Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    •  
      CommentAuthordjh
    • CommentTimeNov 3rd 2021
     
    Posted By: GarethCSay I installed a top notch A++ rated air conditioning multi split system, thereby reducing my heating related emissions significantly. Am I right that, due to the (almost certainly unused) ability to cool, I wouldn't even get an uplift to my home's EPC?

    Why do you think that?
    • CommentAuthorGarethC
    • CommentTimeNov 3rd 2021
     
    Well basically I don't know how SAP (RdSAP?) works and how it would treat air conditioning as the main heating system. i.e. what it would do to my EPC. Any idea how I would go about finding out? Sorry being as clear as mud.
    • CommentAuthorowlman
    • CommentTimeNov 3rd 2021
     
    In my own home I installed an A/A ducted system in a large open plan area, ( I had the available space in the loft above), so it made sense to go the extra mile. I accept that not everyone does, but the various wall units are so efficient and some with filtration the A/A option is an excellent choice.
    The guts of the systems are simple robust technology with fast response and excellent controls. As for cooling, I've had mine installed for 3 years and it's the best form of CH I've experienced. During that time I've probably run the cooling facility on about 5 or 6 occasions and then only for a few hours, the cooling is TOO efficient to have it on longer. and on the days it's been on, my solar PV has more than powered it.
    • CommentAuthorSimonD
    • CommentTimeNov 3rd 2021
     
    Posted By: owlmanIn my own home I installed an A/A ducted system in a large open plan area, ( I had the available space in the loft above), so it made sense to go the extra mile. I accept that not everyone does, but the various wall units are so efficient and some with filtration the A/A option is an excellent choice.
    The guts of the systems are simple robust technology with fast response and excellent controls. As for cooling, I've had mine installed for 3 years and it's the best form of CH I've experienced. During that time I've probably run the cooling facility on about 5 or 6 occasions and then only for a few hours, the cooling is TOO efficient to have it on longer. and on the days it's been on, my solar PV has more than powered it.


    Good to hear your experience here. How do the ducted systems compare to the multi-split units? I've been looking at multi-split systems but once I start to add the necessary number of indoor units, it starts to get expensive.
    • CommentAuthorGarethC
    • CommentTimeNov 3rd 2021
     
    Posted By: owlmanIn my own home I installed an A/A ducted system in a large open plan area, ( I had the available space in the loft above), so it made sense to go the extra mile. I accept that not everyone does, but the various wall units are so efficient and some with filtration the A/A option is an excellent choice.
    The guts of the systems are simple robust technology with fast response and excellent controls. As for cooling, I've had mine installed for 3 years and it's the best form of CH I've experienced. During that time I've probably run the cooling facility on about 5 or 6 occasions and then only for a few hours, the cooling is TOO efficient to have it on longer. and on the days it's been on, my solar PV has more than powered it.


    Do you know the answer to my question about how it affects a home's EPC? I've trawled online but drawn a blank.
    • CommentAuthorowlman
    • CommentTimeNov 3rd 2021
     
    Hi Simon,
    All in all I spent roughly £5K- £6K for the finished job, I've lost track. However, I ended up with high quality components throughout, I didn't skimp on anything.
    I did all the legwork and system design myself. I did all the duct install and the outside unit base preparation and wiring.
    I laboured for the "F" Gas engineer, and together we fitted the refrigerant pipework runs. He tested and commissioned the job and I then did all the duct insulation and making good, so a lot of personal input, but I knew the end result was right.
    Most installers I guess would have used flexi helical ducting, I chose rigid steel and I designed and had specially made, input and outlet plenums for the indoor unit. Flexi would have saved me a lot of time but there is, reputedly, some performance drop off. I also had my own designed ceiling registers made with replaceable filtration on the return grilles, all complete with connecting plenums.

    As for multi splits I'm about to embark on fitting a couple at the other end of the house. I'm not concerned at all about whether their performance will be OK I'm confident it will be.
    A close friend has a ground-floor Mitsi. three split he's had installed for 8 years and shamefacedly admitted the other week he's never had it serviced, still works fine, and also He's never used it for cooling, but swears by it for heating.
    There are many types of indoor units available as you probably know and though there can be some downside with siting overall the whole fit is relatively easy and upheaval free with most of the refrigerant runs able to be done outside or in the roof void.
    • CommentAuthorowlman
    • CommentTimeNov 4th 2021 edited
     
    Hi Gareth,
    Sorry I've no idea as my EPC was done before I fitted the A/A system I described. My guess would be that no one has thought about it. If your question pertains to the Summer cooling mode of A/A in my case I'd argue that any cooling is powered by my solar PV and should therefore not considered detrimental.
  1.  
    Gareth,
    EPCs are based on your SAP rating, currently the 2012 version of SAP which says

    "9.2.7 Heat pumps
    Heat pump data may be obtained from:
    a) The Product Characteristics Database;
    b) Table 4a of this document.


