<?xml version="1.0" encoding="utf-8"?>
	<rss version="2.0">
		<channel>
			<title>Green Building Forum - Advantages of wet plaster</title>
			<lastBuildDate>Sat, 18 Apr 2026 14:16:19 +0100</lastBuildDate>
			<link>https://www.greenbuildingforum.co.uk/newforum/</link>
			<description></description>
			<generator>Lussumo Vanilla 1.0.3</generator>
			<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=31116#Comment_31116</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=31116#Comment_31116</guid>
		<pubDate>Tue, 26 Aug 2008 09:32:57 +0100</pubDate>
		<author>arthur</author>
		<description>
			<![CDATA[I've read various comments on hear about the benefits of wet plaster for airtightness. I wanted to clarify this issue. Should we all be avoiding platerboard for external walls? What about using insulated plasterboard? Context is partial refurb to add internal insulation but not to the whole building (upstairs apartment). I gather a parge coat to the brickwork (for airtightness) and then insulation followed by plasterboard is an option. Would the insulation and plasterboard be attached through the parge to the brickwork or just stuck to the parge? How effective does wet plaster remain for airtightness? Isn't it liable to crack?]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=31126#Comment_31126</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=31126#Comment_31126</guid>
		<pubDate>Tue, 26 Aug 2008 13:01:50 +0100</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[Yes avoid blob and dob like the plague,  With wet plaster you can see any cracks and deal with them on redecoration maintaining air tightness.<br /><br />If you do decide to use insulated boards make sure that you are air sealed EVERYMHERE first.]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=31133#Comment_31133</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=31133#Comment_31133</guid>
		<pubDate>Tue, 26 Aug 2008 15:52:50 +0100</pubDate>
		<author>arthur</author>
		<description>
			<![CDATA[Would it be better to use wet plaster on the inside side of the insulation too?]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=31135#Comment_31135</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=31135#Comment_31135</guid>
		<pubDate>Tue, 26 Aug 2008 15:58:25 +0100</pubDate>
		<author>Paul in Montreal</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: arthur</cite>Would it be better to use wet plaster on the inside side of the insulation too?</blockquote><br /><br />Probably not - the moisture will take a long time to escape if your house is airtight. Though I believe typical practice in the UK is to wet plaster on top of drywall/gyrproc/plasterboard - whereas standard practice over here is to just tape and finish the joints  - skim coating is virtually unheard of except in certain immigrant areas (typically Italian).<br /><br />Paul in Montreal.]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32881#Comment_32881</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32881#Comment_32881</guid>
		<pubDate>Tue, 16 Sep 2008 19:03:59 +0100</pubDate>
		<author>arthur</author>
		<description>
			<![CDATA[Thanks for responses. I'm still concerned about the longterm effectiveness of the airtight parge barrier when its covered by internal insulation - and that fixing this insulation is itself likely to breach the barrier. <br />Would a thicker coat make any difference - or will it still potentially crack if its going to crack. <br />Plaster on the inside of the insulation gives the option of repairing damage.]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32882#Comment_32882</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32882#Comment_32882</guid>
		<pubDate>Tue, 16 Sep 2008 19:13:50 +0100</pubDate>
		<author>Mike George</author>
		<description>
			<![CDATA[Hi Arthur, See <a href="http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=1070&page=1#Item_24" target="_self" rel="nofollow">http://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=1070&page=1#Item_24</a> for my method and other comments on this subject]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32900#Comment_32900</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32900#Comment_32900</guid>
		<pubDate>Tue, 16 Sep 2008 20:41:29 +0100</pubDate>
		<author>Terry</author>
		<description>
			<![CDATA[My understanding is that you need an airtightness barrier on the warm side of the insulation. Any warm air that gets through the insulation will condense on the cold wall causing hidden problems?]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32903#Comment_32903</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32903#Comment_32903</guid>
