<?xml version="1.0" encoding="utf-8"?>
	<rss version="2.0">
		<channel>
			<title>Green Building Forum - Gas pipe handling in screed</title>
			<lastBuildDate>Wed, 22 Apr 2026 10:36:05 +0100</lastBuildDate>
			<link>https://www.greenbuildingforum.co.uk/newforum/</link>
			<description></description>
			<generator>Lussumo Vanilla 1.0.3</generator>
			<item>
		<title>Gas pipe handling in screed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17793&amp;Focus=300921#Comment_300921</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17793&amp;Focus=300921#Comment_300921</guid>
		<pubDate>Thu, 23 Mar 2023 17:33:15 +0000</pubDate>
		<author>cc64</author>
		<description>
			<![CDATA[On another thread #15519 I have detailed the beginnings of my travails with a screed failure localised to my entrance door. I continue these here since they now involve a gas pipe and likely building regs too.<br /><br />Further to the cavity-crossing work, I removed more floor covering, uncovering cracked screed as I progressed, stopping only when the cracks did. This identified the pipe for the house gas supply as a nucleation point for screed failure. <br /><br />This is a 27mm diam pipe, crossing the entrance hall, and resting directly on the blocks of the beam and block floor. It serves a boiler and gas hob. The pipe was flanked by 25mm EPS, and also overtopped by the same, before the screed was poured/laid. The overtopping was not a good idea, reducing the (otherwise 40mm thick) screed to 18mm, and making of the pipe a fulcrum for the 500mm lever of screed to the front door - hardy surprising the screed failed over the pipe.<br /><br />Question is re;fixing this and what particular regs apply to such gas source pipes? It is sleeved through the wall. With generous ventilation gaps both within the sleeve and outside it; any reason not to reach for my Soudal AWS airtight foam to fill those gaps?<br /><br /> The flanking EPS stops 20mm short of each side of the pipe and that gap filled with very fine granular materials. This looks slightly more structured than the usual lackadaisical construction quality I'm dealing with in this house. Is this detail regs related?<br /> <br /> Likewise the overtopping with EPS - this is a shockingly bad idea in terms of its impact on screed longevity - but was it done as per some aspect of regs e.g. perhaps the pipe ought not to be encased in screed directly? <br /><br />Can anyone here point me in the right direction on these details? Is the filled flanking gap  between pipe and EPS required? And the overtopping EPS? Or am I ok directly to embed that gas pipe in the new screed without any such flanking gaps or overtopping EPS?<br /><br />I can imagine the pipe (steel) will be subject to thermal expansion/contraction - which wouldn't do much good to any screed bonded to it; is preventing that bond the objective for the flanking loose fill  gaps and the EPS overtop?<br /><br />Thanks. And happy to hear any other tips from those practiced in the art which will almost certainly come as news to me.]]>
		</description>
	</item>
	<item>
		<title>Gas pipe handling in screed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17793&amp;Focus=300923#Comment_300923</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17793&amp;Focus=300923#Comment_300923</guid>
		<pubDate>Thu, 23 Mar 2023 19:57:10 +0000</pubDate>
		<author>revor</author>
		<description>
			<![CDATA[I presume you are talking about mains gas and not LPG. We are off grid and considered a gas supply (propane) to an Island hob. Had varying advice. 1. You cannot lay pipe in floor without being in accessible duct. i.e an open duct with grid over. 2. You can only put it on an outside wall 3.You can run in a perforated yellow duct i.e.with holes in. In the end we decided on an induction hob. The point I am making is that we could not find a definitive answer but that may due to propane factor. What you describe as being your situation my instinct /common sense would say it was a very dubious way of running the pipe. It feels like an afterthought and pipe should have gone in during construction under the block and beam floor. To my mind it did not meet gas regs nor building regs. Best do some research  to solve the issue I think it would be a brave non qualified person to propose a solution.]]>
		</description>
	</item>
	<item>
		<title>Gas pipe handling in screed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17793&amp;Focus=300926#Comment_300926</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17793&amp;Focus=300926#Comment_300926</guid>
