Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorborpin
    • CommentTimeSep 13th 2023
     
    From The Telegraph https://www.telegraph.co.uk/news/2023/09/12/snp-gas-boiler-ban-housing-crisis-heat-pumps/

    Basically, if you ban the fitting of boilers, and force the installation of HPs and require EV Charging, the local infrastructure requires more power and the Grid cannot support it.

    They cite a development near us that the initial planning was for 8MVA but it now needs 35MVA. They can only get a 15MVA connection from the grid.
  1.  
    I smell a rat somewhere... someone hasn't checked the numbers!

    New homes built to the 2022 Scottish building standards need almost no heating, a kW or two, it wouldn't be economic to lay gas mains and fit boilers for such low heat demand. If they do have say 5kW heat pumps (over sized) then 1.5kW electricity supply each will be plenty, so 1.5 MW for every 1000 houses. Heating is not what they want 35 MW of electricity for!

    Possibly they are thinking about electric cookers (10kW per house) or car chargers (7 kW, but not everyone at once)?

    This story allows the Telegraph to bash both heat pumps and the SNP all at once, so I wouldn't expect arithmetic to stand in the way!

    Edit: and that development started building way back in 2012, it wasn't held up by some unforeseen electricity supply problem with boilers in 2024. Sounds like someone screwed up and is looking for imaginative excuses to ask for more money!
    • CommentAuthorJonti
    • CommentTimeSep 13th 2023
     
    Posted By: WillInAberdeenI smell a rat somewhere... someone hasn't checked the numbers!

    New homes built to the 2022 Scottish building standards need almost no heating, a kW or two.


    I work in the Scottish building industry almost none of the houses being built by the big house builders meet the current building standards. The theory is great however the lived reality for most new home owners is different.
  2.  
    Undoubtedly true and needs changing, but that's not a problem caused by heat pumps or fixed by gas boilers.

    And even if they used 3x or 5x more heat than the law requires, they still wouldn't need 35 MW of electricity for heating their housing development. If you put 35MW of electricity into heat pumps, you get 100 MW of heat out, enough for a whole town.
    • CommentAuthorborpin
    • CommentTimeSep 14th 2023 edited
     
    Posted By: WillInAberdeenso 1.5 MW for every 1000 houses
    I do wonder, but equally, it talks about MVA (not KWh) so this is about all of them to be on at once (total potential load). The sources seem reasonable as well.

    Where you only have an 80A supply, this can be an issue with HP & EV apparently.

    [edit]
    I have seen other news items from different sources saying certain developments cannot go ahead as there is insufficient capacity in the Grid.
  3.  
    The volume housebuilders are well known for taking any chance to protest against heatpumps, insulation, airtightness, or any rules at all (as Jonti said) - I wouldn't believe anything they say as 'reasonable sources'!

    MW is the same as MVA if we have pf=1 (which we should) - sometimes a little different for industrial sites with big induction motors. Yes indeed the actual load will be less than 1.5MW per 1000 homes, because not everyone will be running their heatpump flat out at the same moment.

    An 80A supply is 18.4 kW , which is plenty for a 7kW EV charger to run simultaneous with a 5kW heat pump (IE 1.5kW electric draw) and also a cooker, kettle, and a hundred lightbulbs and a huge TV.

    Many (most?) EV chargers now come with a current clamp that goes on your mains, so if you are getting close to 80A it will slow down charging the EV a bit. Also comes with a timer to charge the EV overnight when the other loads are off.

    Housing is often held up getting utility connections, usually drains and sometimes electric. Has always been so, is nothing to do with heatpumps in 2024, despite what the Telegraph prints!
  4.  
    Scottish Power Energy Networks design guide - discusses that not everyone will use max electricity at the same time (diversity) and so for a development of 4 bed houses they plan on:

    1.5kW per house + 2.5kW per Fast EV charger + capacity of heatpumps

    So for 1000 homes with EV chargers and small heatpumps they'll want (1.5 + 2.5 + 1.5) = 5.5 MW, of which 1.5MW for the heat pumps.

