		<author>john.connett</author>
		<description>
			<![CDATA[<p >My house in Cambridge had a low energy renovation around 15 years ago with triple glazing, increased thermal insulation, solar thermal system, thermal store and MVHR. The MVHR unit is a Vent-Axia Sentinel Kinentic BH.</p> <br /><p >For most of the time since it was installed it has worked very well and I rarely needed to open any of the windows. However, during the recent Amber Heat Alert the house overheated badly. Possibly the high humidity made it worse than in earlier years or my age and, maybe medication, made me less resilient.</p><br /><p >My suspicion is that during an extended heatwave with tropical nights the MVHR is unable to maintain comfortable indoor temperatures. With or without a summer bypass, if the air temperature is over 35º C outside then the MVHR will import that air. Even if the air temperature drops lower overnight it can't catch up and the house continues to retain the heat, made worse by the high quality of thermal insulation.</p><br /><p >Some form of air cooling may be required! My back garden is nowhere near big enough for a ground-coupled heat exchanger so active cooling may be an option.</p><br /><p >I have seen an example where a reversible heat pump was connected to a water/air duct heat exchanger (eg. Zehnder ComfoPost). However, my house has a gas boiler.</p><br /><p >Has anyone else experienced similar problems or can suggest possible solutions?</p>]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310929#Comment_310929</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310929#Comment_310929</guid>
		<pubDate>Thu, 02 Jul 2026 14:43:16 +0100</pubDate>
		<author>Mike1</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: john.connett</cite>With or without a summer bypass, if the air temperature is over 35º C outside then the MVHR will import that air.</blockquote>That may depend on the sophistication of the MVHR unit. My Zehnder cools the incoming air down to a set temperature using the cooler outgoing air, if that's cooler than the incoming air. For the summer, I've adjusted the set temperature down to the minimum 12°C, rather than the default 22°C to take full advantage of any cooler outside air - check your MVHR manual as you may be able to do the same.<br /><br /><blockquote ><cite >Posted By: john.connett</cite>I have seen an example where a reversible heat pump was connected to a water/air duct heat exchanger (eg. Zehnder ComfoPost).</blockquote>Unfortunately air has a low specific heat capacity, so you need to move lots of air to make a big difference - more than an MVHR unit typically handles.<br /><br />Because I had no other viable option, I've installed a HomEvap adiabatic cooler before my MVHR but, even though I can achieve >1 air change per hour, the limited airflow means that it can only provide a few hundred Watts of cooling, even though it does a good job cooling the incoming air (yesterday afternoon from 30°C to 23°C within the MVHR unit). It's enough to somewhat slow the temperature increase in the rooms, but nowhere near enough to reverse it (well, maybe in a Passivhaus with an oversized MVHR unit it might, some of the time).<br /><br /><blockquote ><cite >Posted By: john.connett</cite>My suspicion is that during an extended heatwave with tropical nights the MVHR is unable to maintain comfortable indoor temperatures.</blockquote>If the air is so hot that the building doesn't have chance to cool, as in an extended heatwave, that's a problem that can only be solved by active cooling - typically air conditioning or chilled underfloor central heating. I have the same problem as I have nowhere to install a heat pump.<br /><br />Ceiling-mounted fans are on my list for next year, once my new electrical system is up an running. They can make a room feel significantly cooler, even if the temperature is unchanged, and are well worth considering - much quieter, more effective and energy efficient than desk fans.]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310930#Comment_310930</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310930#Comment_310930</guid>
		<pubDate>Thu, 02 Jul 2026 15:50:20 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[I agree with pretty much everything both John and Mike have said.<br /><br />The summer bypass on my MVHR automatically turns on whenever the outside air is cooler than the inside air and the inside air is warmer than a set point. It turns off if the outside air is warmer than inside.<br /><br />When the air doesn't cool much overnight, the inside does begin to heat up and there's not much the MVHR can do. Even if the summer bypass opens, there isn't a large enough temperature difference between outside and inside to provide much cooling effect.<br /><br />Thermal insulation is generally a good thing, since it slows heat gain when it's hot outside and heat loss when it's cold outside.<br /><br />Ceiling fans are a very good idea. Most houses in tropical areas had them before air-conditioning and many still have them. High ceilings also help.<br /><br />And yes, air-conditioning is a very effective technique.]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310931#Comment_310931</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310931#Comment_310931</guid>
		<pubDate>Thu, 02 Jul 2026 20:34:50 +0100</pubDate>
		<author>WillInAberdeen</author>
		<description>
			<![CDATA[As all said, a Sentinel MHRV doesn't move enough air to control the temperature (not what it's intended for).<br /><br />If the overnight or early morning outside air is cooler than inside, then open all the windows wide to get very large volumes of cooler air through and cool the fabric.<br /><br />If it isn't, then active cooling is required. <br /><br />Actually for the OP in Cambridge with health issues I would not hesitate to get AC, whether portable or fixed. It used to be looked down on as a damaging luxury (by folk who had no such issues with heating!) but this summer there have been record amounts of solar on the grid, so even if a home doesn't have own PV there is plenty of low carbon daytime electricity for AC. <br /><br />Might still want to avoid running it in the evening peak (if possible) for a couple more years, or get a home battery. Overcool the house during daylight hours to take it through the evening.]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310932#Comment_310932</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310932#Comment_310932</guid>
