters requires. To protect the F7 from clogging up with coarse crud I left the G3 filter in place as it also protects the defroster.
Posted By: djhThe plant room where the MVHR is situated is normally plumbed with an extract terminal rather than a supply terminal, FWIW
Posted By: djhAlso cross-posted. Also replying to Simon.http:///newforum/extensions/Vanillacons/smilies/standard/bigsmile.gif" alt="
" title="
" >
https://www.roofingsuperstore.co.uk/product/ubbink-150mm-insulated-duct-2m.html" rel="nofollow" >https://www.roofingsuperstore.co.uk/product/ubbink-150mm-insulated-duct-2m.htmland associated products are good and easy to use. They may be flexible enough to get in place by bending/stretching etc, or you could cut a length at an angle so you could fit both ends in place and then rejoin the angled cut with some glue and duct tape. We secured the connection to the MVHR inlets with very large jubilee clips. Cable ties would probably work as well.
Posted By: WillInAberdeenPosted By: djhThe plant room where the MVHR is situated is normally plumbed with an extract terminal rather than a supply terminal, FWIW
Yes, that's the problem here. It's drawing in more-humid air from the house, with a dewpoint greater than the outdoors temperature, so it inevitably condenses on the duct. Simon needs to surround the duct with air that has a dewpoint no greater than the outdoors temperature
=> supply some warmed dry outdoors air to that location.