		<pubDate>Tue, 16 Sep 2008 20:57:02 +0100</pubDate>
		<author>Mike George</author>
		<description>
			<![CDATA[Not necessarily, depends upon the vapour permeability of the wall itself- many are permeable <br /><br />If in doubt, contact one of the technical helplines who will do a condensation risk analysis for you.]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32905#Comment_32905</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32905#Comment_32905</guid>
		<pubDate>Tue, 16 Sep 2008 21:08:22 +0100</pubDate>
		<author>Terry</author>
		<description>
			<![CDATA[True Mike, but arthur is talking about an "airtight parge barrier when its covered by internal insulation" which will kick permeability into touch?<br /><br />Even if the wall is permeable, if it is colder than the inside air leaking through, surely it will cause condensation - obvoiusly dependant on dew point/RH?]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32906#Comment_32906</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32906#Comment_32906</guid>
		<pubDate>Tue, 16 Sep 2008 21:18:39 +0100</pubDate>
		<author>Paul in Montreal</author>
		<description>
			<![CDATA[As far as I understand the airtightness barrier always goes on the outside of the building between the external rainscreen cladding (no matter what the material is: brick, wood, cement board) and the internal structure that contains the insulation, the purpose being to prevent air entering the insulation and diminishing its effectiveness. The airbarrier is also vapour permeable so that the internal structure has a path for moisture to escape - this is particularly important for timber frame buildings since the timber may have got wet during construction and you want it to be able to dry out. The vapour barrier goes on the warm side of the insulation (inside in a heating climate, outside in a cooling climate) to prevent moisture from the occupants getting into the structure of the building, condensing and causing rot. If you have a solid structure (concrete etc.) then it's not so important to have a vapour barrier (see ICF construction for example where the concrete is sandwiched between two layers of expanded polystyrene (which is not a vapour barrier)). However, your insulation layer may also be an air barrier - just saw a house recently that was built as poured concrete and then sprayed over its entire surface with polyurethane foam before a decorative facade was built out of nice cut stone. No other air or vapour barriers in place as far as I can see - all internal walls regular plasterboard on steel studs.<br /><br />Paul in Montreal]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32921#Comment_32921</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32921#Comment_32921</guid>
		<pubDate>Wed, 17 Sep 2008 02:31:00 +0100</pubDate>
		<author>Terry</author>
		<description>
			<![CDATA[fair comment Paul, getting my barriers in a twist]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32925#Comment_32925</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32925#Comment_32925</guid>
		<pubDate>Wed, 17 Sep 2008 08:45:09 +0100</pubDate>
		<author>tony</author>
		<description>
			<![CDATA[Paul -- I dont think we know where the air tightness barrier goes yet in the UK. Majority of house construction is extreemly air leaky and in masonry construction there is never an air barrier outside the cavity insulation (unless there is either render or paint) so do we have any hope? Even with timber frame the air barrier is often still the same one as the vapour barrier.]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32945#Comment_32945</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32945#Comment_32945</guid>
		<pubDate>Wed, 17 Sep 2008 11:43:30 +0100</pubDate>
		<author>nigel</author>
		<description>
			<![CDATA[It does not actually matter if the air tightness barrier is on the inside or the outside so long as one is chosen and it is used consistently in the same building.<br />Both options have issues such as the intersection of wall and floor when used on the inside and the wall roof junction when on the outside.]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32950#Comment_32950</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32950#Comment_32950</guid>