		<pubDate>Thu, 02 Jul 2026 23:19:57 +0100</pubDate>
		<author>Mike1</author>
		<description>
			<![CDATA[A couple of further comments on this:<br /><br /><blockquote ><cite >Posted By: john.connett</cite>My back garden is nowhere near big enough for a ground-coupled heat exchanger</blockquote>A garden isn't necessary; I've seen a vertical borehole drilled through the floor of a plant room in a London home. It would, however, cost several time the cost of an air source heat pump / aircon unit.<br /><br /><blockquote ><cite >Posted By: Mike1</cite>I've installed a HomEvap adiabatic cooler before my MVHR but...</blockquote>Another 'but' is that you need to have insulated the air distribution ducts & accessories for this to stand a chance, or the cooled air may well have warmed again before it reaches the ceiling vents. I'm loosing 2 to 3°C on mine, but I haven't yet insulated the manifold nor the main duct from the MVHR unit.]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310934#Comment_310934</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310934#Comment_310934</guid>
		<pubDate>Fri, 03 Jul 2026 09:23:13 +0100</pubDate>
		<author>Cerisy</author>
		<description>
			<![CDATA[Our 16 year old Titon unit is fine for most of the year but the summer bypass function is useless in our set up.  In these heat waves (we live in Normandy and recorded a temperature over 41 degrees!) I switch the MVHR unit off during the day with all the windows and upstairs shutters closed.  When the outside temp in lower than in the house I’ll open windows to draw some cooler air through.<br /><br />However at our mid-70’s ages we struggle seriously with the heat and humidity so I had A/C installed for the main lounge and our bedroom.  Not cheap but essential.  We got through the last heatwave okay.  Our son who lives nearby is going for ceiling fans - look a good option and way cheaper!!]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310936#Comment_310936</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310936#Comment_310936</guid>
		<pubDate>Fri, 03 Jul 2026 10:19:33 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Cerisy</cite>Our 16 year old Titon unit is fine for most of the year but the summer bypass function is useless in our set up.  In these heat waves (we live in Normandy and recorded a temperature over 41 degrees!) I switch the MVHR unit off during the day with all the windows and upstairs shutters closed.  When the outside temp in lower than in the house I’ll open windows to draw some cooler air through.</blockquote>Summer bypass can't work when it is hotter outside than inside. In those circumstances the best an MVHR can do is to bring the heat exchanger back into the circuit which makes the supply air a little bit cooler than the air outside. Air con is as you say the only real solution, although fans do help somewhat.]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310945#Comment_310945</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310945#Comment_310945</guid>
		<pubDate>Sun, 05 Jul 2026 12:43:22 +0100</pubDate>
		<author>john.connett</author>
		<description>
			<![CDATA[<p >Many thanks for the replies. Very useful!</p><br /><blockquote ><cite >Posted By: Mike1</cite><blockquote ><cite >Posted By: john.connett</cite>With or without a summer bypass, if the air temperature is over 35º C outside then the MVHR will import that air.</blockquote>That may depend on the sophistication of the MVHR unit. My Zehnder cools the incoming air down to a set temperature using the cooler outgoing air, if that's cooler than the incoming air. For the summer, I've adjusted the set temperature down to the minimum 12°C, rather than the default 22°C to take full advantage of any cooler outside air - check your MVHR manual as you may be able to do the same.</blockquote><br /><p >My Vent-Axia Sentinel Kinentic BH is essentially a stand-alone MVHR. It is located in an insulated loft space with a mains power switch and front panel controls. It does have a remote on/off boost switch which is turned on when the fan in my kitchen cooker hood is running. There may be other controls inside the MVHR but I am reluctant to tamper with them.</p><br /><p >A more sophisticated MVHR might have a wider set of controls and report data that might help understand its operation. If, for example, it was linked to an indoor air quality sensor it could reduce the air flow during extreme hot weather while keeping CO2 below 800 ppm. Maybe even stopping if the house was unoccupied.</p><br /><blockquote ><cite >Posted By: Mike1</cite>I've installed a HomEvap adiabatic cooler before my MVHR</blockquote><br /><p >I wasn't aware of devices like the HomeEvap Cooler adiabatic evaporative cooler (<a href="<a href="https://www.homevap.nl/en/overview-cold-humidification/homevap-cooler/" target="_blank" rel="nofollow">https://www.homevap.nl/en/overview-cold-humidification/homevap-cooler/</a></a" >). Their website states "The HomEvap Cooler is limited by the duct sensor mounted after the Cooler in the duct. This measures the RH in the duct and will switch off the unit when the RH exceeds 85%.". It's possible that it would be less effective during conditions like the Amber Heat Alert from 22/06/2026 to 28/06/2026 when there was both high temperatures and high RH. Here's a Weather Archive Cambridge International Airport (<a href="<a href="https://www.meteoblue.com/en/weather/historyclimate/weatherarchive/cambridge-international-airport_united-kingdom_6296643?fcstlength=15&year=2026&month=6" target="_blank" rel="nofollow">https://www.meteoblue.com/en/weather/historyclimate/weatherarchive/cambridge-international-airport_united-kingdom_6296643?fcstlength=15&year=2026&month=6</a></a" >) covering that time.</p><br /><p >I have a portabe Bosch UniversalFan that runs on a POWERFOR ALL 18V battery which has been very useful! No trailing lead to trip over. However, fans become less effective with high RH and when temperatures approach body heat.</p><br /><p >Portable AC might be a challenge with my Passivhaus specification doors and inward opening tilt/turn windows.</p><br /><p >I will continue to investigate possible solutions.</p></a></a>]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310947#Comment_310947</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310947#Comment_310947</guid>