    Nowhere near the '35MW needed because of heatpumps' claimed in the paper. Presumably the 35MW is actually for the industrial and retail developments nearby.

    https://www.spenergynetworks.co.uk/userfiles/file/ESDD-02-012.pdf
    •  
      CommentAuthordjh
    • CommentTimeSep 14th 2023
     
    I believe that since 2022 all chargers sold must have the capability to delay or reduce charging when instructed by the electricity supplier. So I think their demand can be levelled easily now.

    It's conceivable that heat pumps could be required to have similar control capability, so their demand could be similarly levelled, though not at present.

    Cookers come in various types, but just considering induction hobs, ours has a c 40 A, 10 kW max demand and it would be difficult to legislate against them all being used at once. Similarly some firms (I'm looking at you Neff) produce hobs that are limited to 13 A demand but I can't imagine them being made compulsory. Running a wok would be very difficult, although I know some who do. At that sort of level we're probably back to the classic maximum load of a gazillion kettles being turned on at half time in a football match.

    That SP Networks ADMD calculation is weird. They add up various things and average them in a complicated way when what they're really doing is just totalling the demand and dividing by the number of houses. All the kerfuffle in the middle to get an 'average' is just a waste of space.

    They also use the term 'Heat Pump capacity' exactly once and don't define it. If asked, my first guess would be that meant the output capacity, but from the context I presume they mean the input electrical demand.
    • CommentAuthorphiledge
    • CommentTimeSep 14th 2023
     
    Posted By: WillInAberdeen
    1.5kW per house + 2.5kW per Fast EV charger + capacity of heatpumps

    So for 1000 homes with EV chargers and small heatpumps they'll want (1.5 + 2.5 + 1.5) = 5.5 MW, of which 1.5MW for the heat pumps.


    As I understand it not so long ago the diversified design load per house was 2.5kw, so a new diversified load of 5.5kw per house is more than doubling required grid capacity.

    Hope someone has a coherent plan for world electrification.
    • CommentAuthorborpin
    • CommentTimeSep 14th 2023 edited
     
    Posted By: WillInAberdeenSo for 1000 homes with EV chargers and small heatpumps they'll want (1.5 + 2.5 + 1.5) = 5.5 MW, of which 1.5MW for the heat pumps.


    From the item -

    The SPF raised the example of a very large housing development being built in Winchburgh, West Lothian that originally required eight megavolt-amperes (MVA) of electricity, before the gas boiler ban was announced.

    For the moment let us assume this is correct (I doubt they would try bringing false facts to a committee meeting) this is for 3,400 houses.

    So by your calculation, the old figure would be just over 5MVA (1.5 * 3,400)- allowing for infrastructure (there are 2 high schools and a primary school alone) their stated old figure of 8MVA seems reasonable.

    At 5.5KVA per house, 3,400 would come out to 18.7MVA a fair bit below their 35MVA, but still a significant increase.

    They may be enhancing their argument, but the basis, that they need a much bigger grid connection, isn't wrong and it may well be that the grid cannot supply it.
  5.  
    What about electric sowers (12kw) having a shower in winter whie someone is having a cup of tea...
    A good plumber I know said he thinks alot of houses will need threephase to spread the demand.
  6.  
    *showers
    •  
      CommentAuthordjh
    • CommentTimeSep 14th 2023
     
    Posted By: chrisinbrightonWhat about electric sowers (12kw) having a shower in winter whie someone is having a cup of tea...
    It's not the demand in an individual house that is a problem, it's the overall demand from all the houses together. The Scottish document reckons the supply to each house is 80 A (dunno why, ours is 100 A) which is approx 20 kW (or kVA if you must) so a 12 kW shower plus a 7.36 kW EV charger would be getting up to the limit. Hopefully the charger is smart enough to throttle back if somebody puts the kettle on :devil: I think most showers are 8 to 10 kW though. The 'diversity' calculation assesses the chances of people using high power at the same time in multiple houses. Evidently for car chargers they reckon people all charge overnight and charge one day in three on average (or thereabouts)
  7.  
    Seems some DNOs are standardising on 80A supplies now, and replacing existing 100A supplies with 80A. There's apparently some tolerance in the fuse to supply up to 100A for several hours (23kW), so no problems with the electric shower and cooker running at the same time.
    https://www.linkedin.com/pulse/uk-electricity-networks-need-rapidly-sort-heat-pump-standards-lowes



    Another cracking anti-heatpump story in the Telegraph today, heat pumps are all apparently a Chinese plot to control the world with Putin! Wondering if they're using AI bots to write this stuff.

