Home  5  Books  5  GBEzine  5  News  5  HelpDesk  5  Register  5  GreenBuilding.co.uk
Not signed in (Sign In)

Categories



Green Building Bible, Fourth Edition
Green Building Bible, fourth edition (both books)
These two books are the perfect starting place to help you get to grips with one of the most vitally important aspects of our society - our homes and living environment.

PLEASE NOTE: A download link for Volume 1 will be sent to you by email and Volume 2 will be sent to you by post as a book.

Buy individually or both books together. Delivery is free!


powered by Surfing Waves




Vanilla 1.0.3 is a product of Lussumo. More Information: Documentation, Community Support.

Welcome to new Forum Visitors
Join the forum now and benefit from discussions with thousands of other green building fans and discounts on Green Building Press publications: Apply now.




    • CommentAuthorRex
    • CommentTimeFeb 14th 2024
     
    What ho one and all,

    I do read many of the threads relating to EWI and although I do understand, I also don't understand.

    I am not considering it as I have quite a lot of insulation in my t/f house. However, a neighbour is in the process of having it fitted. Naturally, I do understand the insulation benefits,

    But !

    My house has the insulated inner wall, the cavity and a block and render external. During building, I did consider changing the block and rend for some kind of external insulation and render but wa told by the BCO that as I was changing the specs, I would have to reapply for Building Control.

    But he also told me, and this is what I don't understand about EWI, that since the cavity is ventilated, the outer wall is considered external as it has cold air on both sides and does not improve the insulation values.

    So what am I missing?

    Thanks
    •  
      CommentAuthordjh
    • CommentTimeFeb 14th 2024
     
    Posted By: RexBut he also told me, and this is what I don't understand about EWI, that since the cavity is ventilated, the outer wall is considered external as it has cold air on both sides and does not improve the insulation values.
    You're not missing anything. That's why it's essential to full fill a cavity before applying EWI. And change it from being a ventilated cavity to an unventilated one.
  1.  
    There's a good technical paper on avoiding thermal bypass, available here:

    https://www.passivhaustrust.org.uk/guidance_detail.php?gId=55

    Essentially you really want to avoid convective loops on the warm side of your insulation, especially if these are linked to outside air.

    On a related note, I assume that most of the moisture risks in full-filling existing cavities that are mentioned in this paper would effectively be mitigated by the outer layer of EWI. Clearly you'd need to check this with your installer.
    • CommentAuthorRex
    • CommentTimeFeb 14th 2024
     
    Interesting paper with too many numbers for me to understand!!!!

    I did find it interesting regarding the density of blown cellulose insulation to prevent slumping. I have Warmcel insulation and the internal 'barrier' was the supplied scrim. the insulation had to be pushed back to fit the dry-lining, so I guess I have sufficient density to prevent slumping.

    But....... during the build, it was necessary to do so stuff and I found in a number of locations at the top of the insulation, a 300mm cavity, caused by slumping. Had to get them back to fill the voids.

    Personally, I cannot see how a 2400 x 600 x 180 space filled with blown cellulose cannot slump.

    I would therefore think that blown cavity insulation on a two story house would slump.

    My house is sufficiently warm not to require EWI or cavity filling.
    •  
      CommentAuthorfostertom
    • CommentTimeFeb 14th 2024
     
    Posted By: RexI cannot see how a 2400 x 600 x 180 space filled with blown cellulose cannot slump
    True - you have to put in things for the Warmcel to grip onto, at vertical intervals. For new studwork, weave light galv garden wire in/out of the studs @ 300 vertical c/cs, winding round a nail head, before blopwing it in. Easy, cheap.

    Interesting that your Warmcel was retained by scrim, rather than e.g. the plasterboard - good practice that I've only seen in Americal instructions. The pressure can easily blow the plasterboard off its nails/screws. The scrim is stapled to the sides of the studs, a little way back from their room face. The scrim bulges when filled. You can easily roller back any xs bulges before fixing the pbd. With scrim you can also see visually that all nooks and crannies are filled.
    • CommentAuthorRex
    • CommentTimeFeb 14th 2024
     
    The main reason for using the scrim is that I did not fancy making 100mm holes into each and every vertical drop between studs and then having to fill them all. Scrim was a lot easier.

    I did put some scrap timber 'noggins' in as I was doubtful about the non-slumping claims. I actually wanted the Warmcel to be damp sprayed so that it goes like papier-mâché but the original installation company went into liquidation and the alternative said they could not do it with 180mm depth as there was a tenancy for it to just fall out.
    I'm certain I could have prevented that happening but it would have taken more time and money.

