<?xml version="1.0" encoding="utf-8"?>
	<rss version="2.0">
		<channel>
			<title>Green Building Forum - HELP NEEDED - Backboiler to Thermal store</title>
			<lastBuildDate>Sat, 27 Jun 2026 01:27:08 +0100</lastBuildDate>
			<link>https://www.greenbuildingforum.co.uk/newforum/</link>
			<description></description>
			<generator>Lussumo Vanilla 1.0.3</generator>
			<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308445#Comment_308445</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308445#Comment_308445</guid>
		<pubDate>Tue, 20 May 2025 12:32:09 +0100</pubDate>
		<author>Jacket84</author>
		<description>
			<![CDATA[Hi All,<br /><br />My first post so please bear with me . I joined the forum as looks like a lot of knowledge here with regard to these types of systems. Therefore hoping someone might be able to assist with the problem described below that I’m experiencing with my biomass heating system. To say I’m beyond desperate to get this fixed is probably an understatement. <br /><br />In summary, I had the system installed 2 years ago and it’s never worked properly. I have a 2200 litre Akvaterm thermal store which has the following circuits i.e. flow and return:  <br /><br />1. For the biomass cooker in my kitchen which has a 22kW back boiler (at about 80% efficiency so say 17kW)  the towel radiators in our ensuite bathroom, main family bathroom and spare bedroom ensuite are also on this circuit. <br />2. Central heating i.e. all other radiators in the house<br />3. Domestic hot water<br />4. For the oil boiler which I kept for redundancy / convenience <br /><br />The problem I'm experiencing in the winter months (i.e when I want to use it!) is that as the temperature of the store itself gets hotter, the water in the boiler of the biomass cooker itself  (32 litre volume) seems more and more prone to overheating and as a result the safety valve built in to the cooker (PRV?) is coming on and dumping the water out. The end result is that we can’t use the cooker to heat the store or we can but the fire is so small it can’t produce any meaningful heat to raise the overall temp in the store. I’m probably not describing this very well but it is like the water in the boiler of the cooker isn’t getting moved quick enough and sort of sits in the cooker.  <br /><br />Thankfully I got the installer to do a drawing of the system for me. See image below.<br /><br /><br /><br />I’ve tried to rack my brains as to what is causing this. The system is pressurised so I wondered if it was possibly the issue with the pump on the cooker return (above garage Black one as described on drawing above) either not being near enough to the cooker which is in the kitchen. Or an additional pump on the cookers flow near to the cooker itself is needed to more effectively pump the now heated water in the cooker’s boiler away quicker?  My other thought was is there  an issue with flow rate but the circuit from cooker to store/accumulator was put in at the same time as the store  and pipe work all looks to be same size however the cooker circuit also has our towel radiators in the rooms as per point 1 above so I wondered if the smaller dimension pipework on these could be causing the problem?<br /><br />Any help would be really, really appreciated.<br /><br />P.S. The store was actually sized with the idea of a second 40kW batch boiler being added, hence why it is so big.]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308446#Comment_308446</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308446#Comment_308446</guid>
		<pubDate>Tue, 20 May 2025 15:31:07 +0100</pubDate>
		<author>WillInAberdeen</author>
		<description>
			<![CDATA[The diagram didn't display (try shrinking it to a lower resolution, or posting it somewhere else and putting a link here)?<br /><br />It's important that the heat leak radiators connected directly to the stove are big enough to prevent boiling;  towel radiators sound quite small for such a powerful boiler. And the water should circulate through them by natural convection (heat rises) not by pumping, in case of power cuts. The system is usually vented IE not pressurised, to release any steam safely.<br /><br />These are important for safety and maybe are already covered by the diagram, but if not then maybe ask another installer to look?<br /><br /><a href="https://stovefitterswarehouse.co.uk/pages/heat-sink-radiator" target="_self" rel="nofollow">https://stovefitterswarehouse.co.uk/pages/heat-sink-radiator</a>]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308447#Comment_308447</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308447#Comment_308447</guid>
		<pubDate>Tue, 20 May 2025 16:05:06 +0100</pubDate>
		<author>Peter_in_Hungary</author>
