		<description>
			<![CDATA[I mentioned some time ago that I had a unventilated ceiling to insulate for my current renovation. It's on the top floor of a small apartment block. The existing structure, top to bottom, is:<br /><br />- a tiled pitched roof attic that's subdivided into storage units used by various residents<br />- terracotta floor tiles in lime mortar<br />- thick timber planks<br />- joists at close centres that span between beams.<br /><br />to which I'm adding insulation and a dense plasterboard ceiling.<br /><br />Being rather tricky, I thought I'd better commission a WUFI analysis, and being optimistic I thought I'd kick off seeing what the results would look like with 300mm of hemp insulation batts. The results are now back and don't look pretty. With luck, the images will be below.<br /><br />I'm now considering how far to change the spec for another run of WUFI. I know that some of you - Tom, maybe Tony, maybe others? - have played with WUFI in the past, so am hoping that you may have some thoughts on this.<br /><br />An obvious track would be to cut the insulation. 200mm would be my ideal minimum (U = 0.21 W/m²K). In view of the results for 300mm, any opinions on this or an alternative thickness?<br /><br />No doubt adding a smart VCL would make WUFI results look better, but in reality the stud partitions would pass through and bypass it (they're fixed to the structure). That's leaving aside the advisability of using VCLs in retrofit anyway (I think my scepticism is shared with Tom too?).<br /><br />So, as I don't have endless funds to spend on WUFI models, what to try next?]]>
		</description>
	</item>
	<item>
		<title>WUFI &amp; unventilated ceiling</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=305937#Comment_305937</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=305937#Comment_305937</guid>
		<pubDate>Mon, 03 Jun 2024 21:20:01 +0100</pubDate>
		<author>Mike1</author>
		<description>
			<![CDATA[And the results. The only positive is that the maximum moisture content is showing some signs of stabilising, even if at a level that's unacceptably high:<br /><br />year 1: 63 kg/m³<br />year 2: 67 kg/m³ (+4)<br />year 3: 69 kg/m³ (+2)]]>
		</description>
	</item>
	<item>
		<title>WUFI &amp; unventilated ceiling</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=305941#Comment_305941</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=305941#Comment_305941</guid>
		<pubDate>Tue, 04 Jun 2024 08:46:42 +0100</pubDate>
		<author>sgt_woulds</author>
		<description>
			<![CDATA[A vapour variable membrane will certainly help, and there are some more options coming onto the market like the Partel Vara plus eco that reduce the plastic content.<br /><br />My company tries to design without membranes wherever possible, but there are always edge cases like this that require them.  They require careful detailing and sealing to work effectively.  <br /><br />Some smart membrane manufacturers offer free WUFI studies if you specify and use their membranes:<br /><br />SIGA Majrex®<br />Partel VARA PLUS ECO<br />PRO CLIMA intello plus<br /><br />I'd also recommend speaking to Chris or Andy at 'Back to Earth' as they have experience with tricky renovation jobs like this and understand the building physics involved.]]>
		</description>
	</item>
	<item>
		<title>WUFI &amp; unventilated ceiling</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=305942#Comment_305942</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=305942#Comment_305942</guid>
		<pubDate>Tue, 04 Jun 2024 10:47:23 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[What temperatures and humidities have you assumed above and below the ceiling? I see the times are in the past, so did you measure them?]]>
		</description>
	</item>
	<item>
		<title>WUFI &amp; unventilated ceiling</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=305950#Comment_305950</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=305950#Comment_305950</guid>
		<pubDate>Tue, 04 Jun 2024 18:22:47 +0100</pubDate>
		<author>Mike1</author>
		<description>
			<![CDATA[Thanks for the feedback so far. Re the points made:<br /><br /><blockquote ><cite >Posted By: sgt_woulds</cite>They require careful detailing and sealing to work effectively.</blockquote>Yes, from having done airtightness I know that's not easy on a renovation. And stopping moisture is trickier than stopping air. Then the VCL would have to stay undamaged for the next few decades.<br /><br /><blockquote ><cite >Posted By: sgt_woulds</cite>Some smart membrane manufacturers offer free WUFI studies if you specify and use their membranes:</blockquote>That's certainly interesting to know - I used Pro Clima Mento as part of the airtightness on this project.<br /><br /><blockquote ><cite >Posted By: sgt_woulds</cite>I'd also recommend speaking to Chris or Andy at 'Back to Earth'</blockquote>And another interesting tip, thanks.