<?xml version="1.0" encoding="utf-8"?>
	<rss version="2.0">
		<channel>
			<title>Green Building Forum - external insulation</title>
			<lastBuildDate>Sat, 18 Jul 2026 01:16:53 +0100</lastBuildDate>
			<link>https://www.greenbuildingforum.co.uk/newforum/</link>
			<description></description>
			<generator>Lussumo Vanilla 1.0.3</generator>
			<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295090#Comment_295090</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295090#Comment_295090</guid>
		<pubDate>Sat, 05 Mar 2022 20:47:49 +0000</pubDate>
		<author>chrisinbrighton</author>
		<description>
			<![CDATA[Im just starting to plan the renovation of a Welsh chapel,i can imagine il`l have lots of questions on here!<br /><br />The walls are all 700mm thick stone and one of these walls is covered in slate with a 50mm gap. I was thinking this would be a good place to add insulation.Is there a particular type which would be best and does a vertical slate wall need a breathable membrane?<br />Thanks.]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295094#Comment_295094</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295094#Comment_295094</guid>
		<pubDate>Sat, 05 Mar 2022 22:35:58 +0000</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[Ideally you need a lot more than 50mm of insulation 300mm or 200mm, where would the breather membrane go? Behind the slates? But they are draughty and let water out by design]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295097#Comment_295097</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295097#Comment_295097</guid>
		<pubDate>Sun, 06 Mar 2022 07:14:25 +0000</pubDate>
		<author>Peter_in_Hungary</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: chrisinbrighton</cite>Im just starting to plan the renovation of a Welsh chapel,i can imagine il`l have lots of questions on here!</blockquote><br />What do you mean by 'renovation'<br />Or are we to assume renovation = conversion to a dwelling?<br />Are you governed by planning restrictions concerning the external appearance (or anything other aspect)?]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295098#Comment_295098</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295098#Comment_295098</guid>
		<pubDate>Sun, 06 Mar 2022 10:05:47 +0000</pubDate>
		<author>chrisinbrighton</author>
		<description>
			<![CDATA[Yes conversion to dwelling but listed so slates have to stay(I would want to keep them anyway)<br /><br />Will 50mm of cellotex be hardly any benefit?]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295100#Comment_295100</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295100#Comment_295100</guid>
		<pubDate>Sun, 06 Mar 2022 10:49:47 +0000</pubDate>
		<author>Jonti</author>
		<description>
			<![CDATA[Can you not remove the slates to put on a decent thickness and then replace the slates? Listed doesn't always mean you cannot touch it.]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295102#Comment_295102</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295102#Comment_295102</guid>
		<pubDate>Sun, 06 Mar 2022 11:40:00 +0000</pubDate>
		<author>Nick Parsons</author>
		<description>
			<![CDATA[+1 to Jonti. Worth a discussion with your BCO/Conservation Officer. Also, although it has been done before with Celotex I would be tempted, even if using a plastic insulant, to use graphite EPS. Also since, as I understand, Celotex does not do a non-foil board (and you don't need foil for a VCL as it's the wrong place for a VCL), have you thought of phenolic? This is available non-foiled for EWI.<br /><br />Also, while 50mm is too little, as others state, if you use exg battens it's 50mm insulation with full-depth timber interruptions every however many mm. If you *had* to stick with 50 could you perhaps do 25 ins against the wall, battens, then 25 between, then slate.<br /><br />Agree with Tony re membrane. It wouldn't do any *harm* but you almost certainly don't need it.<br /><br />Edit to add Conservation Officer]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295103#Comment_295103</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295103#Comment_295103</guid>
		<pubDate>Sun, 06 Mar 2022 14:10:27 +0000</pubDate>
		<author>Peter_in_Hungary</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: chrisinbrighton</cite>Yes conversion to dwelling but listed so slates have to stay(I would want to keep them anyway)<br /><br />Will 50mm of cellotex be hardly any benefit?</blockquote><br />Putting 50mm rigid insulation between the wall and slates will (approximately) change the u value from 2.02 to 0.45 so it would have a reasonable effect. (I assumed a sand stone wall, other types of stone will have different values)<br /><br />However if that is the only wall you can do and especially if the slates are in a reasonable condition, I would leave that wall alone and concentrate in the internal surfaces. <br /><br />If you externally insulate on that wall only and internally insulate the rest you will get problems at the juncture of the internal and external insulation (corners) that would make it advisable to internally insulate a good bit of the externally insulated wall to mitigate the cold bridge at the corners so best to just treat the internal insulation as a whole and forget about insulating the outside.<br /><br />One approach that has been made by at least one other here is to build an insulated box inside the walls of the existing structure as opposed to internally insulating the existing walls. Each solution has its own problems and advantages.<br /><br />If you want to play the 'what ifs' with various types of insulation and needs for VCLs against what you have to start with then look at<br />https://www.ubakus.de/u-wert-rechner/?<br />Use the demo version]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295107#Comment_295107</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295107#Comment_295107</guid>
		<pubDate>Sun, 06 Mar 2022 17:03:38 +0000</pubDate>