		<description>
			<![CDATA[What controls the pump on the return to the cooker ?<br /><br />Are there any automatic controls on the cooker fire or is it all manual operation ?<br /><br />Edit to ask<br />What temp. is the store when the cooker over heats ?]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308448#Comment_308448</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308448#Comment_308448</guid>
		<pubDate>Tue, 20 May 2025 17:06:44 +0100</pubDate>
		<author>Jacket84</author>
		<description>
			<![CDATA[Hi both <br /><br />Thank you for your responses<br /><br />@WillInAberdeen The system is a sealed system with a thermal store the towel radiators are on the same circuit by chance really as the previous occupier had a small 3kw back boiler stove that heated hot water and the towel radiators IIRC. The store and the cooker itself have the relevant safety mechanisms should the water get too hot. Any suggestions where I can upload the images of my original post so they show up on here?  <br /><br />@Peter_in_Hungary the pump on the return to the cooker is controlled by a pipe state. I believe the temp in the bottom of the store when the cooker starts to struggle to get rid of the heat/overheat is about 40-45°C . However I  will double check my notes on that!]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308449#Comment_308449</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308449#Comment_308449</guid>
		<pubDate>Tue, 20 May 2025 21:20:13 +0100</pubDate>
		<author>Peter_in_Hungary</author>
		<description>
			<![CDATA[Jacket84<br />What is the temp. at the top of the store when the cooker starts to over heat ?<br /><br />Where is the pipe stat located ?<br /><br />Is the cooker connected to the store via a coil or is it direct ?]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308450#Comment_308450</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308450#Comment_308450</guid>
		<pubDate>Tue, 20 May 2025 21:42:59 +0100</pubDate>
		<author>Jacket84</author>
		<description>
			<![CDATA[Peter_in_Hungary I'll check but I think it's around 50-55°C<br />Pipe stat is actually on the cooker flow pipes I believe installer did this to create the same effects  as that of a laddomat . <br />By a coil do you mean a loop of pipe work before it comes back to the store?]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308451#Comment_308451</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308451#Comment_308451</guid>
		<pubDate>Tue, 20 May 2025 23:04:26 +0100</pubDate>
		<author>Peter_in_Hungary</author>
		<description>
			<![CDATA[By a coil I mean does the cooker go to a coil in the tank and so being an indirect connection.]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308452#Comment_308452</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308452#Comment_308452</guid>
		<pubDate>Wed, 21 May 2025 07:44:02 +0100</pubDate>
		<author>philedge</author>
		<description>
			<![CDATA[If the cookers back boiler is a pressurised system and the pressure relief valve is opening then either the cooker is boiling because the heat isn't being removed or the expansion vessel is undersized/faulty and can't absorb the expansion in the system.<br /><br />While the system is cold, depressurise it and check the expansion vessel is prepressurised. If that's OK, get your installer to double check the expansion vessel is large enough to absorb the system pressure increase as it warms up.<br /><br />If that's OK, depressurise the system and vent all the air out to make sure there's no air locks. There should be a vent point at the highest point in the cookers heating circuit.<br /><br />Further checks depend on whether the cooker circuit is gravity or pumped??]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308454#Comment_308454</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308454#Comment_308454</guid>
		<pubDate>Wed, 21 May 2025 09:31:37 +0100</pubDate>
		<author>WillInAberdeen</author>
		<description>
			<![CDATA[Just to be a bit clearer, it's usually* illegal in the UK and dangerous to have a solid fuel boiler on a sealed system. <br /><br />The building regs for sealed systems require two lines of defence against boiling: an electric safety overheat stat that instantly switches off the burner or immersion (separate from the normal temperature controller); and a mechanical safety valve as backup. The safety valve is like the airbags on a car, shouldn't ever go off!<br /><br />However, solid fires cannot be switched off electrically. So it's important to clarify if the boiler circuit is separate and open vented and exchanging heat with the TS by a coil.