		<pubDate>Wed, 17 Sep 2008 12:36:56 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[That's right Nigel but on balance my vote goes to inboard air barrier - wet plaster when the inner leaf is masonry, or a membrane when it's stud. Much easier to make it continuous, inboard. The only real problem then is floor joist ends wanting to go out through the barrier - that's about all. Paul's wish to put the air barrier outboard is to prevent outside air blowing around within the insulation - fair enough - but outboard vapour permeable sheathing should do a fair job at that, even tho not qualifying as a full air barrier.<br /><br />The outboard vapour permeable insulation-containment sheathing can be Panelvent-type fibreboard, cheap moisture resistant plasterboard - or even OSB maybe, tho there's confusion as to its vapour permeability. I'd like guidance on the latter - if OSB is permeable enough to be used in this outboard position, then that's the structural sheathing plus insulation containment sorted in one go. If not, then I need to do a re-think, as the structural sheathing has to go inboard and has to be duplicated by Panelvent or plasterboard outboard.<br /><br />This <a href="http://www.greensteps.co.uk/tmp/assets/1163178050906.pdf" target="_self" rel="nofollow">http://www.greensteps.co.uk/tmp/assets/1163178050906.pdf</a> which someone posted previously here (can't find the thread - anyone), represents the hardline fuil-breathability with hygroscopicity camp, and gives warnings that have certainly got me worried about previous jobs and re-thinking future ones.]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32955#Comment_32955</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32955#Comment_32955</guid>
		<pubDate>Wed, 17 Sep 2008 12:53:56 +0100</pubDate>
		<author>Paul in Montreal</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: fostertom</cite>Paul's wish to put the air barrier outboard is to prevent outside air blowing around within the insulation - fair enough - but outboard vapour permeable sheathing should do a fair job at that, even tho not qualifying as a full air barrier.</blockquote><br /><br />Have you ever seen a system with sheathing outside (but before the insulation is fitted)? No matter have carefully  installed, there are always gaps. OSB is the usual exterior sheathing used over here and it is somewhat vapour permeable, but it is certainly not airtight. This is why the airtightness barrier must go on the outside. Floor joists are not a problem in this case since they are on the inside of the airtightness barrier. In anycase, there's simple solutions in the case of timber framed houses to make these junctions airtight too - just spray closed cell foam at the junctions - we did this for all the locations where the joists attach to the walls. <br /><br /><blockquote ><cite >Posted By: fostertom</cite>The outboard vapour permeable insulation-containment sheathing can be Panelvent-type fibreboard, cheap moisture resistant plasterboard</blockquote><br /><br />Plasterboard would never work - there's no way you could guarantee to keep it dry during construction and it would be damaged by rain, plus it has not structural strength. Of course, I'm thinking in terms of timber frame buildings - the sheathing is a structural element and is always either plywood or OSB. Plywood is more expensive and doesn't really have any advantages as all the loads are shear loads which the OSB is equally as capable of withstanding. It cannot be made airtight without a barrier though. Well, it could, be the details needed to do so would cost more time than putting a proper airbarrier in the first place. Another function of the airbarrier is that of a water barrier - Tyvek, Typar and the like are waterproof and so protect the building until the rainscreen can be installed (no matter if it's brick, wood siding or whatever).<br /><br />Paul in Montreal.]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32964#Comment_32964</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=32964#Comment_32964</guid>
		<pubDate>Wed, 17 Sep 2008 14:28:27 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[This is good, Paul. Can I get a few things clear:<blockquote ><cite >Posted By: Paul in Montreal</cite>ever seen a system with sheathing outside (but before the insulation is fitted)? No matter have carefully  installed, there are always gaps</blockquote>You're saying serious gaps? - and that 'fair job' isn't good enough to prevent outside air blowing around within the insulation, that 'full air barrier' is reqd for that purpose as well as for preventing internal airchange?<br /><br />Another approach, with inboard air barrier to take care of inboard airchange, is to allow the wind to blow over the outside of the insulation, but the insulation is closed-cell e.g. Cellotex, and is bedded all round and at joints with expanding foam. What about that?