			<![CDATA[Finished floor coverings removed, looking at installing UFH upstairs.<br /><br />Has anyone done a cost to benefit calculation on various methods? <br /><br />I'm thinking: <br /><br />A. 50mm PIR insulation between joists sat on roof batten, 16mm pipe in a 50mm biscuit screed (potential issues for weight?)<br /><br />B. Spreader plates with rockwool insulation below<br /><br />C. Any other alternatives whilst the boards are up? <br /><br />We have approximately 100m2 of upstairs floor area to do. Finished floors will be 18mm OSB with underlay and carpet...]]>
		</description>
	</item>
	<item>
		<title>Underfloor heating upstairs....</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306187#Comment_306187</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306187#Comment_306187</guid>
		<pubDate>Mon, 08 Jul 2024 18:21:00 +0100</pubDate>
		<author>Simon Still</author>
		<description>
			<![CDATA[I can't remember what sort of house construction you've got.<br /><br /><a href="https://www.wundagroup.com/water-underfloor-heating/joisted/" target="_self" rel="nofollow">https://www.wundagroup.com/water-underfloor-heating/joisted/</a> <br />www.wundatrade.co.uk<br /><br />they don't seem to sell the system we used, which was an overlay on top of the chipboard floors (so took about 20mm) in fibreboard panels.   We've got acoustic Rockwool between the floors. <br /><br />On upper floors the considerations are a bit different - you don't necessarily need to create a load of mass (especially if you run continuously at low temperature) <br /><br />(Most of our upstairs rooms get enough heat transmitted from the floor below and we don't actually have the UFH circuits on)]]>
		</description>
	</item>
	<item>
		<title>Underfloor heating upstairs....</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306188#Comment_306188</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306188#Comment_306188</guid>
		<pubDate>Mon, 08 Jul 2024 18:26:46 +0100</pubDate>
		<author>tychwarel</author>
		<description>
			<![CDATA[My system which was installed when the house was built 14 years ago is  option B and has proved to be more than adequate. <br />its cheap and very easy to fit]]>
		</description>
	</item>
	<item>
		<title>Underfloor heating upstairs....</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306189#Comment_306189</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306189#Comment_306189</guid>
		<pubDate>Mon, 08 Jul 2024 18:38:53 +0100</pubDate>
		<author>Victorianeco</author>
		<description>
			<![CDATA[I've used Wunda in my last house for the controls. I'll ring them tomorrow and see what sort of prices were looking at for 100m2 system<br /><br />I always thought a screed mix would retain heat better and also allow a better area of heat transfer. This was what we used in our last house in the first floor bathroom but with tiled floor on top of ply.<br /><br />Tychwarel any issues with noise of plates heating up and expanding etc? I think this would be fastest method of construction, and of course time is money. Do they give enough heat to transfer through the finished floor?]]>
		</description>
	</item>
	<item>
		<title>Underfloor heating upstairs....</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306190#Comment_306190</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306190#Comment_306190</guid>
		<pubDate>Mon, 08 Jul 2024 18:43:06 +0100</pubDate>
		<author>tychwarel</author>
		<description>
			<![CDATA[Very occasionally you get a creak when heating up. My floors vary most are 19mm engineered hardwood with no other finish however the bathroom is 19mm flooring chip board with vinyl overlay and the study is 19mm flooring chipboard with carpet tiles all produce adequate heating.]]>
		</description>
	</item>
	<item>
		<title>Underfloor heating upstairs....</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306191#Comment_306191</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306191#Comment_306191</guid>
		<pubDate>Mon, 08 Jul 2024 18:46:54 +0100</pubDate>
		<author>Victorianeco</author>
		<description>
			<![CDATA[Okay, we are looking to go with 18mm OSB by the looks of things. <br /><br />What temperatures are you running and any suggestion on a supplier for the plates? They seem very expensive for what they are...]]>
		</description>
	</item>
	<item>
		<title>Underfloor heating upstairs....</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306196#Comment_306196</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306196#Comment_306196</guid>
		<pubDate>Tue, 09 Jul 2024 07:45:04 +0100</pubDate>
		<author>Dominic Cooney</author>
		<description>