<br /><br />When the boiler was increased from 3kW to 22kW, the safety heat leak radiators should have been increased in proportion. Without this, the boiler will overheat frequently. Towel radiators are enough for a big boiler like this.<br /><br />The boiler needs to be able to circulate freely (including by gravity during a power cut), so the pipe sizes would also need to be increased in proportion to the 22kW to allow  heat to move to the store fast enough.<br /><br />Here's a useful guide<br /> https://solidfuel.co.uk/pdfs/central-heating-link-up.pdf<br /><br />Would really be good to get a specialist solid fuel boiler installer to check the system and modify as above. <br /><br /><br />*there are a very few solid fuel boilers that come with an automatic safety quench system that avoids the safety valve needing to open, but in this case that's not happening]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308455#Comment_308455</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308455#Comment_308455</guid>
		<pubDate>Wed, 21 May 2025 09:34:17 +0100</pubDate>
		<author>WillInAberdeen</author>
		<description>
			<![CDATA[Edit for correction! Towel radiators are NOT enough for a big boiler !]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308456#Comment_308456</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308456#Comment_308456</guid>
		<pubDate>Wed, 21 May 2025 09:44:56 +0100</pubDate>
		<author>Jacket84</author>
		<description>
			<![CDATA[@Peter_in_Hungary  no its direct to the store the only coil is for the domestic hot water <br /><br />@philedge 1 the original installer came a significant way from the north east to where I'm based in Cheshire to install this and has ghosted me since I attempted to get him to address the issues described, which is frustrating as the system cost me a significant sum of money to install.  It is interesting however that you mention the issue of the expansion vessel as several months ago I paid for another more local installer (who I didn't realise existed prior to the install else I would have commissioned him) visited and his opinion was that it was the expansion vessel not being large enough. I have just checked the gauges and the tow for the vessel are both reading as 0 bar however the two on the tank are also reading the same. I'm assuming this might be because the store is only programmed to come on in the summer when the tank drop to 35 degrees and heats back up to 40 degrees for our hot water needs]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308457#Comment_308457</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308457#Comment_308457</guid>
		<pubDate>Wed, 21 May 2025 09:50:26 +0100</pubDate>
		<author>Jacket84</author>
		<description>
			<![CDATA[WillInAberdeen the cooker with boiler does have the quench coil system you describe with a cold water feed that floods the boiler with cold whilst simultaneously discharging the hot water.]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308458#Comment_308458</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308458#Comment_308458</guid>
		<pubDate>Wed, 21 May 2025 10:05:05 +0100</pubDate>
		<author>philedge</author>
		<description>
			<![CDATA[AFAIK if its a pressurised  system, there should be pressure there when the system is cold so all your gauges reading 0 is likely incorrect....but that could be a legacy from the last time the cooker boiled and blew it's contents out through the relief valve??<br /><br />If your second installer thought the expansion vessel was undersized has that been remedied??]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308459#Comment_308459</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308459#Comment_308459</guid>
		<pubDate>Wed, 21 May 2025 11:06:05 +0100</pubDate>
		<author>WillInAberdeen</author>
		<description>
			<![CDATA[Did the quench coil not operate correctly? If it was working then the safety valve should not have opened?<br /><br />The accumulator in a sealed system is intended to cope with the water expanding a little, it gets a few litres bigger when hot. However if the system boils then the volume of steam created is a lot more than that, tens or hundreds of litres. No accumulator cannot cope with that much volume, hence the safety valve opens and dumping the system. <br /><br />Normally the safety valve should reclose at 3bar and leave at least some residual pressure in the system, but if there was still steam present that would later condense when the system cooled and the pressure would collapse to zero or vacuum.<br /><br />Can the second installer diagnose why the quench coil didn't work, and review the pipe sizes and safety heat leak radiators?]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308460#Comment_308460</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308460#Comment_308460</guid>
