<?xml version="1.0" encoding="utf-8"?>
	<rss version="2.0">
		<channel>
			<title>Green Building Forum - PIV vs dehumidifier</title>
			<lastBuildDate>Tue, 19 May 2026 16:49:49 +0100</lastBuildDate>
			<link>https://www.greenbuildingforum.co.uk/newforum/</link>
			<description></description>
			<generator>Lussumo Vanilla 1.0.3</generator>
			<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307360#Comment_307360</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307360#Comment_307360</guid>
		<pubDate>Sat, 30 Nov 2024 08:18:26 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: gravelld</cite>That implies a constant draw from the unit</blockquote>Correct, if that means constant depression, relative to outdoors, at the fan unit, which therefore has to ramp fan speed up or down depending on the resistance it's 'seeing' i.e. how many extract branch ducts are open.<br /><blockquote ><cite >Posted By: gravelld</cite>once any of the outlets detects high humidity ... the outlets open wider</blockquote>Yes that's the other way to do it, other than humidistat-controlled room inlets from outside. Are your 'outlets' mechnically controlled by humidistat, or electric? If electric, do they send a signal to the unit?<br /><blockquote ><cite >Posted By: gravelld</cite>This allows the unit to draw more air</blockquote>If that's without the unit ramping fan speed up or down i.e fan speed constant regardless, then if just one outlet opens it'll get an excessive extraction, which will drop to maybe insufficient as other outlets open.]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307370#Comment_307370</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307370#Comment_307370</guid>
		<pubDate>Sun, 01 Dec 2024 07:22:21 +0000</pubDate>
		<author>gravelld</author>
		<description>
			<![CDATA[Probably more exhaustive to just link to the manuals for the unit I have!<br /><br /><a href="https://www.aereco.co.uk/wp-content/uploads/2019/09/TF4496_E_V4Apremium_display.pdf" target="_self" rel="nofollow">https://www.aereco.co.uk/wp-content/uploads/2019/09/TF4496_E_V4Apremium_display.pdf</a><br /><br />The unit does have a connection to the outlets, but my understanding is it's just to power them (via 12v wiring). The outlets themselves are responsible for opening/closing with their own sensors - their is no communication between the outlets and the unit. It just relies on constant pressure - when the outlets open more, the unit can run faster.<br /><br />I think that's important for simplicity and it's an elegant solution. It also means no batteries etc to maintain. The only thing I have to do is occasionally dust the outlets and annually clean the filter on the unit.]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307372#Comment_307372</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307372#Comment_307372</guid>
		<pubDate>Sun, 01 Dec 2024 09:07:30 +0000</pubDate>
		<author>Victorianeco</author>
		<description>
			<![CDATA[What's your overall setup then Grave and is there a specific reason you didn't go for MVHR?]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307377#Comment_307377</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307377#Comment_307377</guid>
		<pubDate>Mon, 02 Dec 2024 16:29:00 +0000</pubDate>
		<author>gravelld</author>
		<description>
			<![CDATA[Not airtight 'enough' for MVHR, and it would involve more ducting. I only required a point solution for extract in wet rooms.<br /><br />The outlets are in the kitchen and two bathrooms. The unit is in the loft. The unit extracts through a roof tile. Mostly solid ducting. Anything else you were wondering?]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307379#Comment_307379</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307379#Comment_307379</guid>
		<pubDate>Tue, 03 Dec 2024 11:30:01 +0000</pubDate>
		<author>Victorianeco</author>
		<description>
			<![CDATA[Okay great, I will give aereco a call]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307400#Comment_307400</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307400#Comment_307400</guid>
		<pubDate>Thu, 05 Dec 2024 08:56:01 +0000</pubDate>
		<author>sgt_woulds</author>
		<description>
