			<item>
		<title>Assessment of EWI effectiveness in an 1890 house</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309226#Comment_309226</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309226#Comment_309226</guid>
		<pubDate>Sat, 13 Sep 2025 15:35:00 +0100</pubDate>
		<author>jam295</author>
		<description>
			<![CDATA[Hi all,<br /><br />A couple of years ago, we bought a two-storey 4-bedroom 1890 detached Victorian house in north-west England (108 sqm footprint, 350 sqm wall area) in need of substantial rennovation. We have replastered, replumbed and rewired the interior and it is now heated by a modern gas boiler and radiators, with wet underfloor heating for the kitchen-diner area. The exterior was rendered long ago, and the rendering is in extremely poor condition and needs to be replaced. At the same time as replacing the rendering, we are trying to decide whether to also add external wall insulation (EWI), as the walls are currently uninsulated. We would use breathable external wall insulation, and prefer a natural product such as wood fibre. We have quotes for (uninsulated) Ksystem TC15 Silicone Solo for the render (base, mesh, primer, silicone), which is marketed as "breathable".<br /><br />The house has "early cavity walls", so the cavity is only a few cm, and not wide enough for cavity wall insulation. We decided not to insulate internally due to worries about condensation forming in the walls. There is a loft, and a cellar under the front of the house.<br /><br />I have used the SapJS calculator at <a href="https://openenergymonitor.org/sapjs/" target="_self" rel="nofollow">https://openenergymonitor.org/sapjs/</a> and entered our building's properties, as best as I can estimate them. The modelled annual heating energy usage is about 48,000 kWh, which matches our actual annual usage (measured from gas bills) to within about 8%. I am somewhat skeptical that this is not a fluke, due to all the uncertainties involved, but for the moment let's assume it is roughly right. The model predicts 42% of total heat loss going through the walls.<br /><br />I used a current U-value for the walls of 1 W/m2K, based on the different layers (inner surface, plasterboard, timber battens/gap, inner leaf, air gap, outer leaf, render, outer surface). Bringing this down to 0.3 W/m2K with EWI to meet building regulations would reduce total heating energy usage to 33,000 kWh, and save about £1000 per year.<br /><br />Our motivations are not purely financial; we would also like to reduce our energy expenditure for environmental reasons, so even if it took a while to pay back, we would probably still do it, so long as the upfront cost (over and above the existing project cost of rerendering) was not prohibitive. <br /><br />Ideally, we would eventually like to install a heat pump and solar panels, but our understanding is that the heat pump would only be powerful enough if the house is well-insulated.<br /><br />My concerns are:<br />- My modelling with SapJS is a lay-person's calculation, and I would like to get this professionally assessed. The important question is "How effective will the EWI be?", because if it does not save significant energy, it is not worth doing.<br />- The house has many other heat losses, e.g. from draughts and uninsulated suspended floors in the front of the house. Does this reduce the effectiveness of the EWI, or is this an entirely decoupled problem?<br />- The wall cavities open at the top into the (cold) loft, and there are air bricks in the outer skin for ventilation to reduce moisture in the cavity. If the walls are left like this, then hot air will easily convect out of the top, presumably causing massive heat loss. We could seal the cavities at the top and block the air bricks, but will this cause problems with moisture/condensation? Could the cavity instead be vented internally? Since the cavity will now be warm, as it will be inside the insulation, maybe this is not a problem? Alternatively, could we fill the cavities, since now that they will be warm, interstitial condensation shouldn't be a problem?<br /><br />What sort of professional could I hire to give me the best advice, taking into account the particular nature of this old building, and all the "edge cases" that might be relevant to the decision? I have found companies who will do an energy assessment, but will this be careful and customised enough? I've heard that EPC assessments are often very rudimentary, and I need more than a basic tick-box exercise. Do I need an architect? Some sort of building engineer?<br /><br />How can I know whether the EWI installer will take proper care of all the junctions and edges, which I understand are vital for avoiding cold bridges? Do they need to worry about interstitial condensation?<br /><br />I would appreciate any advice that people here might have.]]>