    "The preferred source of data for heat pumps is the Product Characteristics Database... The data also provide the secondary heating fraction based on the heat pump
    output power and the design heat loss of the dwelling, and take account of any proportion of domestic water
    heating provided by an electric immersion.

    "If a heat pump is not included in the database the appropriate seasonal performance factor (SPF) (given in
    Table 4a), is used "


    Table 4a gives a default SPF of 1.7 for air-air and air-water heatpumps

    So assuming that an air-conditioning model is not included in the SAP database of heat pumps, then it will be assigned a fairly rubbish default value for SPF= 1.7, and will not look very good on the EPC. However if that model is in the database, its SPF will probably be pretty good.


    If there is an air conditioning function, SAP calculates the cooling load based on thermal gains into the house, and uses the SEER ratings to calculate the extra electricity that is used for cooling, which will be set against the EPC.

    Edit: Power generated from PV is calculated separately, and boosts the EPC rating, disproportionately so in the current version of SAP. This anomaly will be removed in the next version, so expect fewer token PV panels will be used to bump up EPCs.
  2.  
    Just to add that SAP and EPCs are based on calculated heating costs in £, not on energy used/saved.

    In SAP 2012 the standard prices per kWh are: 13.19p for electricity and 3.48p for mains gas.

    If your heatpump is in the database and is installed with a SPF greater than (13.19/3.48 *0.9) = SPF= 3.4 , then it will improve your EPC rating. Otherwise it will make it worse.

    For replacing oil boilers (5.44p) or LPG (7.60p) the breakeven SPF is more reasonable, SPF=2.1 or SPF=1.6 respectively.

    I suspect that most people who switch from mains gas to ASHP will be disappointed, because it doesn't improve their EPC. If people use heatpumps that are not in the database and so are assigned a default SPF=1.7, their EPC will get much worse.

    This is a big problem for the private and social rented sector where the landlord has to reach a certain EPC before they can let the property.

    The Scottish gov are apparently thinking about revising the EPC system to reward energy or carbon savings, instead of rewarding cost savings. Will mean redoing everyone's EPC.

    Edit to add: the upcoming next version of SAP10 will have different prices, mains gas users would need to get a heatpump over SPF=4.0 to get a better EPC out of it. Good luck with that...!
    •  
      CommentAuthordjh
    • CommentTimeNov 5th 2021 edited
     
    Posted By: WillInAberdeenIf your heatpump is in the database

    I looked at the database and could see only one air-air HP, from a maker I've never heard of before. So either the database is woefully incomplete, or more likely I don't know how to use it. :devil:
  3.  
    Posted By: GarethCtowering absurdity of current policy.
    In fact, come to think of it, it's even worse

    Yes!

    Some A-W heatpumps are available with cooling, and also as similar models with the cooling disabled, I think with a software setting, possibly as a way round the RHI restrictions.

    I'm guessing that air-conditioning manufacturers haven't seen any commercial reason why to register their products in databases.


    There's a workaround which is: install a coal fired central heating system, declared as your main heating, and use A-A as your 'secondary' system. Coal scores really highly for EPCs, it's very cheap :cry:
    • CommentAuthorGarethC
    • CommentTimeNov 5th 2021
     
    All seems utterly bananas.

    I've been invited to the "Scotland's Race to Zero" COP 26 conference on Thursday 11th in Glasgow. I might actually scour the invite list and see if I can collar a policymaker or two on this issue.

    Basically, if they recognised the impact on space heating emissions of installing high efficiency A/A heatpumps, they at a stroke introduce a relatively affordable, -relatively- low disruption means of lowering space heating emissions by probably at least as much as A/W heat pumps (taking into account potential use for cooling), so what on earth is not to like?

    Might be able to leverage the Scottish Government's constant desire to get one over Westminster in the discussion. I'll report back if I have any success (not highly likely I'll admit).
    • CommentAuthorphiledge
    • CommentTimeNov 5th 2021
     
    Posted By: GarethC
    Basically, if they recognised the impact on space heating emissions of installing high efficiency A/A heatpumps, they at a stroke introduce a relatively affordable, -relatively- low disruption means of lowering space heating emissions by probably at least as much as A/W heat pumps (taking into account potential use for cooling), so what on earth is not to like?