<br /><br />Actually, that's a big no-no according to http://www.greensteps.co.uk/tmp/assets/1163178050906.pdf because any such use of impervious insulation between studs/rafters forces any construction moisture or any interstitial condensation that may happen, to take the only route out, via the timber. So, instead of Cellotex, how about blown-in Warmcel? behind insulation-containment OSB etc, breather membrane, or just tough scrim, which the Warmcel boys use to close any gaps before blowing-in. Anyway, not relying on the OSB or the scrim as air barrier to prevent infiltration of the insulation, just on the compressed gap-filling quality of blown-in Warmcel. Warmcel is very vapour permeable, as well as hygroscopic, so protects the studs/rafters from that having to be that moisture-escape channel.<br /><br />Having said all that about OSB etc as a 'fair job' air barrier (which you say it won't be), of course it will have breather membrane outboard of it. Would you say that such breather membrane, with or without OSB etc, is still not good enough to prevent outside air blowing around within the insulation, unless scrupulously done to full air barrier standard - in which case why duplicate that with an inboard air barrier?<blockquote ><cite >Posted By: Paul in Montreal</cite>Plasterboard would never work</blockquote>Hm, my 1991 Brit Gypsum White Book has a whole section on MR plasterboard as external sheathing behind tilehanging etc, incl 'exposure to external conditions during construction' and I've used it as such with no problems. However current BG advice is only for 'external soffits in sheltered positions'. So I'd better forget that option - pity, as it has 3 times the vapour permeability of even Panelvent, regardless of its resistance to liquid water.<br /><br />So I'd welcome comment on changing my stud/rafter construction from:<br /><br />plain plasterboard on service-space horizontal battens on careful airtight membrane (also acting as near-full vapour barrier) over studs/rafters of minimal structural size, Cellotex between bedded in expanding foam, thus immune to outside air infiltration. Outboard, tilehanging, boarding or render on rendermesh on ventilated-space vertical battens on breather membrane on OSB structural sheathing on the studs/rafters;<br /><br />to:<br /><br />plain plasterboard on service-space horizontal battens on careful airtight membrane over OSB structural sheathing studs/rafters of deeper section, blown Warmcel (apx 1.5x as thick as the Cellotex) between, hopefully immune to outside air infiltration (?).Outboard, tilehanging, boarding or render on rendermesh on ventilated-space vertical battens on breather membrane on the studs. That is, the breather membrane acts as the container of the blown Warmcel. (I've never yet found the need for Panelvent). I should consider changing the inboard air barrier from being a vapour barrier, to airtight but to vapour permeable.]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33000#Comment_33000</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33000#Comment_33000</guid>
		<pubDate>Wed, 17 Sep 2008 18:52:37 +0100</pubDate>
		<author>arthur</author>
		<description>
			<![CDATA[So (in the case of internal insulation of solid brick walls) is a parge coat sufficiently vapour permeable for it to go on the cold side of the insulation? Or does it not matter so long as you have a vapour barrier on the inside?<br /><br />There's still the problem of maintaining the parge air-barrier if its on the cold side - what if it cracks?<br /><br />Seems to me best to have (1) a cold-side parge coat to deal with problem of air entering insulation from outside AND (2) an internal wet plaster finish to ensure aritightness. Plus a vapour barrier on the warmside of the insulation. <br /><br />No?]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33002#Comment_33002</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33002#Comment_33002</guid>
		<pubDate>Wed, 17 Sep 2008 19:05:26 +0100</pubDate>
		<author>Mike George</author>
		<description>
			<![CDATA[Yes - that's the way to do it.]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33004#Comment_33004</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33004#Comment_33004</guid>
		<pubDate>Wed, 17 Sep 2008 20:07:49 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[I wouldn't rely on wet plaster as air barrier unless it was permanently accessible to stop in the hairline cracks that inevitably happen - mostly in the first 6 months but actually forever. Beyond the 6 month, the hairlines will probably relate to some slight movement in the masonry, with associated crack/air passage, so essential to keep it stopped in. That makes it difficult enough to maintain in the floor zone, the area of greatest risk in fact - but impossible if behind dry lining. I wouldn't try to rely for airtightness on parging behind dry lining.]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33009#Comment_33009</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33009#Comment_33009</guid>