			<![CDATA[Regarding DJH comments on costs, it might be more useful to present the total cost of ownership, (including installation, filter changes and servicing) along with power consumption.<br /><br />There used to be an interesting comparison on the Glidevale site comparing ownership costs for their iPSV with MVHR, MEV, and simple extractor fans.  The costs for MVHR have been reduced due to grants, but taken broadly it still supports Dr Rickaby's larger assertions that simple, reliable (and cheap) is best for improving the lives of more people for longer.<br /><br />Much as I'd like to buy into the church of MVHR, increasing household financial constraints, (and personal infirmities) lean me towards a system that provides healthy air without relying on a maintenance budget, (or continued ease of using grid electricity).<br /><br />The original report might still be on the Glidevale site somewhere, the only place I can find a snippet is in the picture gallery for an article here:<br /><br /><a href="https://www.house-builder.co.uk/products/companies/glidevale-building-products/glidevale-ipsv/" target="_self" rel="nofollow">https://www.house-builder.co.uk/products/companies/glidevale-building-products/glidevale-ipsv/</a>]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307404#Comment_307404</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307404#Comment_307404</guid>
		<pubDate>Thu, 05 Dec 2024 11:15:40 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[Again, I'd appreciate a reference to Rickaby's statements, please.<br /><br />"Healthy air" from outside simply adds to your heating budget instead of an identifiable separate maintenance budget. It's smoke and mirrors accounting. Not that I have any objections to the product itself.]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307405#Comment_307405</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307405#Comment_307405</guid>
		<pubDate>Thu, 05 Dec 2024 12:07:28 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[I also can't find Rickaby in print on the subject. You've prob already seen this layman-terms comparison from Aereco<br /><a href="https://www.aereco.co.uk/knowledge-centre/how-to-choose-between-a-humidity-controlled-mev-and-mvhr" target="_self" rel="nofollow">https://www.aereco.co.uk/knowledge-centre/how-to-choose-between-a-humidity-controlled-mev-and-mvhr</a><br /><br />In energy terms, "When the climate is temperate, the MVHR and the humidity sensitive MEV are almost equal."<br />Plus other comparisons on other criteria.]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307406#Comment_307406</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307406#Comment_307406</guid>
		<pubDate>Thu, 05 Dec 2024 12:58:36 +0000</pubDate>
		<author>sgt_woulds</author>
		<description>
			<![CDATA['Again, I'd appreciate a reference to Rickaby's statements, please'<br /><br /><br /><br />I remember he wrote about affordability and reliability of MVHR vs other forms of ventilation in Passive House + magazine - but their search function is useless and I cannot find it.<br /><br />The main points were the installation & maintenance costs of MVHR don't stack up against simpler, cheaper methods - for the majority of lower and middle-income householders with less efficient houses or those in rented accommodation.<br /><br />The small amount of heating costs saved vs additional heating costs from additional cold air volumes.<br /><br />Also factor in the need to replace control systems, fan motors, and proprietary filters outside warranty periods in 10 or so years - if this is anything like most modern products, (as I can attest to from my experience with the PV industry) those parts just won't be available.  <br /><br /><br />Most people already don't have a regular boiler service so we cannot magically expect them to start paying for filter changes, bearing replacements etc. so any MVHR is likely to become unhealthy and unreliable.  <br /><br />The 'average' person who doesn't understand - and doesn't want to understand - the ins-and-outs of maintaining their homes.  <br /><br />The average landlord or local council won't be much better - even if maintenance is legally mandated, it just won't happen for a variety of reasons.]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307407#Comment_307407</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307407#Comment_307407</guid>
		<pubDate>Thu, 05 Dec 2024 13:12:39 +0000</pubDate>
		<author>sgt_woulds</author>
		<description>
			<![CDATA[I should probably add that by 'healthy air', I meant good internal CO2 and moisture levels.<br /><br />'Smart' trickle vents and moisture-detecting extraction is simple and effective.  <br /><br />Most Trickle vents are rubbish however, even the 'smart' ones don't do enough to properly seal the penetrations and reduce the thermal performance of the whole window frame even when the vents are shut. <br /><br />With mine, I've sprayed foam into the frame to seal the window frame chambers before adding the vents.  This means that outside air is only able to pass through the relatively small slots, rather than circulating all around the window frame.]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307408#Comment_307408</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307408#Comment_307408</guid>
