			<title>Green Building Forum - EPS and PVC cables</title>
			<lastBuildDate>Sat, 02 May 2026 11:54:58 +0100</lastBuildDate>
			<link>https://www.greenbuildingforum.co.uk/newforum/</link>
			<description></description>
			<generator>Lussumo Vanilla 1.0.3</generator>
			<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294888#Comment_294888</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294888#Comment_294888</guid>
		<pubDate>Sat, 19 Feb 2022 20:49:03 +0000</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[When PVC cables come into contact with expanded  polystyrene a physical reaction does take place. This is NOT a chemical reaction. What happens is that some of the plasticiser in the PVC migrates (technically  probably diffuses) into the polystyrene which makes it appear to have been attacked. In the process if a gap forms the process stops. <br /><br />There is no evidence that this is dangerous as only a small portion of the plasticiser is lost and only from the outer sheath of the cable. The polystyrene is thinned a tad. <br /><br />Is anyone aware of a resulting problem?]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294889#Comment_294889</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294889#Comment_294889</guid>
		<pubDate>Sat, 19 Feb 2022 22:09:39 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Thanks tony - reality check!]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294890#Comment_294890</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294890#Comment_294890</guid>
		<pubDate>Sat, 19 Feb 2022 22:42:40 +0000</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[Two degrees in Chemistry help]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294894#Comment_294894</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294894#Comment_294894</guid>
		<pubDate>Sun, 20 Feb 2022 01:48:48 +0000</pubDate>
		<author>Mike1</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: tony</cite>Is anyone aware of a resulting problem?</blockquote><br />I seem to recall that the plasticisers used were changed years ago (70s?) to reduce the problem.<br /><br /><blockquote ><cite >Posted By: tony</cite>In the process if a gap forms the process stops.</blockquote><br />...however if the cable was loose-laid on polystyrene - in a loft, for example - the cable may move as the polystyrene shrinks back. Or if the polystyrene becomes sticky, as it might, it could stick to the cable. Either could prevent the process stopping, in theory.<br /><br />It would be interesting to see if anyone has any real-world fire reports though.]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294896#Comment_294896</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294896#Comment_294896</guid>
		<pubDate>Sun, 20 Feb 2022 08:07:12 +0000</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[I have been searching for such reports for years and never found any. Were there any I would expect them to be sufficiently publicised for us to know about them therefore surmise that there arenâ€™t any]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294899#Comment_294899</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294899#Comment_294899</guid>
		<pubDate>Sun, 20 Feb 2022 08:17:55 +0000</pubDate>
		<author>Nick Parsons</author>
		<description>
			<![CDATA[I have found many examples of EPS and XPS sticking to cables (or vice versa!) but the most surprising one was when we were working in an apex roof void and there were several sheets of 600 x 2400 x 50 XPS, presumably the result of good intentions to insulate sloping soffits, never enacted. We needed them out. I moved a couple then picked up another. It lifted about 200mm and then stopped. Couldn't work it out for a minute until I realised it was glued to 2 cables, very firmly. We had to prise it off, mm at a time. The PVC sheathing was 'shiny' but not, apparently, brittle.]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294907#Comment_294907</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294907#Comment_294907</guid>
		<pubDate>Sun, 20 Feb 2022 10:35:27 +0000</pubDate>
		<author>bhommels</author>
		<description>
			<![CDATA[Hearing about this effect I have installed a soak test in my shed: a 200x200x200mm block of graphite EPS with a cable threaded through multiple times. The cable sits very snugly in the holes.<br /><br />4 years on (and counting),the cable is still fine. I can take it out, it is not sticky and I can bend it around without evidence of any cracking of the outer sheath.<br /><br />I am definitely not denying that the effect plays a role. As Tony says, it is likely driven by diffusion and that is strongly temperature dependent. My shed is shaded and does not get very hot in summer, it gets humid in winter, and is probably not the ideal site for accelerated tests, the timescales could be very long.<br /><br />I have installed conduits around all (but two!) cables in contact with EPS as I think it is good practice in any case. Better be safe than sorry.<br /><br />One bit of additional information that could be related: when trying to get my leftover graphite EPS recycled, one plant refused to take it on the grounds that it was produced before a certain year, and thus might contain a compound of which I forgot the abbreviation. If this compound has a high diffusion constant for common cable plasticizer it could be responsible for the effect. Then, it might not :-)]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294937#Comment_294937</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294937#Comment_294937</guid>
		<pubDate>Mon, 21 Feb 2022 12:58:38 +0000</pubDate>
		<author>owlman</author>
		<description>
			<![CDATA[Could EMF intensify the effect?]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294938#Comment_294938</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294938#Comment_294938</guid>