		<pubDate>Sun, 05 Jul 2026 14:02:53 +0100</pubDate>
		<author>Mike1</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: john.connett</cite>The HomEvap Cooler... ...[may be] less effective during conditions like the Amber Heat Alert from 22/06/2026 to 28/06/2026 when there was both high temperatures and high RH.</blockquote>Yes, that was the case here. And, although the cooler discharges the humidified air outside, the incoming moist air cools so its humidity rises too - it pushed internal HR above 50%, which was undesirable (for comparison, at the moment it's around 35% inside, 24% outside). If that became a regular occurrence then a dehumidifier could resolve both issues (increasing cooling and cutting internal humidity), subject to its heat output being low.<br /><br /><blockquote ><cite >Posted By: john.connett</cite>My Vent-Axia Sentinel Kinentic BH is essentially a stand-alone MVHR. It is located in an insulated loft space with a mains power switch and front panel controls. It does have a remote on/off boost switch which is turned on when the fan in my kitchen cooker hood is running. There may be other controls inside the MVHR but I am reluctant to tamper with them.</blockquote>You should be able to control everything through the front panel controls. Looks like the instructions are here: https://asset.eezybridge.com/nc/ba7b9546-29dd-40c4-87a7-885627281b87/442073.pdf which seem to include an option to vary the target indoor temperature (below) - if you have a summer bypass fitted.]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310949#Comment_310949</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310949#Comment_310949</guid>
		<pubDate>Sun, 05 Jul 2026 16:18:38 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: john.connett</cite>Maybe even stopping if the house was unoccupied.</blockquote>My Brink unit has a minimum setting marked '0' that is actually 50 m³/hr and is meant for use when the house is unoccupied. I think it's designed to stop the air becoming stale. I sometimes use it when I'm alone in the house.]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310950#Comment_310950</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310950#Comment_310950</guid>
		<pubDate>Sun, 05 Jul 2026 17:02:32 +0100</pubDate>
		<author>john.connett</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Mike1</cite>You should be able to control everything through the front panel controls. Looks like the instructions are here: https://asset.eezybridge.com/nc/ba7b9546-29dd-40c4-87a7-885627281b87/442073.pdf which seem to include an option to vary the target indoor temperature (below) - if you have a summer bypass fitted.<div class="Attachments" id="Attachments_310947" ><ul ><div ></div></ul></div></blockquote><br /><p >Mine looks similar. The Start Up screen displays<br ><br />Sentinel Kinetic V09<br ><br />Language: English<br ><br />Airflow Units: %<br ><br />Wireless Control: Not Fitted<br ><br />Humidity Sensor: Fitted<br ><br />Note there is no "Control Mode". The firmware may be old. No Internet connection for Over-The-Air updates. The User Mode screen displays<br ><br />Normal Airflow<br ><br />Clock (set to British Summer Time)<br ><br />Indoor Temp: 25 C<br ><br />Note there is no "Outdoor Temp" which, I guess, defaults to 14 C.</p>]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310951#Comment_310951</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310951#Comment_310951</guid>
		<pubDate>Sun, 05 Jul 2026 18:03:45 +0100</pubDate>
		<author>GreenPaddy</author>
		<description>
			<![CDATA[John,<br /><br />I've installed a number of these same units ofver the years, and written up "idot's guides" for my clients. Looking back at these, I note that there is NOT an OUTDOOR TEMP screen per-se, however if you follow this it should bring you to the OUTDOOR TEMP settable value...<br /><br />at INDOOR TEMP screen press SET to choose the required inddor temp.<br />press SET button again to confirm the set value, which brings you to the OUTDOOR TEMP setting.<br /><br />The revision I have (maybe 10 years ago or more) says that the range is 5oC to 20oC (14oC default)<br /><br />To be honest, I suspect the high overnight temps you were experiencing were probably above 14oC anyway, so would not have influenced the bypass operation, but still worth dropping that OUTDOOR TEMP value, just in case.<br /><br />Following W-i-A advice to open all doors and windows early morning for several hours till say 10am works well for us, but being in Scotland, the 15oC night to 28oC day temps are quite different to further south being much higher for both.]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310983#Comment_310983</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310983#Comment_310983</guid>
		<pubDate>Fri, 10 Jul 2026 20:08:16 +0100</pubDate>
		<author>Artiglio</author>
		<description>
			<![CDATA[Very Heath Robinson and only suitable for one room ( handy if you want to make a bedroom a bit more comfortable)<br /><br />Freeze a five litre container of water, stand it in a washing up bowl or similar ( to catch the condensation) set up a fan to blow over it. Keep door and windows shut. Not going to work wonders , but makes a difference, mainly i expect by lowering the humidity.]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310984#Comment_310984</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310984#Comment_310984</guid>
		<pubDate>Sat, 11 Jul 2026 17:01:00 +0100</pubDate>
		<author>WillInAberdeen</author>
		<description>
