Posted By: Dominic CooneyCould this be it, or similar from the same company?Could well be. Well spotted!
https://www.stoveitaly.com/en/portfolio-articoli/fiamma/
Posted By: djhPosted By: Dominic CooneyCould this be it, or similar from the same company?Could well be. Well spotted!
https://www.stoveitaly.com/en/portfolio-articoli/fiamma/
Posted By: LouiseSJPPThe stove (Fiamma 14CS, 15kW, of which 10kW to water)
Posted By: LouiseSJPPThe buffer tank is meant to buffer between log loadings only, I'm not looking for heating when the stove is not running. The 100 litre tank is already there. If it proves inadequate, it could be dualled-up.
Posted By: LouiseSJPPMy worry is how often it may need loading.
Posted By: LouiseSJPPGravity would be failure-proof, I guess, but will be effective in shifting the 10kW??
Posted By: LouiseSJPPit does expect uncontrolled heat source plumbing expertiseThat seems like a sensible prerequisite for installing an uncontrolled heat source. If you don't have it, then engage somebody who does would be my suggestion.
Posted By: Peter_in_Hungary
The buffer tank will give some heat between loading but not too much, however when you reload the stove then you will need time and energy from the stove to reheat the buffer before you get useful heat out into the rads, so IMO if the stove more or less matches the rads then all the buffer will do is shift (delay) the time when the radiator temps drop. (If the stove is oversized for the rads then careful use will be needed to avoid boiling the system as the 100 ltr tank isn't big enough to manage the full output of the stove for more than a short time).
//
If you have a gravity system then it is self regulating so when the heat from the stove drops the circulation slows and the reverse when the stove increases in temp. so a laddomat is not needed and you tend to get (lower) heat to the rads for longer.
//
I have run a 20kW stove and a 40 kW boiler on gravity without problems - the key is getting the design and pipe sizes right. Todays plumbers don't like gravity systems because attention needs to be paid to both the design and the installation for it to work properly. With a pumped system failures in design or installation can usually be overcome by turning up the pump speed.
IMO the simple system would be to install the stove on gravity system with the rads balanced to the stove output and the heat output is controlled by the amount of fuel you put onto the stove. - No tank,pumps, valves or electricity needed. //
I would strongly recommend putting in an external air feed for the stove unless you have a very leaky house with old ill fitting windows - and even then put in an external air feed because when you get fed up with the draughts and fix them then you will need one.
Did you do the calculations to show that the stove will heat the house sufficiently?
Posted By: djhPosted By: LouiseSJPPit does expect uncontrolled heat source plumbing expertiseThat seems like a sensible prerequisite for installing an uncontrolled heat source. If you don't have it, then engage somebody who does would be my suggestion.
Posted By: philedgeWe've got a 17kw WBS heating our DHW tank via an open vented gravity loop that works fine. The tank is the other side of the wall at the back of the stove so about 1.5 metres of inclined 28mm copper connecting the two. Our CH is pumped out of a second set ot tappings on the back of the stove so.no buffer or thermal store for us. Control of the CH pump is via pipe stats on the gravity flow and return. Return temp has to be above 50c for the pump to run and when the flow hits 80c the pump starts.
All works well but CH is direct from the stove rather than from a buffer so a touch different to yours. You'd need to check your input coil to the buffer an dissipate 10kw when the buffer is up to CH operating temp.