			<![CDATA[oops looks like it did not add.]]>
		</description>
	</item>
	<item>
		<title>3 phase electrics</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305178#Comment_305178</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305178#Comment_305178</guid>
		<pubDate>Sun, 04 Feb 2024 12:05:22 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: revor</cite>oops looks like it did not add.</blockquote>maybe it was too large?<br /><br /><blockquote ><cite >Posted By: revor</cite>Having 3P I understand can be dangerous if you happen to mix phases by inappropriate use of extension leads or modify wiring in any way.</blockquote>Indeed, which is why we were surprised to find such a basic error.]]>
		</description>
	</item>
	<item>
		<title>3 phase electrics</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305179#Comment_305179</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305179#Comment_305179</guid>
		<pubDate>Sun, 04 Feb 2024 12:08:18 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[This page mentions 3-phase hobs are real:<br /><a href="https://www.neff-home.com/ie/service/support/induction-hobs/induction-cooker-installation" target="_self" rel="nofollow">https://www.neff-home.com/ie/service/support/induction-hobs/induction-cooker-installation</a><br /><br />Elsewhere I saw mention that it can be difficult to find 3-phase isolators that are attractive in a domestic setting?]]>
		</description>
	</item>
	<item>
		<title>3 phase electrics</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305349#Comment_305349</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305349#Comment_305349</guid>
		<pubDate>Mon, 19 Feb 2024 15:12:37 +0000</pubDate>
		<author>revor</author>
		<description>
			<![CDATA[This caught my eye. Octopus and National grid to collaborate to install 3 phase in homes so as to speed up install time of heat pumps EV chargers and solar pv. To me it seems to be a tall order and whose going to pay?. I have 3P to my outbuildings and had my single phase to the house put underground me doing the ductwork and trench etc. (£800)<br />They offered to do 3P to the house about 35 metres of cable think was about £3k (2010) and that was with 3P on site. I declined because my intention was to use less power not more.<br /><br /><a href="https://www.homebuilding.co.uk/news/octopus-and-national-grid-join-forces-to-upgrade-homes-to-three-phase-electric-as-part-of-heat-pump-and-ev-charger-rollout" target="_self" rel="nofollow">https://www.homebuilding.co.uk/news/octopus-and-national-grid-join-forces-to-upgrade-homes-to-three-phase-electric-as-part-of-heat-pump-and-ev-charger-rollout</a>]]>
		</description>
	</item>
	<item>
		<title>3 phase electrics</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305351#Comment_305351</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305351#Comment_305351</guid>
		<pubDate>Mon, 19 Feb 2024 16:44:27 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[I don't understand the article. First off why is three-phase needed? The DNO they were talking to happens to be my local one and if you have a 30 A or 60 A fuse, they will upgrade it to an 80 A or 100 A one for free!<br /><br />Secondly how is a heat pump installer going to upgrade a 'fuse' to three phase? Surely that involves digging up the road and connecting two more phases, not just changing a fuse? I'd have thought there aren't many heat pump installers that are certified for that, and it wouldn't make much sense since there's very little overlap between the two skill sets.<br /><br />And third, how does putting lots of houses on to three phase benefit the network? It's the total kW or total A that matters. It doesn't matter whether there's 300 single phase connections using 25 kW each, or 300 three phase connections using 25 kW each. The total down each wire is going to be the same beyond half a dozen houses or so.]]>
		</description>
	</item>
	<item>
		<title>3 phase electrics</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305353#Comment_305353</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305353#Comment_305353</guid>
		<pubDate>Mon, 19 Feb 2024 17:55:29 +0000</pubDate>
		<author>Dominic Cooney</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: djh</cite>why is three-phase needed?</blockquote><br /><br />Is it so that large, poorly insulated houses can switch over to heat pumps? <br />When I looked in to GSHP for our house, Kensa specified a 14kW model, which was the largest single-phase one they did (at the time, just having a quick look on their website today they do a 13kW and a 17kW in single phase, then a 15kW in 3-Phase) <br />So presumably any larger than this would need 3-Phase.]]>
		</description>
	</item>