		<pubDate>Thu, 05 Dec 2024 13:30:21 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Last para - another priceless gem!]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307409#Comment_307409</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307409#Comment_307409</guid>
		<pubDate>Thu, 05 Dec 2024 13:48:10 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[&lt;blockquote&gt;&lt;cite&gt;Posted By: sgt_woulds&lt;/cite&gt;Passive House + magazine - but their search function is useless&lt;/blockquote&gt;<br />True, it's wierd. I may go thro my back issues for Rickaby articles.  'Peter Rickaby in Passive House + Plus magazine' in DuckDuckGo got a lot more. But PH+ Search did produce<br /><a href="https://passivehouseplus.co.uk/articles/ventilation/thin-air?highlight=WyJtdmhyIiwibXZocnMiLCJtZXYiXQ==" target="_self" rel="nofollow">https://passivehouseplus.co.uk/articles/ventilation/thin-air?highlight=WyJtdmhyIiwibXZocnMiLCJtZXYiXQ==</a><br />with some interesting insights.]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307416#Comment_307416</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307416#Comment_307416</guid>
		<pubDate>Fri, 06 Dec 2024 10:41:30 +0000</pubDate>
		<author>Doubting_Thomas</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: sgt_woulds</cite>Also factor in the need to replace control systems, fan motors, and proprietary filters outside warranty periods in 10 or so years - if this is anything like most modern products, (as I can attest to from my experience with the PV industry) those parts just won't be available.<br /><br /><br />Most people already don't have a regular boiler service so we cannot magically expect them to start paying for filter changes, bearing replacements etc. so any MVHR is likely to become unhealthy and unreliable.</blockquote><br /><br />Without wishing to prolong this bizarre MVHR pile-on, everything that you've listed there, with the possible exception of filters, applies equally to PIV, MEV and MVHR systems and to present it otherwise is a strawman argument. As soon as you introduce mechanical anything there is a maintenance burden from the tech that some people will buy into and others won't. Plenty of tech-averse and financially constrained people still manage to maintain their phone updates, car mechanics, replacement hoover bags etc. without civilization collapsing.<br /><br />At a very basic level the 'debate' between systems is really just whether or not you are recovering heat as it's leaving the building. Any incoming air will always need heating, whether via the space heating system or a heat exchanger. So the economics just come down to the cost of heating that air vs the components involved.<br /><br />At the moment heat and power is still relatively cheap compared to the cost of replacement parts. So ethics and carbon budgets etc. aside its still cheaper to piss away the warm air rather than recover it, but over time those factors may change.]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307418#Comment_307418</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307418#Comment_307418</guid>
		<pubDate>Fri, 06 Dec 2024 12:43:01 +0000</pubDate>
		<author>sgt_woulds</author>
		<description>
			<![CDATA[Hi Thomas,<br /><br />Don't take it personally, neither Tom nor I are saying there is anything wrong with MVHR as a technology - it produces fantastic results and I'd love to buy a house with MVHR fitted - as long as the previous owner had absorbed the upfront installation costs :-)<br /><br />Regarding maintenance, the examples you quote are not equivalent; phones update automatically, (until the manufacturer no longer supports the hardware and you are left with an unsecured device) so there is no need for user input.  Hoovers stop working with a full bag, so users are 'forced' to change them.  Cars require an MOT every year, skimping on servicing might mean a fail - so again, car users are forced to maintain them - although most do the bare minimum to scrape another year of mobility.<br /><br />In terms of maintaining cars out of warranty, it is already hard to find OEM parts for some vehicles made 15 years ago and repro parts can be overpriced and of a quality that is downright dangerous.  Luckily we still have a fairly good availability of parts from scrapped vehicles.  This won't be the case for MEV or MVHR units.<br /><br />My mum has a 35 year old boiler.  It has failed on 2 occasions in the last 20 years and generic parts have been available to replace it off the shelf for less than £25.  <br /><br />My brother has an 11 year old combi boiler which has needed replacement parts almost every year of service.  