    Maybe Im missing something but as a boiler replacement option, A2A HPs seem a potentially expensive and disruptive option!! As I understand things youve got a choice of a central unit with ducting or individual units per room.

    With a ducted system retrofitting ducting means floors up/ceilings down and structural alterations to floor joists where ducts have to pass through them. It maybe possible to work round the occupants but likely they would have to move out while the ducting goes in. .

    For individual room heaters theres likely a need for a unit per room or maybe some adjacent rooms can share a unit?? Even so a typical 3 bed house would likely need 5/6 units each needing an isolator/cable installing.

    For both systems DHW with point of use heaters cables/isolators need running to all points of use and these could be quite substantial loads for bath/shower heaters. Once the system is in, the redundant boiler, DHW cylinder, pipework, radiators all need stripping out, making good and redecorating.

    Assuming Ive understood A2A options correctly, it seems to me that an A2W system is a better fit for retrofit boiler replacements???
    • CommentAuthorowlman
    • CommentTimeNov 5th 2021
     
    It seems to me Will that there is no one technology fits all, every home is different, as is every occupant with their individual needs and their ability to pay.
    Excluding a simple robust option from the mix citing a few gallons of DHW as the driver seems daft.

    In the case of new builds not cluttering walls with an outdated radiator space heating delivery system is an accepted rationale, hence UFH.
    A modern warm air delivery system in those particular circumstances too offers benefits of combining it with MVHR and an automatic built in cooling mode. Both these modes are delivered in double quick time which wet systems can't even begin to compete with. Less running time, equals less energy used, which over longer period of time tips the long term COP performance even further towards A/A.
    IMO, rigidly coupling space heating and DHW is a bit like the the old endowment mortgages, an unholy mix of investment and borrowing, not serving either in the best way. It just seems a over complex way of heating up a relatively small amount of potable hot water.
    •  
      CommentAuthordjh
    • CommentTimeNov 5th 2021
     
    Posted By: philedge
    Posted By: GarethC
    Basically, if they recognised the impact on space heating emissions of installing high efficiency A/A heatpumps, they at a stroke introduce a relatively affordable, -relatively- low disruption means of lowering space heating emissions by probably at least as much as A/W heat pumps (taking into account potential use for cooling), so what on earth is not to like?


    Maybe Im missing something but as a boiler replacement option, A2A HPs seem a potentially expensive and disruptive option!! As I understand things youve got a choice of a central unit with ducting or individual units per room.

    I think you're missing something.

    With a ducted system retrofitting ducting means floors up/ceilings down and structural alterations to floor joists where ducts have to pass through them. It maybe possible to work round the occupants but likely they would have to move out while the ducting goes in.

    Possibly, but for suitable properties I imagine ducts could be led without the need for cutting joists. In lofts, with drops to the ground floor where necessary, maybe? Multiple indoor units to serve separate ducts perhaps? Or install as part of a refit. But it would suit some circumstances, I think.

    For individual room heaters theres likely a need for a unit per room or maybe some adjacent rooms can share a unit?? Even so a typical 3 bed house would likely need 5/6 units each needing an isolator/cable installing.

    I'd think those estimates are the upper limits. But anyway, running a cable, and don't forget the F-gas pipes, isn't the end of the world. A lot of the world has done this for years to install A/C units, so it's not that difficult.

    For both systems DHW with point of use heaters cables/isolators need running to all points of use and these could be quite substantial loads for bath/shower heaters. Once the system is in, the redundant boiler, DHW cylinder, pipework, radiators all need stripping out, making good and redecorating.

    No, if there is already a DHW cylinder then the obvious thing to do is not strip it out but use its immersion (or fit one) to produce the DHW. And fitting a new DHW cylinder is an obvious alternative to using point-of-use heaters. Yes the boiler and radiators will want removing at some point, though not as a matter of urgency, so undoubtedly it's easier to install a completely new heating system as part of a general refit. But upgrading insulation, airtightness and ventilation also involves disruption; there's nothing unique here.

    Assuming Ive understood A2A options correctly, it seems to me that an A2W system is a better fit for retrofit boiler replacements???

    I agree that it's just as easy to fit an A/W system in place of a boiler, so perhaps Gareth did overstate the case a bit, but A/A systems are still noticeably cheaper than A/W systems for some reason, despite being more capable in some regards, in that they can do cooling.
  4.  
    I think multi split A-A are a good alternative option for retrofits. Especially for houses without existing UFH. It's surprising that we only seem to hear about A-W.

