<?xml version="1.0" encoding="utf-8"?>
	<rss version="2.0">
		<channel>
			<title>Green Building Forum - Water main replacement</title>
			<lastBuildDate>Wed, 07 Oct 2026 00:43:44 +0100</lastBuildDate>
			<link>https://www.greenbuildingforum.co.uk/newforum/</link>
			<description></description>
			<generator>Lussumo Vanilla 1.0.3</generator>
			<item>
		<title>Water main replacement</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306231#Comment_306231</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306231#Comment_306231</guid>
		<pubDate>Wed, 10 Jul 2024 21:52:31 +0100</pubDate>
		<author>Artiglio</author>
		<description>
			<![CDATA[Evening all<br /><br />Anyone have any input for the following.<br /><br />My place was connected to town gas and mains water around 1935, both were run in “water barrel” steel/iron pipe.<br />Same trench about 4 inches apart and buried about 500mm max ( it’s around 400mm nearer the point it enters the building) Later the gas was rerun by passing aplastic pipe through the old gas pipe and a water meter fitted.<br />There’s a weep in the incoming water pipe  close to where it enters the house and ideally it all needs replacing back to the meter. However the existing burial depth and proximity to the gas make it all rather problematic. <br /><br />If it follows the same route going down to 750mm risks going below the footings ( old barn spread brick off of chalk) plus gas pipe is very close. <br />I’ve dug down in 4 spots and located the gas and water pipes.( both are parallel to and within 400mm of the wall.  Water pipe seems to be bitumen coated and in fair condition given its age. <br />A little wary of calling out waterboard just in case it opens a can of worms regarding proximity of the gas along with the shallow burial depth of the existing. <br />I’ve located a joint in the pipe , what are the chances of that undoing with a bit of heat and gentle persuasion? ( i could then connect a plastic pipe and run it into the house ( i’ve installed a duct to the correct depth for the entry point ))<br />Has  anyone any recent dealings with gas/water utilities ? If so what sort of response have you had?  It wouldn’t be impossible to reroute both in a loop  away from the building and back in , but a huge amount of work i’d really rather not do at this point , plus no idea as to what costs i could be liable for from gas and water board ( trench within my boundary i can deal with).]]>
		</description>
	</item>
	<item>
		<title>Water main replacement</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306232#Comment_306232</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306232#Comment_306232</guid>
		<pubDate>Wed, 10 Jul 2024 22:42:52 +0100</pubDate>
		<author>philedge</author>
		<description>
			<![CDATA[If there's a stop cock upstream of the meter, can you trench to the meter and replace all the old pipe from the meter to the house?]]>
		</description>
	</item>
	<item>
		<title>Water main replacement</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306234#Comment_306234</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306234#Comment_306234</guid>
		<pubDate>Thu, 11 Jul 2024 19:35:18 +0100</pubDate>
		<author>revor</author>
		<description>
			<![CDATA[Where is your meter? Looks like might be in the roadway? I would be inclined to dig out new trench and  and replace the whole pipe with modern stuff from the water meter to the house. Could be an opportunity to choose where you want it entering the building. Doing it this way you can do most of the work without disruption to you current supply I would not be too concerned about the water board the fact you are laying a new pipe making improvements they tend to welcome. They will make the connection to the meter. You could put a larger bore pipe as replacement the billing is based on your pipe size which you will find somewhere on your bill. You may find it near your meter number. It might vary with water authority but it will usually be size 015. This is not the size from the meter to your house but the size from the main supply pipe to your meter. You can from the meter put whatever size you want. I replaced our pipe when we started the improvements to our house and learnt all of this from the water board. (I am with Welsh Water). It was they that recommended I put large bore in as we had about a 100 M run. I do not want to be alarmist but we had an issue with our previous house where we had settlement on one corner of the building and had it underpinned, The cause was a gas main had been moled under the drive during the time of a previous owner and had gone under a soil drain pipe fractured it and the leak caused the soil/sand to be washed from under the footings. So it would be best to put in a new supply given the age of the existing if only for this reason.]]>
		</description>
	</item>
	<item>
		<title>Water main replacement</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306236#Comment_306236</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306236#Comment_306236</guid>
		<pubDate>Fri, 12 Jul 2024 11:46:51 +0100</pubDate>
		<author>Artiglio</author>
		<description>