			<![CDATA[We did option B in the barn conversion. Despite being careful I still managed to put a screw through a pipe when building a stud wall, luckily the plumbers are very good and easily repaired my error.<br />It was where the loops of pipe crossed over the floor joists, we chiselled them into the top because the joists are existing and very old and rock hard pitch pine. Should probably have gone through half way down but that would have been even more epic.<br />Low temperature for us due to GSHP usually 30-35 degrees C<br />We used 18mm solid oak floorboards as the structural floor and finished surface I had to be very careful screwing them down (hidden fixings through the tongue) to avoid any pipes. <br />I prefer hard floors to carpets.]]>
		</description>
	</item>
	<item>
		<title>Underfloor heating upstairs....</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306197#Comment_306197</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306197#Comment_306197</guid>
		<pubDate>Tue, 09 Jul 2024 07:52:09 +0100</pubDate>
		<author>Dominic Cooney</author>
		<description>
			<![CDATA[We got the plates from <br />underfloorparts.co.uk<br />Probably the cheapest I could find, but maybe they had the size(s) we needed because we had some odd joist spacings! I had to plan it out carefully to work out what I needed and where, and the pipe route.]]>
		</description>
	</item>
	<item>
		<title>Underfloor heating upstairs....</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306201#Comment_306201</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306201#Comment_306201</guid>
		<pubDate>Tue, 09 Jul 2024 09:26:23 +0100</pubDate>
		<author>Dominic Cooney</author>
		<description>
			<![CDATA[It was quite funny to have a look at this again about 3 years later, how time flies. It's only one half of the upstairs, I must have started on the &quot;easy&quot; side and then realised that I had to plan it more carefully. The spreader plates had options for 3 or 4 grooves, with 4 the pipe comes back to the same end that you started, with 3 it ends up at the far end. It took some head scratching! <br />Top left is &quot;under bath&quot;, and there are some void areas over MVHR pipes because there just wasn't enough room for everything in the floor void.]]>
		</description>
	</item>
	<item>
		<title>Underfloor heating upstairs....</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306203#Comment_306203</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306203#Comment_306203</guid>
		<pubDate>Tue, 09 Jul 2024 10:10:23 +0100</pubDate>
		<author>Simon Still</author>
		<description>
			<![CDATA[Other things that I vaguely remember - part of the objective of your floor mass is increasing the transmission area.  Spreader plates are trying to do the same thing.  High density of pipes also makes a big difference (and lets you lower the temperature) <br /><br />Low temperature for us due to GSHP usually 30-35 degrees C<br /><br />That's not really that low - the heating curve for flow temp on for my upper floors (overlay under wood/tile) only hits 29C at 0C external (32 at -10).]]>
		</description>
	</item>
	<item>
		<title>Underfloor heating upstairs....</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306206#Comment_306206</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306206#Comment_306206</guid>
		<pubDate>Tue, 09 Jul 2024 11:11:52 +0100</pubDate>
		<author>Dominic Cooney</author>
		<description>
			<![CDATA[I was also surprised by the flow temperature that is required, the boffins at Kensa explained it to me in detail, something to do with the surface temperature being lower than the flow temperature and lower than the room temperature….<br />In my head 20 degrees water in the pipes would give 20 degrees in the room, but I was soon disabused of that concept.<br />I guess the heat loss of the room/building is critical, it’s needs heat input faster than it loses it.]]>
		</description>
	</item>
	<item>
		<title>Underfloor heating upstairs....</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306209#Comment_306209</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306209#Comment_306209</guid>
		<pubDate>Tue, 09 Jul 2024 16:19:08 +0100</pubDate>
		<author>Gareth J</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Simon Still</cite>)<br /><br />(Most of our upstairs rooms get enough heat transmitted from the floor below and we don't actually have the UFH circuits on)</blockquote><br /><br />That's something my folks say about their barn conversion which has UFH downstairs and rads upstairs. Radiators are only on very occasionally.<br /><br />Similar in our cottage. There's no heating upstairs except bathroom/ensuite. Occasionally we run out filled rads in bedrooms as and when.<br /><br />Have to wonder about the economics/carbon investment in installing heating upstairs if it's only used barely ever. Regs are regs though I guess.]]>
		</description>
	</item>
	<item>
		<title>Underfloor heating upstairs....</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306210#Comment_306210</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306210#Comment_306210</guid>