		<pubDate>Mon, 21 Feb 2022 13:20:34 +0000</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[No]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294939#Comment_294939</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294939#Comment_294939</guid>
		<pubDate>Mon, 21 Feb 2022 14:34:37 +0000</pubDate>
		<author>owlman</author>
		<description>
			<![CDATA[Here is an interesting summary, the precaution checklist page 2 is worth a read.<br /><br /><br /><a href="https://www.buildmagazine.org.nz/assets/PDF/BUILD65-26-ElecCableInPoly.pdf" target="_self" rel="nofollow">https://www.buildmagazine.org.nz/assets/PDF/BUILD65-26-ElecCableInPoly.pdf</a>]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294940#Comment_294940</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294940#Comment_294940</guid>
		<pubDate>Mon, 21 Feb 2022 16:57:49 +0000</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[Thanks for that Owlman, they say that samples take from cables in real buildings show minimal loss of plasticiser, so comforting to see.<br /><br />The last point about cable sizing may be the most important.]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294941#Comment_294941</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294941#Comment_294941</guid>
		<pubDate>Mon, 21 Feb 2022 17:20:05 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[Agree it's a useful article. I'm not sure about one point though; it says:<br /><br />  3. Donâ€™t use EPS beads: Loose-fill EPS beads<br />  (â€˜beansâ€™) must not be used as insulation since these<br />  could potentially maintain permanent contact with<br />  the cable (since gravity would keep moving new<br />  beads into contact with the cabling).<br /><br />That seems a bit over-protective. Firstly in many installations the beads are coated with glue so even when loosed-filled they won't move about afterwards. Secondly even if they can move they won't achieve anything near to close contact over the whole surface of the cable since there is in theory just a single point of contact between each bead and the cable. So I'd expect a lot less trouble than in many other circumstances.]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294942#Comment_294942</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=294942#Comment_294942</guid>
		<pubDate>Mon, 21 Feb 2022 18:10:04 +0000</pubDate>
		<author>revor</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: tony</cite>The last point about cable sizing may be the most important.</blockquote><br /><br />BS 7671 17th edition 523.9 state that cables should not be installed in situations where they are possibly covered in insulation. If there is a situation where it unavoidable up to 500 mm is allowed for which there is a sliding scale  derating factor for the cable depending on the length surrounded from 50 mm to 400 mm.  500mm and above of  cable in insulation the cable is derated by 0.5 i.e. only allowed to carry half the current of that cable when clipped in the open.<br />So bottom line don't cover with insulation.<br />I can find no reference in there for EPS specifically.]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=295065#Comment_295065</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=295065#Comment_295065</guid>
		<pubDate>Fri, 04 Mar 2022 07:31:16 +0000</pubDate>
		<author>TimSmall</author>
		<description>
			<![CDATA[Might be worth asking on the IET wiring regs forum for this, there have been a few discussions of it there in the past I think.]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299752#Comment_299752</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299752#Comment_299752</guid>
		<pubDate>Thu, 19 Jan 2023 18:56:57 +0000</pubDate>
		<author>wookey</author>
		<description>
			<![CDATA[Interesting thread. I had assumed that eventually the PVC got brittle (probably took decades), but the info here suggests probably not. Is there an equilibrium between the cable sheath and the EPS or will all the plasticiser move eventually, if they stay in contact?]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299754#Comment_299754</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299754#Comment_299754</guid>
		<pubDate>Thu, 19 Jan 2023 19:48:57 +0000</pubDate>
		<author>Jeff B</author>
		<description>
			<![CDATA[What about the situation when IWI is applied onto a plastered wall and the electrical cable is buried in the cement render behind the plaster? Does that have an effect on the current carrying capacity of the cable?]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299755#Comment_299755</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299755#Comment_299755</guid>
		<pubDate>Thu, 19 Jan 2023 20:03:15 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: wookey</cite>Interesting thread. I had assumed that eventually the PVC got brittle (probably took decades), but the info here suggests probably not.</blockquote>Dunno. I do remember seeing old rubber-insulated mains cables in a cellar that had become so brittle that pieces just flaked off with very little provocation. But PVC is different, I think. I mean UPVC windows aren't especially brittle are they?]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299756#Comment_299756</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299756#Comment_299756</guid>
		<pubDate>Thu, 19 Jan 2023 20:04:43 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Jeff B</cite>What about the situation when IWI is applied onto a plastered wall and the electrical cable is buried in the cement render behind the plaster? Does that have an effect on the current carrying capacity of the cable?</blockquote>Not particularly, because plaster and cement are reasonably good conductors of heat. Plus the cables are often covered with a metal protective strip that's an even better conductor.]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299760#Comment_299760</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299760#Comment_299760</guid>
