			<item>
		<title>Setting up a solar installation trial run</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303913#Comment_303913</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303913#Comment_303913</guid>
		<pubDate>Wed, 18 Oct 2023 19:52:40 +0100</pubDate>
		<author>LouiseSJPP</author>
		<description>
			<![CDATA[When we downsized to a smaller house, in northern Spain, we were full of plans for living more sustainably, without going as far as the hairshirt path. A decent solar / battery installation was central to this.<br />As it turns out, things are not that straightforward. The electricity in the state we live in, Navarra, is 100% renewable. The price is stupendously low: 4c per kw/hr. There is no home-generation buy-back: you can offset your own consumption to some extent, but no more. This means there is neither an economic case to be made for a solar installation nor an ecological one.<br />What we do have instead is a practical case. We have a 25amp mains supply, and to upgrade it would be very expensive. It's also unreliable, subject to failure in wind and rain, and sometimes for long periods, living in the wilds as we do. We remain interested in an almost offgrid installation.<br />However, we have many friends who all tell us how disappointed they are with their shiny new solar installations, falling far short of expectation. I don't want to make a big investment to be similarly disillusioned.<br />I'm wondering if there's a way to get a small installation up this winter in order to minitor performance before launching on a bigger project. The problems I see with this are the amount of kit which will either need to be bought 'full-size' in the full size in the first place, and maybe issues with measuring output in a meaningful way. Will the system have to have full load all the time in order to produce all it can, in order to measure it. How would this be done? Or can it all be modular so that putting in one panel this winter can be the start of a system which can have more panels added later? Maybe with micro-invertors, it's possible.<br />Have you any thoughts, advice or experience you can share?]]>
		</description>
	</item>
	<item>
		<title>Setting up a solar installation trial run</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303919#Comment_303919</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303919#Comment_303919</guid>
		<pubDate>Thu, 19 Oct 2023 08:11:50 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[I wonder why your friends' installations should be disappointing, unless poorly specified? Or unrealistic expectation. Perhaps, because sun power seems so 'easy' there, the local installers aren't that competent, or honest. Do you know the PVGIS website, where you can generate reliable output forecast for your location, and can optimise orientation, angle etc?]]>
		</description>
	</item>
	<item>
		<title>Setting up a solar installation trial run</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303922#Comment_303922</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303922#Comment_303922</guid>
		<pubDate>Thu, 19 Oct 2023 08:53:05 +0100</pubDate>
		<author>Peter_in_Hungary</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: LouiseSJPP</cite>This means there is neither an economic case to be made for a solar installation nor an ecological one.<br />What we do have instead is a practical case. We have a 25amp mains supply, and to upgrade it would be very expensive. It's also unreliable, subject to failure in wind and rain, and sometimes for long periods, living in the wilds as we do. We remain interested in an almost offgrid installation.</blockquote><br />As you say there is no real case for a solar installation.<br />I am assuming that the 25 A supply will suffice even if you have to schedule power hungry devices e.g. overnight charging of an EV at 16 A only etc.<br />Perhaps forget solar and think about a battery back up for your grid supply. Then you have to decide for how long you want to cover a power outage and what you want to run during that outage. Once you have a base load and time for an outage then look at battery options. Almost no break switchovers with alarms are readily available for grid back up. If you want to further insure against a long outage - depending on the expected frequency - then a generator might be a consideration, not very green but if you are only expecting to use it once a year or so to save the contents of your freezer then perhaps acceptable.]]>
		</description>
	</item>
	<item>
		<title>Setting up a solar installation trial run</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303928#Comment_303928</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303928#Comment_303928</guid>
		<pubDate>Thu, 19 Oct 2023 13:05:28 +0100</pubDate>
		<author>philedge</author>
		<description>
			<![CDATA[A battery is going to help get past your 25 amp restriction, if you need to?? At 4c a unit it's hard to see how investing in solar would be worthwhile when you can charge from a "green" grid for peanuts, but... where does the claimed 100% renewable energy come from on a still night?<br /><br />There's plenty of hybrid inverters/ battery combos that will power significant loads when the grid goes down, but if your grid goes down in bad weather then you'll need a very big battery and/or generator as solar isn't going to be much help in bad weather.]]>
		</description>
	</item>
	<item>
		<title>Setting up a solar installation trial run</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303930#Comment_303930</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303930#Comment_303930</guid>
		<pubDate>Thu, 19 Oct 2023 13:51:13 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[As others have said, a battery is likely to be more useful than PV in your situation. PVGIS is a good starting point as Tom says. You should do a lot of research to find out what sort of installation is most sensible. I expect it will all be more expensive than 4c per kWh. Try to find a local contractor who knows what they are doing.<br /><br />I'm not sure about the 100% renewable claim, BTW. <a href="https://investinnavarra.com/en/renewable-energy/the-energy-plan-for-navarra-plans-to-mobilise-2300-million-euros-by-2026/" target="_self" rel="nofollow">https://investinnavarra.com/en/renewable-energy/the-energy-plan-for-navarra-plans-to-mobilise-2300-million-euros-by-2026/</a> <a href="https://www.100-percent.org/navarre-spain/" target="_self" rel="nofollow">https://www.100-percent.org/navarre-spain/</a>]]>