	<item>
		<title>3 phase electrics</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305355#Comment_305355</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305355#Comment_305355</guid>
		<pubDate>Mon, 19 Feb 2024 22:17:29 +0000</pubDate>
		<author>WillInAberdeen</author>
		<description>
			<![CDATA[I fear that publication has got its wires crossed...<br /><br />The deal between Octopus and NG has been widely reported but no other reports I saw have suggested that they will install 3 phase.<br /><br />The deal seems to be that, if a customer needs their existing single phase fuse upgraded say 60A to 80A, then Octopus will do that themselves while they are on site, instead of waiting weeks for NG to send someone else out to do it. <br /><br />They also had their range of heatpumps pre-approved by NG, so NG don't have to assess each application individually, saving more weeks.<br /><br /><a href="https://www.edie.net/national-grid-moves-to-speed-heat-pump-and-solar-panel-installations/" target="_self" rel="nofollow">https://www.edie.net/national-grid-moves-to-speed-heat-pump-and-solar-panel-installations/</a><br /><br />A typical 16kW heatpump has a 32A MCB but draws 20A max, about half of an electric shower. So nowhere near needing 3 phase in this country. <br /><br />But as Peter mentioned, many countries wouldn't allow that. Heatpumps are made from parts that are sold in many countries, so have to comply with everyone's rules, you don't really get &gt;16kW+ heatpump compressors made exclusively for the UK market.]]>
		</description>
	</item>
	<item>
		<title>3 phase electrics</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305359#Comment_305359</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305359#Comment_305359</guid>
		<pubDate>Tue, 20 Feb 2024 08:17:20 +0000</pubDate>
		<author>Artiglio</author>
		<description>
			<![CDATA[FWIW<br /><br />When i bought my place ( old listed barn/oast) , i made a few enquiries regarding heat pumps both ground and air sourced. The companies that got back to me (3) all said i’d need 3 phase on the basis of the buildings levels of insulation at that point ( basically zero) they wouldn’t take into account my intended levels of insulation. They seemed to think i needed 25kw of heat. <br />I ended up fitting an 18kw system boiler that so far keeps the place cosy running at 50-55 degrees. Hopefully by time i eventually finish this will be reduced/ boiler run times are less.<br /><br />I then enquired about 3 phase supply, the estimate for that was 12k, of which 5k was for traffic management on a residential side road. House has been plumbed / wired with nod towards an eventual heatpump, cables run will be able to supply 40 amps max if needed.]]>
		</description>
	</item>
	<item>
		<title>3 phase electrics</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305364#Comment_305364</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305364#Comment_305364</guid>
		<pubDate>Tue, 20 Feb 2024 10:08:37 +0000</pubDate>
		<author>WillInAberdeen</author>
		<description>
			<![CDATA[Kensa do/did a 24kW single phase heatpump - a write-up here of what they think is possible with single phase:<br /><br /><a href="https://www.kensaheatpumps.com/installer/heat-pumps-and-single-phase-electricity/" target="_self" rel="nofollow">https://www.kensaheatpumps.com/installer/heat-pumps-and-single-phase-electricity/</a><br /><br />TLDR: the European market for large heatpump compressors is 3-phase. They can use electronics to convert a UK 1-ph supply into a waveform to run a larger 3ph compressor. Or they can simply put two smaller 1ph compressors in the heatpump, to give double the output.]]>
		</description>
	</item>
	<item>
		<title>3 phase electrics</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305368#Comment_305368</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305368#Comment_305368</guid>
		<pubDate>Tue, 20 Feb 2024 16:29:18 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Artiglio</cite>I then enquired about 3 phase supply, the estimate for that was 12k, of which 5k was for traffic management on a residential side road.</blockquote>Was that the DNO's price? I believe it's contestable work?]]>
		</description>
	</item>
	<item>
		<title>3 phase electrics</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305369#Comment_305369</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305369#Comment_305369</guid>