		<pubDate>Thu, 19 Jan 2023 21:42:25 +0000</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[There was talk from the regulators about the need to derate cables in that situation when cavity wall insulation was introduced. A long time ago and clearly not necessary.]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299761#Comment_299761</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299761#Comment_299761</guid>
		<pubDate>Thu, 19 Jan 2023 22:37:04 +0000</pubDate>
		<author>Jeff B</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: djh</cite><blockquote ><cite >Posted By: Jeff B</cite>What about the situation when IWI is applied onto a plastered wall and the electrical cable is buried in the cement render behind the plaster? Does that have an effect on the current carrying capacity of the cable?</blockquote>Not particularly, because plaster and cement are reasonably good conductors of heat. Plus the cables are often covered with a metal protective strip that's an even better conductor.</blockquote><br /><br />That's my feeling too. I think applying IWI should make the wall cooler which would enhance conduction of heat away from the cables.]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299786#Comment_299786</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299786#Comment_299786</guid>
		<pubDate>Fri, 20 Jan 2023 21:12:16 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Jeff B</cite>That's my feeling too. I think applying IWI should make the wall cooler which would enhance conduction of heat away from the cables.</blockquote>It will actually reduce the conduction, because it increases the average insulation value, but it would start from a lower base (as long as there's no CWI or EWI as well) so sums would have to be done.]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299794#Comment_299794</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299794#Comment_299794</guid>
		<pubDate>Sat, 21 Jan 2023 13:26:17 +0000</pubDate>
		<author>bhommels</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: wookey</cite>Interesting thread. I had assumed that eventually the PVC got brittle (probably took decades), but the info here suggests probably not. Is there an equilibrium between the cable sheath and the EPS or will all the plasticiser move eventually, if they stay in contact?</blockquote><br />Assuming it is diffusion driving the process, 'all' the plasticiser will move into the EPS.]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299802#Comment_299802</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299802#Comment_299802</guid>
		<pubDate>Sat, 21 Jan 2023 22:07:37 +0000</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[No, as the plasticiser moves into the eps it dissolves it and the eps shrinks away from the pvc <br /><br />EPS has so little mass that it canâ€™t absorb all the plasticiser in the pvc. <br /><br />If there was a problem we would know about it by now, eps and pvc cables have been in close proximity for 40 years or more, touching and no reported incidents.]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299806#Comment_299806</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299806#Comment_299806</guid>
		<pubDate>Sun, 22 Jan 2023 15:14:42 +0000</pubDate>
		<author>Mike1</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: tony</cite> eps and pvc cables have been in close proximity for 40 years or more, touching</blockquote>It would be interesting to know to what extent that's the case. I've seen odd examples from retrofit cavity wall insulation but, at least for UK new-build housing under the NHBC, EPS & PVC cables are banned from coming into contact, and it's such a commonly known and warned-about 'issue' that it's probably infrequently done elsewhere.<br /><br />However from what I've read, with modern cables the risk seems to be more theoretical than real, and is probably confined to unrestrained cables that are subject to movement.]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299807#Comment_299807</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299807#Comment_299807</guid>
		<pubDate>Sun, 22 Jan 2023 15:45:58 +0000</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[I agree about new houses not being a big problem but eps is widely used for renovations and in the commercial sector which is where I have seen most of the problems that I have observed.]]>
		</description>
	</item>
	<item>
		<title>EPS and PVC cables</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299808#Comment_299808</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17397&amp;Focus=299808#Comment_299808</guid>
		<pubDate>Sun, 22 Jan 2023 16:54:42 +0000</pubDate>
		<author>revor</author>
		<description>
			<![CDATA[Many years ago I went on a stand at a show where the use of ICF was being talked about. They had as an example an electrical cable in a chased out trench in the polystyrene, that was a no no. Not only from the perceived issue of the contact between the cable and causing a reaction but the fact that also one should only run cable within insulation within allowed parameters or uprated cables. Many watching the presentation could have gone away and thought it was allowed practice. BS 7671 regulation 522.5.3 applies. In NICEIC publication Snags and Solutions Part 2 it is specifically referred to. It states that the plasticiser migrates and the cable cover become sticky and soft and eventually becomes hard and brittle. The process is accelerated by heat e.g warming of the cable through passage of current and insulation preventing cooling. Although not stated I expect the deterioration in the cable would result in its electrical insulation properties being compromised.]]>
		</description>
	</item>
	