		<pubDate>Wed, 17 Sep 2008 21:18:19 +0100</pubDate>
		<author>Mike George</author>
		<description>
			<![CDATA[Tom,  I don't see how the following cannot be airtight. I have done this on several jobs and I know it to be very effective. So much so that the internal doors wouldn't stay closed until I cut a nice gap underneath them. Not a million miles from what Arthur is proposing<br /><br />1. Ensure the wall is free of cracks and missing beds/perps<br />2. Parge coat of 6:1:1 sand:Cement:Lime. [Nice and flat]<br />3. Dot and dab PUR insulation backed platerboards, taking extreme care that the perimeter is covered with a consistent, uninterupted band of adhesive. Bands of adhesive also at 400mm ctrs<br />4. Ensure a gap between floor and boards of say 30mm<br />5.When adhesive is dry, fill the gap between the floor and the plasterboards with expanding foam.<br />6. Fix skirting, then plaster walls.<br />7. Allow timber to acclimatise then seal the junction of floor and skirting with a mastic.<br /><br />What do you think is missing?  My one concern would be regarding the vapour barrier. I have been told by the the manufacturers technical department that the PUR boards laminated with a foil backed plasterboard do amount to a Vapour Control Layer, Though I have read some comments here that suggest foil backed baords are not effective in this way. <br /><br />Anyone clarify?]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33012#Comment_33012</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33012#Comment_33012</guid>
		<pubDate>Wed, 17 Sep 2008 21:22:35 +0100</pubDate>
		<author>Timber</author>
		<description>
			<![CDATA[Mikes, from what i have seen, the foil backed boards are ok, but get damaged easily and the foil cannot be lapped at corners or junctions, the likely place for cracks to from!<br /><br />it works, but there are better solutions!<br /><br />Timber]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33042#Comment_33042</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33042#Comment_33042</guid>
		<pubDate>Thu, 18 Sep 2008 10:58:19 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[Hi Mike<br /><br />I expect your method would work fine, if having to put lightweight insulation/dry lining inside a masonry wall. I haven't done that for a while, for all the thermal massiveness reasons we know, but if I did ...<br /><br />Your method is real belt and braces but would you say it's principally the dry lining that lifts the air sealing from 90% to 99%? and the perp filling and parging just gets you to the 90% mark, which isn't enough by itself? AFAIK you agree with me that it's permanently closing *all* the pinholes and hairlines that gets you from mere 90% to useful 99%? Left to itself, wet plaster (or parging) will initially and continually produce such hairline cracks, and unless regularly stopped in, paint filled or maybe wallpapered over, will degrade in airtightness, e.g. if inaccessible. Disagree?<br /><br />I've been impressed by the advice at AECB conference seminars etc given by pressure-tester Paul Jennings of <a href="http://www.stroma-ats.co.uk," target="_self" rel="nofollow">http://www.stroma-ats.co.uk,</a> that sticky tapes, adhesives, mastic and foam gradually lose bond, if only in a few places, and that's enough to hit that vital top 10% of airtightness for six, after a few years. He says that only continuous mechanical clamping  is durable, and that's how I've been proceeding. I'm sure that manufacturers will eventually develop patent products that make effective airtightness easy, just like they did for through-ventilation after about 5yrs of struggling with battens and flyscreen mesh. The sooner the present crop of so-called airtightness tapes and gunges disappear, the better.<br /><br />I'm hoping that blown-in Warmcel, which is highly gap-filling and hopefully remains in elastic compression forever, amounts to a continuous mechanical closing of its surface and clamping of its perimeter to the materials around it, and so would not require a scrupulous airtight membrane outboard of it, to prevent outside air infiltrating its surface and body. Any comment?]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33276#Comment_33276</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33276#Comment_33276</guid>
		<pubDate>Sat, 20 Sep 2008 17:48:02 +0100</pubDate>