    Can't find it now but was reading a while back that 'PV is a problem' (a change from blaming 'heatpumps and EV chargers'!) The story was that DNOs used to set their transformers up at 253V to overcome cable resistances during peak winter demand, so the supply would still arrive at the homes within legal tolerance of 230V±10%. But then if everyone is exporting PV, the voltage in the homes goes above 253V on a sunny day. So the transformer voltage setting has to be reduced and then cannot deal with peak winter power demand.
    • CommentAuthorArtiglio
    • CommentTimeSep 15th 2023 edited
     
    My house had a 60amp fuse when i moved in, i enquired about an upgrade , (preferably 3 phase for future proofing plus i do a bit of woodwork and have 3 phase machines), 3 phase would have cost 12k , which included 7k for traffic management on a quiet residential road ( when there was work on the gas close by recently they just shut the road for a week). The incoming existing cable was too small for 100 amps , so i ended up with a new fuse for 80amps and a rotary converter for the woodworking. The house is heated with gas, i’ll see how the wind blows for 10 years or so before thinking of a change, spent as much time effort and money as i had insulating where i could as well as was reasonably possible ( house is listed) to keep heating requirement down.
    The chap that did the change, was of the opinion that there was a push towards making 80amps the norm because so many homes already had them with supply cables that could’nt take 100 amps , that if the industry accepted 100 amp supplies as the norm in the future if the drive for electrification was successful vast numbers of homes would need upgrading of the supply cables, with the attendant costs. So from the DNO’s point of view it was better to encourage better consideration and design in homes as to the amount of electricity required.

    He also said that whilst not a massive problem , they had regular call outs to homes that were having issues, the recent addition of a car charger usuallybeing the last straw, having been installed without sufficient regard to the homes existing useage and age/condition/quality of the consumer unit ( more recent wylex boards being seen as more likely to have issues). He said the reports from such visits were collated and dissected to see how things should be guided going forward.

    But when asked what the biggest problem was he saw, “unauthorised connections ” was the swift response.
    • CommentAuthorMike1
    • CommentTimeSep 15th 2023
     
    Posted By: ArtiglioMy house had a 60amp fuse when i moved in
    That's a typical connection for an electrically heated house in France - the maximum monophase connection offered, I think. For those on gas, it's typically 30A. Around 70% of all domestic properties, including apartments, have a 30A connection.

    That's low compared to the UK for 2 reasons:
    - the power chosen determines the standing charge, so there's an incentive to keep it low (a 60A connection costs in the region of €19/month, 30A around €12.50, down to €9.25 for the minimum 15A supply)
    - a load-shedder can be fitted to the consumer unit that temporarily disconnects one or more selected low-priority loads (water heating, central heating, washing machine, etc.) if the total load approaches the maximum - for example while fully using an electric hob.

    Because France relies much more than the UK on electric heating, it has a much higher electricity demand (around 50% more) - more like the UK needs to become as it transitions away from gas. It may well be that the UK needs to consider a French style charging scheme to help moderate the grid expansion that will be required.

    Posted By: WillInAberdeenSeems some DNOs are standardising on 80A supplies now
    Posted By: Artigliothere was a push towards making 80amps the norm
    Looks like that is now National Grid policy - https://connections.nationalgrid.co.uk/news-and-events/latest-news/standardisation-of-fusing-to-80a
    •  
      CommentAuthordjh
    • CommentTimeSep 16th 2023
     
    Posted By: Mike1Looks like that is now National Grid policy - https://connections.nationalgrid.co.uk/news-and-events/latest-news/standardisation-of-fusing-to-80a
    Yes, for some DNOs at present. My DNO - UKPN - still supports 100 A and there are calls for a national standard to be agreed one way or the other. Lots of bun fights ahead :bigsmile:
    • CommentAuthorArtiglio
    • CommentTimeSep 16th 2023 edited
     