		</description>
	</item>
	<item>
		<title>Assessment of EWI effectiveness in an 1890 house</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309227#Comment_309227</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309227#Comment_309227</guid>
		<pubDate>Sat, 13 Sep 2025 16:20:45 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: jam295</cite>What sort of professional could I hire to give me the best advice, taking into account the particular nature of this old building, and all the "edge cases" that might be relevant to the decision? I have found companies who will do an energy assessment, but will this be careful and customised enough? I've heard that EPC assessments are often very rudimentary, and I need more than a basic tick-box exercise. Do I need an architect? Some sort of building engineer?<br /><br />How can I know whether the EWI installer will take proper care of all the junctions and edges, which I understand are vital for avoiding cold bridges? Do they need to worry about interstitial condensation?</blockquote>Forget EPCs and people who do them. They have very little relevance, and a very poor reputation. My advice is to take your time, and make as many contacts as you can, and through them other contacts etc. Eventually you will find good choices, both for the overall design and for the EWI installation and any other work.<br /><br />Depending where you are in the north-west, you might start at somewhere like the Carbon Co-op in Manchester, or other places people might recommend.<br /><br />edit to add: you might also consider hiring an independent project manager/foreman to supervise all the details on-site if you feel worried about doing it yourself.]]>
		</description>
	</item>
	<item>
		<title>Assessment of EWI effectiveness in an 1890 house</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309228#Comment_309228</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309228#Comment_309228</guid>
		<pubDate>Sat, 13 Sep 2025 18:56:08 +0100</pubDate>
		<author>GreenPaddy</author>
		<description>
			<![CDATA[I did a very similar project for a client last year, same floor area, but less wall area (your wall area seems very large, being 3 times the footprint, usually about double).<br /><br />I'd say your numbers look about right, with a quick comparison to the heat loss calcs I did, though what window and floor Uvalues you used I don't know, which would alter the 42% number.<br /><br />Consider insulating under the floors if they are suspended timber, though perhaps you've refurbed internally already, so won't want to start lifting floors etc.<br /><br />Get a quote for the EWI, and compare it versus the render only quote. Then you'll know if it's worth considering financially. Your GAS heating makes the financial return case more tricky.<br /><br />The project I mentioned above were on electric storage heaters, so we installed an ASHP. The EWI brought the heat loss down by about 60%, and so the ASHP could be a large single phase, rather than a huge 3 phase. Gas cuts across all those considerations. That said, you mention possible future ASHP. Get your heatloss at 21oC delta T down to 7-8kW, and you're in ASHP teritory easily.<br /><br />Maybe consider polystyrene (EPS) EWI (get a quote at least, as well as the &quot;natural&quot; product). I suspect EPS will be substantially cheaper, partly due to material costs, but more so due to availablity of installers.<br /><br />Close off the wall vents, but maintain the floor vents (for suspended floors). Close off the cavity at the wall heads.]]>
		</description>
	</item>
	<item>
		<title>Assessment of EWI effectiveness in an 1890 house</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309231#Comment_309231</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309231#Comment_309231</guid>
		<pubDate>Sat, 13 Sep 2025 20:16:58 +0100</pubDate>
		<author>revor</author>
		<description>
			<![CDATA[I would get hold of a book called External wall Insulation by Christopher J Pearson. It is an excellent book full of detailed drawings. It will help you to understand more about the topic and help you with the conversations with potential installers. I suspect most installers will not have heard of the book never mind having read it.]]>
		</description>
	</item>
	<item>