    "With scrim you can also see visually that all nooks and crannies are filled." Yes, but inevitably, the density will be greater at the bottom than the top, hence why I subsequently found gaps at the top where settlement had occurred.
    •  
      CommentAuthordjh
    • CommentTimeFeb 15th 2024
     
    With our Warmcel they used a mixture of scrim in some places and behind Panelvent in others. IIRC the stuff has glue or something to hold it together and prevent slumping? The pump measures the quantity supplied to guarantee that there aren't gaps, I believe. We have a certificate of the amount installed.
    •  
      CommentAuthorfostertom
    • CommentTimeFeb 15th 2024
     
    Posted By: Rexinevitably, the density will be greater at the bottom than the top
    I wouldn't think so - friction against containing things would initially exceed downward compression by weight. Later on, yes slump may occur, slowly bit by bit.
    • CommentAuthorJayarc
    • CommentTimeJan 16th 2025
     
    Looking to fit EWI to my 1910 house which has solid walls on one side of the house. There are insulated,cavity walls on the other side as it was extended before I moved in. We notice some damp always travelling to the colder wall. I'm hoping that insulation might reduce the damp but there seem to be so many different products on the market: woodfibre, cork, EPS, XPS foam, rock wool.
    I don't really understand the relative benefits of them. I feel like the cork option may be good for a damp wall as it sounds like it is more breathable than some other options but can anybody give me unbiased advice? I seem to find that most of the information out there which is comprehensible for a non-professional in the building industry is sales material so its hard to weigh up the relative merits of the options. Thank you so much if you can help.
    •  
      CommentAuthordjh
    • CommentTimeJan 16th 2025
     
    Welcome to the forum! :) The first thing to do is to find out where the damp is coming from, or tell us if you already know. Is it internal condensation or an external leak or rain?

    If it is is condensation then increasing the ventilation or turning the heating up a bit may cure the problem. Insulation is likely an alternative to heating, but not so much for ventilation.

    Whereabouts are you (roughly) as local conditions can vary.
    • CommentAuthorJayarc
    • CommentTimeJan 17th 2025
     
    Hello DJH, thank you for your very swift reply.

    The damp is definitely internal condensation. It mainly accumulates on a west facing wall which is a solid wall with no insulation.

    I'm keen to install EWI for environmental reasons, I've looked into other things I can do to my home to make it greener and there's not much I can do. The shape of the roof, direction of sun and position of working chimney make solar panels impractical and the property's current heating needs couldn't be met by an air source heat pump unless insulation is improved.

    However, I don't want to exacerbate the damp by fitting insulation and would ideally want to see an improvement in it for the kind of cost of EWI!

    I am in the south of England.
  2.  
    If you know for certain it is condensation caused by warm moist air condensing on a cold wall then, with a number of provisos (good room ventilation and a reasonable 'running temperature' in the house among them) you don't need to worry about trapping 'the damp' in, because you know what causes it and you have removed the cause.

    ''there seem to be so many different products on the market: woodfibre, cork, EPS, XPS foam, rock wool.
    I don't really understand the relative benefits of them.''

    Woodfibre and cork are less irritating to work with, but WF particularly produces a hell of a lot of 'fluff' (great for wetting and stuffing any open joints (of which, of course, there should be none). Rockwool is, in my opinion, horrible to work with. If you have more than 2 storeys you will probably have to use it is only as a 200mm fire-break, but I hate using it. It is also completely non-combustible, which is really good.

    EPS, XPS, phenolic foam are better than the others for a given thickness, but they are plastic. If you do not like plastic you will either not use them, or you will perhaps use them and wish forever that you hadn't. My preferred materials for EWI and IWI are WF and cork.
    •  
      CommentAuthordjh
    • CommentTimeJan 17th 2025
     
    How is the room/house ventilated? Do you regularly open the windows for example, or have mechanical ventilation of some kind?

    Have you got a temperature/relative humidity meter? Simple ones are very cheap and can tell you a lot about the conditions in your house. I have several Govee H5075 which work well.
    • CommentAuthorJayarc
    • CommentTimeJan 18th 2025
     
    Thank you that's helpful Nick I was leaning towards cork anyway and that feedback has made me more likely to go with cork.

    The ventilation isn't great I suppose in winter but it's not ideal opening windows while the heating is running.

    There's no mechanical ventilation. I think the humidity is usually around 50-55. I don't keep a hygrometer in that room - although maybe I will going forward - but when I've placed one in there from another area of the house it usually reads around 52.
    •  
      CommentAuthordjh
    • CommentTimeJan 19th 2025
     
    Posted By: JayarcThe ventilation isn't great I suppose in winter but it's not ideal opening windows while the heating is running.
    Well, no but then condensation isn't great either!

    There's no mechanical ventilation. I think the humidity is usually around 50-55. I don't keep a hygrometer in that room - although maybe I will going forward - but when I've placed one in there from another area of the house it usually reads around 52.
    Hmm, you wouldn't be seeing condensation at those sort of levels, so maybe the meter hasn't been experiencing the same conditions as the wall? Or maybe the conditions change overnight or something?