			<![CDATA[I was playing with using ice to shift heat/cooling load from day to night, but found <br /><br />1) every kWh of cold you get from an ice block is matched by an extra kWh-and-a-bit of heat that comes out of the fins on the back of the freezer. So unless the freezer is outdoors, the net effect is the house gets hotter.<br /><br />2) the heat/cold stored in a kg ice is actually not that much - about 0.1 kWh - one-seventh as much as in a kg of water vapour. So you need a lot of kg of ice to have much effect on room temperature, or to condense much water vapour.<br /><br />3) ice doesn't conduct heat very well from the air so takes a long time to cool things in air (much quicker in water). A five litre bottle has 0.15m2 surface area and gives about 30W of cooling.<br /><br />4) domestic freezers are not very powerful, can freeze about one 5kg ice block each day.<br /><br /><br /> The second best way to use ice for cooling is to put ice and water in a hot water bottle, wrap it in a towel and take it to bed. The best way to use ice for cooling is to drink it!<br /><br /><br />My original idea was to freeze ice blocks in the freezer on cheap overnight electric, and then put them in the fridge so it didn't have to use electricity or give out heat during the daytime. But wasn't really worthwhile.]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310987#Comment_310987</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310987#Comment_310987</guid>
		<pubDate>Mon, 13 Jul 2026 14:48:48 +0100</pubDate>
		<author>john.connett</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: GreenPaddy</cite>John,<br /><br />I've installed a number of these same units ofver the years, and written up "idot's guides" for my clients. Looking back at these, I note that there is NOT an OUTDOOR TEMP screen per-se, however if you follow this it should bring you to the OUTDOOR TEMP settable value...<br /><br />at INDOOR TEMP screen press SET to choose the required inddor temp.<br />press SET button again to confirm the set value, which brings you to the OUTDOOR TEMP setting.<br /><br />The revision I have (maybe 10 years ago or more) says that the range is 5oC to 20oC (14oC default)</blockquote><br /><p >Many thanks! The description in the manual of <b >Normal Mode</b>, <b >Evening-purge Mode</b> and <b >Night-time purge Mode</b> is interesting. It looks like the MVHR is trying to respond well given the limited information available to it (time, temperature sensors, temperature setpoints, humidity ). Unfortunately, there appears to be no easy way for it to report these parameters. A smarter MVHR might be able to report more about its operation and, perhaps, use input from a CO2 sensor</p><br /><blockquote ><cite >Posted By: GreenPaddy</cite>To be honest, I suspect the high overnight temps you were experiencing were probably above 14oC anyway, so would not have influenced the bypass operation, but still worth dropping that OUTDOOR TEMP value, just in case.<br /><br />Following W-i-A advice to open all doors and windows early morning for several hours till say 10am works well for us, but being in Scotland, the 15oC night to 28oC day temps are quite different to further south being much higher for both.</blockquote><br /><p >Although Cambridge was only in the <b >Amber Heat Alert</b> area the combination of high temperatures and humidity together with tropical nights were extremely difficult! The local <b >Heatwave Threshold Daily Maximum Temperature</b> (<a href="<a href="https://www.metoffice.gov.uk/about-us/news-and-media/media-centre/weather-and-climate-news/2022/heatwave-threshold-changes" target="_blank" rel="nofollow">https://www.metoffice.gov.uk/about-us/news-and-media/media-centre/weather-and-climate-news/2022/heatwave-threshold-changes</a>" >UK Climate Change in action</a>) is 28oC. Today is the first day that is likely to stay below that for some time! Tomorrow is forecast to be above again. If that continues for three days then that's another heatwave.</p><br /><p >The recent heatwave has been more manageable! I have opened the windows when the outside temperature is lower and closed them, starting on the south side, once the outside temperature is higher. I have also tried turning off the MVHR during the time when the windows are closed and monitoring the CO2 level. It gradually rose but did not go above 1000ppm. Yesterday, I left the MVHR running and didn't notice any adverse heating.</p><br /><p >My house is not certified to EnerPHit but has similar features. I saw <a href="<a href="https://www.linkedin.com/pulse/how-we-keep-enerphit-home-cool-during-heatwave-richard-dudzicki-qiuie" target="_blank" rel="nofollow">https://www.linkedin.com/pulse/how-we-keep-enerphit-home-cool-during-heatwave-richard-dudzicki-qiuie</a>" >How We Keep an EnerPHit Home Cool During a Heatwave</a>. I don't have space for an awning but was doing roughly the equivalent. The author dodges the question of "whether Passive Houses overheat"! I think that the answer is that for EnerPHit the frequency of overheating (over 25oC) must be a maximum of 10% of the time.</p><br /><p >I think EnerPHit designates East Anglia as having a <b >Cool-temperate</b> climate (PHPP 9?). Don't know if that has changed in the latest version of PHPP? Wonder if the recent heatwaves in the UK and Europe will result in changes?</p>]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310988#Comment_310988</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310988#Comment_310988</guid>
		<pubDate>Mon, 13 Jul 2026 15:12:07 +0100</pubDate>
		<author>john.connett</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Artiglio</cite>Very Heath Robinson and only suitable for one room ( handy if you want to make a bedroom a bit more comfortable)<br /><br />Freeze a five litre container of water, stand it in a washing up bowl or similar ( to catch the condensation) set up a fan to blow over it. Keep door and windows shut. Not going to work wonders , but makes a difference, mainly i expect by lowering the humidity.</blockquote><br /><p >That's similar to a swamp cooler/evaporative cooler except using the phase change of ice to water. It might improve your comfort but as it is a closed system it won't change the temperature of the surroundings.</p><br /><p >The <a href="<a href="https://www.homevap.nl/en/overview-cold-humidification/homevap-cooler/" target="_blank" rel="nofollow">https://www.homevap.nl/en/overview-cold-humidification/homevap-cooler/</a>" >HomeEvap Cooler adiabatic evaporative cooler</a> is an interesting variation that can produce cooling. It attaches into the extracted air connection before the MVHR and depends on the summer bypass NOT being used. The outgoing cold air chills the incoming air via the heat exchanger. The cooling comes from evaporation and a cold water supply which feeds the evaporator and discharges to a drain. Quite a neat approach! Disadvantages are that it can use up to 2 litres of water per hour (not great if, like me, you live in water stressed East Anglia) and the "wet pads" are a consumable item.</p>]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310993#Comment_310993</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=310993#Comment_310993</guid>