    When I looked into them, I couldn't find one that could connect to the ten indoor units that we'd need for our house (4beds, 2 living, 2 bath, kitchen, stairs). Each outdoor unit seemed to support at most about 5 or 6 indoor units. So to buy and install 2 outdoor units and 10 indoor units, it was looking more expensive than retrofitting A-W, even before the exclusion from RHI. On the plus side, multiple outdoor units on different sides of the building, would help keep the pipe runs simpler/cheaper, and the better SCoP than with HT A-W would save some running costs.

    We are also a bit uncertain about fan noise from the indoor units in bedrooms.

    A ducted system would address those issues, but our heat load is a bit much to distribute that way without retrofitting very large ducts.

    Its a good principle to separate DHW from CH, but direct immersion heating is a bit pricey and less efficient, I'd still be looking for some kind of dedicated A-W heat pump for that.

    Others people might have different circumstances so A-A could work well, shame it doesn't get the same govt support as A-W.
    • CommentAuthorEd Davies
    • CommentTimeNov 6th 2021
     
    A disadvantage of multiple outdoor units would be that they wouldn't be covered by permitted development rights which only allow one heat pump.
  5.  
    Scottish PD legislation Class 6H specifically allows only one air source heat pump, which must only be for heating, IE if it has a cooling function then it's not PD.

    I can't work out if Class 2B allows zero, one or many air conditioning units.

    I think Gareth said something about utterly bananas.
  6.  
    If multi split A-A heat pumps are installed can any existing pipework from legacy radiator CH systems be used or would it be a rip out of all the old pipes and install new?

    If A-A heat pumps are used for cooling will the pipes need to be insulated to prevent condensation forming on them? If so I presume most would find this a aesthetic problem unless boxed in.
  7.  
    New pipes, like microbore plumbing, but with thicker walls and flared connections and insulation of OD perhaps 20-30mm. There's also a comms/power cable, and if it's used for cooling there will be a condensate drain pipe. All run behind linings, or in fat trunking if run on the surface.

    Edit AIUI the refrigerant pipes cannot just tee off to different indoor units - instead each indoor units is connected radially from the outdoor unit, or possibly from a manifold unit, so piping will get congested near there.
  8.  
    Posted By: WillInAberdeenNew pipes, like microbore plumbing, but with thicker walls and flared connections and insulation of OD perhaps 20-30mm. There's also a comms/power cable, and if it's used for cooling there will be a condensate drain pipe. All run behind linings, or in fat trunking if run on the surface.

    Edit AIUI the refrigerant pipes cannot just tee off to different indoor units - instead each indoor units is connected radially from the outdoor unit, or possibly from a manifold unit, so piping will get congested near there.

    All of the above would IMO amount to a disincentive to install A-A heat pump if you have an existing radiator based CH system that could take a high(ish) temp. heat pump with little changes to the CH system.
    • CommentAuthorowlman
    • CommentTimeNov 8th 2021 edited
     
    WillInAberdeen 1 day ago edited quote
    New pipes, like microbore plumbing, but with thicker walls and flared connections and insulation of OD perhaps 20-30mm. There's also a comms/power cable, and if it's used for cooling there will be a condensate drain pipe. All run behind linings, or in fat trunking if run on the surface.

    Edit AIUI the refrigerant pipes cannot just tee off to different indoor units - instead each indoor units is connected radially from the outdoor unit, or possibly from a manifold unit, so piping will get congested near there.


    The micro and smallbore pipes used for refrigerant are more often than not swaged and brazed, or connected using power compression/crimp type fittings. The ability to withstand the high test pressures that "F" gas engineers subject the pipework to before filling is critical with refrigerant.
    The location of indoor units and hence outdoor unit is critical also IMO. If possible it's best done on outside walls to keep pipe and cable runs simple. It's possible for them to be sited on interior walls but probably best done so that connecting services can be done between joists rather that crossing joists if using ceiling or high wall units.
    •  
      CommentAuthordjh
    • CommentTimeNov 8th 2021
     
    Interesting point I just read. If you convert a gas boiler to hydrogen, you'll need to replace all the radiators with larger ones, just like for a heat pump. The reason is that a hydrogen boiler produces water vapour and that needs to be condensed, just as it is in a gas boiler, in order to achieve high efficiencies. And since the energy density of hydrogen is less, efficiency is important. Unfortunately, to condense all the water vapour you'll need to reduce the flue temperature and hence the radiator temperature. Oops!
  9.  
    Posted By: djhInteresting point I just read. If you convert a gas boiler to hydrogen, you'll need to replace all the radiators with larger ones, just like for a heat pump. The reason is that a hydrogen boiler produces water vapour and that needs to be condensed, just as it is in a gas boiler, in order to achieve high efficiencies. And since the energy density of hydrogen is less, efficiency is important. Unfortunately, to condense all the water vapour you'll need to reduce the flue temperature and hence the radiator temperature. Oops!