		<pubDate>Wed, 21 May 2025 12:24:49 +0100</pubDate>
		<author>Peter_in_Hungary</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: philedge</cite>If your second installer thought the expansion vessel was undersized has that been remedied??</blockquote><br />Yes, but an undersized expansion tank won't cause the cooker to overheat.<br /><br /><blockquote ><cite >Posted By: Jacket84</cite>no its direct to the store the only coil is for the domestic hot water</blockquote>Thats the cooker to store direct.<br />DHW on a coil and the rest direct (cooker and central heating) would be correct for the described system, so what is the expansion tank doing.<br /><br />There is a pump on the flow from cooker to the store so the pipework size whilst it may not be enough for gravity circulation I would expect a pump to be able to overcome pipe size deficiencies.<br /><br />Jacket84 said that the cooker starts to overheat with the store temp. at 55 deg. top and 45 deg. at the bottom should give enough capacity to takr additional heat <br /><br />Jacket84 Is the pump running on max ? Is it a usual central heating pump ?]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308461#Comment_308461</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308461#Comment_308461</guid>
		<pubDate>Wed, 21 May 2025 12:55:10 +0100</pubDate>
		<author>Jacket84</author>
		<description>
			<![CDATA[@philedge - Apologies the lack of pressure may be due to some recent new radiators we installed. I've re-pressurized the system now <br /><br />"If your second installer thought the expansion vessel was undersized has that been remedied??" No it hasn't. Mainly  just due to me being keen to avoid any further expenditure unless I think there's a good chance they will resolve the issue(s) faced.<br /><br />@will "Did the quench coil not operate correctly? If it was working then the safety valve should not have opened?" it did I was just under the impression they both operated in sync simultaneously]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308462#Comment_308462</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308462#Comment_308462</guid>
		<pubDate>Wed, 21 May 2025 13:03:50 +0100</pubDate>
		<author>Jacket84</author>
		<description>
			<![CDATA[@ Peter_in_Hungary yes I think its just a central heating pump its a Grundfos one and I'm sure in the past I've changed the speed to max to see if that helped]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308463#Comment_308463</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308463#Comment_308463</guid>
		<pubDate>Wed, 21 May 2025 19:15:56 +0100</pubDate>
		<author>GreenPaddy</author>
		<description>
			<![CDATA[attached, hopefully, are a system drwg and Therm Store photo, from Jacket84]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308464#Comment_308464</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308464#Comment_308464</guid>
		<pubDate>Wed, 21 May 2025 19:23:49 +0100</pubDate>
		<author>GreenPaddy</author>
		<description>
			<![CDATA[Ah Jeez, I give up with uploading to this website.]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308465#Comment_308465</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308465#Comment_308465</guid>
		<pubDate>Wed, 21 May 2025 19:31:54 +0100</pubDate>
		<author>GreenPaddy</author>
		<description>
			<![CDATA[try again <img src="/newforum/extensions/Vanillacons/smilies/standard/cry.gif" alt=":cry:" title=":cry:" />]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308466#Comment_308466</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308466#Comment_308466</guid>
		<pubDate>Wed, 21 May 2025 19:33:11 +0100</pubDate>
		<author>GreenPaddy</author>
		<description>
			<![CDATA[photo??]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308467#Comment_308467</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308467#Comment_308467</guid>
		<pubDate>Wed, 21 May 2025 19:33:57 +0100</pubDate>
		<author>GreenPaddy</author>
		<description>
			<![CDATA[WTF]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308468#Comment_308468</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308468#Comment_308468</guid>
		<pubDate>Wed, 21 May 2025 20:05:03 +0100</pubDate>
		<author>GreenPaddy</author>
		<description>