		<pubDate>Fri, 24 Mar 2023 10:27:14 +0000</pubDate>
		<author>cc64</author>
		<description>
			<![CDATA[Yes is mains gas.<br />Yes Wow that's quite a diversity of advice you received. <br /><br />This pipe routing quite possibly looks like an afterthought but if so likely to be the case also in the ~100 other houses on the estate.<br /><br />Will track down my gas-safe certified boiler installer and enquire whether that cert. qualifies him on such details]]>
		</description>
	</item>
	<item>
		<title>Gas pipe handling in screed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17793&amp;Focus=300943#Comment_300943</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17793&amp;Focus=300943#Comment_300943</guid>
		<pubDate>Fri, 24 Mar 2023 21:51:03 +0000</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[In the very old days before CORGI we use to use plastic coated copper pipe in screeds wrapping the fittings in something and using oversized ducts through walls.]]>
		</description>
	</item>
	<item>
		<title>Gas pipe handling in screed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17793&amp;Focus=300945#Comment_300945</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17793&amp;Focus=300945#Comment_300945</guid>
		<pubDate>Sat, 25 Mar 2023 07:37:17 +0000</pubDate>
		<author>cc64</author>
		<description>
			<![CDATA[From the technical advice section of GasSafe (0800 408550 #4) I learn of the contents of BS6891 as amended 2015 & 2019<br /><br />It is indeed acceptable to bury such a pipe in screed provided said pipe run is either parallel or at right angles, is suitably protected against corrosion, and is covered by screed of at least 25mm depth.<br /><br />Suitable protection against corrosion include any of factory finishes intended for that purpose, wrapping in PVC tape maintaining a 55% overlap at everyturn, bituminous paint, or densotape. Densotape themselves recommend protection of their tape with a pvc overtaping for good measure.<br /><br />For new such installations trackpipeCC is recommended.]]>
		</description>
	</item>
	<item>
		<title>Gas pipe handling in screed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17793&amp;Focus=300946#Comment_300946</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17793&amp;Focus=300946#Comment_300946</guid>
		<pubDate>Sat, 25 Mar 2023 10:17:20 +0000</pubDate>
		<author>revor</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: cc64</cite>From the technical advice section of GasSafe (0800 408550 #4) I learn of the contents of BS6891 as amended 2015 & 2019<br /><br />It is indeed acceptable to bury such a pipe in screed provided said pipe run is either parallel or at right angles, is suitably protected against corrosion, and is covered by screed of at least 25mm depth.<br /><br />Suitable protection against corrosion include any of factory finishes intended for that purpose, wrapping in PVC tape maintaining a 55% overlap at everyturn, bituminous paint, or densotape. Densotape themselves recommend protection of their tape with a pvc overtaping for good measure.<br /><br />For new such installations trackpipeCC is recommended.</blockquote><br /><br />That is very informative. Is there a requirement to indicate there is a pipe in the floor. hate to think what would be consequence of drilling into the pipe accidentally.]]>
		</description>
	</item>
	<item>
		<title>Gas pipe handling in screed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17793&amp;Focus=300954#Comment_300954</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17793&amp;Focus=300954#Comment_300954</guid>
		<pubDate>Sat, 25 Mar 2023 23:58:19 +0000</pubDate>
		<author>cc64</author>
		<description>
			<![CDATA[No such requirement was mentioned. Doesn't mean there isn't one<br /><br />I'd say that was such a no brainer that I will mark it<br />s location with suitable tape on screed surface much as I mark water pipe runs on chipboard flooring]]>
		</description>
	</item>
	<item>
		<title>Gas pipe handling in screed</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17793&amp;Focus=300962#Comment_300962</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17793&amp;Focus=300962#Comment_300962</guid>
		<pubDate>Sun, 26 Mar 2023 13:41:40 +0100</pubDate>
		<author>Artiglio</author>
		<description>
			<![CDATA[Tracpipe is a superp product and not that expensive if you have  time to keep an eye on the auction site, lots of it appears on there, finding the actual pipe is easy getting the fittings you want needs a bit more patience.]]>
		</description>
	</item>
	
		</channel>
	</rss>