		<title>Assessment of EWI effectiveness in an 1890 house</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309235#Comment_309235</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309235#Comment_309235</guid>
		<pubDate>Sun, 14 Sep 2025 09:13:36 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: jam295</cite>Bringing this down to 0.3 W/m2K with EWI to meet building regulations</blockquote>I wouldn't stop there, at that quite abitrary 'target'. Go all the way, in insulation thickness, to the optimum point of diminishing returns (by my rule of thumb, 200mm EPS or wood fibre), or alternatively to the calculated thickness reqd to achieve the Passive House target in the case of your particular house's configuration and climatic region. Thickness of the insulation boards makes up a small part of the total cost of a EWI project; making it a bit thicker or thinner has a quite affordable impact on the total cost.]]>
		</description>
	</item>
	<item>
		<title>Assessment of EWI effectiveness in an 1890 house</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309248#Comment_309248</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309248#Comment_309248</guid>
		<pubDate>Mon, 15 Sep 2025 10:01:43 +0100</pubDate>
		<author>Doubting_Thomas</author>
		<description>
			<![CDATA[If you have the details from your SAPjs inputs (wall thickness, materials etc.) I'd recommend setting up a free account and inputting them on this website: <a href="https://www.ubakus.de/en/u-wert-rechner/?" target="_self" rel="nofollow">https://www.ubakus.de/en/u-wert-rechner/?</a><br /><br />It's reasonably intuitive and with Google Translate on hand for the odd German term, you should be able to get a pretty decent idea of your u-values before and after adding insulation layers, along with an idea of drying time, environmental input and moisture risk***<br /><br />***Of course, as the calculator itself warns, this is only an estimate and the method used is simplified. But, it should give you a rough idea of the risk thresholds involved in insulating with different materials and to different targets. To be honest you probably don't want to be any more precise and 'on the line' at this stage anyway, as you'll need some real-world tolerance.<br /><br />Another endorsement for both Carbon Co-op (<a href="https://carbon.coop/" target="_self" rel="nofollow">https://carbon.coop/</a>) and People Powered Retrofit (<a href="https://retrofit.coop/" target="_self" rel="nofollow">https://retrofit.coop/</a>) as places to get professional advice. I'd also echo @fostertom's point above about doing more than just the minimum whilst you're already paying for the labour and scaffolding etc. <br /><br />Finally, a good supplier should be able to offer WUFI hygrothermal (moisture & heat) calculations for your property, which will take into account far more factors than the simple calculator I linked to above; and are worth asking for once you have a firmer idea of what you are going to do.]]>
		</description>
	</item>
	<item>
		<title>Assessment of EWI effectiveness in an 1890 house</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309475#Comment_309475</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309475#Comment_309475</guid>
		<pubDate>Fri, 10 Oct 2025 18:03:48 +0100</pubDate>
		<author>wookey</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: jam295</cite>Hi all,<br /><br />At the same time as replacing the rendering, we are trying to decide whether to also add external wall insulation (EWI), as the walls are currently uninsulated. We would use breathable external wall insulation, and prefer a natural product such as wood fibre. We have quotes for (uninsulated) Ksystem TC15 Silicone Solo for the render (base, mesh, primer, silicone), which is marketed as "breathable".<br />We decided not to insulate internally due to worries about condensation forming in the walls.<br /></blockquote><br />This is a good plan. I did the same thing (woodfibre+silicone render) on the front on my house. It's great.<br />There is a video about the project (and retrofit in general) here: https://wookware.org/house/retrofit/ (also on youtube).<br /><br /><blockquote ><br />I have used the SapJS calculator.<br />Bringing this down to 0.3 W/m2K with EWI to meet building regulations<br /></blockquote><br />Don't make your EWI that thin. Most of the cost is in the work. If you are doing it, do it properly. I had 160mm on the front, and 200mm on the side. These were dictated by the step-side of tiles (had to add one at the gable end), and the soffit overhang, and the requirement to get to EnerPhit or close. (which typically means U=0.15ish for walls)<br /><br />On calculators, SAPjs will give you some ballpark figures, but SAP is fundamentally a bit crap, because it is designed as a comparison tool, not a house model.