			<![CDATA[Cheers gents, in no particular order,<br /><br />Yes the meter is in the road way, just a bit too far for me to “tunnel under” and do the connection myself, so it will be a waterboard job.<br /><br />If i can get away with just following the current route and going a bit deeper it’s my favoured option. However i first need to dig down and make sure this doesn’t go below the spread brick on the barn wall footing  ( current main runs less than 300mm from wall).<br /><br />I also need to be sure that the proimity to the gas main isn’t an issue ( common sense says it wouldn’t be ,but in this day and age who knows when the inspector arrives) <br /><br />Either way i’ll do a short replacement section, to remove the section that’s weeping and into house ( new entry  duct has already been done) , then deal with replacing th rest at a later date.]]>
		</description>
	</item>
	<item>
		<title>Water main replacement</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306237#Comment_306237</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306237#Comment_306237</guid>
		<pubDate>Fri, 12 Jul 2024 12:14:19 +0100</pubDate>
		<author>Artiglio</author>
		<description>
			<![CDATA[Managed to get hold of someone who’s pragmatic and practically minded , in my situation a reduced burial depth is acceptable, i just need to use something along the lines of “SHalloduct”, proximity of gas whilst not ideal is a historical ( and not uncommon) arrangement and as the new mdpe has been slid into the old iron gas pipe and there’s no sensible way of moving it ( especially given it’ll most likely run next to the meter and there’s no way the utility companies will change the arrangement).<br />Just a matter now of trying yo get hold of the appropriate department at my water provider, which is beginning to look like a mission in itself.]]>
		</description>
	</item>
	<item>
		<title>Water main replacement</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306241#Comment_306241</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306241#Comment_306241</guid>
		<pubDate>Fri, 12 Jul 2024 16:18:44 +0100</pubDate>
		<author>Peter_in_Hungary</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Artiglio</cite>There’s a weep in the incoming water pipe  close to where it enters the house and ideally it all needs replacing back to the meter.</blockquote><br />If there is a weep in the pipe (rather than a failed fitting joint) this would imply a corroded pipe, in which case is the remainder of the pipe not far behind? Which may/will give problems connecting the new pipe <br /><br /><blockquote ><cite >Posted By: Artiglio</cite>I’ve located a joint in the pipe , what are the chances of that undoing with a bit of heat and gentle persuasion?</blockquote><br />This depends upon the condition of the pipe. You might finish up chasing back down the pipe looking for a bit good enough to either cut a thread or a joint that will separate without sheering off.<br /><br />If you are going to replace the whole run within the foreseeable future then over here you can get clamp on joint fittings that clamp to the outside of the pipe and have rubber seals to provide water tightness. (a bit like a compression fitting) to connect to what ever follow on pipe you use. They avoid the stress to the pipe of thread cutting or the need to undo fittings that are probably rusted in over the last 80 - 90 years but they do need to go on a clean(ed) pipe. They probably should be regarded as a temporary fix but as we all know there is no such thing as temporary.<br /> <br /><br /><blockquote ><cite >Posted By: Artiglio</cite>Just a matter now of trying yo get hold of the appropriate department at my water provider, which is beginning to look like a mission in itself.</blockquote><br />why do you need to talk to your water provider to do this repair?]]>
		</description>
	</item>
	<item>
		<title>Water main replacement</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306244#Comment_306244</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306244#Comment_306244</guid>
		<pubDate>Sat, 13 Jul 2024 20:21:52 +0100</pubDate>
		<author>philedge</author>
		<description>
			<![CDATA[AFAIK you're responsible for the pipe on your land and the water company are responsible for the pipe/meter if its not on your land. On that basis can you replace the pipe to the boundary so any future failure of the old pipe is down to the water company to sort out?? If you let your water supplier know you think the pipe is failing and you're planning to replace your bit, they may come and do the bit to the meter so you can run your new pipe all the way to the meter?? Worth a try??]]>
		</description>
	</item>
	<item>
		<title>Water main replacement</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306245#Comment_306245</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306245#Comment_306245</guid>
		<pubDate>Sun, 14 Jul 2024 07:57:08 +0100</pubDate>
		<author>Peter_in_Hungary</author>
		<description>
			<![CDATA[I wouldn't contact the water supplier, you don't know what kind of bureaucratic can of worms you could end up with. And with most water cos. strapped for cash and under pressure they will certainly try to put as much on to the consumer as they think they can get away with.]]>
		</description>
	</item>
	<item>
		<title>Water main replacement</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306252#Comment_306252</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306252#Comment_306252</guid>
		<pubDate>Sun, 14 Jul 2024 10:50:59 +0100</pubDate>
