Posted By: Peter_in_HungaryRobL and bhommels Thanks for that. It would seem that the modern modulating heat pump would be running most of the time and modulating down to match the heat demand - Correct?
That being the case I will continue collecting the heat loads but in January (our coldest month) I will go to daily readings / 24 then account for the DHW and then add some for the cushion effect.
RobL - is there a reason that you heat the DHW as a dedicated run time rather than an on demand like the CH? Is this the normal way of running a heat pump when doing CH and DHW or is this particular to your system?
Posted By: tonyIn Canada they design heat pump to cover all but the coldest two weeks and top up with direct electric if needed. Additional capital cost outweighs the cost of the energy needed for the additional heating
Belt and braces approach costs too much.
Posted By: WillInAberdeenHe was able to choose a heatpump near the top of that range, but which could modulate down.Yes. An oversize HP doesn't help as it cannot modulate down to where you need.
Posted By: WillInAberdeenWhy would such a big direct electric heater (CoP=1) be helpful in a heatpump system, wouldn't it drag down the performance of the heatpump?It is a question of whether the losses from the system (holding hot water that isn't used and cools) and the lower COP of heating to a higher temperature are outweighed by the COP of One for the direct heating. In a household with highly variable DHW requirements (think teenagers), the flexibility of just heating to a lower temp using the HP, might be more efficient overall.
Posted By: WillInAberdeenusing assumed heat lossesAssumptions make an ass out of u and me and are the mother of all foul ups.
Posted By: WillInAberdeenpeople in poorly insulated stone houses are getting good CoPsOf course you can get good COP, but does it keep the house warm. Just because you get a lower COP, that doesn't mean it actually can do the job.
Posted By: WillInAberdeenAlso has some explanation on that page how he heats DHW with a CoP of 3.5 - just heating it from cold feed temperature directly up to shower temperature, rather than heating it to 60â°+ and then blending it back down with cold water.Thing is, there are lots of other factors that must be considered. Is the shower close to the HP outlet? how quickly does it heat, what do you do for other DHW, what happens when the incoming temp drops? how hot do you like your shower? What sort of HP will be fitted?
Posted By: WillInAberdeenBorpin, here is the MCS's heat loss survey, it's a very detailed room-by-room calculation and takes hours of the HP designer's time to complete it. But if you dig into the Excel, it is full of assumptions about as-built U values and air permeability and winter temperatures, which cannot be verified during the survey.
https://mcscertified.com/wp-content/uploads/2021/04/MCS-Heat-Pump-Calculator-Version-1.10-locked.xlsm" rel="nofollow" >https://mcscertified.com/wp-content/uploads/2021/04/MCS-Heat-Pump-Calculator-Version-1.10-locked.xlsm
In our case, it calculated a HP about 30-40% bigger than I wanted, based on my data of the house's heat load using the existing heating system.
Posted By: Peter_in_Hungarywith presumably monthly (?) 60 deg. boost to keep the legionella happy.Only required if you are storing the water to be used. If you supply main water to a coil in the tank that heats the water, then there is no (well, virtually zero) risk so no cycle required.
Posted By: borpinPosted By: Peter_in_Hungarywith presumably monthly (?) 60 deg. boost to keep the legionella happy.Only required if you are storing the water to be used. If you supply main water to a coil in the tank that heats the water, then there is no (well, virtually zero) risk so no cycle required.
Posted By: WillInAberdeenAgreed! But beware that data was from the older R410A era of heatpumps, the current R32/R290 machines are rather better than those were.
Posted By: Peter_in_HungaryMy DHW is an indirect tank of 300 lts (serving 2 houses) that is heated either by an immersion in the summer or by a coil from the TSIf the water stored is used, then yes, you need the legionella cycle.