<br /><br />PHPP is generally reckoned to be the best house model, but it is very detailed so either takes a long time or costs a lot (£300?) if paying someone else.<br /><br />The new Zebra model from Bath uni is a spreadsheet model like PHPP, but much simplified, whilst also remaining reasonably accurate. https://www.zebra-model.org/<br /><br />I've put my house though all three tools. Zebra and PHPP give results within 17% of each other. I don't have the SAPjs numbers to hand, but can dig them out.<br /><br /><br />There is also HEMS (UK govt proposed replacement for SAP at some point - a dynamic, rather than static,  model), espr (Strathclyde Uni)  and the US energyplus. I have not used these 3 seriously.<br /><br /><blockquote ><br />Ideally, we would eventually like to install a heat pump and solar panels, but our understanding is that the heat pump would only be powerful enough if the house is well-insulated.<br /></blockquote><br />Any house can be heated with a heatpump (or more), but if you do this EWI first (and maybe some other fabric improvements like airtightness) you will more than halve the size of HP needed. My house will have less than 10% of its original heating load when I'm finisihed with it - i.e. a 90+% drop.<br /><br /><blockquote ><br />My concerns are:<br />- My modelling with SapJS is a lay-person's calculation, and I would like to get this professionally assessed. The important question is "How effective will the EWI be?", because if it does not save significant energy, it is not worth doing.<br /></blockquote><br />EWI is generally excellent. Combined with decent windows, airtightness and loft/roof insulation it will make your house amazingly nicer to live in. A 90% reduction in heat load is a perfectly reasonable target. The EWI alone will not do all of that, but a decent chunk. the 42% number you got is plausible, especially if the glazed area is not too high.<br /><br /><blockquote ><br />- The house has many other heat losses, e.g. from draughts and uninsulated suspended floors in the front of the house. Does this reduce the effectiveness of the EWI, or is this an entirely decoupled problem?<br />- The wall cavities open at the top into the (cold) loft, and there are air bricks in the outer skin for ventilation to reduce moisture in the cavity. If the walls are left like this, then hot air will easily convect out of the top, presumably causing massive heat loss. We could seal the cavities at the top and block the air bricks, but will this cause problems with moisture/condensation? Could the cavity instead be vented internally? Since the cavity will now be warm, as it will be inside the insulation, maybe this is not a problem? Alternatively, could we fill the cavities, since now that they will be warm, interstitial condensation shouldn't be a problem?<br /></blockquote><br />As you have realised, the one significant risk is if the cavity has a gale blowing through it as that will 'bypass' the EWI and greatly reduce it effectiveness. So you do want to look at fixing holes into the cavity, and checking that the top edge is sealed. This report is excellent for understanding that issue: https://aecb.net/thermal-bypass-risks-a-passivhaus-report-by-mark-siddall/<br /><br />I sealed the tops of my cavities all round (not all at once - over several years). And my cavity was already filled (quite badly, big gaps, with fibreglass bits). The EWI worked very well indeed when only half the cavity-top was sealed, but I don't have air-bricks to let air in the bottom. <br /><br />Yes, once the house has a nice 'waterproof tea-cosy' on the outside, there is no reason not to fill cavity. Normally people put insulation in and up the U-value a bit, but it could be filled with something else to add to the internal thermal mass (which would make a very stable-temped building as you would have both leaves operating as internal thermal mass).<br /><br />The air-bricks need to stay so long as you have a suspended timber floor that is not being dried any other way, but make just sure that they only vent into the underfloor space, not into the cavity (just a plastic pipe through is all that is needed).  <br /><br /><blockquote ><br />What sort of professional could I hire to give me the best advice, taking into account the particular nature of this old building, and all the "edge cases" that might be relevant to the decision? I have found companies who will do an energy assessment, but will this be careful and customised enough? I've heard that EPC assessments are often very rudimentary, and I need more than a basic tick-box exercise. Do I need an architect? Some sort of building engineer?