		<author>Artiglio</author>
		<description>
			<![CDATA[Good morning, again thanks for the replies, i obviously wasn’t too clear in my op, yes the whole pipe needs replacing , but i am /was hoping to put off the full replacement until a more conveneint time. <br /><br />As stated above i’m responsible for the pipe on my property and can do that work, i’m not allowed to excavate outside my boundary or connect to the meter. If it were a lead pipe it’d generally be covered by at worst a modest fee. It’s not and as also stated above the water companies are mercenary in their charging these days. <br /><br />The weep was on a branch that went to a garden tap, the pipe was rotten, i cut it back as close to the main as i could and bodged a plug to seal the pipe. It’ll be ok for a week or so. The barn used to be stables and i’d not be surprised if there are other t’s off the pipe.<br /><br />I’d managed to speak to a water board crew via my plumber, who basically said if i get a jobsworth inspector the job will grow arms and legs , and the jobsworths are seemingly more numerous these days. They warned against contacting the water board as i’d have to give the address and it’d flag the property  for an inevitable meter inspection and if the leak was detectable “ put me in the system”.<br /><br />On the back of that i decided to run a new main from the house to a meter inside my boundary and connect to the old pipe. I’ve dug out under my boundary and only a foot or so out found the connection between the meter and my old pipe. ( apparently it’s usual for there to be a short tail my side of the meter, makes meter installation easier).<br />No indication of any issues that end of things, so plan is to connect a metre my side of the meter , with a loop in the pipe. Make sure that the new main is sound and connections good, give it a few weeks, identify the fitting on the meter tail and get the appropriate adaptor for the new main, and use the loop to get rid of the last section of metal pipe.<br /><br />The waterboard website is a minefield that just sends you to an application page for works required, in my case as the meter is technically on the highway (due to their being a historically missing section of footpath) traffic management may be required and that 2k plus to start.<br /><br />In the early 2000’s i had a connection to serve a building connected to 4 flats and new supplies to a new build of 4 flats. They were simplicity itself in comparison, one phone call, a very nice chap comes out , we went through what i wanted he came up with best solution, handed me some forms , filled them in, they came back with a reasonable quote, i agreed and paid, informed them when site was ready, they turned up and did it, the new build required tapping the main in the road way, traffic management was the van and half a dozen cones. <br /><br />When did life get so complicated?]]>
		</description>
	</item>
	<item>
		<title>Water main replacement</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306253#Comment_306253</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306253#Comment_306253</guid>
		<pubDate>Sun, 14 Jul 2024 11:18:18 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[There's a description of who's responsible for what at <a href="https://www.ofwat.gov.uk/households/supply-and-standards/supply-pipes/" target="_self" rel="nofollow">https://www.ofwat.gov.uk/households/supply-and-standards/supply-pipes/</a>]]>
		</description>
	</item>
	<item>
		<title>Water main replacement</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306254#Comment_306254</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306254#Comment_306254</guid>
		<pubDate>Sun, 14 Jul 2024 12:41:57 +0100</pubDate>
		<author>Artiglio</author>
		<description>
			<![CDATA[Thanks for that, should be part of every utility companies web site search results. I can now quite happily connect to the fitting i can see with no worries, expect it would be different if i had to excavate outside my boundary.]]>
		</description>
	</item>
	<item>
		<title>Water main replacement</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306292#Comment_306292</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18159&amp;Focus=306292#Comment_306292</guid>
		<pubDate>Sat, 20 Jul 2024 00:30:56 +0100</pubDate>
		<author>Artiglio</author>
		<description>
			<![CDATA[Pretty much all done, initially it wasn’t possible to reach the fitting on the tail from the meter box, but whilst digging out it became apparent why the brick pier ( pipe ran under the garden gate) was leaning away from the building ( it had been built in the dim and distant past on earth and had just 2 courses of brick underground).<br />So pier is now down and digging out for a decent footing meant reaching the “tail”fitting was possible.<br />Now have a 25mm mdpe pipe from meter to the house. I was rather impressed that the existing coupling (philmac -universal transition coupling) came apart and with a clean and some silicon grease accepted my new pipe and sealed first time. <br />The meter stopcock not working properly was in the end no problem , the amount leaking past was minimal.<br />The old steel main, had been weeping in 4 places , so a job that definitely needed doing.<br />Thanks all formthe input.]]>
		</description>
	</item>
	