			<![CDATA[Initial thoughts;<br /><br />- I don't like using stats to control the switch on of pumps, as a fixed temp is not always appropriate. eg If the TS is 80oC, and the stat is set at 70oC, the pump will keep running, even with the oven off. I always use a differential controller. (that's not the issue here, but it's not good practice).<br />- the stat is on the return leg weirdly. The oven needs to heat the return pipe, initially by thermosyphon, or heat migrating up the return pipe. No likey.<br />- when the oven gets hot, even if the pump comes on, it will switch off quickly, as cooler water is drawn from the TS. That's going to lead to over-temp in the oven, and high pressure relief.<br />- the towel rad circuit could be taking all/most of the flow from the pump, if the press drop in that loop is less than the press drop thru the oven, starving the oven.<br /><br />I think the stat is wrongly located, and I don't like the the towel rad influence, but to confirm that, I would do the following;<br /><br />1.  set the stat ON temp to 0oC, which will make the pump run all the time.<br />2. shut off/down the towel rad circuit. This needs to be done with an isolation valve, not at the rad valves, as it's likely a flow&amp;bypass set-up. When you've done that successfully, the hot from the TS will flow through the oven (feel warm pipes in/out of oven), and NOT through the towel rad legs (stay cold) on flow and return at the branches with the oven.<br />3. Then run the oven, and keep eye on the flow and return pipes. If the flow (from the oven) gets way hotter than the return (to the oven via the pump), the flow rate is too low versus the heat input by the oven, so turn the pump speed UP. That should reduce the flow temp, to closer to the return temp.<br /><br />Try the above, to at least start to ID the problem. Then we can look at resolutions.]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308469#Comment_308469</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308469#Comment_308469</guid>
		<pubDate>Wed, 21 May 2025 20:10:20 +0100</pubDate>
		<author>Peter_in_Hungary</author>
		<description>
			<![CDATA[GreenPaddy<br />Probably too large !<br /><br />Jacket84<br />A standard CH pump should be fine. That is what is inside a Laddomat. However a pumped circuit from cooker to store even controlled by a stat. won't emulate a Laddomat The Laddomat function is to recirculate the wood burner water until up to temp. and then proportionally mixes the return and the recirculated water to maintain the stove (cooker) temp. (Oh and the Laddomat opens to allow gravity flow in the event of a power cut)<br /><br />That said a CH pump should give more than enough flow to move the heat from cooker to store and it won't matter where on the circuit the pump is placed providing there isn't a possibility of the pumped water short circuiting the cooker due to, say, preferential routes due to pipe resistances.  <br /><br />Much has been said above about heat leak rads. which is correct and should be rectified - but for the purposes of your problem solution not relevant as the store should be capable of taking the heat. (unless the heat leak rads provide a preferential short circuit. BTW what is the temp of the towel rail when the cooker over heats).<br /><br />When the heat leak rads. issue is addressed make sure that both the rads. and the cooker to store have a gravity circulation capability.<br /><br />Does the cooker to store have a gravity circulation now ?<br /><br />I am a bit concerned that you have a pressurised system with a solid fuel burner (echoing above comments) but another aspect could be the design capabilities of the cooker. What does the installation manual for the cooker say about the max. working pressure of the cooker and does it mention installing on a closed system ? (My wood burner boiler has a heat dump coil and a pressure relief valve but can't be used on a pressurised system) <br /><br />Silly question (perhaps) Is the cooker to store pump installed the right way around ?<br /><br />Are there any valves, non return or otherwise, in the cooker to store circuit ?<br /><br />What is the size of the cooker to store pipe work ?<br /><br />Has the store pipework been verified to ensure all the pipe connections are in the correct places ?<br /><br />Do you have an IR thermometer ? (V. useful to check pipe temps. when fault finding).]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308470#Comment_308470</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308470#Comment_308470</guid>
		<pubDate>Wed, 21 May 2025 20:17:59 +0100</pubDate>
		<author>Peter_in_Hungary</author>
		<description>
			<![CDATA[cross posted with GreenPaddy<br /><br />Jacket84 said the pump stat. is on the flow.<br /><br />However doing a test run and noting pipe temps. and forcing the pump to run has to be a starting point.]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308471#Comment_308471</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308471#Comment_308471</guid>