<br /></blockquote><br />You need someone who understands building physics. EPCs are indeed useless.<br />Try and find local retrofit professionals who are members of the AECB. Go along to your local group if it holds meetings and talk to them. There are job-titles, and qualifications, for this stuff e.g. 'retrofit designer'. And companies that specialise in it, e.g. '21 degrees' who are yorkshire-based and very competent.<br /><br />I would advise working out a whole-house plan, before embarking on any one stage of this. Once you have done a Zebra or a PHPP model for the house it gets much clearer how much the EWI, the windows, the suspendedn floor, the airtightness, the roof account for your heat losses, so you can start to make sensible plans about what you ought to do in the long term. I ended up doing new 3G windows and EWI at the same time because it's way better to do both and in that case it makes sense to do the windows first.<br /><br />The other thing you need to think about is what level of retrofit are you trying to achieve? AECB carbonlite (50kW/m2.a)? EnerPHit (25kWh/m2.a)? Something else? I always advise anyone to aim for at least carbonlite as a good basic standard for 'reasonable building'. If you current building is really using 48,000kWh/yr for a 108m2 footprint then that is a truly appalling 480kWh/m2.a. I think of 300 as 'really bad' so anything you do will be a huge improvement. But presuming you intend to stay for a few years, you don't want to be doing any of this twice, so get a handle on it to start with and make a plan.<br /><br />I started off aiming for carbonlite, but switched to EnerPHit part-way through when I realised it was possible, which is not ideal. I would have done a quicker and better job, and saved myself quite a lot of faff (it was mostly DIY) if I had realised this up-front.<br /><br /><blockquote ><br />How can I know whether the EWI installer will take proper care of all the junctions and edges, which I understand are vital for avoiding cold bridges? Do they need to worry about interstitial condensation?<br /></blockquote><br />If you employ a good retrofit company they will get this stuff right, but random EWI installers will not. The only way to be sure you get good results is learn enough to tell when you are being given bad advice/a bad job. You have clearly understood the basics pretty well. Now you just need some numbers and some details specific to your building. This forum will generally get you pretty good advice, but at some point you need to get a building-specific assessment, which you can do yourself, but will be a lot quicker and easier (but more expensive) if you get in some professionals who have done it before.]]>
		</description>
	</item>
	<item>
		<title>Assessment of EWI effectiveness in an 1890 house</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309598#Comment_309598</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309598#Comment_309598</guid>
		<pubDate>Sun, 09 Nov 2025 14:29:59 +0000</pubDate>
		<author>stonecold</author>
		<description>
			<![CDATA[<ref><ref>So, much of this including "breathable" EWI is what we have done, and I can tell you thinner EWI to 0.60 U made a dramatic and immediate difference... a local charity did a retrofit recommendations report in advance and like you it said 46% heat loss was from walls.<br /><br />However, the most cost-effective savings and damp improvements will almost certainly be MVHR with recirculating kitchen hood, switching from gas to induction hob, solar PV (payback 7-10 years with batteries), and a porch. Possibility chimney removal below roof level/above attic insulation. <a href="<a href="https://www.esru.strath.ac.uk/Documents/MSc_2015/MacLean.pdf" target="_blank" rel="nofollow">https://www.esru.strath.ac.uk/Documents/MSc_2015/MacLean.pdf</a>" >Maclean's study of Scottish EnerPHit retrofit cost effectiveness</ref> for different EWI measures, using the "pink house" as a case study was something we found later. Aldo EWI will make it far more comfortable, less damp and less drafty, which was a big comfort improvement.<br /><br />EWI is best done AFTER windows and doors because taking out the old ones really made a mess (internally)<br /><br />BTW LPG hobs (and possibly LPG cooker) causes lots of condensation, especially with an extractor fan. Moving to induction hob really improved this (£50 on eBay, still going strong 2 years later) but getting the electrics done for it cost quite a bit more!