<br /><br /><blockquote ><cite >Posted By: djh</cite>What temperatures and humidities have you assumed above and below the ceiling? I see the times are in the past, so did you measure them?</blockquote>The external temperatures are based on real ones from the local 2009-2020 weather data. Not sure exactly how WUFI uses them, but from the dates on the graph I'd guess that it's using the actual data from those years.<br /><br />Internal temperature and humidity used are based on ASHRAE 160 - not something I've studied, and I know that there are other options, but presume that's a reasonable choice. From just having Googled it, looks like that uses a (minimum?) indoor temperature of 21°C, and that the indoor RH is related to the external RH, presumably from the weather data. Thinking about it, what I'm less sure about is what additional vapour load is added to account for people being in the apartment - for example whether that takes into account a specific number of people, or a flat load per m³, or whatever; maybe that needs looking at?<br /><br />I've also got MVHR factored in at 0.42 ACH which, after calculating it in multiple ways according to the recommendations of various different organisations, seems a sensible minimum in this case (for 1 person occupancy).<br /><br />Another thought since yesterday is whether there might be any benefit in tapping into the MVHR supply & return to add some minor ventilation to the space above the plasterboard. Never heard of anyone doing that, but it would (partially) decouple it from the internal moisture load. Hmm.]]>
		</description>
	</item>
	<item>
		<title>WUFI &amp; unventilated ceiling</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=305953#Comment_305953</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=305953#Comment_305953</guid>
		<pubDate>Tue, 04 Jun 2024 20:44:58 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[To add to sgt_woulds comment about membranes & maunfacturers, we used Intello+ in our roof and what's now called Solitex UM connect on the outside, under the standing seam. There's warmcel in between. EBS did a WUFI analysis and provided a warranty for the roof (since there's no ventilation, except that provided by the Solitex). I have no idea whether it provides any tangible benefits since we thankfully have had no problems, but it makes me feel better.<br /><br />I'd think a better way to estimate internal T & H would be to measure them directly. Also isn't the space above the ceiling internal rather than external? In which case measuring that seems like the best approach too.<br /><br />If I'm reading the graph correctly it's saying the humidity under the ceiling is pretty much always between 70% and 75%? That seems way too high for the inside of a building even without an MVHR. With an MVHR I'd expect it to normally be between 40% and 50% and never higher than 60%. Something's weird.<br /><br />For calibrating MVHR, I use 30 m³/hr per person rather than an ACH figure. The only time I can see any concern now I've got a CO2 meter is in our bedroom at night with two of us in it, when the CO2 rises from 'good' to 'normal' (>800 ppm) with 50 m³/hr into the house.]]>
		</description>
	</item>
	<item>
		<title>WUFI &amp; unventilated ceiling</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=305954#Comment_305954</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=305954#Comment_305954</guid>
		<pubDate>Tue, 04 Jun 2024 22:52:37 +0100</pubDate>
		<author>Mike1</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: djh</cite>we used Intello+ in our roof and what's now called Solitex UM connect on the outside, under the standing seam. ...I have no idea whether it provides any tangible benefits.</blockquote>I have seen a couple of WUFI studies comparing elements with and without smart VCLS; I may have a one filed away somewhere on my PC. From memory, they had the effect of smoothing the highs and lows, but weren't dropping the HR behind them radically. But the Solitex UM Connect on the outside would certainly be very helpful.<br /><br /><blockquote ><cite >Posted By: djh</cite>isn't the space above the ceiling internal rather than external? In which case measuring that seems like the best approach too.</blockquote>Yes, it is, but at the moment there is no ceiling, so I can't measure it yet. It may be worth putting some sensors up their when I install it though, if I can find something suitable. Anyone know of a university that may be interested?<br /><br /><blockquote ><cite >Posted By: djh</cite>If I'm reading the graph correctly it's saying the humidity under the ceiling is pretty much always between 70% and 75%? That seems way too high for the inside of a building even without an MVHR. With an MVHR I'd expect it to normally be between 40% and 50% and never higher than 60%. Something's weird.