		<pubDate>Wed, 21 May 2025 20:49:59 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Peter_in_Hungary</cite>GreenPaddy<br />Probably too large !</blockquote>And maybe he tried to attach more than one image to a post? I think you have to attach the photo to a separate post. And it needs to be the corret size as PiH says. Less than 500k IIRC?]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308472#Comment_308472</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308472#Comment_308472</guid>
		<pubDate>Wed, 21 May 2025 23:02:48 +0100</pubDate>
		<author>WillInAberdeen</author>
		<description>
			<![CDATA[The pump is "above the garage" - is that an up+over pipe loop, that can trap a pocket of air? (Ours does that)<br /><br />Presume the heavy store and the kitchen cooker are down on ground floor in separate rooms, no syphon between them?<br /><br />The accumulator needs to be sized for 2000+litres system volume, a standard CH system accumulator isn't enough.<br /><br />Quench coil system should prevent overheat situation happening (like car brakes). It should prevent opening the safety valve - that reacts after situation is already happening (like car airbags).<br /><br />Hopefully (?) it is difficult to shut off the safety heat leak radiators, eg they shouldn't have thermostatic valves.]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308475#Comment_308475</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308475#Comment_308475</guid>
		<pubDate>Thu, 22 May 2025 09:55:37 +0100</pubDate>
		<author>philedge</author>
		<description>
			<![CDATA[If your going to do any testing you're likely going to need a fully filled and vented system so you've not got any vapour/air locks. If the cooker relief valve is venting as things heat up because the expansion vessel can't absorb the expansion then you're not going to have a fully filled system for long so probably need to sort out the expansion vessel sizing/function as a priority. A quick Google search suggests they aren't very expensive. You can replace what you've got or you can add a second unit to give enough volume for the size of the system you have]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308476#Comment_308476</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308476#Comment_308476</guid>
		<pubDate>Thu, 22 May 2025 11:46:24 +0100</pubDate>
		<author>Peter_in_Hungary</author>
		<description>
			<![CDATA[When testing get an instant read out thermometer e.g. an IR thermometer and build a small fire only to check flow temps. on the pipes. When testing turn the pump controlling stat. to ON and then check that the pump is actually running. Physically check the pump by unscrewing the large screw on the back of the pump and check for rotation. If the pump is not rotating then turn the pump by means of the screw slot in the armature. They do get stuck sometimes. Oh and a few drops of water come out when the inspection screw is removed.<br /><br />IMO careful testing with frequent monitoring during the test would not need the expansion vessel upgraded until the problem is found and a solution is planed. But be prepared to shut down the cooker or remove or douse the fire  if things start to get out of hand. Increasing the expansion vessel size won't do anything for the problem, it will just stop the over pressure valve from blowing off, which should not happen if the testing is sufficiently controlled.<br /><br />I still doubt that the cooker is capable of running a pressurised system as most solid fuel stoves are constructed from plate steel which is flat and won't take much pressure before bowing out of shape. Vessels designed to take pressure are almost always cylindrical. The cooker data needs checking. Akvaterm also make 2 types of stores, a 1,5 bar type for vented systems and a 3 bar for pressure systems - perhaps check this as well.]]>
		</description>
	</item>
	<item>
		<title>HELP NEEDED - Backboiler to Thermal store</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308478#Comment_308478</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18296&amp;Focus=308478#Comment_308478</guid>
		<pubDate>Thu, 22 May 2025 13:18:53 +0100</pubDate>
		<author>philedge</author>
		<description>
			<![CDATA[Once the PRV has vented one or more times, then that's going to leave a system with a void/vapour lock in it ie not 100% full. It seems to me that without knowing the physical layout of the pipework it's quite feasible that the void/vapour lock could stop or impede hot water circulation between the cooker and the store. That could lead to the cooker overheating, as is being reported. Seems to me that trying to test a system with potential voids/vapour/vacuum pockets in it is going to be problematic.<br /><br />@jacket84. When the system was first installed did the installer fire up the cooker and heat the store without any problems?]]>
		</description>
	</item>
	
		</channel>