Posted By: WillInAberdeenI smell a rat somewhere... someone hasn't checked the numbers!
New homes built to the 2022 Scottish building standards need almost no heating, a kW or two.
Posted By: WillInAberdeenso 1.5 MW for every 1000 housesI do wonder, but equally, it talks about MVA (not KWh) so this is about all of them to be on at once (total potential load). The sources seem reasonable as well.
Posted By: WillInAberdeen
1.5kW per house + 2.5kW per Fast EV charger + capacity of heatpumps
So for 1000 homes with EV chargers and small heatpumps they'll want (1.5 + 2.5 + 1.5) = 5.5 MW, of which 1.5MW for the heat pumps.
Posted By: WillInAberdeenSo for 1000 homes with EV chargers and small heatpumps they'll want (1.5 + 2.5 + 1.5) = 5.5 MW, of which 1.5MW for the heat pumps.
Posted By: chrisinbrightonWhat about electric sowers (12kw) having a shower in winter whie someone is having a cup of tea...It's not the demand in an individual house that is a problem, it's the overall demand from all the houses together. The Scottish document reckons the supply to each house is 80 A (dunno why, ours is 100 A) which is approx 20 kW (or kVA if you must) so a 12 kW shower plus a 7.36 kW EV charger would be getting up to the limit. Hopefully the charger is smart enough to throttle back if somebody puts the kettle on I think most showers are 8 to 10 kW though. The 'diversity' calculation assesses the chances of people using high power at the same time in multiple houses. Evidently for car chargers they reckon people all charge overnight and charge one day in three on average (or thereabouts)
Posted By: ArtiglioMy house had a 60amp fuse when i moved inThat's a typical connection for an electrically heated house in France - the maximum monophase connection offered, I think. For those on gas, it's typically 30A. Around 70% of all domestic properties, including apartments, have a 30A connection.
Posted By: WillInAberdeenSeems some DNOs are standardising on 80A supplies now
Posted By: Artigliothere was a push towards making 80amps the normLooks like that is now National Grid policy - https://connections.nationalgrid.co.uk/news-and-events/latest-news/standardisation-of-fusing-to-80a
Posted By: Mike1Looks like that is now National Grid policy - https://connections.nationalgrid.co.uk/news-and-events/latest-news/standardisation-of-fusing-to-80aYes, for some DNOs at present. My DNO - UKPN - still supports 100 A and there are calls for a national standard to be agreed one way or the other. Lots of bun fights ahead
Posted By: ArtiglioOwlman - was that new tails from the main fuse or did your upgrade include a new cable from the “road” ?
Posted By: owlmanThe contractor dug a hole in the garden to locate the conduit and then split it and installed new tails back to the chamber and forward to the meter box.That sounds strange. I wonder why they didn't just pull through a cable from one end to the other. Is the conduit bent or something?
Posted By: owlmanHe discovered on pulling the main fuse that the fuse cartridge itself was in fact 80A although clearly labelled as 100A on the outside casing.Ours is the same, I think that's normal. It means the fuse holder unit can handle up to 100A (80A fuses are the same size and are normally what's fitted). Same as with a 13A plug or FCU that can have a 5A or 3A fuse fitted, the only way to know what's inside it is for the electrician to open up and look!
Posted By: djhPosted By: owlmanThe contractor dug a hole in the garden to locate the conduit and then split it and installed new tails back to the chamber and forward to the meter box.That sounds strange. I wonder why they didn't just pull through a cable from one end to the other. Is the conduit bent or something?