		</description>
	</item>
	<item>
		<title>Setting up a solar installation trial run</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303946#Comment_303946</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303946#Comment_303946</guid>
		<pubDate>Fri, 20 Oct 2023 09:32:58 +0100</pubDate>
		<author>revor</author>
		<description>
			<![CDATA[Charging from the grid seems like your best option but you will have to decide on what size. There are a couple of issues to consider how big a capacity for storage and how much current you want to supply. If you were charging via solar a nominal 48 system you would need a sizeable inverter and hefty cabling to get say 40 amps so a 240 V battery array would be the best option. That gets you over the low voltage high current scenario and you then need to decide the size of your "bank". At nominally 2v per cell you could be talking a lot of batteries wired in series to give you the volts and paralleled to give you the capacity so not a cheap option. Used batteries from FLT ex submarine or UPS could be an option. I have no experience of these but I was aware of someone who did an array of batteries' using ex UPS batteries but being off grid charged them up with a generator driven by a tractor using diesel so not very green. UPS bats  are changed well before the end of their life so are good bet if can get hands on them. Then there are ex EV batteries if you can get someone knowledgeable to configure a set up. A friend has just bought 20Kw from a scrapped BMW for his solar system linked to a 10Kw inverter but had someone supply it and configure it.]]>
		</description>
	</item>
	<item>
		<title>Setting up a solar installation trial run</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303947#Comment_303947</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303947#Comment_303947</guid>
		<pubDate>Fri, 20 Oct 2023 11:24:10 +0100</pubDate>
		<author>Peter_in_Hungary</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: revor</cite>Charging from the grid seems like your best option but you will have to decide on what size. There are a couple of issues to consider how big a capacity for storage and how much current you want to supply. If you were charging via solar a nominal 48 system you would need a sizeable inverter and hefty cabling to get say 40 amps so a 240 V battery array would be the best option. That gets you over the low voltage high current scenario and you then need to decide the size of your "bank". At nominally 2v per cell you could be talking a lot of batteries wired in series to give you the volts and paralleled to give you the capacity so not a cheap option. Used batteries from FLT ex submarine or UPS could be an option. I have no experience of these but I was aware of someone who did an array of batteries' using ex UPS batteries but being off grid charged them up with a generator driven by a tractor using diesel so not very green. UPS bats  are changed well before the end of their life so are good bet if can get hands on them. Then there are ex EV batteries if you can get someone knowledgeable to configure a set up. A friend has just bought 20Kw from a scrapped BMW for his solar system linked to a 10Kw inverter but had someone supply it and configure it.</blockquote><br />Or you just get a Tesla powerwall or SunPower SunVault, or the Enphase Encharge (others are available) get a manufactures guarantee and support, plug and play and off you go and save your self all the problems of a home brew bit of kit.]]>
		</description>
	</item>
	<item>
		<title>Setting up a solar installation trial run</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303957#Comment_303957</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303957#Comment_303957</guid>
		<pubDate>Fri, 20 Oct 2023 16:14:52 +0100</pubDate>
		<author>revor</author>
		<description>
			<![CDATA[<blockquote>blockquote><cite >Posted By: Peter_in_Hungary</cite>Or you just get a Tesla powerwall or SunPower SunVault, or the Enphase Encharge (others are available) get a manufactures guarantee and support, plug and play and off you go and save your self all the problems of a home brew bit of kit.</blockquote><br /><br />Yes fine if you have deep pockets Â£900 -Â£1000 per kwh so looking at 3/4 Powerwalls you are looking at Â£30/35K + inc install for a 40kwh job that may see you with good management through a lengthy power outage.]]>
		</description>
	</item>
	<item>
		<title>Setting up a solar installation trial run</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303959#Comment_303959</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303959#Comment_303959</guid>
		<pubDate>Fri, 20 Oct 2023 17:44:27 +0100</pubDate>
		<author>Peter_in_Hungary</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: revor</cite>Yes fine if you have deep pockets Â£900 -Â£1000 per kwh so looking at 3/4 Powerwalls you are looking at Â£30/35K + inc install for a 40kwh job that may see you with good management through a lengthy power outage.</blockquote><br />But it depends what you want out of your backup. If you are happy with lights and fridge/freezer only running for a day and postpone the washing machine and dishwasher for later then the power requirements drop drastically. Longer than a day the get the gennie out. <br /><br />As with most things define the requirements first, list the nice to haves and the must haves, then look at the costings and the budget...........and then go down the pub 'cos you just realised you can't afford any of it with todays prices.]]>
		</description>
	</item>
	<item>
		<title>Setting up a solar installation trial run</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303962#Comment_303962</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=17999&amp;Focus=303962#Comment_303962</guid>
		<pubDate>Fri, 20 Oct 2023 18:41:38 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Especially the beer.]]>
		</description>
	</item>
	