At the last visit the boiler man told him the control board he needed hadn't been made for two years and there were no NOS or repro parts available so the boiler needs replacing.  Obsolescence is built-in to all modern products and we don't have any 'right to repair' laws to protect consumers from sharp practices.<br /><br />They are both unusual because they have their boilers serviced under contract every year.  Mum's next-door neighbours have the same boiler and only have work done when it goes wrong.  I doubt she's had more than 4 call- outs in the same period.  I imagine most owners with a humming box in the loft will pay just as little attention to it until it goes wrong.<br /><br />So in 10 to 15 years customers with PIV, MEV, or MVHR will all likely face a bill for replacement units, but the MVHR owners will be left with a much larger hole in their wallet.<br /><br />I agree the cost of heat vs replacement parts is cheap - unfortunately, I don't see a future where that changes.  <br /><br />So yes, I agree with Rickaby, for most people the important thing will be to have healthy indoor air quality - peeing away heat will always be cheaper and easier.  <br /><br />Sad, but true.]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307420#Comment_307420</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307420#Comment_307420</guid>
		<pubDate>Fri, 06 Dec 2024 14:52:08 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Doubting_Thomas</cite>Any incoming air will always need heating, whether via the space heating system or a heat exchanger. So the economics just come down to the cost of heating that air vs the components involved.</blockquote>True - but a demand-controlled MEV will pull less air than a constant-rate MVHR when CO2/RH levels are low, possibly more air when they're exceptionally high, as demanded - but generally less. That feature is essential to MEV's justification.<br /><br />MEV's only electrical bit is the fan; no filters; the regulating input (habitable rooms) or extract (wet rooms) air-valves are mechanical, needing no maintenance, only when they fail.]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307421#Comment_307421</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307421#Comment_307421</guid>
		<pubDate>Fri, 06 Dec 2024 15:01:58 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: sgt_woulds</cite>11 year old combi ... control board he needed hadn't been made for two years and there were no NOS or repro parts available so the boiler needs replacing</blockquote>Just scrapped 8yr old Miele d/w and w m/c simultaneously, the w m/c for exactly that reason, the d/w because new pump would be £360. A firm in Sunderland claimed to repair control boards by return post, but failed after two attempts (lasted less than one cycle ea time). Miele f'crissake - superbly built, supposed to last forever, like a Mercedes. Which BTW our 23yr old 18mpg caravan-tractor does, parts available, at a price, prob no worse than any newer Merc parts.]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307423#Comment_307423</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307423#Comment_307423</guid>
		<pubDate>Fri, 06 Dec 2024 16:09:42 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: sgt_woulds</cite>So yes, I agree with Rickaby</blockquote>I don't know whether I agree with Rickaby or not, because nobody has been able to point me towards what he actually said!]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307424#Comment_307424</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307424#Comment_307424</guid>
		<pubDate>Fri, 06 Dec 2024 16:11:47 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: fostertom</cite>True - but a demand-controlled MEV will pull less air than a constant-rate MVHR when CO2/RH levels are low</blockquote>Compare like-for-like. If the MEV has a humidity sensor, then include one with the MVHR too!<br /><br />And lack of filtering is not a feature. Just as more dust and flies is not either.]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307425#Comment_307425</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307425#Comment_307425</guid>
		<pubDate>Fri, 06 Dec 2024 16:14:12 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[Oh and aren't rented properties required to have an annual boiler service as part of the gas safety regime? I suppose homeowners are supposed to be safety conscious enough to arrange it themselves, though I admit we never did. I'm much happier in a house with no fuels/combustion!]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307426#Comment_307426</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307426#Comment_307426</guid>