</blockquote>Well spotted! That could be the key to the problem. I was reading 'point A' as being above the plasterboard, but checking the text it does say that it is 'a control point to represent the impact of the indoor environment' - which probably does mean that it is on the underside, in the room. If so, that does indeed look very wrong. I'll go back to the consultant and check that.<br /><br /><blockquote ><cite >Posted By: djh</cite>For calibrating MVHR, I use 30 m³/hr per person rather than an ACH figure.</blockquote>I calculated it various ways (litres per person, by room and by volume using UK, French, German, Passivhaus and ACECB guidelines). The volume in this case is only around 90 to 100 m³, so using your 30 m³/h that would be roughly 0.33 ACH, compared to my 0.42, so we're not too far apart on that :)]]>
		</description>
	</item>
	<item>
		<title>WUFI &amp; unventilated ceiling</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=305956#Comment_305956</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=305956#Comment_305956</guid>
		<pubDate>Wed, 05 Jun 2024 08:29:22 +0100</pubDate>
		<author>sgt_woulds</author>
		<description>
			<![CDATA[From your build-up, (hard to see the text) it looks like you have a service void between the plasterboard and insulation.  Placing the VVCL behind the battens will protect it from most accidental penetrations from future plasterboard fixings.  <br /><br />Adding nail tape between the battens and membrane will also seal penetrations during installation and provide some additional protection if something is screwed through a batten in the future.<br /><br />Connecting the service void to the MVHR is an interesting idea.  I know that in in Europe, some ventilated roofs (eaves and ridge ventilation but over 10m length) are required to have additional measures, such as connection to forced ventilation which may include MVHR.  There must be some information 'out there' about effective strategies for force ventilation of narrow cavities.]]>
		</description>
	</item>
	<item>
		<title>WUFI &amp; unventilated ceiling</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=305961#Comment_305961</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=305961#Comment_305961</guid>
		<pubDate>Wed, 05 Jun 2024 20:03:45 +0100</pubDate>
		<author>Mike1</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: sgt_woulds</cite>From your build-up, (hard to see the text) it looks like you have a service void between the plasterboard and insulation.</blockquote>Actually only about 50% of the ceiling area has a void - the diagram was for modelling the 'worst case'.<br /><br /><blockquote ><cite >Posted By: sgt_woulds</cite>I know that in in Europe, some ventilated roofs (eaves and ridge ventilation but over 10m length) are required to have additional measures, such as connection to forced ventilation which may include MVHR.  There must be some information 'out there' about effective strategies for force ventilation of narrow cavities.</blockquote>That's interesting to know and would certainly be worth trying to track down. Otherwise I've been thinking that irrigation drip-pipes, or the equivalent in small diameter waste pipe, tapped into the ceiling plenums, might be worth experimenting with.<br /><br />However hopefully it won't be necessary, as djh's spot on the  internal RH is surely pointing to an error in the modelling. I've contacted the consultant so we will see.]]>
		</description>
	</item>
	<item>
		<title>WUFI &amp; unventilated ceiling</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306473#Comment_306473</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306473#Comment_306473</guid>
		<pubDate>Sun, 18 Aug 2024 15:54:06 +0100</pubDate>
		<author>Mike1</author>
		<description>
			<![CDATA[Returning again to this topic after a summer break, and several days experimenting with the free version of WUFI has been enlightening. Although the free version has restrictions on the materials and external climate that can be used, it's been close enough to turn out some useful results.<br /><br /><blockquote ><cite >Posted By: Mike1</cite>Internal temperature and humidity used are based on ASHRAE 160 - not something I've studied, and I know that there are other options, but presume that's a reasonable choice.</blockquote>Turns out that this was not a reasonable choice at all. ASHRAE 160 can take into account air changes, but only at external temperature & RH, modified only by heating or aircon - there's no MVHR or other heat exchange option. That makes it very driven by building volume, and for a small volume like mine the internal climate generated is sub-tropical - in my case forecasting year-round internal RH at about 70%. Which is nuts.<br /><br />In fact, there's nothing in WUFI that can properly simulate an MVHR internal climate. Apparently the entire building would need to be simulated in WUFI Plus (€1,790.00 + VAT for a 1-year license) to achieve that.<br /><br />The closest would be to use a custom 'sine curve' of internal RH throughout the year. That would need to take into account two components:<br /><br />1) the RH of the internal air based on the RH of the external air & the internal-external temperature difference - which is easy to calculate using a couple of formulae. Internal RH varies from 25% to 52% on this basis - chart below<br /><br />2) the additional RH caused by moisture sources in the building. And I can find no published data on this in MVHR homes.<br /><br />So I'm wondering whether any of you may have MVHR and logged temperature and humidity data, and may be willing to share it?]]>