		<pubDate>Tue, 14 Jul 2026 19:45:23 +0100</pubDate>
		<author>stonecold</author>
		<description>
			<![CDATA[It is always at least 5C degrees cooler inside here, even without setting upsummer bypass and the MVHR continuing to do heat recovery for baths/showers and cooking. It is much cooler here since not in SE England although the hottest it got inside was 22.5C at the end of the last (more intense heatwave) when it was in the low 30s outside. Like you we have high embodied energy although in our case that's external insulation so any heat there still has to get through thick some walls to the inside.<br /><br />One thing helping us massively is the lack of solar gain, only 2 GF rooms warm up in the morning, the 2 FF rooms have curtains shut and we don't feel it. Outside faces mostly North and South side doesn't seem sunny - the West side is kitchen and bathrooms with few windows and sun absolutely scorches you outside.<br /><br />I think shading over the windows seems to be one of the key things suggested. Possibly add some internal wall insulation for key rooms/S or W external walls with a low embodied energy although afaik I think there is only the likes of polystyrene and such. There is much better insulated plaster around now - aerogel plaster and Cornerstone SuperTherm (I'm not sure what level you have now, ours is good for age of building but not new build standard).<br /><br />Cross-ventilation from front to back of house or from one side to another, and no longer making hot meals will probably help it feel cooler.<br /><br />Given how it's going with climate change, what about solar PV to run a/c (or even to run a portable A/C unit in the room where the first uninsulated MVHR ducting is?<br /><br />Overnight bedroom temperature plus the ability to fully shade a good chunk of outside space seem key - I'm hoping you arent in a flat.<br /><br />Air to air heat pumps can do cooling - but doesn't Vent-Axia have options or accessories for warm climates? Zehnder does I think.]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311001#Comment_311001</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311001#Comment_311001</guid>
		<pubDate>Wed, 15 Jul 2026 13:30:40 +0100</pubDate>
		<author>john.connett</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: stonecold</cite>It is always at least 5C degrees cooler inside here, even without setting upsummer bypass and the MVHR continuing to do heat recovery for baths/showers and cooking. It is much cooler here since not in SE England although the hottest it got inside was 22.5C at the end of the last (more intense heatwave) when it was in the low 30s outside. Like you we have high embodied energy although in our case that's external insulation so any heat there still has to get through thick some walls to the inside.</blockquote><br /><p >That sounds pretty good! In the less extreme heatwaves parts of my house rose to over 25oC, possibly up to 28oC. Enough thermal inertia to stay below the external maximum. Uncomfortable, especially for sleeping, but survivable. I moved out to air-conditioned hotel rooms over the Amber Heat Alert and left the house to its own devices with windows closed and MVHR on. Very hot on my return but gradually cooled down with all the windows and doors wide open.</p><br /><blockquote ><cite >Posted By: stonecold</cite>One thing helping us massively is the lack of solar gain, only 2 GF rooms warm up in the morning, the 2 FF rooms have curtains shut and we don't feel it. Outside faces mostly North and South side doesn't seem sunny - the West side is kitchen and bathrooms with few windows and sun absolutely scorches you outside.</blockquote><br /><p >My house is a mid-terrace with North and South outside faces and neighbours on the East and West. Windows on the South face are PassivHaus spec triple glazed with a venetian blind on the outside protected by a fourth pane.  The ground floor kitchen window is medium sized and the first floor bedroom window is fairly small. The wooden front door is also PassivHaus spec with a triple glazed panel in the top half. No additional insulation in the 1996 cavity walls. The architects for the low energy renovation were of the opinion that the greatly improved windows and door together with the relatively small area of wall would be sufficient. The outer bricks are "Cambridge White" style which are pale coloured. Probably not a lot more that could practically be done to reduce solar gain.</p><br /><p >The North face has a Passivhaus spec triple glazed patio door with small matching windows either side in the ground floor lounge. The first floor study has an identical window to the first floor bedroom.</p><br /><p >The second floor bedroom and shower room is essentially a pre-built loft extension. The renovation significantly increased the roof insulation. The Velux windows on the North were upgraded with the best double glazing units available. The Velux window in the bedroom has a solar powered external shutter.</p><br /><blockquote ><cite >Posted By: stonecold</cite>I think shading over the windows seems to be one of the key things suggested. Possibly add some internal wall insulation for key rooms/S or W external walls with a low embodied energy although afaik I think there is only the likes of polystyrene and such. There is much better insulated plaster around now - aerogel plaster and Cornerstone SuperTherm (I'm not sure what level you have now, ours is good for age of building but not new build standard).</blockquote><br /><p >I think the windows are doing a pretty good job. I also have heavyweight curtains inside all the vertical windows except for the kitchen. I did consider phase change plasterboard, like Knauf ComfortBoard, under the second floor ceiling but didn't have it installed. Not sure how well it would have performed in a heatwave? It would increase the thermal mass around the phase change range but might not help if it was heated above that range?