		<pubDate>Tue, 20 Feb 2024 16:32:45 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: WillInAberdeen</cite>Kensa do/did a 24kW single phase heatpump - a write-up here ...</blockquote>Thanks for that <img src="/newforum/extensions/Vanillacons/smilies/standard/bigsmile.gif" alt=":bigsmile:" title=":bigsmile:" /> Looking at the other articles in the magazine I see in https://www.acrjournal.uk/heat-pumps/airsourceheatpumps-a-reality-check/ something I haven't heard before:<br /><br />"The real issue that has been ignored and will prove an expensive cost to the homeowner within a relatively short time, is that all the systems fitted now but containing R32 refrigerant will need replacing in under ten years because the ‘F Gas’ refrigerants are being phased out by 2030 and this equipment is not suitable electrically to be retrofitted due to the flammability of the replacement natural refrigerant alternatives."<br /><br />If that's true then as far as I'm concerned that's a real killer for any consideration of an R32 heat pump. <img src="/newforum/extensions/Vanillacons/smilies/standard/devil.gif" alt=":devil:" title=":devil:" />]]>
		</description>
	</item>
	<item>
		<title>3 phase electrics</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305375#Comment_305375</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305375#Comment_305375</guid>
		<pubDate>Wed, 21 Feb 2024 09:02:35 +0000</pubDate>
		<author>WillInAberdeen</author>
		<description>
			<![CDATA[That's not true, the same as many of the other points in that rant.<br /><br />The legislation going through the EU at the moment is to ban manufacturers from launching new HFC systems in the EU after 2027 (monoblock) and 2035 (split system), but there's no ban on using existing products until 2050, and no indication if UK will follow suit.<br /><br />You don't have to look far in the internet to find this kind of shouting-at-clouds, even on previously 'reliable' sources. R4 You and Yours did a piece on heatpumps recently and saw fit to invite the gas industry's lobby group to provide their expert advisor - unsurprisingly he advised all the callers to keep on burning gas! And if you read the EV articles in a certain longstanding national newspaper, you'd understand why it has just been bought by a petrostate. It's the post-truth era now.<br /><br />As you said, this sowing-doubt stuff has real-world consequences, because it kills off people considering the transition.]]>
		</description>
	</item>
	<item>
		<title>3 phase electrics</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305381#Comment_305381</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305381#Comment_305381</guid>
		<pubDate>Wed, 21 Feb 2024 09:47:16 +0000</pubDate>
		<author>WillInAberdeen</author>
		<description>
			<![CDATA[Edit: forgot the link<br /><br /><a href="https://www.consilium.europa.eu/en/press/press-releases/2023/10/05/fluorinated-gases-and-ozone-depleting-substances-council-and-parliament-reach-agreement/" target="_self" rel="nofollow">https://www.consilium.europa.eu/en/press/press-releases/2023/10/05/fluorinated-gases-and-ozone-depleting-substances-council-and-parliament-reach-agreement/</a><br /><br /><br />Incidentally, there are proposals to ban PFAS "forever chemicals" in the EU, which will include the R1234 now used in nearly all car aircon systems. The legislation will work through over a number of years and existing cars will not be affected, but new car models will eventually switch over to something else. So don't let that kill any consideration of buying a current model of car!<br /><br /><a href="https://r744.com/volkswagen-plans-to-convert-all-bev-models-to-r744-by-2030/" target="_self" rel="nofollow">https://r744.com/volkswagen-plans-to-convert-all-bev-models-to-r744-by-2030/</a>]]>
		</description>
	</item>
	<item>
		<title>3 phase electrics</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305383#Comment_305383</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18069&amp;Focus=305383#Comment_305383</guid>
		<pubDate>Wed, 21 Feb 2024 09:51:39 +0000</pubDate>
		<author>Artiglio</author>
		<description>
			<![CDATA[DJH, the quote was provided by my electricity provider , had a site visit and only took 3 weeks, as to who would have been doing what i don’t know. 12k was at the time not an option, the ground source outfit were talking of 50k and the air source were only interested if i had UFH, neither would consider the insulation i was planning, so i gave up and went with gas boiler and rads, 8k all in. I bought a rotary converter to power the woodwork machines and had a free fuse upgrade to 80amps for the incoming supply. <br />Depending on finances, i may look into it once again before the drive is done ( as this is the last point a new incoming cable would be practical) but the 3 phase head has to go in an external cabinet and that would mean dealing with the conservation officer and getting listed building consent. The thought of the latter alone is enough to make me not even try.]]>