<br /><br />We used Diathonite Evolution by Diasen, calcs by distributor Ecological Building Systems but aI think it was 55 or 57mm Diathone Evolution over 500-600mm solid stone walls (approx 2.1 U valve), with a top code of Lime Green's Finish WP providing a lesser amount of insulation. A possibly cheaper option with the same U value is wood insulation eg Lime Green Warm Shell, Gutex, Pavatex (sp?). Our choice of Diathonite was influenced by the <a heef="<a href="https://www.ecologicalbuildingsystems.com/project-gallery/cumbrian-coastal-cottage-renovation" target="_blank" rel="nofollow">https://www.ecologicalbuildingsystems.com/project-gallery/cumbrian-coastal-cottage-renovation</a>" >case study of Percy Kelly's damp, cold house (PDF)</ref>.<br /><br />THERMAL MASS is a huge thing to be aware of, if you live in an area where heat waves make some nights really bad then any hgh thermal mass will mean that by the second night of the heat wave your nights will be warmer, which can make it harder to sleep (daytime peaks will be cooler but you might be at work/in the garden much of the time). Mostly for SE England especially cities high thermal mass will be bad - you could add EPS or similar IWI perhaps for bedrooms? But honestly in windswept cold very Northern England warmer nights in a heat wave aren't awful and the payback is toasty evenings and nights in winter. We have 0.60 U valves so much less than your plan).<br /><br />Unfortunately it was hugely expensive due to some costs that would have been needed anyway due to the poor condition of some walls and the dreadful state of the concrete render:<br />1. Removing the concrete render was expensive (75sq m floor area, 2 floors - I think 248sq m external walls), in some places it was blown or cracked but in some places there were several layers that were extremely difficult to remove and had to be done by hand<br />2. Poor condition of walls = dubbing coat labour, but the overall result on those walls was better<br />3. Walls need some dubbing to roughly level them in order to get the right EWI thickness when applying Diathonite - it is a flexible sprayed on insulation <br />4. Being a semi that was slightly staggered we had a party wall with a neighbor who understandably would not allow EWI on that wall because it would have encroached partly on their front garden, we also couldn't have 100mm plus EWI on the front because the house is right on the road (no pavement), but 57mm was ok<br />5. Skip costs of removing old concrete render, which had to be done since it was falling off<br />6. We didn't initially extend the roofline but it really needed doing, we needed a new roof so just did it then. Before that though rain was coming directly off the slates and down part of some walls.<br />7. Walls probably aren't straight and most likely buldge at the bottom so if you want rigid or semi-rigid EWI then you need them thickened at the top, ideally with more EWI but you can't always get it in narrow sizes, loose fill can be blown in but it can be tricky unless fitters use some kind of wet build-up coat and trowel it on<br />8. Building regs state an insulation level which would never achieve a 15 year payback for us, and the cost and benefits for damp were a big parr of oyr reason to use breathable EWI at 0.60 when initially we had wanted EneePHit.<br />9. For it to be vapour-open, any gypsum plaster internally on the external walls meeds replacing. Using Cornerstone insulating plaster/render and possibly thin IWI eg Diathonite Thermactive is extra labpur/disruption. We haven't done this but are finding massive improvements (no damp or condensation) although we also have MVHR put in a few months after.<br />10. Boiler flues need extending, although there isn't always an extension available so we just have a shorter flue protruding - we hope to move to heat pump perhaps next year.<br />11. If you are painting it you need a silicate paint eg Grapgenstone GCS Exterior or Earthborn silicate ones, plus primer, which costs plus probably labour cost (primer + 2 coats, which need enough time between them and the weather must be dry and not too hot so basically spring/autumn, and frustratingly slow.<br />12. EWI needs thermally broken fixings to avoid thermal bridges and the ones we got (EJOT hammer in) were not really compatible with things like EV charger brackets, external solar PV equipment (most people put in in their house or garage though), drainpipes, guttering etc. The house sign and letter box we fixed to wood and used thermal fixings on the wood.