</p><br /><p >The South side faces onto the street so options are limited unless all the houses in the terrace do the same</p><br /><p >If there was something that could increase the reflectivity of the bricks on the South face without significantly changing its appearance I would be willing to give that a try.</p><br /><blockquote ><cite >Posted By: stonecold</cite>Cross-ventilation from front to back of house or from one side to another, and no longer making hot meals will probably help it feel cooler.</blockquote><br /><p >Already using cross-ventilation on the first floor and stack effect to allow hot air to rise out of the Velux windows on the second floor. Also not cooking hot meals and avoiding other heat generating activities like running the washing machine.</p><br /><blockquote ><cite >Posted By: stonecold</cite>Given how it's going with climate change, what about solar PV to run a/c (or even to run a portable A/C unit in the room where the first uninsulated MVHR ducting is?</blockquote><br /><p >Most recent addition has been solar PV with a storage battery and gateway. Should be able to run off-grid for a few days, maybe a bit less when running active cooling. Tilt and turn windows are less than idea for portable A/C. Heavy to cart upstairs. Might compromise security on the ground floor.</p><br /><blockquote ><cite >Posted By: stonecold</cite>Overnight bedroom temperature plus the ability to fully shade a good chunk of outside space seem key - I'm hoping you arent in a flat.</blockquote><br /><p >Not in a flat. Lucky to have a small park on the opposite side of the street with plenty of trees and shade. The trees do not block the solar PV in the summer and shed their leaves to let the low winter sun through.</p><br /><blockquote ><cite >Posted By: stonecold</cite>Air to air heat pumps can do cooling - but doesn't Vent-Axia have options or accessories for warm climates? Zehnder does I think.</blockquote><br /><p >Still investigating options. Zehnder have their ComfoPost air to water heat exchangers. However, I have been told there might be issues as some of my MVHR ducts are uninsulated steel from Lindab.</p><br /><p >Ideally, I'm looking for a minimally invasive solution. Really don't want a major building project (been there, done that!). The existing MVHR unit is in a loft space on the North side. An external chiller on the outside North wall or in the back garden providing cooling up the wall to something in the loft space might be suitable. Like the idea of using a <a href="<a href="https://blueheartenergy.com/" target="_blank" rel="nofollow">https://blueheartenergy.com/</a>" >BlueHeart Energy</a> Thermoacoustic Engine! Willing to consider anything suitable that planning and building regulations will allow.</p>]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311003#Comment_311003</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311003#Comment_311003</guid>
		<pubDate>Thu, 16 Jul 2026 13:57:31 +0100</pubDate>
		<author>john.connett</author>
		<description>
			<![CDATA[<p >Saw a mention of a device that combines an MVHR and AC in a Facebook group I follow. It's the <a href="<a href="https://www.nuaire.co.uk/products/residential-fans-and-ancillaries/mechanical-ventilation-with-heat-recovery-mvhr/mrxbox-with-cooling-solution/" target="_blank" rel="nofollow">https://www.nuaire.co.uk/products/residential-fans-and-ancillaries/mechanical-ventilation-with-heat-recovery-mvhr/mrxbox-with-cooling-solution/</a>" >MRXBOX Hybrid Cooling System</a> from Nuaire.</p><br /><p >It consists of an AC unit that sits on top of the MVHR and connects to the duct spigots. All of the components of the AC are within the top box so the heat generated must be dumped out of the exhaust connection.</p><br /><p >The combined height of the two boxes (and a stand) would be too tall to fit in the height restricted loft space housing my existing MVHR. However, it could be a good fit for others with overheating problems.</p><br /><p >If anyone knows of other solutions, please add details to this topic.</p>]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311004#Comment_311004</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311004#Comment_311004</guid>
		<pubDate>Thu, 16 Jul 2026 14:42:01 +0100</pubDate>
		<author>Doubting_Thomas</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: john.connett</cite>Like the idea of using a<a href="https://<a href=" rel="nofollow" >https://blueheartenergy.com/</a>" >BlueHeart Energy Thermoacoustic Engine!</blockquote><br /><br />That Blueheart system looks amazing - worthy of it's own discussion thread if it hasn't been covered already!]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311005#Comment_311005</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311005#Comment_311005</guid>
		<pubDate>Thu, 16 Jul 2026 15:05:15 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[There seem to have been some more unhelpful changes to the forum. People are posting broken web links that link to a non-existent page in the forum. I don't know what the cause is since I've just tested and the old rule of "if you want working links, use Text format" works for me and similarly using Html format doesn't produce an active link at all. So I've no idea how people are generating these broken links, but please take extra care when posting, and test after posting a link, and you can edit your post if necessary.]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311038#Comment_311038</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311038#Comment_311038</guid>
		<pubDate>Mon, 20 Jul 2026 09:25:21 +0100</pubDate>
		<author>john.connett</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: djh</cite>There seem to have been some more unhelpful changes to the forum. People are posting broken web links that link to a non-existent page in the forum. I don't know what the cause is since I've just tested and the old rule of "if you want working links, use Text format" works for me and similarly using Html format doesn't produce an active link at all. So I've no idea how people are generating these broken links, but please take extra care when posting, and test after posting a link, and you can edit your post if necessary.</blockquote><br />My apologies if it was my HTML Links that were a problem. I am used to using other systems that either provide a "link" button or accept correctly formatted HTML Links with the syntax described in https://www.w3schools.com/html/html_links.asp. I have also found a "preview" button very useful!]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311040#Comment_311040</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311040#Comment_311040</guid>