    You could try putting the meter very close to where the apparent condensation is occurring, with the expectation it will see something much closer to 100%. Or if you have an IR thermometer you can point it at the condensation to measure its temperature, and then use a site like http://dpcalc.org/ to compare that against the dewpoint shown from your T&H readings. Or you could dry the wall where it is damp and stick some sellotape on the wall and see if condensation forms on top of the sellotape - that will confirm it really is condensation.
    • CommentAuthorJayarc
    • CommentTimeJan 19th 2025
     
    Thank you djh, some really good ideas to investigate further there. Really appreciate it.
    •  
      CommentAuthordjh
    • CommentTimeJan 19th 2025 edited
     
    After I posted I thought that maybe clingfilm might stick to the wall and not be as destructive to take off as sellotape! :bigsmile:
    • CommentAuthorGreenPaddy
    • CommentTimeJan 19th 2025
     
    If I'm reading my psychrometric chart correctly, room air at 50% RH and 20oC would reach dew point at around 13oC, which I guess the wall internal surface temp could be? So condensation from internal air vapour is possible, maybe even likely.
    • CommentAuthorGreenPaddy
    • CommentTimeJan 19th 2025
     
    Ooops, now I've put my glasses on, maybe it would need to be 8oC internal wall temp, so less likely.
    •  
      CommentAuthordjh
    • CommentTimeJan 19th 2025
     
    I suppose the humidity & temperature readings might be more useful if Rachel can compare the inside and outside measurements. That will tell us something about whether more ventilation is likely to help much, and might be able to help with U-value estimation. Although more detail about the wall construction is probably best for that.
    • CommentAuthorRex
    • CommentTimeJan 23rd 2025
     
    Having started this thread and now understand that EWI only works if the cavity is filled.....

    But both external and internal walls are isolated from the damp by a DPC. If the cavity is filled, surely whatever the fill material is, goes below the DPC and since there is no DPC in the cavity itself, damp can rise within the insulation.

    And today, there is some government guidance about EWI poor workmanship. I'm afraid that I still cannot understand the how EWI works?
    •  
      CommentAuthorfostertom
    • CommentTimeJan 23rd 2025
     
    Cavity fill is or should be non-capillary i.e. unlike masonry it doesn't 'soak' liquid water up (or across).
    • CommentAuthorRex
    • CommentTimeJan 24th 2025
     
    Thanks, did not know that. But is not some cavity fill something like Warmcel? If so, that certainly soaks up water.
    • CommentAuthorphiledge
    • CommentTimeJan 24th 2025
     
    The older parts of our house have a blown in fluffy CWI which has been in there 20+ years without any damp problems so fair to assume that's non capillary
  3.  
    ''Thanks, did not know that. But is not some cavity fill something like Warmcel? If so, that certainly soaks up water.''

    It'll be Rockwool, I suspect which, for CWI, is white.

    ''The older parts of our house have a blown in fluffy CWI which has been in there 20+ years without any damp problems so fair to assume that's non capillary''

    Or that you have not got a wet outer leaf...
    • CommentAuthorphiledge
    • CommentTimeJan 24th 2025
     
    EWI works in the same way as wearing a high performance coat. If the coat fits you you'll be nice and snug. If the coat is too big and there's gaps all around between the coat and your body, you'll be cold. The gaps allow draughts to carry heat away so the coat does next to nothing. Same with an unfilled cavity.... draughts in the cavity carry away the heat and the EWI does next to nothing.
    •  
      CommentAuthordjh
    • CommentTimeJan 24th 2025
     
    I googled and apparently some people do use warmcel (or equiv)! Seems like a poor choice to me for reasons Rex and Tom and Nick at least understand. It would only make sense on dry ground and with an outer leaf that wasn't porous. e.g. a timber render over the structure, or maybe a waterproof render?

    (or even better, a waterproof render over EWI, and some reason to suppose there's no water at ground level)
    • CommentAuthorphiledge
    • CommentTimeJan 24th 2025
     
    "Or that you have not got a wet outer leaf..."

    Outer leaf is painted render so likely pretty impermeable but it does get wet on the inner face of the outer leaf which I assume is moisture from the interior condensing on the cold outer leaf?? We removed a chimney breast a few years ago an was very surprised how wet it was but no evidence of the condensate wicking back across the CWI.
    • CommentAuthorJeff B
    • CommentTimeJan 24th 2025
     
    We had CWI installed in our last house. It was Rockwool fibre coated with an oil* and blown in. It was very effective, as our gas consumption fell by about one-third over the year, compared to the previous year and continued to be approximately the same year on year thereafter. We moved 29 years later and there was never any sign of damp penetration in all that time.

    *I don't know if the same stuff is still available.
  4.  
    Posted By: philedgeEWI works in the same way as wearing a high performance coat. If the coat fits you you'll be nice and snug. If the coat is too big and there's gaps all around between the coat and your body, you'll be cold. The gaps allow draughts to carry heat away so the coat does next to nothing. Same with an unfilled cavity.... draughts in the cavity carry away the heat and the EWI does next to nothing.

    Love this explanation


    Posted By: philedgeOuter leaf is painted render so likely pretty impermeable but it does get wet on the inner face of the outer leaf which I assume is moisture from the interior condensing on the cold outer leaf?? We removed a chimney breast a few years ago an was very surprised how wet it was but no evidence of the condensate wicking back across the CWI.

    The addition of EWI will move the dew point outboard of the inner face of the outer leaf which will prevent any condensation here.

    The typical EWI (EPS wit thin film render) will not wick moisture through to the bricks.
   