Posted By: enerk1) Can I use a large unit (suitable for 120m2 house) use partially or would that cause some issues?As well as area, its usual to deal with MVHR in terms of internal volume, since they output mĀ³/hr and adequacy is rated in terms of ACH. But in general turning and MVHR down doesn't cause issues, in fact it's usually beneficial. Ours is nominally 300 mĀ³/hr but we don't normally run it above 125 mĀ³/hr and never above 165 mĀ³/hr.
2) Does providing exhaust through the roof make sense? Im worried about positioning ducting upwards.It can be done. The no-no is having the intake and exhaust on different walls, or one on a wall and the other on the roof. They need to experience similar external pressures to each other regardless of wind direction.
3) What unit to choose?Horses for courses I suppose. I live in a PH so we have a PH-certified Brink unit. The benefits are independent 3rd-party certification of performance. Good airtightness; quiet; well-built. etc. But PH cost more than some others.
4) Ideally I would want a unit I can control over wifi but do I actually need it?Well mine doesn't have it, so no you don't need it. But it might be convenient sometimes.
5) Either the unit would be supplied with good filters or have an option to upgrade it depending on needs.Look for washable filters. The slots in mine are thick enough that I can put either a G3 or a G4 or both together (which is what I do on the intake) or an F7 filter.
6) Noise - needs to be quiet!As mentioned; PH tests for noise level.
Posted By: enerkPosition of my house is such that I can't put the exhaust and intake on a wall hence thinking about roof. If I run it through sofits (which would probably accommodate max 100-125mm shall I then double it?Our MVHR unit uses 160 mm ducts. We're 145 mĀ²-ish so a bit bigger than you and we have some fairly high ceilings (approx 440 mĀ³ IIRC) but those are PHPP values so perhaps measured differently. But I'd think 100-125 mm was too small, yes. Low velocity is important for noise.
If i go with roof how to make sure it doesn't cause mould? I know that with bathroom extractors it does cause issue often but would it be different here because it's always on?
Posted By: djhBe sure to use a dry trap, not a U-bend wet one.
Posted By: djhI'm not sure what you're proposing in your last sentence? You mean omitting the trap and connecting it directly to a sink? I believe the trap is specificed by the MVHR manufacturer in the installation instructions.
Posted By: Peter_in_HungaryConnecting the MVHR drain pipe to a sink outlet above the trap or to a washing machine up-stand drainI suspect in most case it would be difficult to do that whilst keeping the condensate drain flowing downhill.
Posted By: ArtiglioIs there not a bit of confusion here between the air ducts and condensate drain when it comes to talking of downhill?I was wondering that. I think the condensate drain should go downhill and I think that the intake and exhaust ducts should basically go downhill if they run through a wall. Obviously the ducts can't if they're going up through the roof. And they can't go uniformly down if they emerge from the top of the MVHR unit as mine do. I think the idea is to deal with any rain that enters through the outside grille. The condensate drain deals with anything that occurs within or above the MVHR unit.
The only thing that iād have done differently and which may get done once everything else is finished , is to have fitted direct extraction to the outside from the cooker hood rather than relying on the filter/recirculation and mvhr when cooking.I suppose it depends on the style and quantity of cooking you do, as well as the arrangement of the extract terminals, but FWIW we haven't missed having an externally-vented cooker hood. In fact we hardly use the cooker hood at all.
Posted By: djhI think that the intake and exhaust ducts should basically go downhill if they run through a wallThe terminal should have a rain screen, so rain entry shouldn't normally be a big issue, though an outward slope is still a good idea.