<br /><br />We found all breathable EWI was pretty much the same U value, around 0.44, so the choice came down to cost, labour cost, and rigid vs flexible. With such an old house none of the walls were straight horizontally OR vertically and trying to make it totally straight like you would for rigid eg EPS would change the character of the house and may be problematic around windows.<br /><br />Benefits:<br />- we are on oil so there isn't an energy price cap, so any reduction of heating costs is more dramatic for us, plus it is all in one go so £1000+ each time we need more oil with prices shooting up right before winter every single year<br />- Far less draughty<br />- We had Diathonite put on in an unusually warm early September and immediately noticed the change from 2.1 down to 0.60 U valve. <br />-- No need for vents in windows<br />- if you also have MVHR you can block bathroom/kitchen vents and get recirculation cooker hood, which for us meant the kitchen stayed warm<br />- you can do an airtight vapour control membrane under loft insulation but unless you have a MVHR before the EWI it will mean condensation <br />- oil cost savings are much more than for gas<br />- we had hot water on electric immersion heater so EWI reduced heat ss here, although tbh we should wrap extra insulation around it<br />- it is lime/clay/cork render so should flex rather than crack over time, is very easily repairable, and has NO AIR GAPS between EWI and the uneven walls <br />- significant damp and condensation causing black mould is the norm for old houses in this area, but ours is now soeted<br />- we didn't have a functioning dampproof course and 2 rooms are a bit below ground level, and now do not need tanking or DPC and the plaster is actually dry<br />- much faster to warm up the house<br />-we now have the heating on 20C instead of the 19C before (which was lower in some rooms)<br />- it is our forever home so cost vs sale value is less important than future running costs and comfort.<br />- with Diathonite if you ever do need to patch a bit you can order a bag and do it yourself, also true of the top coat line render if you aren't so bothered about the finish<br /><br />Evenings especially the house kept warm and if you wanted to stay up until 1-3am you don't need heating on again overnight with heating having gone off at 10pm and the final layer of EWI not on yet (0.69 U value). Thus is down to thermal.nass not just insulation. The kitchen had an extractor fan venting to outside and also has the main external door so this became a warmer room<br /><br />Final curing of Diathonite takes months but no change in temperature after.<br />We had MVHR fitted a few months after EWI and no more damp walls, condensation and black mpuld all killed off and hasn't returned.<br /><br />While much more expensive than expected, some re-rendering had to be done anyway, and the gains were much better than getting really good Internorm tilt and turn windows plus doors beforehand (we had double glazing previously).<br /><br />EWI has provided much more noticeable comfort than doing window and door triple glazing, MVHR than anything else.<br /><br />Our only issue is that the colored Lime Green top coat is showing some patches or a spider web effect where there isn't a dubbing coat, this only shows after heavy rain. This might not have happened if the internal plaster had been line or if a dubbing coat used throughout and wouldn't show if we had painted.<br /><br />BTW We aren't sure what the change in oil usage is because we had over half a tank left when we did the EWI. It is definitely less, and the house is noticeably warmer, and far more comfortable  Previous oil use was 24,500kwh (2,365L) plus 4,500kwh wood burner but was pared back to the minimum with some areas set to frost on TVRs, supplemented with wood burner (no longer needed), and this didn't even provide hot water. Electricity use overall is about the same despite changing LPG cooker and hobs to electric fan oven and induction hobs.</a></a>]]>
		</description>
	</item>
	<item>
		<title>Assessment of EWI effectiveness in an 1890 house</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309611#Comment_309611</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309611#Comment_309611</guid>
		<pubDate>Wed, 12 Nov 2025 21:44:21 +0000</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: stonecold</cite>For it to be vapour-open, any gypsum plaster internally on the external walls meeds replacing.</blockquote>I see this said a lot, but it is wrong. Gypsum plaster is vapour permeable, and so is paper-faced plasterboard. It's the aluminium facing on plasterboard that makes such sheets impermeable. Of course many types of paint and some wallpapers can also make a wall impermeable.]]>