		<pubDate>Fri, 06 Dec 2024 16:32:41 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: djh</cite>Compare like-for-like. If the MEV has a humidity sensor, then include one with the MVHR too!</blockquote>I assumed any repectable MVHR would have one, but a different thing from the multiple humidity sensors of a demand-controlled MEV.<br /><br />The latter adjust individual rooms' flow rate, from zero/nominal to 'BOOST' depending on ea room's instantaneous humidity (as proxy also for CO2). Nett flow over time is then alleged to be lower than a MVHR's, thus alleged less elecricity consumed. This room-by-room economy measure is vital to the case for demand-controlled MEV vs MVHR.<br /><br />Whereas a MVHR, with or without a single humidity sensor in the mixed entry to the fan unit, must maintain a minimum flow that's adequate for the humidity/CO2 of the worst-case room, meaning wasteful for all the other rooms.<br /><br />Fairer to say would be "If the MEV has individual room control by multiple humidity sensors, then include similar individual room control with the MVHR too!"]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307427#Comment_307427</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307427#Comment_307427</guid>
		<pubDate>Fri, 06 Dec 2024 17:34:04 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[In my experience, humidity and CO2 even themselves out pretty rapidly by diffusion and the general air movement of an MVHR so I've never considered it worthwhile to think about per-room sensors. But then I've never bothered to fit even a single sensor, because I can't see any value in it.<br /><br />I turn the MVHR speed DOWN when I have a shower because I'm more concerned about increasing comfort than any risk of increased H2O. YMMV.]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307430#Comment_307430</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307430#Comment_307430</guid>
		<pubDate>Fri, 06 Dec 2024 18:15:58 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Not meaning to be adversarial - it's useful tho, bringing relative merits and differences to light.]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307431#Comment_307431</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307431#Comment_307431</guid>
		<pubDate>Fri, 06 Dec 2024 18:26:28 +0000</pubDate>
		<author>Victorianeco</author>
		<description>
			<![CDATA[Is there a decent schematic or layout for a decentralised system? I feel this suits our 4 bed property better than a MVHR setup as getting the ducting to every habitable room appears to be difficult with various steels and joists running direct directions in different rooms?]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307434#Comment_307434</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307434#Comment_307434</guid>
		<pubDate>Fri, 06 Dec 2024 20:07:29 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[With ventilation you need to get somebody who knows what they're doing to design a custom layout for your particular situation. IIRC we got a couple of designs done and one was OK so they got the business.]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307453#Comment_307453</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307453#Comment_307453</guid>
		<pubDate>Sun, 08 Dec 2024 01:57:22 +0000</pubDate>
		<author>Mike1</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: sgt_woulds</cite>The 'average' person who doesn't understand - and doesn't want to understand - the ins-and-outs of maintaining their homes.</blockquote>Sadly, it seems that many don't even know what they need to maintain.<br /><br />According to surveys reported in "Ventilation performance and end-user interaction: Comparison of natural and mechanical strategies in new-build social housing", by Gráinne McGill and Tim Sharpe:<br /><br />- in homes with dMEV and passive stack ventilation, only 56% of households were aware of the presence of trickle vents<br />- 93% of households stated that mechanical extract fans were present in their home, despite many utilising passive stack ventilation<br />- in homes with MVHR, 39% of households were unaware of the presence of boost switches<br /><br />- most dMEV systems had been turned off by the building occupants at the local isolator switch (due to being too noisy)<br />- in homes with adjustable vents, half of were found to be in the closed position<br /><br />As the authors say: Issues with end-user engagement and interaction in homes with dMEV and MVHR suggest significant advancements are required to ensure these systems are designed and installed in a way that is user-friendly, transparent, engaging and even captivating to building users.<br /><br />https://pureportal.strath.ac.uk/en/publications/ventilation-performance-and-end-user-interaction-comparison-of-na]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307458#Comment_307458</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307458#Comment_307458</guid>