		<author>chrisinbrighton</author>
		<description>
			<![CDATA[Thanks for the replies,very useful.<br />The slates have got to come off anyway so it will be a good time to add insulation.I like the idea of doing a two layer unfoiled design(Nick Parsons) and will try and push for more than 50mm.<br />At present I cant see that the other stone (slate possibly) walls can easily be internally insulated.]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295111#Comment_295111</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295111#Comment_295111</guid>
		<pubDate>Sun, 06 Mar 2022 18:30:38 +0000</pubDate>
		<author>chrisinbrighton</author>
		<description>
			<![CDATA[pic attached]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295117#Comment_295117</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295117#Comment_295117</guid>
		<pubDate>Sun, 06 Mar 2022 19:06:38 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Oo - so would the EWI behind slates wrap around that return, so standing out from the side wall stonework? Might be hard for Listed Buildings to swallow; on the other hand it would go a long way to creating the overlap between EWI and IWI that Peter mentions.<br /><br />There's a quite modest limit to how insulative IWI can safely be, before it leaves the wall outboard of it so cold all winter through, like it's never before been, that so much winter condensation builds up within it, that it never quite evaporates in summer, leading to gradual accumulation of water in the masonry. EWI has no such problem, thicker the better, as that keeps the wall warmer than it's ever been!<br /><br />If wanting to IWI up beyond that danger level, that's where Peter's 'insulated box inside the walls' comes in, which must be coupled, strangely, with really free ventilation to outside air of the airspace between wall and box, so the wall becomes effectively a freestanding garden wall, at which it should have no problem. However I doubt you'll be trying to insulate by IWI up to that danger level.]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295179#Comment_295179</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295179#Comment_295179</guid>
		<pubDate>Tue, 08 Mar 2022 18:06:02 +0000</pubDate>
		<author>chrisinbrighton</author>
		<description>
			<![CDATA[Doesn`t external wall insulation need to be breathable.Im assuming warm dampness will work its way through the thick stone walls.<br /> ...and EPS or phenolic are not breathable I understand ?]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295182#Comment_295182</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295182#Comment_295182</guid>
		<pubDate>Tue, 08 Mar 2022 20:15:31 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: chrisinbrighton</cite>Doesn`t external wall insulation need to be breathable.Im assuming warm dampness will work its way through the thick stone walls.</blockquote>Not necessarily. As long as the EWI is thick enough that the temperature on its inner face is above the dewpoint for whatever humidity you have inside the house then there'll be no condensation on the inner surface so no problem. The problems can come with IWI, because it's cold outer face is against the stone (or other) wall surface, so condensation is much more likely.<br /><br /><blockquote >...and EPS or phenolic are not breathable I understand ?</blockquote><br />EPS is breathable to some extent or at least not impermeable to moisture. Âµ is 20-40 for EPS 70. Phenolic is a lot more vapour resistant, as is XPS]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295297#Comment_295297</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295297#Comment_295297</guid>
		<pubDate>Sat, 12 Mar 2022 07:29:36 +0000</pubDate>
		<author>Beau</author>
		<description>
			<![CDATA[I am no pro but I insulated two outside walls of my dad's farmhouse behind slate cladding. I used 3"x2" verticals (on edge) at 600mm spacing. Used injection resin studs to secure them to the 600mm thick stone walls. 60mm PU board between the studs and filled all gaps with PU foam from a gun. Then a layer of Tyvec, battens then slate. This was around 10 years ago and no problems we are aware of.<br /><br />In hindsight, it would have been nice to stop the thermal bridge of the uprights to the wall but it's way better than it was. The house used to get condensation on the inside of walls but this now never happens]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295324#Comment_295324</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=295324#Comment_295324</guid>
		<pubDate>Sun, 13 Mar 2022 22:36:47 +0000</pubDate>
		<author>chrisinbrighton</author>
		<description>
			<![CDATA[Thanks for replies,all my questions have been answered..ill let you know how it goes.]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=310283#Comment_310283</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=310283#Comment_310283</guid>
		<pubDate>Mon, 23 Feb 2026 21:20:04 +0000</pubDate>
		<author>chrisinbrighton</author>
		<description>
			<![CDATA[Im at the stage of actually starting this insulation/Slating job now .<br />One thing im not sure about is the 700mm thick granite  stone wall is very uneven so will there be a `large` air gap(mabe averarage 15mm) between rigid insulation and stone...will this air gap blow away the warmth from the building?<br />Could it be better to use Rockwool  that can squash up against the rough stone?]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=310289#Comment_310289</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=310289#Comment_310289</guid>
		<pubDate>Tue, 24 Feb 2026 15:35:37 +0000</pubDate>