    Mike1, cheers , interesting how different places do things. The flats i converted/ built all have 60 amp supplies from a 3 phase supply that was bought into the building then split. That was 20 years ago so things may well have changed. If i am ever forced to heat these buildings with other than gas, as things things currently stand i’d be better off upgrading the insulation on the block built 20 years ago and relying on resistive heating , the other block having been built in 1870 would likely need a communal ashp and attendant distribution and ufh in the flats, but if it ever goes that way it’ll be better to turn it back into one/two larger home/s,(assuming local planning would allow it, ) as i don’t see any realistically economically viable way of getting that building away from gas. It’s not listed but in a conservation area in an area that doesn’t command the high property prices to support substantial investment into the building as it currently is.
    If it weren’t for the woodworking 60amps would probably be enough for me ( whilst heating with gas ) unless i put a car charger in , but even then if it were intelligent ( my description) I wouldn’t forsee many problems. My usual consumption is around 8kwh / day , with workshop use on top and even then an enthusiastic day of making shavings and dust might top that out at 30 or so.

    I’ve put in extra cabling to enable me to fit an electric boiler or ashp in the future ( for a brief period i bought into the notion that eventually electricity would be so plentiful as to be cheap enough to rely on resistive heating, with a woodstove supplement in cold spells, but have moved away from that occuring in my lifetime) but with the push toward 80 amp supplies , i’m guessing that any request for 100 amp supplies is going to leave the consumer liable for the upgrade costs, for which i see costs in the future will include an infrastructure charge similar to those imposed by the water companies. Which means i’m planning it all around the current going forward.
    • CommentAuthorowlman
    • CommentTimeSep 16th 2023 edited
     
    Last year I asked for my 60A supply to be upgraded to 100A.
    Request confirmed and the free upgrade went ahead including some new incoming tails.
    Fast forward 12 months and I decided to ask my electrician to install a a 100A double pole isolator in the meter cabinet. He discovered on pulling the main fuse that the fuse cartridge itself was in fact 80A although clearly labelled as 100A on the outside casing.

    P.S. The electrician said, " they do this all the time"
    • CommentAuthorArtiglio
    • CommentTimeSep 16th 2023
     
    Owlman - was that new tails from the main fuse or did your upgrade include a new cable from the “road” ?
    • CommentAuthorjms452
    • CommentTimeSep 16th 2023
     
    Really interesting thread I'm enjoying reading.

    The level of discussion/knowledge on GBF is in a different league - thanks:bigsmile:
    • CommentAuthorowlman
    • CommentTimeSep 16th 2023
     
    Posted By: ArtiglioOwlman - was that new tails from the main fuse or did your upgrade include a new cable from the “road” ?



    The supply, is from a pole on the opposite side of the road from my property, it passes under the road and into a chamber near my boundary and then under my front garden to the meter box on the house wall.
    The contractor dug a hole in the garden to locate the conduit and then split it and installed new tails back to the chamber and forward to the meter box. The total distance is about 25M, give or take. The originals were 16mm and they've been upgraded to 25mm.
    •  
      CommentAuthordjh
    • CommentTimeSep 16th 2023
     
    Posted By: owlmanThe contractor dug a hole in the garden to locate the conduit and then split it and installed new tails back to the chamber and forward to the meter box.
    That sounds strange. I wonder why they didn't just pull through a cable from one end to the other. Is the conduit bent or something?
  8.  
    Posted By: owlmanHe discovered on pulling the main fuse that the fuse cartridge itself was in fact 80A although clearly labelled as 100A on the outside casing.
    Ours is the same, I think that's normal. It means the fuse holder unit can handle up to 100A (80A fuses are the same size and are normally what's fitted). Same as with a 13A plug or FCU that can have a 5A or 3A fuse fitted, the only way to know what's inside it is for the electrician to open up and look!
    It would be nice if they put a sticker on it or something to help with planning. If you have an electrical inspection report then the fuse rating might be written on that, if it was opened.
    • CommentAuthorowlman
    • CommentTimeSep 16th 2023
     
    Posted By: djh
    Posted By: owlmanThe contractor dug a hole in the garden to locate the conduit and then split it and installed new tails back to the chamber and forward to the meter box.
    That sounds strange. I wonder why they didn't just pull through a cable from one end to the other. Is the conduit bent or something?


    Yes, and yes.