		<pubDate>Sun, 08 Dec 2024 11:30:07 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[What's the situation in countries where good airtightness and mechanical ventilation have been around for a longer time? (I'm guessing places like Canada, Sweden, maybe Germany? et al)<br /><br />i.e. Is our problem due to lack of exposure to such situations, as well as apparently poor workmanship either in construction or maintenance?]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307462#Comment_307462</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307462#Comment_307462</guid>
		<pubDate>Sun, 08 Dec 2024 12:41:32 +0000</pubDate>
		<author>Victorianeco</author>
		<description>
			<![CDATA[djh: I have reached out to both BPC and Nuaire wo gave me some decent quotes for MVHR<br /><br />I will see what recommendation they come back with for decentralised options.<br /><br />If only they did a 50mm radial ducting system that would be the easiest solution for retrofit]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307469#Comment_307469</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307469#Comment_307469</guid>
		<pubDate>Sun, 08 Dec 2024 16:24:42 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Victorianeco</cite>If only they did a 50mm radial ducting system that would be the easiest solution for retrofit</blockquote>The problem with smaller diameter ventilation ducts is that you then require a faster flow speed to shift the same quantity of air. So most radial systems use 75 mm diamter. Even then we had to run two ducts in parallel to our kitchen extract point to get the required rate. Our ducts are 50 mm vertical and 100 mm wide.]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307480#Comment_307480</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307480#Comment_307480</guid>
		<pubDate>Mon, 09 Dec 2024 10:31:30 +0000</pubDate>
		<author>sgt_woulds</author>
		<description>
			<![CDATA["What's the situation in countries where good airtightness and mechanical ventilation have been around for a longer time? (I'm guessing places like Canada, Sweden, maybe Germany? et al)"<br /><br /><br /><br />My colleagues in Germany - who work in one of the healthiest and best-ventilated buildings in Europe, (breathable construction, all-natural low VOC building materials, active shading, MVHR) - still throw open all the windows and doors every few hours to practice purge ventilation.  A holdover from a historic practice first promoted in the '20's, (I think) to deal with the poor indoor air quality of mass housing at the time.  <br /><br />This ventilation strategy seems deeply ingrained in the German psyche and it is quite a shock to walk into a modern building in the middle of winter and find it as warm and welcoming as a Glaswegian bus stop.<br /><br />This isn't due to a lack of education - they know all about the building, (quite a few of them helped to design it!) -  but habits and perceptions hard-wired through repetition and indoctrination are hard to break. <br /><br />Luckily the MVHR controls are centralised and vent openings are fixed or I'm sure they'd be adjusting them.<br /><br />Humans are weird - whatever strategies are put into place to protect their health there will always be someone bloody-minded or ill-educated who will circumvent them.<br /><br />Witness the current crop of idiots taking selfies on the SS Richard Montgomery having passed warning buoys and signage warning of extreme explosive danger!]]>
		</description>
	</item>
	<item>
		<title>PIV vs dehumidifier</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307491#Comment_307491</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18242&amp;Focus=307491#Comment_307491</guid>
		<pubDate>Tue, 10 Dec 2024 18:34:54 +0000</pubDate>
		<author>Victorianeco</author>
		<description>
			<![CDATA[BPC Advised:<br /><br />By installing paired Single Room Heat Recovery units it is possible to provide cross flow ventilation through a room or rooms.<br />This utilised the principle of supply in one and exhaust out the other thereby providing a push/pull scenario of air movement.<br /><br />The paired units operated for a period of time in one configuration before swapping to the opposite direction providing a constant change in air direction, air freshness and heat recovery.<br /><br />With a property design utilising multiple Single Room Heat Recovery units, this should provide a full property ventilation solution and negate the requirement for natural ventilation methods such as wall passive vents and window vents (depending onfinal design and background ventilator reduction allowance to the calculations).]]>
		</description>
	</item>
	
		</channel>