		<pubDate>Mon, 20 Jul 2026 10:49:08 +0100</pubDate>
		<author>WillInAberdeen</author>
		<description>
			<![CDATA[Think it also depends on browsers. Chrome on android opened John's links ok for me if I select/highlight the link address without the trailing ".<br /><br />Very sorry to hear you were driven out from your home by the severity of the weather, despite the care and effort youve put into it - that's quite shocking when we think about it.<br /><br />Really do think that active cooling is the way to go, the passive measures are already very extensive. Mini split air-air heatpump with fan units in at least one room on each floor. Use it in winter to displace gas boiler. <br /><br />Interesting ideas around MHRV integration; phase change plasterboard; acoustic heatpump, thanks for posting those! But I would KISS and go for something conventional. Let the MHRV do air quality (that's it's job) and the air conditioner do cooling (that's it's job) and don't combine them.<br /><br />Interesting blog<br /><a href="https://protonsforbreakfast.wordpress.com/2026/05/13/pv-and-ac/" target="_self" rel="nofollow">https://protonsforbreakfast.wordpress.com/2026/05/13/pv-and-ac/</a>]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311058#Comment_311058</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311058#Comment_311058</guid>
		<pubDate>Tue, 21 Jul 2026 18:34:27 +0100</pubDate>
		<author>Mike1</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: john.connett</cite>The author dodges the question of "whether Passive Houses overheat"!</blockquote>They don't, much, overall. However there is research that Passivhaus bedrooms in the UK can be 1.6°C warmer than in regular houses - https://www.mdpi.com/1996-1073/15/10/3829. Passive houses are also currently designed using current climate data, not - as they should be IMHO, now that the data is available - using future climate projections.<br /><br /><blockquote ><cite >Posted By: john.connett</cite>HomeEvap Cooler adiabatic evaporative cooler is an interesting variation... [but] ...can use up to 2 litres of water per hour (not great if, like me, you live in water stressed East Anglia) and the "wet pads" are a consumable item.</blockquote>They quote confusing maximum figures of 2L/hr & 5L/hr, but even at boosted MVHR speeds it's likely to more like a maximum 0.5L/hr evaporated + some extra for flushing. In principle I could measure it (but haven't as my meter is encased in protection while I finish the renovation).<br /><br />The cellulose matrix is indeed a consumable (it can become encrusted with minerals), but in principle can be 'refreshed' at least once. I also know of an Italian supplier that sells it in sheets for a fraction of the cost of the cut-to-size official replacement; there must be others as the same material is used in regular aircon units.]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311123#Comment_311123</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311123#Comment_311123</guid>
		<pubDate>Mon, 27 Jul 2026 12:56:36 +0100</pubDate>
		<author>john.connett</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Mike1</cite><blockquote ><cite >Posted By: john.connett</cite>The author dodges the question of "whether Passive Houses overheat"!</blockquote>They don't, much, overall. However there is research that Passivhaus bedrooms in the UK can be 1.6°C warmer than in regular houses - https://www.mdpi.com/1996-1073/15/10/3829. Passive houses are also currently designed using current climate data, not - as they should be IMHO, now that the data is available - using future climate projections.</blockquote><br />Thanks. That paper looks interesting. I think the Passivhaus threshold for overheating is 25oC which can be exceeded for 10% of (the hours?) in a year? The Richard Dudzicki item on Linkedin recommended purge ventilation at night by opening windows. I went on a daytime walk near the Passivhaus accommodation for Cambridge University students at Cranmer Road during hot weather and saw that a number of them had their windows open. Not sure what the Passivhaus philosophy is on opening windows?<br /><blockquote ><cite >Posted By: Mike1</cite><blockquote ><cite >Posted By: john.connett</cite>HomeEvap Cooler adiabatic evaporative cooler is an interesting variation... [but] ...can use up to 2 litres of water per hour (not great if, like me, you live in water stressed East Anglia) and the "wet pads" are a consumable item.</blockquote>They quote confusing maximum figures of 2L/hr & 5L/hr, but even at boosted MVHR speeds it's likely to more like a maximum 0.5L/hr evaporated + some extra for flushing. In principle I could measure it (but haven't as my meter is encased in protection while I finish the renovation).<br /><br />The cellulose matrix is indeed a consumable (it can become encrusted with minerals), but in principle can be 'refreshed' at least once. I also know of an Italian supplier that sells it in sheets for a fraction of the cost of the cut-to-size official replacement; there must be others as the same material is used in regular aircon units.</blockquote><br />I suspect you are correct about the water usage. I think the 5L/hr was for the solenoid valve stuck in the fully open position. Cambridge water has high carbonate hardness so becoming encrusted would be likely. As I am in England another issue might be the Water Regulations Approval Scheme (WRAS) for the HomeEvap Cooler.]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311125#Comment_311125</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311125#Comment_311125</guid>
		<pubDate>Mon, 27 Jul 2026 15:11:46 +0100</pubDate>