		</description>
	</item>
	<item>
		<title>Assessment of EWI effectiveness in an 1890 house</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309613#Comment_309613</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309613#Comment_309613</guid>
		<pubDate>Thu, 13 Nov 2025 08:56:23 +0000</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Agreed.<br /><br /><blockquote ><cite >Posted By: djh</cite>the aluminium facing on plasterboard that makes such sheets impermeable</blockquote>Or polythene facing. These are examples of that phenomenon: effective enough to be a problem (when you want breatheability); feeble enough to be no use (when you want a vapour barrier).<br /><br />A shiny facing (also common on some breather felts) may add a bit to insulative value, but only if not dust coated, and 'looking at' free air space, which together are so unlikely in use as to be best avoided.<br /><br />The polythene facings were originally sold as vapour barriers, later demoted to 'vapour retarders' when the effect of unsealed joints and surface scrags were publicised, but a useless concept, as in first para above.]]>
		</description>
	</item>
	<item>
		<title>Assessment of EWI effectiveness in an 1890 house</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309624#Comment_309624</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309624#Comment_309624</guid>
		<pubDate>Fri, 14 Nov 2025 09:24:37 +0000</pubDate>
		<author>Doubting_Thomas</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: stonecold</cite>So, much of this including "breathable" EWI is what we have done, and I can tell you thinner EWI to 0.60 U made a dramatic and immediate difference...</blockquote><br /><br />Just wanted to say thank you @stonecold for writing such a comprehensive post. It echoes a lot of what I've heard on here and through others in the industry and it should prove useful for others.]]>
		</description>
	</item>
	<item>
		<title>Assessment of EWI effectiveness in an 1890 house</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309629#Comment_309629</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309629#Comment_309629</guid>
		<pubDate>Mon, 17 Nov 2025 09:15:01 +0000</pubDate>
		<author>WillInAberdeen</author>
		<description>
			<![CDATA[+1, great writeup.<br /><br />Fitting EWI is a good chance to fit nest cavities for bats and Swifts - we tend to block up the nooks and crannies at the roofline of old houses, but easy to provide replacement nest holes, like this one specifically to go in EWI<br /><br /><a href="https://actionforswifts.blogspot.com/2021/03/pvc-nest-boxes.html?m=1" target="_self" rel="nofollow">https://actionforswifts.blogspot.com/2021/03/pvc-nest-boxes.html?m=1</a>]]>
		</description>
	</item>
	<item>
		<title>Assessment of EWI effectiveness in an 1890 house</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309630#Comment_309630</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18350&amp;Focus=309630#Comment_309630</guid>
		<pubDate>Mon, 17 Nov 2025 09:58:28 +0000</pubDate>
		<author>WillInAberdeen</author>
		<description>
			<![CDATA[I'm halfway through IWiing a stretch of stone wall using breathable wood fibre boards with gypsum plasterboard as surface finish. IWi because I can't afford EWI. The plasterboard is because I can't get a lime plasterer and I don't have the lower back strength to do it myself! The supplier did wufi modeling before hand. <br /><br />The buildup is: stone wall; existing lime plaster patched many times; wood fibre boards temporarily mech fixed; intello airtight membrane; battens mech fixed through to stone; wood fibre between battens; plasterboard taped and filled <br /><br />Materials cost about £60/m2 from a small/helpful/expensive supplier, could get cheaper online.Will write it up if I get round to it.<br /><br /><br /><br />'Breathable' can mean different things which causes confusion:<br /><br />- ability for moisture vapour to pass through (SD and mu value) - gypsum and lime plasters are similar <br /><br />- ability to adsorb, store and release water vapour - lime may be better, wood fibre is best<br /><br />- wicking ability to transport moisture from damp to dry areas - lime and wood fibre for the win here<br /><br />- retention of structural properties when damp and redried - gypsum not great, goes mushy]]>
		</description>
	</item>
	
		</channel>
	</rss>