    So perhaps the only advantage of a hydrogen boiler is the price difference between a hydrogen boiler (about the same as a conventional gas boiler) and a heat pump. And heat pump is available now - if the grid can cope with wholesale installation of heat pumps.
    •  
      CommentAuthordjh
    • CommentTimeNov 8th 2021
     
    Posted By: Peter_in_HungaryAnd heat pump is available now - if the grid can cope with wholesale installation of heat pumps.

    Certainly more likely than that the gas grid can supply sufficient truly green hydrogen to sufficient hydrogen boilers now. :devil: :bigsmile: :cry:
    • CommentAuthorgravelld
    • CommentTimeNov 8th 2021
     
    That's interesting!
  10.  
    The same is actually true of condensing natural gas boilers: they condense more effectively if they run cooler (eg 45⁰C), so really need bigger radiators than non condensing boilers do, and ideally UFH. However most were retrofitted in place of a previous non condensing boiler, so the legacy radiators are often not big enough. Also, many are oversized to provide instant DHW, so they run a few hours a day at high power / high temperature, instead of more hours at lower temperatures, which would require weather compensation controls and better modulation. So in trials, most were found to be running far less efficiently than their manufacturers' claimed.

    If this could be fixed easily, it would save ~10% of natural gas consumption, which coincidentally is more than the energy content of the proposal to blend 20% by volume of hydrogen into the gas mains.

    In a hydrogen boiler, nearly all of the combustion oxygen goes into making water vapour, versus a natural gas boiler where half the oxygen makes CO2 and only half makes water. So the hydrogen boiler exhaust should contain more water, so condense more easily and have a higher dewpoint than a gas boiler's exhaust - it can run hotter and still condense. They may be doing inefficient things to suppress NOx which might require lower temperatures.

    Personally I think it would be a brave politician who approves hydrogen in the gas mains, as energy bills will have to go up as a result and the opponents will point this out. Hydrogen is inevitably going to be more expensive than the natural gas or electricity which are the starting ingredients for making it, so people will find it cheaper to use electric heating, in some form or another.
    •  
      CommentAuthordjh
    • CommentTimeNov 9th 2021
     
    Posted By: WillInAberdeenIn a hydrogen boiler, nearly all of the combustion oxygen goes into making water vapour, versus a natural gas boiler where half the oxygen makes CO2 and only half makes water. So the hydrogen boiler exhaust should contain more water, so condense more easily and have a higher dewpoint than a gas boiler's exhaust

    I think the higher dewpoint is a bit misleading. It's true that water will begin to condense earlier but if you want to condense nearly all the water then it's the temperature after most of the water has condensed that is going to matter.

    Also, as you mention, it's likely hydrogen boilers will run well below a stoichiometric ratio for various reasons including NOx suppression as you say. I was somewhat stupid in not recording the source of the claim I found, which I can't now find again :cry: :shamed:

    Personally I think it would be a brave politician who approves hydrogen in the gas mains, as energy bills will have to go up as a result and the opponents will point this out. Hydrogen is inevitably going to be more expensive than the natural gas or electricity which are the starting ingredients for making it, so people will find it cheaper to use electric heating, in some form or another.

    I fully agree. I don't understand why the whole notion seems to have so much traction at present. It's like all the manufacturers have their heads stuck in the sand, although some do make heat pumps and fuel cells as well, so I guess they're just covering all bases to minimise risk from their point of view. Pity doing so costs the planet.
    • CommentAuthorRobL
    • CommentTimeNov 9th 2021
     
    <blockquote><cite>Posted By: djh</cite>I don't understand why the whole notion seems to have so much traction at present</blockquote>

    It represents business as usual for gas extraction and distribution companies, also for boiler manufacturers. It's something that I'm sure they are all lobbying for, and would dearly wish to happen. It's something the public would dearly love to be plausible; replace the gas boiler with something about the same that is "green" and just works with minimal fuss. Everybody is on board wanting it to work!

    I think though that where the hydrogen comes from is key to whether the result of all of the above would be greenwashing (CCS of Nat gas given expected methane emissions) or inefficient poor engineering hence expensive (electrolysis of water using renewable electricity) - neither approach seems to make long term sense to me, and will eventually be seen to be a blind alley, effectively another climate delay tactic.
    • CommentAuthorLF
    • CommentTimeNov 9th 2021
     
    Is hydrogen in a house not bonkers ? Much more flammable than gas, leaks more and inlet gas pipe will need to be made bigger (in my case) again to pass same kWs of energy (3 times volume)
   