		<author>Doubting_Thomas</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: john.connett</cite>Not sure what the Passivhaus philosophy is on opening windows?</blockquote><br /><br />It's actually a requirement for certification, under the Occupant Satisfaction section:<br /><br />"All rooms with prolonged occupancy must have at least one operable window. This does not apply in rooms situated on the inside, in open-plan offices, and if there are important reasons against this (e.g. protection against burglary for a museum)."<br /><br />The point is that whilst overheating of the building (i.e. +25°C) is capped at 10%, good practice aims for a limit of 5% and ideally for none at all. So there should be enough of a safety factor there to allow for the odd student opening their windows for the psychological comfort of a controllable draught, even if that isn't in their best thermal interest. Clearly if they stick a fan heater on, actively trying to overheat the room, the passive measures will reach their natural limits..!]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311128#Comment_311128</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311128#Comment_311128</guid>
		<pubDate>Tue, 28 Jul 2026 12:24:10 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: john.connett</cite>Not sure what the Passivhaus philosophy is on opening windows?</blockquote>A few more comments on that topic:<br /><br />To prevent overheating, it's generally a bad idea to open windows when it's hotter outside than inside. For the same reason my MVHR's summer bypass automatically turns off in the same conditions. It warms the inside of the house, though fairly slowly compared to sunlight.<br /><br />My MVHR is also a 'constant volume' type, which means it doesn't care about how many windows I have open and what the wind is doing.]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311131#Comment_311131</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311131#Comment_311131</guid>
		<pubDate>Tue, 28 Jul 2026 15:27:37 +0100</pubDate>
		<author>john.connett</author>
		<description>
			<![CDATA[The <b >Part O Overheating: Future Homes Standard Guide</b> (https://home-energy-model.co.uk/future-homes-standard/overheating/) has some requirements.<br /><br />Using the <b >The Simplified Model</b>: <i >Cross-ventilation: Whether the dwelling can achieve effective cross-ventilation through openable windows on opposite facades (adjacent facades do not qualify as cross-ventilation under AD O)</i>.<br /><br />Using <b >Dynamic Thermal Modelling</b>: <i >Bedroom temperature criteria: bedrooms must not exceed 26°C for more than 1% of annual occupied hours (typically around 32 hours per year)</i>.<br /><br />The bedroom temperature threshold is 1°C higher than Passivhaus but the 1% of annual occupied hours may be stricter than the Passivhaus 10% (of all hours?).<br /><br />It is interesting that limiting unwanted solar gains only considers the amount of solar energy entering the dwelling through windows, rooflights, and other glazed elements. I have a suspicion that heatwave overheating of my house may be caused by the non-glazed elements of the south side. Direct sunlight onto the bricks heats them so that they become hot to touch. They act like the bricks in an old-fashioned night storage heater, absorbing the heat during the day then releasing it at night. Could explain why room temperatures continue to rise when outside temperatures are falling.<br /><br />I have ordered an infrared thermometer to take measurements of just how hot the bricks become. It may be that it is not primarily a ventilation/active cooling issue! A possible passive solution might be improved shading to reduce direct sunlight in summer. I will take a serious look at brise soleil.]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311132#Comment_311132</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311132#Comment_311132</guid>
		<pubDate>Tue, 28 Jul 2026 19:34:53 +0100</pubDate>
		<author>Mike1</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: john.connett</cite>I think the Passivhaus threshold for overheating is 25oC which can be exceeded for 10% of (the hours?) in a year?</blockquote>Yes, that's the limit for the house as a whole - but based on climate data that is rapidly becoming obsolete. Better to use future climate data instead - see https://colbe.bath.ac.uk/.<br /><br />Night purging through the windows is good, as long as the local environment allows it - rain, noise, intruders, pollution, etc.<br /><br /><blockquote ><cite >Posted By: john.connett</cite>As I am in England another issue might be the Water Regulations Approval Scheme (WRAS) for the HomeEvap Cooler.</blockquote>The cooler connects in the same way as a washing machine / dish washer, for which WRAS approval isn't required (AIUI). So provided the pipe serving it has a check valve to prevent backflow, then I'd guess it's not a problem. It's quite likely that the cooler has an integral check-value too (as a washing machine would), but I've not disassembled it.<br /><br /><blockquote ><cite >Posted By: djh</cite>it's generally a bad idea to open windows when it's hotter outside than inside.</blockquote>+1. This advice is in every French article about coping with a heatwave.<br /><br /><blockquote ><cite >Posted By: john.connett</cite>I have a suspicion that heatwave overheating of my house may be caused by the non-glazed elements of the south side... ...Could explain why room temperatures continue to rise when outside temperatures are falling.</blockquote>That's certainly possible.]]>
		</description>
	</item>
	<item>
		<title>MVHR, heatwaves, chiller?</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311135#Comment_311135</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=18451&amp;Focus=311135#Comment_311135</guid>
		<pubDate>Wed, 29 Jul 2026 13:30:20 +0100</pubDate>
		<author>djh</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: john.connett</cite>I have a suspicion that heatwave overheating of my house may be caused by the non-glazed elements of the south side. Direct sunlight onto the bricks heats them so that they become hot to touch.</blockquote>Yes, if you can stop the sun reaching the wall (or at least reduce it), it will help. The insulation in the walls also helps to reduce the internal warming and delays it (how much depends on the type of insulation) - so-called decrement delay.]]>