		</description>
	</item>
	<item>
		<title>WUFI &amp; unventilated ceiling</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306480#Comment_306480</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306480#Comment_306480</guid>
		<pubDate>Sun, 18 Aug 2024 18:04:19 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Mike1</cite>In fact, there's nothing in WUFI that can properly simulate an MVHR internal climate. Apparently the entire building would need to be simulated in WUFI Plus (€1,790.00 + VAT for a 1-year license) to achieve that.</blockquote>Surely WUFI Passive must deal with an MVHR? I don't think there are many without one!<br /><br /><blockquote ><cite >Posted By: Mike1</cite>I'm wondering whether any of you may have MVHR and logged temperature and humidity data, and may be willing to share it?</blockquote>I have internal T&H data logged from last November. I've got three external readings since 2018 or so - one is my own in an outdoor cupboard; one is a neighbour's weather station, which goes offline for a day or more at a time sometimes, and the third is Wattisham airbase which is pretty reliable but six miles away.]]>
		</description>
	</item>
	<item>
		<title>WUFI &amp; unventilated ceiling</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306481#Comment_306481</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306481#Comment_306481</guid>
		<pubDate>Sun, 18 Aug 2024 18:05:59 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[The graph above shows all the feeds. The one below shows the internal, plus my own in blue and Wattisham in red over a shorter period. I can show you more graphs to your specification or send you CSV data if you want.]]>
		</description>
	</item>
	<item>
		<title>WUFI &amp; unventilated ceiling</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306482#Comment_306482</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306482#Comment_306482</guid>
		<pubDate>Sun, 18 Aug 2024 18:12:53 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[Just to add that I think the internal T&H values and relationship will depend quite a bit on the materials in the house.]]>
		</description>
	</item>
	<item>
		<title>WUFI &amp; unventilated ceiling</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306498#Comment_306498</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306498#Comment_306498</guid>
		<pubDate>Mon, 19 Aug 2024 15:58:49 +0100</pubDate>
		<author>Mike1</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: djh</cite>Surely WUFI Passive must deal with an MVHR?</blockquote>It does, and uses WUFI Plus in the calculation:<br /><br /><i >the Fraunhofer-Institute for Building Physics (IBP) and the Passive House Institute US (PHIUS) developed WUFI® Passive combining the WUFI® Plus building simulation tool with a Passive House Verification feature... ...all <br />features of WUFI® Plus are incorporated into WUFI® Passive</i><br /><br />What I hadn't spotted is the price - €515 +VAT for 1 year. Unless they've missed a digit off that price, it's by far the cheapest of all their software, despite apparently doing more. Not sure how the economics of that works.<br /><br /><blockquote ><cite >Posted By: djh</cite>I have internal T&H data logged from last November... ...I can show you more graphs to your specification or send you CSV data if you want</blockquote>That's excellent news! I'd be very happy to plough through the CSV data :)<br /><br />BTW, what are you logging with? I'm thinking of buying a batch of sensors in the next week or so, to bury in the ceiling before in insulation goes in - probably DHT22s wired up to Rasperry Pi.]]>
		</description>
	</item>
	<item>
		<title>WUFI &amp; unventilated ceiling</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306499#Comment_306499</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306499#Comment_306499</guid>
		<pubDate>Mon, 19 Aug 2024 15:59:05 +0100</pubDate>
		<author>Mike1</author>
		<description>
			<![CDATA[Duplicate post]]>
		</description>
	</item>
	<item>
		<title>WUFI &amp; unventilated ceiling</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306506#Comment_306506</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306506#Comment_306506</guid>