		<pubDate>Tue, 09 Jul 2024 17:38:16 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Gareth J</cite>Regs are regs though I guess.</blockquote>What regs are there nowadays?]]>
		</description>
	</item>
	<item>
		<title>Underfloor heating upstairs....</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306212#Comment_306212</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306212#Comment_306212</guid>
		<pubDate>Tue, 09 Jul 2024 17:57:15 +0100</pubDate>
		<author>Dominic Cooney</author>
		<description>
			<![CDATA[We resorted to Oil-filled radiators in the bedrooms in the last place we did, because they could get too cold in winter. We assumed that heat would rise, but obviously it didn't do so quick enough. Which is why we put the UFH in upstairs this time. Insulation in the walls wasn't as good as it could be though, due to space constraints.]]>
		</description>
	</item>
	<item>
		<title>Underfloor heating upstairs....</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306215#Comment_306215</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306215#Comment_306215</guid>
		<pubDate>Tue, 09 Jul 2024 18:23:22 +0100</pubDate>
		<author>Gareth J</author>
		<description>
			<![CDATA[Good question. I don't know! But if it can be shown that heating rooms below will meet whatever the regs require, could save a lot of people a lot of installation.]]>
		</description>
	</item>
	<item>
		<title>Underfloor heating upstairs....</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306240#Comment_306240</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306240#Comment_306240</guid>
		<pubDate>Fri, 12 Jul 2024 13:32:24 +0100</pubDate>
		<author>Rex</author>
		<description>
			<![CDATA[I wanted Lewis Deck  (<a href="https://lewismetaldeck.com/" target="_self" rel="nofollow">https://lewismetaldeck.com/</a>) on my first floor but the structural engineer told me it was not possible.<br /><br />Have the pipe in polystyrene insulation with spreader plates.  Heating is not a noticeable as the ground floor (screed) but what annoys me is every time the heating come on, the floor pop and bangs.  I figure it is the expansion of the pipe where it is a push fit into the plates, but it is really annoying and frequently wakes us in the early morning.]]>
		</description>
	</item>
	<item>
		<title>Underfloor heating upstairs....</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306283#Comment_306283</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306283#Comment_306283</guid>
		<pubDate>Fri, 19 Jul 2024 09:09:57 +0100</pubDate>
		<author>Simon Still</author>
		<description>
			<![CDATA[I'm not sure the regulations make any requirements of heating - our neighbours Passive build had only a couple of plug in radiators initially (they've now installed a single Air-Air heat pump unit)<br /><br /><br /><br /><blockquote ><cite >Posted By: Rex</cite>what annoys me is every time the heating come on, the floor pop and bangs.  I figure it is the expansion of the pipe where it is a push fit into the plates, but it is really annoying and frequently wakes us in the early morning.</blockquote><br /><br />Interesting.  What's your flow temperature?  suspect it's far too high.  Our Wunda overlay system in fibre mats with spreader plates has never made any noise but flow temp is 21-30ish.  <br /><br /><blockquote ><cite >Posted By: Dominic Cooney</cite>We resorted to Oil-filled radiators in the bedrooms in the last place we did, because they could get too cold in winter. We assumed that heat would rise, but obviously it didn't do so quick enough. Which is why we put the UFH in upstairs this time. Insulation in the walls wasn't as good as it could be though, due to space constraints.</blockquote><br /><br />That's the thing.  We're over 3 floors (tall narrow townhouse).  The top floor gets cooler but is probably OK, the middle floor where our bedroom doesn't need the UFH).  <br /><br />Ultimate solution now is probably Wet UFH on ground floor and air-air for upper floors as top up/summer aircon (which is justifiable if you're powering off your own solar).]]>
		</description>
	</item>
	<item>
		<title>Underfloor heating upstairs....</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306287#Comment_306287</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18157&amp;Focus=306287#Comment_306287</guid>
		<pubDate>Fri, 19 Jul 2024 13:29:53 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Simon Still</cite>I'm not sure the regulations make any requirements of heating - our neighbours Passive build had only a couple of plug in radiators initially (they've now installed a single Air-Air heat pump unit)</blockquote>I think the regulations require that there is the capability to heat the property (to 18°C in bedrooms and 21°C in living areas) according to the SAP model that is also required. There are specific extra regulations if the heating uses a boiler or whatever.]]>