		<author>Mike George</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: fostertom</cite>Hi Mike<br /><br />Your method is real belt and braces but would you say it's principally the dry lining that lifts the air sealing from 90% to 99%? and the perp filling and parging just gets you to the 90% mark, which isn't enough by itself? AFAIK you agree with me that it's permanently closing *all* the pinholes and hairlines that gets you from mere 90% to useful 99%? Left to itself, wet plaster (or parging) will initially and continually produce such hairline cracks, and unless regularly stopped in, paint filled or maybe wallpapered over, will degrade in airtightness, e.g. if inaccessible. Disagree?</blockquote><br /><br />Not sure, It would be a convoluted path for air to travel freely through hairline cracks and the masonry itself. I think your 9% is excessive for losses via this route, especially ones I have plastered<img src="/newforum/extensions/Vanillacons/smilies/standard/bigsmile.gif" alt=":bigsmile:" title=":bigsmile:" /><br /><br /><blockquote ><cite >Posted By: fostertom</cite>Hi Mike<br /><br />I've been impressed by the advice at AECB conference seminars etc given by pressure-tester Paul Jennings of<a href="<a href="http://www.stroma-ats.co.uk,/" target="_blank" rel="nofollow">http://www.stroma-ats.co.uk,/</a>" rel="nofollow" >http://www.stroma-ats.co.uk,</a>that sticky tapes, adhesives, mastic and foam gradually lose bond, if only in a few places, and that's enough to hit that vital top 10% of airtightness for six, after a few years. He says that only continuous mechanical clamping is durable, and that's how I've been proceeding. I'm sure that manufacturers will eventually develop patent products that make effective airtightness easy, just like they did for through-ventilation after about 5yrs of struggling with battens and flyscreen mesh. The sooner the present crop of so-called airtightness tapes and gunges disappear, the better.</blockquote><br /><br />Agree totally about the mechanical clamping. Eg. I always use a polythene barrier for ceilings on the warm side which is trapped between insulation and plasterboard. This is continued down the walls and subsequently trapped [or continued] into the wall construction, depending on what the wall is made up of.<br /><br /><br /><blockquote ><cite >Posted By: fostertom</cite>Hi Mike<br /><br />I'm hoping that blown-in Warmcel, which is highly gap-filling and hopefully remains in elastic compression forever, amounts to a continuous mechanical closing of its surface and clamping of its perimeter to the materials around it, and so would not require a scrupulous airtight membrane outboard of it, to prevent outside air infiltrating its surface and body. Any comment?</blockquote><br /><br />No, I have not heard of warmcell having this kind of property. Never had the opportunity to use it because of the thickness necessary]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33318#Comment_33318</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33318#Comment_33318</guid>
		<pubDate>Sat, 20 Sep 2008 22:35:56 +0100</pubDate>
		<author>Ed Davies</author>
		<description>
			<![CDATA[<blockquote ><cite >Posted By: Mike George</cite>No, I have not heard of warmcell having this kind of property.</blockquote><br /><br />http://www.unitedinsulations.co.uk/Warmcel-brochure-2001.pdf<br /><br /><blockquote >Warmcel 500 combines high levels of insulation and air-tightness with excellent hygroscopic qualities.</blockquote><br /><br />The air-tightness is one reason I really like the idea of using Warmcel.]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33320#Comment_33320</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33320#Comment_33320</guid>
		<pubDate>Sat, 20 Sep 2008 22:46:43 +0100</pubDate>
		<author>Mike George</author>
		<description>
			<![CDATA[Thanks Ed. Will try and read that when I have some more time. The tradis system looks good at first glance.]]>
		</description>
	</item>
	<item>
		<title>Advantages of wet plaster</title>
		<link>https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33337#Comment_33337</link>
		<guid isPermaLink="false">https://www.greenbuildingforum.co.uk/newforum/comments.php?DiscussionID=2436&amp;Focus=33337#Comment_33337</guid>
		<pubDate>Sun, 21 Sep 2008 09:50:56 +0100</pubDate>
		<author>fostertom</author>
		<description>
			<![CDATA[I have used Warmcel once and it was and seems to continue to be very satisfactory. Its gap-filling ability is remarkable, the way it finds its way tightly into unanticipated odd spaces. The installers come well prepared with scrim to quickly fix over any uncontained areas - the blowing-in requires absolute containment.]]>
		</description>
	</item>
	
		</channel>