		<author>Peter_in_Hungary</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: chrisinbrighton</cite>One thing im not sure about is the 700mm thick granite  stone wall is very uneven so will there be a `large` air gap(mabe averarage 15mm) between rigid insulation and stone...will this air gap blow away the warmth from the building?</blockquote><br />IMO yes.If there is any air flow in the gap between the insulation and the wall then heat will be removed which will affect the effectiveness of the EWI.<br /><br />What I do when installing EWI is to use standard EPS 80 grade batts at whatever thickness meets your target U value which I attach to the wall with a band of adhesive on all 4 sides (at the edge) and then 5 dollops in the centre. This I press firmly on to the wall until the adhesive squeezes out at the visible sides and to match the height of the adjacent batts, any adhesive squeezed beyond the visible edges I scrape off to mane the next batt easier to butt up. In this way there is no path for air to wick away heat.<br /><br />I don't bother to try to get the walls to be straight and plumb but rather I follow any contours the wall may have. No one expects a 200 year old stone/rubble walled building to have straight and square walls <br /><br />If you want something a bit more breathable than standard EPS Baumit do an EPS with perforations that allow better vapour diffusion than standard EPS (there may be others equally as good)<br />See https://baumit.co.uk/products/external-wall-insulation/opensystem-breathable-ewi/baumit-opentherm<br />They also do and internal render designed for such walls.<br />I have no connection with Baumit, just (so far) a happy user.<br /><br />If you are going to put slates hung on the EWI then under the horizontal battens either vertical battens or spacers will be needed to hold the horizontal battens off the EWI to allow and water to drain away <br /><br />I would put the EPS fully across the wall (rather than between studs) and then fix battens through the EPS to the wall.]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=310297#Comment_310297</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=310297#Comment_310297</guid>
		<pubDate>Wed, 25 Feb 2026 13:10:46 +0000</pubDate>
		<author>Nick Parsons</author>
		<description>
			<![CDATA[If the gap is 'only' about 15mm why not parge-coat first, then do full-bed adhesive? P-in-H's system works too, as long as you are 100% sure that the perimeter (and preferably cross-hatched)adhesive will always 'seal', meaning that any air ingress (and there shouldn't be any) is confined to the space behind one board. Agree with straight-to wall and battens on top of the EWI. Oh, and I also agree with my own suggestion made in March 2022!]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=310304#Comment_310304</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=310304#Comment_310304</guid>
		<pubDate>Wed, 25 Feb 2026 17:56:31 +0000</pubDate>
		<author>chrisinbrighton</author>
		<description>
			<![CDATA[Hi Nick, yes your `lattice` idea of insulation back in March 2022 seems very good and im thinking of using kootherm papered. People have said that i need an air gap behind the slates though ?. As an alternative to adhesive could i just add some fluffy rockwool between the back of the kooltherm and stone wall?<br />Also the vertical studs need to stay i think as they are holding alot of weight.]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=310306#Comment_310306</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=310306#Comment_310306</guid>
		<pubDate>Thu, 26 Feb 2026 08:50:54 +0000</pubDate>
		<author>GreenPaddy</author>
		<description>
			<![CDATA[Hi Chris,<br /><br />not 100% sure it's the same product, but I used the tissue faced kooltherm boards before, and it turned out they have to be kept completely dry in storage and during installation, or the tissue face peels of, making them useless. Discovered this after the supplier dropped them off in the rain at site on a Friday, so by Monday they were a soggy mess. Please double check the fine print before getting the tissue faced product, as storing pallets of boards under cover before installation might be a challenge.]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=310322#Comment_310322</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=310322#Comment_310322</guid>
		<pubDate>Sat, 28 Feb 2026 13:08:10 +0000</pubDate>
		<author>Beau</author>
		<description>
			<![CDATA[Why not just run a bead of adhesive foam around the perimeter of each piece of rigid insulation?<br /> Should stop any air movement and hold it in place]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=310354#Comment_310354</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=310354#Comment_310354</guid>
		<pubDate>Sat, 07 Mar 2026 09:30:48 +0000</pubDate>
		<author>chrisinbrighton</author>
		<description>
			<![CDATA[Green Paddy-I didnt think the paper actually did anyrhing other than give a clean surface?<br /><br />And yes a few cans of squirty foam seems obvious to glue the boards on!]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=310434#Comment_310434</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=310434#Comment_310434</guid>
		<pubDate>Tue, 31 Mar 2026 15:38:17 +0100</pubDate>
		<author>Doubting_Thomas</author>
		<description>
			<![CDATA[There's a good paper on 'thermal bypass' of insulation here: <br /><br /><a href="https://www.passivhaustrust.org.uk/UserFiles/File/Technical%20Papers/Thermal%20bypass%20risks%20v1.0%20222909.pdf" target="_self" rel="nofollow">https://www.passivhaustrust.org.uk/UserFiles/File/Technical%20Papers/Thermal%20bypass%20risks%20v1.0%20222909.pdf</a><br /><br />Some good guidance on how to deal with wind washing through gaps in insulation.]]>
		</description>
	</item>
	<item>
		<title>external insulation</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=310437#Comment_310437</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17406&amp;Focus=310437#Comment_310437</guid>
		<pubDate>Wed, 01 Apr 2026 17:37:28 +0100</pubDate>
		<author>chrisinbrighton</author>
		<description>
			<![CDATA[Very interesting re windwashing, ive certainly got gaps at least 15mm between insulation and wall face. Im wondering if polystyrene balls could be trickled down to fill this gap.]]>
		</description>