		<pubDate>Mon, 19 Aug 2024 20:25:47 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Mike1</cite>That's excellent news! I'd be very happy to plough through the CSV data :)</blockquote>If you whisper me an email address I'll see what I can do.<br /><br /><blockquote ><cite >Posted By: Mike1</cite>BTW, what are you logging with? I'm thinking of buying a batch of sensors in the next week or so, to bury in the ceiling before in insulation goes in - probably DHT22s wired up to Rasperry Pi.</blockquote>The main logging system is an OpenEnergyMonitor system &lt; https://openenergymonitor.org/ > an emonbase and two emonTx - they've recently updated the range so a new configuration might well be different. The emonbase is basically a pi plus a radio so I also run some scripts on it to import data from various places including the local weather station (screen scraping) and the met office DataPoint API for Wattisham. I have another pi (PiZeroW) outside with a T&H sensor attached that posts data to the emonbase. There's an emonTH that supplies the internal T&H data, although I've recently acquired a bunch of Govee T&H sensors that I intend to include fairly soon.<br /><br />I buried a bunch of sensors when I built but they're connected to a custom system that died soon after I got it :( I think the si7021 is better than DHT22, and the BME280 or BME680 better yet.]]>
		</description>
	</item>
	<item>
		<title>WUFI &amp; unventilated ceiling</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306529#Comment_306529</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306529#Comment_306529</guid>
		<pubDate>Wed, 21 Aug 2024 21:53:48 +0100</pubDate>
		<author>Mike1</author>
		<description>
			<![CDATA[Much appreciated - whisper just sent.<br /><br /><blockquote ><cite >Posted By: djh</cite>The main logging system is an OpenEnergyMonitor system &lt; https://openenergymonitor.org/ ></blockquote> I'll certainly take a look at that, as I've not progressed the thought process much beyond the sensors.<br /><br />Just been taking a deeper look as sensors, and the BME280, which looks good and is well priced (if they're genuine). The BME680 seems less common and costs 3x as much, without a 3x jump in performance difference. I also found someone who'd done a comparison, in which the Bosch came out best too: http://www.kandrsmith.org/RJS/Misc/Hygrometers/calib_many_afterbake.html<br /><br />However I then came across the SHT30-DIS-F (and some in the newer SHT4 range), which incorporates a PTFE film to protect it from contamination, which would be a plus. The sensors are cheap enough, but I haven't spotted anyone selling one on a PCB yet (other than the CN0537 £60 smoke detector board). I don't have time to play as well as doing a renovation, so the BME280 is looking most likely - thanks for pointing it out.]]>
		</description>
	</item>
	<item>
		<title>WUFI &amp; unventilated ceiling</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306535#Comment_306535</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306535#Comment_306535</guid>
		<pubDate>Thu, 22 Aug 2024 12:41:38 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Mike1</cite>Just been taking a deeper look as sensors, and the BME280, which looks good and is well priced (if they're genuine). The BME680 seems less common and costs 3x as much</blockquote>Yes, the difference is the VOC sensing built-in to the BME680; if you don't need that the 280 is as good ISTR.<br /><br /><blockquote >I then came across the SHT30-DIS-F (and some in the newer SHT4 range), which incorporates a PTFE film to protect it from contamination, which would be a plus. The sensors are cheap enough, but I haven't spotted anyone selling one on a PCB yet</blockquote>Ah, I'd forgotten the SHT4 range. Adafruit sell them on little PCBs, among others. There's also the SCD4 CO2 sensor range.]]>
		</description>
	</item>
	<item>
		<title>WUFI &amp; unventilated ceiling</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306621#Comment_306621</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18138&amp;Focus=306621#Comment_306621</guid>
		<pubDate>Wed, 28 Aug 2024 22:39:51 +0100</pubDate>
		<author>Mike1</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Mike1</cite>However I then came across the SHT30-DIS-F (and some in the newer SHT4 range), which incorporates a PTFE film to protect it from contamination, which would be a plus.</blockquote><br /><blockquote ><cite >Posted By: djh</cite>I'd forgotten the SHT4 range. Adafruit sell them on little PCBs</blockquote><br />Thanks for the Adafruit tip - it helped me find some similar DFRobot SHT31-F sensors (SEN0332). The PTFE protective film seems worthwhile as they'll be buried in hemp insulation. I've ordered a couple to test, together with Adafruit LTC4311 range extenders, to overcome the distance limitations of I2C.]]>
		</description>